    Hello. What is the required turn-off time for an RCD switch according to the standard? Does the 0.2/0.4/5 sec rule also apply in the case of RCDs? I know that the switch-off time depends on the fault current that will flow through the RCD, but I want to determine the efficiency of the switch using electrical measurements. Regards.
  • ADVERTISEMENT
  • Helpful post
    #2 12314185
    .Jack
    Electrician specialist
    voytalo wrote:
    What is the required turn-off time for an RCD switch according to the standard?

    The operating time depends mainly on the switch and not on any residual current - (what is this residual current?).
    And the activation time depends on the multiplicity of the residual current. For a multiple of one, for a standard RCD, it is 0.3 s, for a multiple of two, it is 0.15 s, for a multiple of five, it is 0.04 s.
    voytalo wrote:
    I`m talking about determining the efficiency of a circuit breaker during electrical measurements

    The latest standard for checking electrical installations in Poland does not provide for checking and documenting the operation time of the residual current circuit breaker, so it can be omitted in the protocol. A measuring electrician should know this.
  • ADVERTISEMENT
  • #3 12314222
    elpapiotr
    Electrician specialist
    You have to add it though, my friend .Jack , when it is recommended to check the required shutdown times.
  • ADVERTISEMENT
  • #4 12314224
    voytalo
    Level 25  
    Residual current is one of the terms for residual current - an electrician should know about it.
    I`m not a measuring electrician, but I deal with measurement protocols in which I encounter a record of the RCD activation time, that`s why I`m asking.

    Added after 2 [minutes]:

    elpapiotr wrote:
    You have to add it though, my friend .Jack , when it is recommended to check the required shutdown times.

    I know that this time should be checked in the case of a second-hand RCD test. But what good is measuring time if I have no reference point? Hence my question about the requirements.
  • ADVERTISEMENT
  • Helpful post
    #5 12314274
    elpapiotr
    Electrician specialist
    The reference point is in section 411.3.2.2 of the PN-HD 60364-4-41 standard of November 2009
  • #6 12314283
    voytalo
    Level 25  
    elpapiotr wrote:
    The reference point is in section 411.3.2.2 of the PN-HD 60364-4-41 standard of November 2009

    Unfortunately, I don`t have access to the PN, so if you could cite this entry, I would be grateful.
  • #7 12314473
    .Jack
    Electrician specialist
    voytalo wrote:
    Residual current is one of the terms for residual current

    It is not the fault current, but the standard specifies: residual fault current. Anyway, never mind. In my opinion, this is an incorrect spelling or poorly translated from English. But you know what I mean.
    voytalo wrote:
    Unfortunately, I don`t have access to the PN, so if you could cite this entry, I would be grateful.

    This point contains a table: Maximum switch-off times for final circuits with a current not exceeding 32 A.
  • #8 12314489
    elpapiotr
    Electrician specialist
    Alright.
    You do not need to have access to the relevant PN to determine the effectiveness of protection by ensuring SWZ for protection devices, including RCDs, for specific (and permissible) activation times.
    This is the basis for environmental conditions, etc.
    You definitely have this data, and if not, calculate it.
  • #9 12314632
    voytalo
    Level 25  
    After all, in the first post I asked whether SWZ is used to ensure the required switch activation times of 0.2/0.4/5 s. It should have been written right away that the required shutdown time for RCDs is the same :) Anyway, thanks for clarifying the situation
  • #10 13308996
    elpapiotr
    Electrician specialist
    You have the required RCD switch-off time:

    What Is the Standard Turn-Off Time for RCD Switches? Does 0.2/0.4/5 Sec Rule Apply?
  • #11 13309783
    Anonymous
    Anonymous  
  • #12 13309885
    elpapiotr
    Electrician specialist
    For terminology, blame Sonel, not the measuring person, bro Bronek:

    What Is the Standard Turn-Off Time for RCD Switches? Does 0.2/0.4/5 Sec Rule Apply?

Topic summary

The discussion centers on the standard turn-off times for Residual Current Devices (RCDs) and the applicability of the 0.2/0.4/5 second rule. It is established that the required switch-off time for standard RCDs is 0.3 seconds for a residual current multiple of one, 0.15 seconds for a multiple of two, and 0.04 seconds for a multiple of five. The PN-HD 60364-4-41 standard outlines these requirements, although some participants note that the latest Polish standards do not mandate the documentation of RCD activation times. The conversation also touches on the importance of measuring these times for second-hand RCDs and ensuring compliance with safety protocols.