Connecting TNC Network to Home Switchgear: PEN Conductor Separation & GSU Strip Placement

mof1707 58317 30
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11809266
    mof1707
    Level 10  
    Hello.
    I have a problem because I am helping my colleague install electrical wiring in a single-family house. According to the conditions, the house will be connected to the TNC network. The arrival will be in a separate outbuilding about 30m from the house, there will be a meter. I have a question about how to properly connect the switchgear at home. If the PEN conductor is separated at the meter, is the connection method in Figure 1 correct? And if the division is only in the switchgear at home, is the fig. 2 correct. I would like to add that I want to divide it into the TNS network. I would like to add that the cooperage is connected to the foundations of the building and the lightning rod. Where to place the gsu strip? How to connect the hoop iron from the outside of the building to the switchgear? Can I use a rail under the switchgear? Can I immediately connect to the rail in the switchgear? because I read somewhere that it should be done? Is it necessary? What cable should I use for this?
    I count on your understanding in responses :D Connecting TNC Network to Home Switchgear: PEN Conductor Separation & GSU Strip Placement Connecting TNC Network to Home Switchgear: PEN Conductor Separation & GSU Strip Placement
  • ADVERTISEMENT
  • #2 11809268
    Łukasz-O
    Admin of electroenergetics
    Before I answer that, let me ask you. Is the colleague qualified to deal with the installations?
  • #3 11809355
    Anonymous
    Level 1  
  • #4 11810214
    mof1707
    Level 10  
    I counted on help, not checking my qualifications. Honestly, I have them, but I just never did the entire installation. It was always, for example, half of the building or apartment where the power supply was already connected with the earth electrode. And the fact that I wrote at night, I don't know what that has to do with anything?
  • ADVERTISEMENT
  • #5 11810274
    kSmuk
    Level 21  
    mof1707 wrote:
    I would like to add that I want to divide it into the TNS network

    If anything, it's TN-CS.

    1. Split the PEN conductor to PE and N as close to the house as possible, that is in the distribution board in the building.

    2. Install the GSW / GSU rail in a convenient place, remembering to make equalizing connections with a minimum of 6mm? Cu, and the connection between the PE rail in the switchboard and the GSW / GSU with 10mm?.

    3. Connect the bednarke to the GSU / GSW, from there you pull the 10 mm? Cu cable to the switchboard, which you connect to the PE rail. On this bus, you also split the PEN conductor into PE and N.

    4. As for the coverage of heating pipes with equalizing connections, all the heating conductive elements should be covered with equalizing connections. If the heating installation is made with PEX pipes, you do not need to make equalization connections of these pipes.

    5. As for the distribution board, if you want to use two grounding bars, the PE bus must have a galvanic connection to the second PE bus. In addition, you make the N connection directly to the FR switch, and not to the N bus. You will need N busbars for RCDs, one for each.
  • #6 11810305
    elpapiotr
    Electrician specialist
    Hello.
    kSmuk wrote:
    In addition, the N connection is made directly to the FR circuit breaker and not to the N bus.
    Why is that ?
  • #7 11810363
    mof1707
    Level 10  
    kSmuk wrote:


    1. Split the PEN conductor to PE and N as close to the house as possible, that is in the distribution board in the building.

    ad.1 Is the chapter shown in the picture correct?
    kSmuk wrote:


    2. Install the GSW / GSU rail in a convenient place, remembering to make equalizing connections with a minimum of 6mm? Cu, and the connection between the PE rail in the switchboard and the GSW / GSU with 10mm?.

    ad.2 Do equipotential bonding have to be made with a strand? cannot there be a wire?
    kSmuk wrote:

    4. As for the coverage of heating pipes with equalizing connections, all the heating conductive elements should be covered with equalizing connections. If the heating installation is made with PEX pipes, you do not need to make equalization connections of these pipes.

    ad.4 the installation will be made in alupex, I understand that equalizing connections should have the shortest possible route, what else do we connect them to, apart from e.g. gas installation? What may be the maximum distance from the rail? Should the equalizing conductor diameter be increased depending on the distance?

    In short, what should you remember when installing an installation in a single-family house? Apart from all those gsw, gsu ... Where can you make the biggest mistakes?
    Regards.
  • ADVERTISEMENT
  • #8 11810530
    zbich70
    Level 43  
    And the connection between PE and GSU is what? Mounting rail TH?
  • #9 11810651
    mof1707
    Level 10  
    zbich70 wrote:
    Mounting rail TH?


    what????
  • #10 11810677
    michcio
    Electrician specialist
    The TH rail is the flat bar on which the devices in the switchgear are latched.
    The PE rail must be connected to the GSU.
  • #11 11810708
    mof1707
    Level 10  
    I know what the th rail is. Only I don't understand why zbich70 wrote that the PE connection with GSU is to be made with this rail ...?!
  • #12 11810726
    zbich70
    Level 43  
    mof1707 wrote:
    I just don't understand why zbich70 wrote that the PE connection with GSU should be made with this rail ...?!

    Connecting TNC Network to Home Switchgear: PEN Conductor Separation & GSU Strip Placement
  • #13 11810812
    mof1707
    Level 10  
    It will not be connected by a rail :D I just drew it like this, of course the connection will be directly on the terminal block. I am waiting for an answer, for an earlier post by kSmuk.
  • #14 11810826
    Anonymous
    Anonymous  
  • #15 11810844
    elpapiotr
    Electrician specialist
    Hello.
    Quote:
    These are equalizing connections is another topic. You can make them with a copper wire, eg DY minimum with a cross-section of 6mm ^ 2.
    Why not 4 or 10 mm??
    Where did your friend get these 6?
  • #16 11810867
    mof1707
    Level 10  
    I will add photos later, because I don't have one. In short, what we connect to the GSU bus and what to the GSW? It is not one and the same? Can not be combined?
    If there is an installation in the building, what about alupex, what to connect to the equalizing rail?
  • #17 11811053
    mrst
    Level 18  
    Hello. GSU and GSW are practically the same. The PE conductors of the installation and foreign conductive parts are connected to the grounded GSW.
  • #18 11811083
    Anonymous
    Anonymous  
  • #19 11811176
    mof1707
    Level 10  
    mrst wrote:
    Hello. GSU and GSW are practically the same. The PE conductors of the installation and foreign conductive parts are connected to the grounded GSW.

    After all, one cable will go from the PE switchgear towards GSW. So why connect each PE conductor of the circuits in the house to the GSW bus, since they will be connected in the switchgear?
    In general, what to pay attention to when installing the installation in the house? In short, we stretched the cables to individual receivers, then we will install GSW and connect some conductive elements in the building to it, what then? What else is important in such an installation?
  • #20 11811217
    Anonymous
    Anonymous  
  • #21 11811233
    mrst
    Level 18  
    mof1707 wrote:
    After all, one cable will go from the PE switchgear towards GSW. So why connect each PE conductor of the circuits in the house to the GSW bus, since they will be connected in the switchgear?


    When writing PE conductors, I meant PE busbars of the switchgear to which all PE conductors are connected.
  • #22 11811686
    mof1707
    Level 10  
    cKKqa wrote:

    That everything should be in accordance with the norms and applicable standards.

    I know, I was just hoping that you might give me a hint about what still needs to be done with such an installation ...
  • Helpful post
    #23 11811885
    kSmuk
    Level 21  
    mof1707 wrote:
    After all, one cable will go from the PE switchgear towards GSW. So why connect each PE conductor of the circuits in the house to the GSW bus, since they will be connected in the switchgear?

    PE conductors from sockets or lighting points are led together with the phase conductor and the neutral conductor directly to the switchboard (using, for example, YDYp directly flush-mounted). There you connect the phase conductor to the overcurrent protection, the neutral one to the N bus of the RCD to which this circuit is connected, while the PE protective conductor is connected to the PE bus. To the PE rail in the distribution board, you also connect the overvoltage protection, if fitted, and all PE conductors of the socket circuits, devices supplied directly (air conditioning, induction hob, etc.). From the PE rail of the switchboard to the main equalizing rail GSW you run a cable or a Cu wire (as you prefer) with a thickness of preferably 10 mm?.

    You connect all conductive foreign elements to the GSW bus (you cover with equipotential bonding). They are, for example, a bathtub, a shower tray, a heating stove, air conditioning, steel pipes (e.g. gas pipes), a boiler, etc.

    To the GSW bus, from the earthing control window outside the building, you lead a Cu wire of at least 10 mm?, or a hoop. The link or the cordage is connected with the connector in the earthing control window. You then have easy access to the grounding terminal in order to perform a control earth resistance measurement over time.
  • #24 11811942
    mof1707
    Level 10  
    All clear. What kind of cables should be used for equipotential bonding? Does it not bother that there will be a distance of 20 m from GSW to e.g. a bathtub? How to attach equalizing pipes, e.g. to a bathtub, etc.?
  • #25 11812112
    jacur
    Level 32  
    mof1707 wrote:
    How to attach equalizing pipes, e.g. to a bathtub, etc.?


    Lepiglut for an acrylic bathtub :D
  • ADVERTISEMENT
  • #26 11812435
    mof1707
    Level 10  
    yes, are you made at home? :-P
    I asked about metal elements ...
  • #27 11812444
    Anonymous
    Anonymous  
  • #28 11812496
    mof1707
    Level 10  
    Approx. Thanks.
    Just one more question, should equalizing pipes such as DY be put in a conduit or tube? Can they lie freely in the concrete (will they be poured over the floor screed)?
  • #29 11813736
    arek59
    Level 29  
    I put DY in a conduit, sometimes without a conduit, depending on the type of building, application, funds, etc. PE equalizing conduit minimum CU 10mm.
    The lightning protection installation should not be connected to the earthing and equipotential bar. (How badly I wrote it to correct me.)
  • #30 11814627
    mof1707
    Level 10  
    Why do you think you shouldn't connect the lightning rod to the alignment rail? In my opinion, this should be done and then the whole thing should be connected to the EP. And, of course, use the appropriate surge arresters.

Topic summary

The discussion revolves around the installation of electrical wiring in a single-family house connected to a TNC network, focusing on the proper connection of switchgear and the separation of the PEN conductor. Key points include the correct methods for splitting the PEN conductor into PE and N, the placement of GSU and GSW strips, and the requirements for equipotential bonding. Participants emphasize the importance of adhering to standards, using appropriate cable sizes (e.g., 10mm² for connections), and ensuring that all conductive parts are properly bonded. The conversation also touches on the connection of lightning protection systems and the necessity of underground connections for safety.