How to test a carbon monoxide sensor yourself – no alarm over burner?
cordoba_2004 39087 41
How can I safely and reliably test whether my carbon monoxide/gas detector is working at the correct threshold?
You can only reliably test it with the manufacturer’s calibration/test gas applied in the way specified for that detector; lighters, cigarettes, burner gas, sprays, car exhaust, and other improvised methods are unreliable and can overrange, decalibrate, or damage the sensor [#16965083][#20474332] A TEST button, if present, only checks the alarm electronics and does not verify the sensor’s real response to gas [#13238375] Some detectors also have a peak-concentration memory that can show whether elevated CO was detected, but it still does not prove the alarm threshold is correct [#17811635] For a home user, there is generally no safe and dependable way to confirm exact CO sensing performance without proper reference gas and conditions [#16965083]
  • #1 13234150
    cordoba_2004
    Help: 18
    Rate: 361
    Do you have any ways and methods to check the correct operation of the carbon monoxide and gas sensor. I bought one for PLN 100 and hung it over the gas released from the burner. He doesn't answer, but he should.
    Thank you
    jacekko0
    Help: 145
    Rate: 246
    I brought it closer to an open oven and it worked right away.
    rosomak44
    Help: 9
    Rate: 11
    The sensor reacts to carbon monoxide, not to gas, you have it written in the manual. Carbon monoxide is produced by improper combustion.
  • #4 13234295
    cordoba_2004
    Help: 18
    Rate: 361
    The sensor I bought is a gas and carbon monoxide sensor and the manual says that it reacts to meta, lpg, and carbon monoxide.
    I put the photo in the attachment
    piracik
    Help: 557
    Rate: 1977
    Depends on how high you held it above that burner and what type of gas you have.
    Bottled gas is heavier than air, so keep it close to the burner.
  • #6 13234345
    cordoba_2004
    Help: 18
    Rate: 361
    I kept close to the burner above the burner itself and the gas is from the gas pipeline, not the cylinder.
    And how to check it? are there any methods to check such a sensor? So reliable, because such sensors owe life or not.
  • #7 13234387
    Sono2020
    Help: 36
    Rate: 146
    Well, I guess you checked it out and draw your own conclusions!!!
    piracik
    Help: 557
    Rate: 1977
    There are calibration gases, but it should react the fastest to the test you gave it.
    I check them all with a lighter. I fire it up, blow it out and put it on for a while. Everyone should start screaming!
  • #9 13234823
    cordoba_2004
    Help: 18
    Rate: 361
    It has to react from the gas from the lighter even.
    And the carbon monoxide sensor is checked with a lit cigarette, it is supposed to react to the smoke from the cigarette placed against it and that's it.
    piracik
    Help: 557
    Rate: 1977
    Cigarette smoke detector? It probably won't work.
  • #11 13234885
    cordoba_2004
    Help: 18
    Rate: 361
    that's what the service told me, I checked one in the store and it reacted to a strong puff of smoke
  • #12 13237605
    Kot-huncwot
    Help: 31
    Rate: 93
    This will work on CO. It's in cigarette smoke.
  • #13 13238342
    mirrzo
    Help: 441
    Rate: 2609
    ...or press: TEST ;)
    EURO-DOM
    Krótka, Elbląg, 82-300
  • #14 13238375
    piracik
    Help: 557
    Rate: 1977
    But the test does not check the real gas response of the sensor, it only checks the general functioning of the alarm.
  • Lighter-gas tests risk sensor damage and lack calibrated concentration
    #15 13238393
    mirrzo
    Help: 441
    Rate: 2609
    And that's it.
    There is no need to make an effort to react to carbon monoxide. You also do a test with a cigarette or gas from a lighter, but with an unknown gas concentration. You know that the sensor burns out every day and its sensitivity decreases. By pounding his throat with a nice dose of gas from the lighter... Then why do we have to calibrate our sensors so often?
    Here, in my opinion, proper ventilation is required, which settles the subject. Supply and exhaust.
    EURO-DOM
  • #16 13240263
    Kot-huncwot
    Help: 31
    Rate: 93
    Of course, you should read the manufacturer's instructions in terms of the need to calibrate the sensor after triggering. Unfortunately, some electrochemical sensors require calibration after being triggered. The sensor, on the other hand, can be triggered by cigarette smoke exhaled by the smoker.
  • #18 16965083
    Domelski
    Level 19  
    Help: 30
    Rate: 113
    Forgive me for digging up the topic, but the suggestions contained in it simply knock down.
    Detectors are properly tested only with the use of calibration (or test) gases.
    Any other activities such as lighters, cigarettes, gas from the installation or cylinders, sprays, etc. are unreliable and may cause decalibration and damage to the detectors.
    Example:
    A household methane detector detects this gas in the range of 0-100% LEL (Lower Explosion Limit). The lower explosion limit of methane is 4.4%v/v according to EU standards. So the detector detects in the range of 0-4.4%v/v. Gas from a lighter, cylinder or burner has 100%v/v, which is about 20 times more than the measuring range of the detector.
    Household explosive gas detectors are built on the basis of a semiconductor sensor (rarely a more expensive catalytic sensor). Such sensors first need to have oxygen to measure. If the sensor chamber is filled to a large extent with gas displacing oxygen, the measurement will be incorrect.
    In addition, exceeding the range can cause decalibration or even damage to the detector.
    At the same time, such a "test" if successful, will not give us information whether the detector detects at the correct level. The detector is supposed to alarm at 10%LEL (0.44%v/v), and we gave the gas 100%v/v, which is about 200 times more. How do we know at what threshold it worked? Equally well, a decalibrated detector may react after exceeding the threshold of 100% LEL and will not be able to activate the alarm in an emergency situation or it will be its last alarm.
    A home carbon monoxide detector usually detects in the range of 0-100/0-200/0-300ppm. Giving him a cigarette or other smoldering elements, we give him from 1000ppm to even several thousand ppm.
    It is also risky to use carbon monoxide sprays. The concentration inside the spray can is specified (eg 300ppm). However, by spraying it, we significantly dilute them in the air. Thus, we do not know at what threshold the detector worked. Such a test is unreliable. And even more so, such a test is pointless in the case of detectors that are supposed to react to 20, 30 or 60ppm.
    In order for the detector to work properly, it must receive a specific reference gas mixture. For this, the detector needs time to react and stabilize the gas in the measuring chamber.
    Exactly. The ones out of calibration, measuring incorrectly too.
    I just don't understand why such advice comes from users signing themselves as "specialist in heating systems". Forgive me, but such tests of detectors do not check the correctness of their responses, therefore such a service is invalid.
    These are safety devices on which human life depends. Such a disrespectful approach is unacceptable if someone claims to be a service or specialist.
    It's just that the calibration gas costs money, and the lighter is cheap, right? And the service is cheaper than the competition. And the fact that the client is left with a decalibrated sensor is only then the court cares after the accident. Something to think about for all "specialists" who offer their services to others.
    Unfortunately, this is also not true. What happens to the sensor over time depends on its type. What my colleague wrote concerns the catalytic sensor (extremely rarely used in home detectors). But a semiconductor or electrochemical sensor with "burn-in" has little to do with it.
  • #19 16965130
    BUCKS
    Help: 536
    Rate: 1087
    As for the "specialist in heating systems", this status is granted automatically. I don't know the exact criteria, but I generally assume that if someone has a counter of posts on a given topic, they get this description. Therefore, a given user may be an amateur and not a professional. Whether someone professionally deals with heating and detectors can possibly result from the posts of a specific user.
    There are many professionals here who can and should be expected to be professional, but there are also many amateurs who are only interested in widely understood heating, etc.
    Generally, like all internet forums, Elektroda should be treated with a grain of salt, because among the valuable information you can always find advice that can do more harm than good.
  • #20 16965414
    Domelski
    Level 19  
    Help: 30
    Rate: 113
    I also treat forums with a grain of salt, but I wrote this post because unfortunately I come across these tips implemented in practice on unaware customers. And not only on home sensors.
    The subject of "how to check" is unfortunately catchy in our reality for various types of "pseudoservices".
    That's why my post is a bit of a warning for "checkers", but also for users who are looking for information.
    Manufacturers used to allow this type of launch (cigarette lighter, cigarette)
    You can see that a colleague "specialist" works in the topic (> 2000 posts) and wrote that he checks.
    But I didn't know that "specialist" was automatically broadcast. Mea culpa. :please:
  • #21 16965559
    BUCKS
    Help: 536
    Rate: 1087
    I used to play once in testing a carbon monoxide sensor to see if it works at all. I used a chalk spray for this and followed the instructions on the package.
    But I came up with the fact that I have no idea what the real concentration is in the bag at the time of the test and whether I have overdone it. As a result of such a test, I only checked whether the sensor reacts at all, but I had no idea if it reacted correctly.
    Therefore, I also consider such a test to be pointless.
    It is said that a man learns best from his own mistakes, but it is also worth using the experience of others so as not to repeat the same mistakes.
  • #22 16965735
    Domelski
    Level 19  
    Help: 30
    Rate: 113
    BUCKS, such a test with a spray and a bag can be done, for example, for your own home sensor. If you have a range up to 300ppm and a spray up to 300ppm, you will not exceed the range and check if the detector will work at all.
    It is important not to fill the bag to the max - in the sense of not increasing the pressure in which the sensor works.
    However, as you say, such a test is not reliable and does not tell us anything about whether the sensor is out of calibration.
    But I've already seen aces with such ideas that the head is small, testing people's sensors in buildings and issuing protocols.
    I've seen guys with a hose for the exhaust pipe, types with a lighter and an 8m pipe for methane detectors (no one told them that propane-butane doesn't really want to go up, detectors burnt and drowned because no one said that the lighter should not be lit :please: ) etc.
    Proper testing is very difficult actually because in addition to gases you have external conditions (temperature, humidity, pressure, flow, debris in the air, problem with filling the chamber, etc.). Therefore, for example, calibration is already done rather in a laboratory where you can have stable conditions.
    As for me, at home everyone checks what they want and how they want as long as they don't pose a threat. But if someone does it for others, I'm sorry, but there is no mercy.
  • #23 17810420
  • #24 17810555
    Domelski
    Level 19  
    Help: 30
    Rate: 113
    Adamcyn wrote:
    I started the car in the garage for a few seconds.
    After a few minutes, I returned to the garage and the peak concentration reading was 24 ppm.
    I think that this is a minimally invasive and economical method for the sensor and the examiner, allowing to determine the activation of the sensor.
    I'm going to protest a bit here. The amount of carbon monoxide in the exhaust depends on many factors (correct combustion of the mixture, oxygen access - which decreases with the amount of exhaust gas in the garage, which makes the detector work worse, but that's a different topic) and most importantly on the catalytic reactor (i.e. the catalyst). The catalytic converter, unless it is cut out at all, works properly only when it warms up to operating temperature.
    And now. We did research in garage halls and we had cases (not rarely) when the car emitted thousands of ppm well above the scale of measuring devices at a very fast pace. These are the cars that are to be "caught" by the detection system.
    If you were not in the garage, and your car will have such a defect and its emission will be very high, you can hit a deadly high concentration at the entrance to the garage. Just over 1% is enough for 2-3 breaths to end in death.
    https://en.wikipedia.org/wiki/Oxide_poisoning_w%C4%99gla
    Also, paradoxically, such a functional test can end fatally. Why are you inhaling those smells? It's a pity for the lungs because there's a lot of crap there.
    See this case: https://www.elektroda.pl/rtvforum/topic3430753.html
    I'm sorry, but the only valid detector test is with a dedicated test gas applied in the right way and under the right conditions. Any other games will in no way determine whether the device is working properly, and most of these games even lead to damage to the device, which is often invisible.
  • #25 17810764
  • #26 17810807
    Domelski
    Level 19  
    Help: 30
    Rate: 113
    I'm sorry, I'm honored.
    Somehow I didn't notice that "several seconds". :please:
    Of course, this type of normal exploitation will not kill anyone.
  • #27 17811521
  • #28 17811635
    BUCKS
    Help: 536
    Rate: 1087
    The one you bought has that option. This is a nice test to see if something bad happened, such as when we were away or when we slept.
    It is a pity that it does not show the date and time of occurrence of this concentration, and at most it tells us that the given result took place in the meantime since the last check of the highest concentration, when it was still 0, or since its deletion.
    Low concentration is not signaled with an alarm, but it can be seen on the display or read the highest value.
  • #29 17811666
  • #30 17811778
    piracik
    Help: 557
    Rate: 1977
    I can see my friend that you are very fond of me.
    Nowhere did I write that I perform tests under protocols.
    I don't calibrate the detectors and check them as you do as part of their inspections.
    I also do not have the signature of a specialist detectors, only heating systems, and these are probably two different fields.
    I only wrote how I check if the entire system, e.g. gazex, works. Whether the detector responds to gas, an alarm occurs and the valve closes. So I check for myself. I am not interested in the exact activation concentration because this measurement and calibration is within the scope of the service. Detectors are shipped every 2 years.
    There was no mention of earnings testing anywhere. Only from you.
    You got me a little confused here.
    I had the detector calibrated about two months ago. I had a pretty serious gas leak last week. The detector got 100% of the dose. Do I need to recalibrate it? How to avoid such situations in the future?
    Are smaller doses of such gas safe for the detector or can they also decalibrate or damage it?
The discussion revolves around methods to check the functionality of carbon monoxide and gas sensors. Users share various techniques, including placing the sensor near an open flame or using calibration gases. It is emphasized that carbon monoxide sensors react to improper combustion, while gas sensors detect specific gases like LPG and methane. Some users suggest using cigarette smoke or lighter gas for testing, although this is debated as potentially unreliable and harmful to the sensor. The importance of following manufacturer guidelines for calibration and testing is highlighted, with warnings against using makeshift methods that could damage the sensors. The conversation also touches on the activation thresholds for carbon monoxide detectors and the risks associated with improper testing.
TL;DR: 30 ppm CO should raise no alarm before 120 min, but 300 ppm must scream within 3 min [PN-EN 50291-1:2010]. “Only test with reference gas” [Elektroda, Domelski, post #16965083] Calibrate, don’t use lighters—full guide and DIY check below.
Why it matters: A mistested sensor can silently fail, leaving no protection against lethal carbon-monoxide or explosive gas leaks.
• EN 50291-1 alarm timing: 50 ppm 60–90 min, 100 ppm 10–40 min, 300 ppm <3 min [PN-EN 50291-1:2010] • Calibration gas canister (300 ppm CO, 100 L): approx. €25–40 [GasLab, 2023] • MOS sensor drift: 5–10 % per year [Figaro, 2021] • Kidde 10LLDCO: sealed 10-year lithium battery, peak-level memory [Kidde Datasheet, 2023] • Home CO/LPG detector price: PLN 100–200 [Allegro Price Scan, 2024]
Can I test a CO detector with lighter gas?
You can ignite a detector, but you should not. Lighter gas is 100 % v/v propane-butane—around 200 × the detector’s measuring range. Such overdosing can decalibrate or destroy the sensor, giving false security [Elektroda, Domelski, post #16965083] Manufacturers forbid “gases of uncontrolled concentration” [PN-EN 50291-1:2010].
What is the safe way to verify sensor operation at home?
Use a dedicated test-gas kit: 300 ppm CO in air for CO units or 10 % LEL methane for gas units. Clamp the hood, apply gas for the time stated (usually 30 s), confirm alarm, then ventilate [Elektroda, Domelski, post #20474332]
How do I run that test step-by-step?
  1. Clip the supplied test hood over the detector.
  2. Open the calibration-gas valve for 30 s.
  3. Wait for the alarm; note the response time, then remove hood and air the room. “Follow cylinder pressure and expiry dates,” reminds service techs [Elektroda, teko-2008, post #16264631]
Will cigarette smoke trigger a CO alarm?
Possibly. Cigarette smoke contains CO, but humidity and particulates also fool some semiconductor cells [Elektroda, Kot-huncwot, #13237605; Elektroda, Domelski, #18111095]. Smoke tests give no information about correct threshold calibration.
How often should I replace or recalibrate a home detector?
Replace electrochemical units every 7–10 years and perform functional tests yearly. Semiconductor sensors drift 5–10 % per year and need calibration every 12–36 months, as specified by the maker [Figaro, 2021; Elektroda, Domelski, #16965083].
What are the exact EN 50291 alarm thresholds?
30 ppm: no alarm before 120 min; 50 ppm: alarm 60–90 min; 100 ppm: alarm 10–40 min; 300 ppm: alarm within 3 min [PN-EN 50291-1:2010].
Is car-exhaust testing safe or accurate?
No. Cold engines may emit thousands of ppm CO, exceeding lethal limits after two breaths [Elektroda, Domelski, post #17810555] Exhaust tests risk poisoning and over-ranging the detector without proving correct low-level response.
Where should I mount sensors for LPG versus natural gas?
Mount LPG detectors 20–30 cm above the floor because propane-butane is heavier than air. Mount methane detectors 30 cm below the ceiling. Place CO detectors at head height, away from cooking steam [Elektroda, piracik, #13234340; PN-EN 50291-1:2010].
Does the Kidde 10LLDCO store peak readings?
Yes. Press “Peak” to display the highest recorded CO value since the last reset [Elektroda, Adamcyn, post #17811521] This helps diagnose intermittent leaks even when no audible alarm occurred.
How do humidity and temperature affect semiconductor detectors?
Rapid humidity shifts can cause false alarms, while high temperatures accelerate sensor drift. “Moist breath alone can trip some MOS cells” [Elektroda, Domelski, post #18111095] Keep within the 0–40 °C, 15–90 % RH range specified by makers [Figaro, 2021].
Do detectors record low-level events under the alarm point?
Some do. Models with displays log and show concentrations as low as 10 ppm. Although no siren sounds, the memory warns of chronic exposure [Elektroda, BUCKS, post #17811635]