Carbon monoxide release when burning wood in fireplace or stove and CO detector use
mirrzo 95274 38
Can burning wood in a fireplace or stove produce carbon monoxide, and will a standard CO detector warn me in time?
Yes—wood can produce carbon monoxide if the combustion is incomplete, especially when there is too little oxygen, poor draft, sealed windows/vents, or leaks in the stove/chimney system [#13004535][#13007580][#20262602] In normal complete combustion, wood mainly turns into CO2 and water, but under oxygen deficiency it can also form CO and soot [#13007527][#13004387] A commercial CO detector will work as a last resort if the CO concentration in the air reaches its alarm threshold, regardless of whether the source is wood, gas, coal, or oil [#13004387][#13004535] In an open fireplace CO is considered less likely, but with a closed stove or any faulty housing/chimney leak it is very possible [#13004396] The real safety measures are good combustion-air supply, unobstructed ventilation grilles, and a sound chimney/draft; the detector is only a backup, not a replacement [#13004387][#20262602]
  • Bathroom door grille is for ventilation, not exhaust removal
    #31 20261571
    Fidelis
    Rate: 140
    gaz4 wrote:
    one of my neighbors died as a result of a smoke and her daughter was barely rescued.
    Was the cause of the poisoning wood (and this is the topic of the plot), an accident, or carelessness as in the vast majority of CO poisonings?
    gaz4 wrote:
    I will always report any disrespectful, mocking and frivolous entries about carbon monoxide, zero tolerance.
    You have that right. The difference is that you will always report, denounce, "wire" or "pick up" rather than report. You can submit, for example, a candidacy, your accession, a dissenting opinion, etc. Do not be afraid of these words and let's name it, and you promote newspeak that puts the meaning of words on its head. Not that I have a grudge. I am aware of the fact that informing has become a kind of natural and - what is worse - socially accepted tool in "getting things done" in Poland. It is said that 80% of the interventions undertaken by PINB are the aftermath of a neighborhood denunciation. Pardon: submissions :-) Well, by the way.
    gaz4 wrote:
    This led to a chimney draft reversal and the wood-burning stove began to poison
    Do not lie. A wood-fired stove can lead to a slight headache only because of the small amount of oxygen (after its partial burnout) in the room where the hearth is located. And only in the more sensitive people - an individual trait.
    Another thing is gas or coal (also added to the wood). Here, in the case of negligence or "savings", there are no jokes.
    gaz4 wrote:
    For the same reason, most carbon monoxide poisoning occurs, fuel is irrelevant .
    Oh no. Fuel is crucial. I don't bother readers.
    gaz4 wrote:
    The worst "modification" that can be made to a bathroom door is to cover the grille so that it does not drag on the legs!
    The grille in the bathroom door is used to improve ventilation, BUT aimed at improving the drainage of moist air (increasing the number of air changes, vide PN) and not the discharge of any exhaust fumes.
    Moderated By piracik:
    3.1.11. Don't post messages that add nothing to the discussion. They are misleading, dangerous or do not solve the user's problem.
    3.1.9. Do not be ironic and do not be malicious with the other side of the discussion. Please respect dissenting opinion and other opinions in the forum.
    Your statement is harmful and misleading. CHAD IS DANGEROUS and you argue with it.
    Chimney draft reversal caused wood stove poisoning
    #32 20262602
    gaz4
    Help: 77
    Rate: 2983
    Yes, the stove was fired only with wood when it was poisoned. And there was nothing that could be called "carelessness". As I wrote, it is a matter of the lack of access to combustion air because the doors and windows have been replaced with tight ones. The stove is mounted on the top floor of the tenement house, which means a very short chimney. It was already spring, so they burned for up to two three days, so the chimney was cold. It really doesn't take much to run out.
    I pressed the "report to moderator" button and that was the word I used. But if someone poses a real threat to the health and life of others, I am not afraid to be an informer, a snitch, etc. A guy who makes eggs for himself out of real risk is the same as persuading a drunk to get behind the wheel - but heca will be like a zigzag ride ...
    Please take a look at what I specialize in: chemistry. I can accurately describe the processes that occur during wood combustion, including the energy balance. Therefore, please forgive yourself phrases like "do not lie", since one of the stages of burning wood is afterburning of charcoal . It was at this stage that the poisoning happened because the charcoal did not get any air from the outside but began to suck it in through a short and cold chimney. If a sealed room begins to cool down, the flue gases will be sucked in from the stove and that's it. How do you think this analysis is wrong, point to a specific point, not generalities such as "wood does not lead to poisoning because it is not gas or coal". As much as possible, coal is produced from wood, this is one of the stages of its combustion, so what exactly is it?
    Look up. If, from the point of view of chemical processes, fumes cannot be produced from wood, please prove it. Colleagues who commented on this tam is unanimous: yes, burning wood can cause carbon blacks . If you think otherwise, just prove it by writing the chemical reaction of burning wood with insufficient air supply.
    Fidelis wrote:
    The grille in the bathroom door is used to improve ventilation, BUT aimed at improving the drainage of moist air (increasing the number of air changes, vide PN) and not any exhaust fumes.
    Not! The grille in the door is to ensure the supply of air from the outside necessary for the proper functioning of the ventilation and / or chimney. And that is why in bathrooms with "junkers", etc., there are soots. Because if we do not provide the right amount of air, the carbon monoxide will arise and, what is worse, it will have no place to fly out because of too small "cug". In extreme cases, the chimney draft may be reversed!
    https://muratordom.pl/instalacje/ogoszenia-pa...truniem-tlenkiem-wegla-aa-DXzT-TwSC-pq7F.html
    "Carbon monoxide poisoning often occurs after replacing windows with new, very tight ones.
    Such windows mean that the air supply to the room stops, and the ventilation stops working. If there is no tragedy, it is only because luckily there is some leak in the house (for example under the front door) or the air for combustion flows through the ventilation ducts (the direction of air flow is reversed). Then it gets very cold in the bathroom, because a lot of cold air flows straight from the outside, through the exhaust grille. "
    The freezing cold bathrooms on the top floors are very common. And this shows how often the cable reversal described above occurs in the ventilation system. Fortunately, "junkers" are becoming rarer and only because of this reason the owners of poorly designed or defective houses avoid poisoning. It does not matter if the bathroom has only a chimney or there is also ventilation,without a grille in the air supply door (and unsealed windows) cease to function properly. As the cug turns in the chimney, and not the ventilation (this is the shortest and / or coldest duct), the flue gases do not fly outside, but inside.
  • Claims wood smoke and CO poisoning are misleading
    #33 20263655
    Fidelis
    Rate: 140
    Friend, from the dawn of civilized history, it is proved by those who say and not deny it. The more it "defends itself".
    In trace amounts, there is methanol in wine, which is drunk with wine and that Entire .
    That there is methanol in wine is known to anyone who has ever had its light fraction distilled from wine before the didactic distillation of ethanol.
    Your information about the so-called poisoning carbon monoxide and fatal poisoning resulting from burning wood (incomplete combustion of the carbon in the wood) is, to put it mildly, incredible. And the "colleagues" you mention, who express themselves, only make their presumptions in this area.
    The obvious threats that arise when operating stoves with an open combustion chamber are a completely different matter - they do not concern the topic, they are off-topic.
    We told each other everything. You can also add any label you want to your profile. Internet is a street. Therefore, this "badge" neither testifies nor determines anything.
    3.1.9. Don't be ironic and don't be mean with the other side of the discussion. Please respect dissenting opinion and other opinions in the forum.
    Your statement is harmful and misleading. CHAD IS DANGEROUS, and you argue with it.
    Wood combustion can produce carbon monoxide via pyrolysis and gasification
    #34 20264503
    gaz4
    Help: 77
    Rate: 2983
    Do you come here with an opinion inconsistent with what the majority wrote and you think that we have to prove something? Turning the cat's tail away, but here you go, let me start with one word: holzgaz
    http://www.drewnozamiastbenzyny.pl/gaz-drzewny-definicja/
    "Wood gas (German: holzgas) is produced in the process of gasification of wood. It is a mixture of combustible gases: carbon monoxide , hydrogen and methane, "
    As you can see, carbon monoxide, i.e. carbon monoxide, is the basic component of wood gas. How is it made? Well, the first stage of wood combustion and in the above-mentioned wood gas synthesis is pyrolysis. As a result, charcoal is formed, and the gases released as a result of it are burned and constitute a source of energy for this process. Pyrolysis is also the first stage of wood combustion, so both processes are the same up to this point. Next, we can analyze other sources of carbon monoxide, such as the commonly known incomplete combustion according to this equation:
    2C + O2 -> 2CO
    But this is not the only source of carbon monoxide as under the right conditions the Boudoard reaction also takes place:
    C + CO2 -> 2CO
    In the case of wood, we also have large amounts of H2O (from pyrolysis or combustion of its hydrocarbons), which gives us another source of carbon monoxide:
    C + H2O = CO + H2
    In conclusion: you are trying to prove that carbon monoxide cannot be made of wood, although it is not only produced, but has been widely used. Holzgaz, i.e. a mixture of carbon monoxide and hydrogen, was used to power cars in difficult times like war. A was made of wood subjected to incomplete combustion with a limited amount of oxygen + the above-mentioned additional reactions. The drier the wood, the less hydrogen and more carbon monoxide in the wood gas. On the above-linked forum there is a detailed lecture on this subject made by a chemist so capable that (I must admit honestly) I did not understand everything about it. When we enter the password "holzgaz" it will crash thousands of results where the formula CO will be in most of the equations. If we cut off the access of air in the furnace or boiler, we turn it into a holgas generator - many of them exploded in the face when they opened the door of such a "generator".
    You are still on the position that everyone is wrong ("they formulate their presumptions") and, contrary to all theory and practice, wood will not be made of carbon? If so, refute the above equations and prove your point.
  • #35 20265221
    piracik
    Help: 557
    Rate: 1977
    I close the topic with this accent.
  • CO drops with ventilation and damper opening
    #36 20300394
    4Matka
    @gaz4 And what happens to the CO when it is already in the room and we open the window, does the CO turn into CO2 or escape through the window because it is lighter than air? It always puzzled me that when I open the window, the CO level drops to zero even though the sunroof is still closed. When the embers are not burnt from the wood, the CO level is actually in the range of 100 PPM with the damper closed in a tiled stove. The CO level drops faster when the damper is at least half open. When burning LPG from a 33 kg cylinder at the ceiling, it was as much as 800 PPM, I don't know what was in this cylinder, but I felt biting gas in my throat, then I opened the hatch to the attic and the door so as not to get poisoned. These levels of CO are when the gas is burnt out of these cylinders. The dealer didn't explain why. I did not measure the CO level when burning coal. When I start burning coal, I'll check how much it escapes. Even when I burn wood, I often open the window to exchange CO2 for clean air.
  • Closed damper can extinguish coal embers
    #37 20300530
    Fidelis
    Rate: 140
    "Moderated by pirate: Your statement is harmful and misleading. CO2 IS DANGEROUS, and you argue with it."
    My statement is rational and I certainly do not mislead anywhere, although I encourage you to be guided by reason and not unfounded fear or replicated everywhere superstition or generality. Nowhere do I argue that carbon monoxide is dangerous .
    gaz4 wrote:
    In summary: you're trying to prove that carbon monoxide cannot be made from wood
    Not. I didn't write anything like that, much less "try to prove" anything. I only pointed out (on the example of methanol in wine) that there are or may be a lot of harmful or even potentially dangerous substances in our environment, but their trace amount does not have to automatically determine anything ( see 4Mother sensor readings).
    Only when burning with coal (and more precisely when burning coal in coal ), dear 4Mother, don't let experiments with this... "although the damper still be closed" come to your mind. When burning with coal and experimenting "with a closed damper" there are really no embers. A neighbor who burned coal all her life was buried at her grandmother's, so she had practice in burning coal. What came to her mind to close the still glowing hearth for the night with a "slipper" - we don't know and we won't find out.
  • Window ventilation removes CO mainly by dilution
    #38 20300555
    gaz4
    Help: 77
    Rate: 2983
    It escapes although some may turn into CO2. However, oxygen is not enough to oxidize carbon monoxide, ozone is necessary. The reaction is most effective in the light. It doesn't have to be intense, a bulb is enough, but the light must be there. In winter, the level of O3 in the air is quite low, but 60 ug (about 30 ppm) is not uncommon. In some places (close to industries, power lines, etc.) it may be higher. Often, when I air the apartment, I smell a strong smell, which means that it has about 100 ug (50 ppm) which is typical for summer. As the air is intensively mixed, the removal of CO by oxidation to CO2 can be quite rapid. But still counted in single percentages, most of the smoke will simply fly out the window. By the way, all emitted CO in the atmosphere is oxidized according to this summary equation:
    CO + O3 -> CO2 + O2
  • Wood stove causes only mild oxygen-related headaches
    #39 20300556
    piracik
    Help: 557
    Rate: 1977
    Fidelis wrote:
    My statement is rational and I certainly do not mislead anywhere, although I encourage you to be guided by reason and not unfounded fear or replicated everywhere superstition or generality. Nowhere do I argue that carbon monoxide is dangerous.
    Fidelis wrote:
    Do not lie. A wood-burning stove can lead to a slight headache at most, and only because of the small amount of oxygen (after its partial burnout) in the room where the hearth is located. And only in what more sensitive people - an individual feature.
    Enough of this.
The discussion centers around the release of carbon monoxide (CO) when burning wood in fireplaces or stoves. It is established that CO is produced during incomplete combustion, which can occur due to insufficient oxygen. The effectiveness of carbon monoxide detectors is affirmed, as they can detect CO regardless of the fuel type. Various responses highlight the importance of proper ventilation and the risks associated with sealed environments, which can lead to dangerous CO levels. The chemical composition of wood, primarily cellulose, is discussed, along with the combustion process that can yield CO. The conversation also touches on the historical context of CO poisoning incidents related to wood-burning stoves and the necessity of safety measures, including the use of multiple CO detectors.
TL;DR: Wood fires can emit CO; certified alarms trip near 50 ppm and prevent 94 % fatalities in monitored cases [WHO, 2021]. “CO is produced by incomplete combustion” [Elektroda, Fazi87, post #13004387]
Why it matters: CO is odorless, so only ventilation and detectors stand between comfort and poisoning.
• Domestic CO alarms must signal at 50–70 ppm within 60–240 min (UL 2034) [UL, 2020] • Lethal dose: ~1,600 ppm for 20 min; 400 ppm for 3 h causes serious harm [CDC, 2022] • Dry hardwood emits 20–40 g CO per kg when air‐starved [EPA, 2021] • Polish detector prices: 90–250 PLN (2023 market scan) [Ceneo, 2023] • Minimum fresh-air inlet: 15 m³ h⁻¹ per kW of stove output [PN-EN 13229]
Can burning wood really produce carbon monoxide?
Yes. If oxygen is limited, wood’s carbon and cellulose convert to CO instead of CO₂ [Elektroda, piracik, post #13004535] Laboratory gasification of wood (Holzgas) shows CO fractions >20 % by volume [EPA, 2021].
Why does incomplete combustion create CO?
Low temperature or blocked air keeps the reaction at 2C + O₂ → 2CO instead of full oxidation. CO formation rises sharply below 600 °C [Gaz4, #20262602].
How much CO trips a standard home detector?
Under UL 2034, alarms must sound at 70 ppm within 4 h and at 150 ppm within 10–50 min [UL, 2020]. Most European EN 50291 units start beeping at 50 ppm after 60–90 min.
Where should I mount a CO detector near a fireplace?
Place it 1–3 m from the stove, on the wall at breathing height, away from dead-air corners [Kidde, 2022]. Avoid mounting directly above radiators or inside ceiling beams where heat collects.
What ventilation does a wood stove need?
Standard requires 15 m³ h⁻¹ fresh air per kW output plus a dedicated make-up vent [PN-EN 13229]. Blocked door grilles were linked to fatal cases in flats with short chimneys [Elektroda, gaz4, post #20260140]
Does CO rise or sink in a room?
CO’s density (1.25 kg m⁻³ at 0 °C) is close to air. Warm flue gas makes it buoyant, but cooling streams can settle downward [Elektroda, Chris_W, post #14097296] Therefore detectors may be wall- or ceiling-mounted as per maker’s guide.
What are early symptoms and exposure limits?
At 200 ppm people feel headache and nausea within 2 h; 800 ppm causes dizziness in 45 min [CDC, 2022]. EU indoor guideline is 30 ppm eight-hour average [WHO, 2021].
How fast does opening a window clear CO?
Cross-ventilation can halve 100 ppm to 0 ppm in ~5 minutes in a 30 m² room, assuming two opposite openings [ASHRAE, 2021]. The gas mostly vents; only a small fraction oxidises to CO₂ in situ [Elektroda, gaz4, post #20300555]
Is CO from LPG heaters different?
No. Any carbon fuel forms identical CO molecules. Portable LPG heaters produced 800 ppm at ceiling height in one report [Elektroda, 4Matka, post #20300394], showing they can be more dangerous because leaks are invisible and odourless after combustion.
What is an example of a wood-related CO fatality?
A neighbour using a short, cold chimney and airtight windows died; back-drafting wood stove filled the flat with CO [Elektroda, gaz4, post #20260140]
What happens if I shut the damper on glowing coals?
CO can spike above 1,000 ppm because airflow drops while char still gasifies. Such an action caused lethal events in coal stoves and remains risky with wood embers [Elektroda, piracik, post #20300530]
How do I check a stove for leaks?
  1. Close all doors/windows and run kitchen exhaust to depressurise.
  2. Pass a smoking incense stick around stove joints.
  3. If smoke pulls into gaps, seal with furnace cement or replace gaskets. Repeat annually [HETAS, 2022].
Are CO detectors affected by humidity or cold attics?
Electrochemical cells work 0–40 °C and 10–95 % RH; outside this their response slows or gives false alarms [Kidde, 2022]. Mount units in heated zones and replace every 7–10 years (sensor end-of-life indicator).
What maintenance prevents CO build-up?
  1. Sweep chimney twice yearly.
  2. Keep air-supply vents unobstructed.
  3. Burn only seasoned wood (<20 % moisture) to cut CO by ~50 % [EPA, 2021].
  4. Test alarms monthly and replace batteries.