Title: Chapter PEN, Protector Selection & Switchgear Diagram for Single-Family House: TN-C System

piter_admin 30345 15
Best answers LABEL_AI_GENERATED

Can I split the PEN conductor in my single-family house installation after the meter, and which RCD and surge arrester type should I use for a TN-C supply?

Split the PEN in the house switchboard/RG, not before the meter; the thread says Tauron does not allow PEN division in ZK/ZL, so the only place for it is the home RG [#17598077][#17600875] If you keep a TN-C feeder into the RG, use a TN-C SPD such as DEHN 951300 and connect PEN to the PE bar through the SPD’s PEN clamp; if you split to TN-S before the board, then use a TN-S SPD with an N-PE module instead [#17598077][#17599273] For the RCDs, type A is preferred over AC, but AC was still described as usable; do not use one 4-pole RCD for the whole house, and separate circuits/RCBOs are a better approach [#17598077][#17598042] The DEHNventil back-up protection was said to be unnecessary in this case because it can extinguish line-follow current up to 50,000 A, and its documentation states when backup is required [#17598077] For the SPD wiring, keep the connections short, use the manufacturer’s minimum conductor cross-section (mentioned as at least 10 mm²), and prefer a distribution block rather than a direct connection to the RCD [#17598077][#17599273]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17597226
    piter_admin
    Level 9  
    Posts: 10
    Rate: 6
    Hello
    I would like to kindly request your opinion on the switchgear diagram in a single-family house.
    Necessary data
    - Protection in ZK3a - 32A
    - The pre-meter protection is 16A - 3f
    - The network system is TN-C (4x70mm? Al cable connection - 115m to ZK3a)
    - Power supply to the above-mentioned connection from a straight-through pole.
    - A set of valve lightning arresters GZa0.66 / 1.5kVA with grounding type TA3x7 (steel tape 30x5 - 30m) is mounted on the pole
    - Distance of the connection point from the transformer 100m
    - 250kVA transformer power
    - Short circuit voltage 4.5%
    - Steel wire 6mm? laid parallel to the cable (after 30 years maybe 3-4mm? remained: /)

    I am planning to modernize the internal installation.
    I have a project but it is very general and does not provide detailed information about the surge arrester, PEN distribution point, etc.
    My questions ?
    1. According to the diagram in the appendix, can I split the PEN after the meter (as shown in the picture) or should I do it before the meter?
    2. Can I use an AC circuit breaker or do I have to buy an A?
    3. Should a surge arrester back-up be used?
    4. What about the equalizing connection of the gas pipe when there is no insulation insert?
    5. Are there errors in the schematic? If so, what should I improve?

    I will be grateful for any suggestions.
    Title: Chapter PEN, Protector Selection & Switchgear Diagram for Single-Family House: TN-C System
  • ADVERTISEMENT
  • #2 17597255
    mawerix123
    Level 39  
    Posts: 4150
    Help: 482
    Rate: 951
    Arrester for the TN-C system
    Protection between the switch and the arrester is pointless.
  • ADVERTISEMENT
  • #4 17597700
    mawerix123
    Level 39  
    Posts: 4150
    Help: 482
    Rate: 951
    Yes, but what value ... the security of your protectors is in ZK, there is no point in duplicating it.

    Type A RCDs are a better choice than AC but one 4P for the whole house is a bad idea.

    Check what the manufacturer recommends regarding the conductor cross-section for SPD or 10 and 16mm? is enough.
  • #5 17597854
    piter_admin
    Level 9  
    Posts: 10
    Rate: 6
    Approx. I thought that the distance of the inserts from the limiter also matters.
    As for the RCD, there is only one in the following appendix and it is 3F for the whole house. The photo comes from the project.
    As for the cross-sections of the PE conductor from the limiter, the manufacturer writes about min. 10mm2. There will be a maximum of 20cm of 16mm? cable from the limiter to the GSU. Then a hoop for a pin earth electrode, and in the spring, a ring earth electrode and a lightning conductor will be made.
    Ultimately, I am planning separate differentials for the circuits
    -Gas boiler 1f A
    -Recuperator 1f A
    - Washing machine 1f A
    -Electric kitchen 3f AC
    -External sockets 1f A

    Title: Chapter PEN, Protector Selection & Switchgear Diagram for Single-Family House: TN-C System
  • ADVERTISEMENT
  • #6 17598042
    kSmuk
    Level 21  
    Posts: 401
    Help: 27
    Rate: 100
    piter_admin wrote:
    Ultimately, I am planning separate differentials for the circuits
    -Gas boiler 1f A
    -Recuperator 1f A
    - Washing machine 1f A
    -Electric kitchen 3f AC
    -External sockets 1f A

    In that case, it's probably RCBO.
    On the other hand, the recuperator and the heating plate, as devices installed permanently, do not require the use of circuits protected by a residual current device.

    For your convenience, you should separate the circuits into separate RCDs.
    And protecting single-phase circuits with a four-pole circuit breaker is asking for trouble.
  • Helpful post
    #7 17598077
    emigrant
    Level 29  
    Posts: 1605
    Help: 107
    Rate: 326
    piter_admin wrote:
    1. According to the diagram in the appendix, can I split the PEN after the meter (as shown in the picture) or should I do it before the meter?

    If possible, make a breakdown in the switchboard.
    piter_admin wrote:
    2. Can I use an AC circuit breaker or do I have to buy an A?

    As far as I remember, AC is already banned in some western countries. In my switchgear, all RCDs are of type A, but that was my whim, because for now you can use RCD type AC as you want.
    piter_admin wrote:
    3. Should a surge arrester back-up be used?

    Since you are going to use DEHNventil, it can extinguish the line sequence arc up to 50,000 A. Additional protection of such an SPD is completely unnecessary. The DEHNventil documentation specifies when to apply a back-up.
    piter_admin wrote:
    5. Are there errors in the schematic? If so, what should I improve?

    Badly matched SPD. In the drawing, you connect the PEN conductor to the PE strip. While the distance between the PE and N rails is small ? 50 cm, use the SPD for the TN-C system (https://www.dehn.de/store/d?locale=en&product=951300&type=specification). You connect to the PE rail from the PEN clamp on the SPD. The overvoltage will be limited on the PE and N busbar. Here, the SPD with the N-PE module is unnecessary - something else if you had a PEN division before the switchgear with 5-wire WLZ. I do not know how big you are going to have the switchgear, but the distance between the SPD and the PE busbar is also relatively short ? 50 cm. This distance is more important than between the SPD and the GSU.
    For the SPD, I would use a distribution block, not a direct connection to the RCD.
  • #8 17599225
    piter_admin
    Level 9  
    Posts: 10
    Rate: 6
    So, can the PEN of the lz be 10mm??
    If :
    - BMy in ZK3a - 35A
    - 16A pre-meter protection
    - wire from ZK to ZL 4x10mm? CU
    - wlz 5x10mm? CU (free PE wire)
    In the figure below, the S2 wire (L1, L2, L3) can be 10mm?, but the S3 and S4 wires must be 16mm?.

    Title: Chapter PEN, Protector Selection & Switchgear Diagram for Single-Family House: TN-C System
  • #9 17599273
    emigrant
    Level 29  
    Posts: 1605
    Help: 107
    Rate: 326
    How is it possible that you have decided to use such a small (contracted) connection capacity? This is my first time meeting with the 16 A pre-meter protection. After all, it will be unusable.

    piter_admin wrote:
    In the figure below, the S2 wire (L1, L2, L3) can be 10mm?
    But the S3 and S4 wires must be 16mm?

    Yes. Cables from the terminal with the grounding symbol and PEN are exposed to high surge currents that can come directly from the lightning protection system to the SPD via the GSU. In addition, all phases are connected via a spark gap and a varistor to the double ground / PEN terminal. During the operation of the SPD, all phases are connected to the double PEN terminal for this time in order to equalize the potential difference.
    PS
    Then finally decide what WLZ should be. There is no such thing as a free PE vein or hanging in the air. If you are going to split the PEN in front of the switchgear, you cannot use SPD for TN-C. Must be for TN-S with N-PE module.
  • #10 17599446
    kortyleski
    Level 43  
    Posts: 12265
    Help: 957
    Rate: 3860
    You have TN-C. What about grounding? Is you like Fundamentowe, otok or cuś?
  • #11 17600384
    piter_admin
    Level 9  
    Posts: 10
    Rate: 6
    emigrant wrote:
    How is it possible that you have decided on such a small (contracted) connection capacity? This is my first time meeting with the 16 A pre-meter protection. After all, it will be unusable.
    I found such a security.
    I will try to change this protection when taking the meter out. The contracted capacity is 14kW
    emigrant wrote:
    PS
    Then finally decide what WLZ should be. There is no such thing as a free PE vein or hanging in the air. If you are going to split the PEN in front of the switchgear, you cannot use SPD for TN-C. Must be for TN-S with N-PE module.

    The situation is developmental, hence my questions.

    As I wrote earlier.
    For ZK 3a there is a 4x70Al cable + 6mm? steel wire. There is only 4x10mm?Cu (but only 2m) between the ZK and the meter, and a new 5x10mm?Cu wire is laid from the meter. That is why I am writing about the fact that the PE conductor is free, i.e. not connected. But nothing prevents you from distributing the PEN in the ZL or earlier in the ZK when the meter is raised outside the ZK

    Added after 5 [minutes]:

    kortyleski wrote:
    You have TN-C. What about grounding? Is you like Fundamentowe, otok or cuś?

    At the moment there is a 6mm? steel wire in ZK and a 1x3m pin earth electrode connected with a 30x5 hoop to the GSU. In the spring, a ring earth electrode will also be made.
  • Helpful post
    #12 17600481
    opornik7
    Electrician specialist
    Posts: 4508
    Help: 316
    Rate: 1569
    piter_admin wrote:
    But nothing prevents you from distributing the PEN in the ZL or earlier in the ZK when the meter is raised outside the ZK

    There is no such option in Tauron.
  • ADVERTISEMENT
  • #13 17600767
    piter_admin
    Level 9  
    Posts: 10
    Rate: 6
    opornik7 wrote:
    piter_admin wrote:
    But nothing prevents you from distributing the PEN in the ZL or earlier in the ZK when the meter is raised outside the ZK

    There is no such option in Tauron.

    So I have to understand that Tauron does not agree to the implementation of the PEN division in ZK or ZL and the only place of division is RG at home?
  • Helpful post
    #14 17600875
    opornik7
    Electrician specialist
    Posts: 4508
    Help: 316
    Rate: 1569
    Yes buddy. It is as you wrote.
  • #15 18050756
    piter_admin
    Level 9  
    Posts: 10
    Rate: 6
    So, can I use the Dehn 951300 (TN-C) limiter when separating the PEN in the RG?
    If so, please provide information on what conditions I have to meet in order for it to be done properly.
  • PEN split and SPD wiring in TN-C system

    #16 19206275
    Anonymous
    Level 1  

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the switchgear diagram for a single-family house utilizing a TN-C system. Key points include the protection setup with a 32A ZK3a and 16A pre-meter protection, the use of a 4x70mm² aluminum cable for a 115m connection, and the installation of valve lightning arresters with specific grounding requirements. Participants debate the appropriateness of splitting the PEN conductor after the meter, the necessity of using Type A RCDs over Type AC, and the implications of conductor cross-sections for surge protective devices (SPDs). The conversation also touches on the limitations imposed by the local utility provider, Tauron, regarding PEN division locations and the use of specific SPDs like the Dehn 951300. Recommendations include ensuring proper grounding and the use of separate RCDs for different circuits to enhance safety and functionality.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: For TN-C upgrades, a DEHNventil can quench 50,000 A, and "Additional protection of such an SPD is completely unnecessary" when sized per spec. This FAQ shows where to split PEN, how to pick SPD/RCD, and how to wire safely. [Elektroda, emigrant, post #17598077]

Why it matters: It helps homeowners and electricians modernizing a TN-C single-family house avoid miswired PEN splits, wrong SPD/RCD choices, and nuisance trips.

Quick-Facts

Quick Facts

Where should I split the PEN in a TN-C supply—before or after the meter?

Split the PEN in the house main switchboard (RG). Tauron does not allow PEN division in ZK or ZL. Treat the split as part of the consumer installation and perform it in RG. [Elektroda, opornik7, post #17600875]

Can I use DEHN 951300 (TN-C) if I split the PEN inside RG?

Yes, when PE and N bars are close together. Use a TN‑C SPD and land its PEN terminal on the PE bar. If PEN were split before the board, use a TN‑S SPD with an N‑PE module instead. Keep leads short. [Elektroda, emigrant, post #17598077]

Do I need a backup MCB/fuse in front of a Type 1 SPD?

For DEHNventil, an extra protective device is typically unnecessary. It quenches line‑to‑line arcs up to 50,000 A. Follow the datasheet to confirm. Often, upstream protection already covers it. “Additional protection of such an SPD is completely unnecessary.” [Elektroda, emigrant, post #17598077]

What RCD type should I install—AC or A—and how many?

Choose Type A RCDs. Do not use a single four‑pole device for the entire house. Split loads across multiple RCDs to improve selectivity and reduce outages. “One 4P for the whole house is a bad idea.” [Elektroda, mawerix123, post #17597700]

Are RCBOs a good choice for per‑circuit protection?

Yes. RCBOs give each circuit independent residual and overcurrent protection. They localize faults and reduce nuisance tripping. They work well for laundry, boiler, or outdoor socket circuits. Keep single‑phase circuits on single‑pole devices, not a shared four‑pole unit. [Elektroda, kSmuk, post #17598042]

Do fixed appliances like a cooktop or a recuperator require RCD protection?

These are permanently installed loads, so RCD‑protected circuits are not required in this context. You may still add RCDs if the project or local rules require it. Confirm with your inspector before energizing. [Elektroda, kSmuk, post #17598042]

Why is a four‑pole RCD/MCB on single‑phase circuits a problem?

It links unrelated circuits and phases, increasing nuisance trips and complicating faults. The guidance is clear: using a four‑pole breaker for single‑phase circuits is asking for trouble. Use separate single‑phase devices or RCBOs. [Elektroda, kSmuk, post #17598042]

What cross‑sections should I use for SPD and PEN connections?

Use 16 mm² conductors on SPD terminals that carry surge currents, especially the ground/PEN terminals. Those paths see the highest impulse energy. Size other conductors per the SPD datasheet and local regulations. [Elektroda, emigrant, post #17599273]

How short must the SPD leads be, and which distance matters most?

Keep the SPD close to the PE bar. About 50 cm or less is desirable. This length is more critical than the distance to the GSU. Short conductors reduce the let‑through voltage and improve protection. [Elektroda, emigrant, post #17598077]

How do I wire the PEN split and SPD inside RG (TN‑C)?

Follow this 3‑step approach:
  1. Bring L1‑L3 and PEN into RG; land PEN on the PE bar and phases on the main switch and SPD (TN‑C).
  2. Bridge PE and N bars to make the PEN split; use a bridge equal to WLZ size or ≥10 mm².
  3. From GSU, run a conductor to a distribution block, then to the SPD and PE bar; add a second SPD lead from the PE/PEN bar. [Elektroda, Anonymous, post #19206275]

Should I put protection between the main switch and the SPD?

No. A protective device between the main switch and arrester is pointless here. Use the upstream service protection already provided. [Elektroda, mawerix123, post #17597255]

Is 16 A pre‑meter protection acceptable for a modern home?

It is unusually small and will feel unusable in daily operation. Request an upgrade when moving the meter outside and revising the installation. Align protection to your contracted capacity. [Elektroda, emigrant, post #17599273]

Any tips for the earth electrode and testing?

Build a solid earth electrode and verify it before storm season. Use substantial conductors for short SPD bonds; many installers fit 35 mm² to the SPD clamp. Good earthing improves surge diversion and safety margins. [Elektroda, Anonymous, post #19206275]

How should I bond a gas pipe without an insulating insert?

Apply main equipotential bonding near the pipe entry, before the gas meter. Clamp the bonding conductor to the pipe and connect it to the main earthing terminal. If an insulating insert exists, bond only the building side. Follow national rules. [IEC 60364-5-54]
AI summary based on the discussion. May contain errors.