Vitodens 100 F1 Error: Flue Gas Temperature High After Service Checks—What Next?

Vitodens 38592 31
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 13130096
    Vitodens
    Level 9  
    _uki_ wrote:
    at worst, the motherboard



    It could always be worse - to replace the heat exchanger.

    After firing the furnace, the exchanger heats up very quickly and strongly in two places. These are places where it was suspected that the gaps between the coils are too large. The rest of the exchanger barely warm. It appears that the coil may be deforming, and the cause was probably the freezing of the system.

    Theoretically the problem solved.

    PS
    I think I will add a little and buy a new furnace, at least I will have a warranty and almost a set of spare parts.
  • ADVERTISEMENT
  • #32 21325771
    benrahtjohn
    Level 1  
    Hi all, today I beat the F1 on the Viotodens 200 WB2B. I did the exchanger service including removal, pump service, 3-way valve, all hoses, vessel etc. 5 hours, vented through a faulty vent!!!! Such a trivial thing to do and it gave a hard time. Good luck, hope it's useful.

Topic summary

The discussion addresses the Vitodens 100 F1 error indicating excessively high flue gas temperature despite comprehensive service checks including burner inspection, exchanger cleaning and descaling, pump replacement, chimney draught measurement, and CO2 level verification. Flue gas temperature readings reached 130-140°C, ruling out sensor faults. Venting the boiler and pump was performed without improvement. The exchanger was suspected to have deformities caused by freezing, potentially increasing coil gaps and reducing heat transfer efficiency, leading to high exhaust temperatures and uneven heating. Suggestions included flushing the entire heating system under pressure to remove scale and rust deposits, checking gas nozzles for correct sizing and gas pressure, and verifying the absence of chimney obstructions such as birds. The possibility of replacing the heat exchanger was considered costly, prompting consideration of purchasing a new boiler for warranty and spare parts. A related note mentioned a similar F1 error on a Vitodens 200 WB2B resolved by thorough exchanger and pump servicing and proper venting.
Summary generated by the language model.