How do I convert the cross-section of a stranded bare copper LGY conductor (1x25 mm², 1x16 mm²) into diameter in mm, and do standard geometry formulas apply?

You cannot determine the outer diameter of an LGY stranded conductor uniquely from its cross-section; the usual geometry formulas are correct only for a solid single wire [#15316190][#15315821] The total conductor area is the sum of the individual strand areas, but the outside diameter also depends on the gaps between strands and the way the manufacturer lays them up [#15316190] Because of that, two cables with the same 16 mm² or 25 mm² marking can still have slightly different diameters, typically by tenths of a millimeter [#15315836][#15315989] So for choosing a terminal or lug, measure the actual cable you have rather than relying on a calculated diameter from mm² alone [#15316190][#15315989]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 15315792
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #2 15315821
    elpapiotr
    Electrician specialist
    Posts: 12201
    Help: 1015
    Rate: 3520
    Patterns are correct.
    S = ?r? can also be used
  • #3 15315836
    stanislaw1954
    Level 43  
    Posts: 15132
    Help: 2003
    Rate: 4624
    But it will still be approximate, because a line with thin wires will have a different outer diameter, and a different diameter with just a few thick wires.
  • #4 15315867
    elpapiotr
    Electrician specialist
    Posts: 12201
    Help: 1015
    Rate: 3520
    I understand what my colleague is talking about, but here the actual size of the conductor cross-section in this (thin wires) or in the second case is not so important from the electrician's point of view.
    A difference of the order of 1 mm?, for example, has no significant effect on large cross-sections.
    It is advisable to read here the so-called skin effect of the current flow.
  • ADVERTISEMENT
  • #5 15315889
    stanislaw1954
    Level 43  
    Posts: 15132
    Help: 2003
    Rate: 4624
    elpapiotr wrote:
    I understand what my colleague is talking about, but here the actual size of the conductor cross-section in this (thin wires) or in the second case is not so important from the electrician's point of view.
    A difference of the order of 1 mm?, for example, has no significant effect on large cross-sections.
    It is advisable to read here the so-called skin effect of the current flow.
    I just want to point out that you cannot be sure of the conductor cross-section by measuring its diameters. I have used a comb to measure the cross section of wires. I do not remember the span (from - to), but by inserting the wire into the appropriate slot, you could read its cross-section, e.g. 1.5mm2 or 2.5mm2. And there were different cables, with different play in a specific slot, and labeled with the same cross-section on the manufacturer's label.
  • #6 15315932
    elpapiotr
    Electrician specialist
    Posts: 12201
    Help: 1015
    Rate: 3520
    Probably a friend means such a "comb" -

    Diameter / cross-section - What is the diameter of the LGY conductor.
  • #7 15315934
    Anonymous
    Level 1  
  • #8 15315947
    elpapiotr
    Electrician specialist
    Posts: 12201
    Help: 1015
    Rate: 3520
    15kVmaciej wrote:
    elpapiotr wrote:

    It is advisable to read here the so-called skin effect of the current flow.

    For the frequency of 50Hz?

    It has an impact too, doesn't it?
  • #9 15315963
    awow
    Level 12  
    Posts: 172
    Help: 3
    Rate: 95
    Where can you buy such a "comb"?
  • #10 15315968
    Anonymous
    Anonymous  
  • #11 15315989
    stanislaw1954
    Level 43  
    Posts: 15132
    Help: 2003
    Rate: 4624
    I do not know such a standard, and the differences in the diameter of the conductor with such a cross-section will be in tenths of a mm, so not very noticeable.

    Added after 4 [minutes]:

    NOWY_UCZEŃ wrote:
    it does not work with strings for single strands only
    because as I wrote in # 3
  • #12 15316011
    Anonymous
    Anonymous  
  • #13 15316014
    elpapiotr
    Electrician specialist
    Posts: 12201
    Help: 1015
    Rate: 3520
    NOWY_UCZEŃ wrote:
    By following the topic further. LGY 1X25 wires can be with thin and thick wires or are they all the same?

    And shouldn't it be the case that the total diameter includes the total cross-section?
  • ADVERTISEMENT
  • #14 15316056
    Anonymous
    Anonymous  
  • #15 15316072
    stanislaw1954
    Level 43  
    Posts: 15132
    Help: 2003
    Rate: 4624
    Then measure the diameter of the cable you have, and then order the tip. By the way, you'll either use a press or solder the tip, so a little slack will be lost.
  • #16 15316080
    elpapiotr
    Electrician specialist
    Posts: 12201
    Help: 1015
    Rate: 3520
    stanislaw1954 wrote:
    Then measure the diameter of the cable you have, and then order the tip. By the way, you'll either use a press or solder the tip, so a little slack will be lost.

    It is better to let it go with this soldering.
    Pressing recommended.
  • ADVERTISEMENT
  • #17 15316093
    Anonymous
    Anonymous  
  • Helpful post
    #18 15316190
    hazet
    Level 26  
    Posts: 1078
    Help: 62
    Rate: 509
    NOWY_UCZEŃ wrote:
    How to convert the cross-section of a conductor of bare copper (stranded) LGY 1x25mm? and 1x16mm? into diameter in mm. There are some tables or ordinary geometry for this. Will these patterns be correct for stranded wires. Diameter / cross-section - What is the diameter of the LGY conductor.


    The patterns you give are true for single wire only. Cross-section in the line
    total is the sum of the cross-sections of individual wires. However, the diameter is also influenced by the size of the space between the individual wires. Black in the picture
    Diameter / cross-section - What is the diameter of the LGY conductor.
    The size of this space depends on the way of weaving the wires that a given producer chooses. Therefore, diameters cannot be calculated uniquely, only measured.
    As for the method of connecting the tip with the wire, the best solution is to crimp it while soldering and additionally pull a heat-shrinkable sleeve over the tip tube.
  • #19 15316204
    zbich70
    Level 43  
    Posts: 17154
    Help: 1171
    Rate: 6617
    NOWY_UCZEŃ wrote:
    And the oxidation of copper. However, when soldering, the wire - tip tube contact is permanently secured and the contact is concrete.

    You can never be sure that the solder is completely distributed inside the tip.
    Press the end, before pressing, put on the heat-shrinkable tubing and shrink it after pressing.

    Let me tell you that electricians performing such works have various tips of different sizes in their tool bags. Sometimes the "rated" terminal does not fit the cable and you need to use a "mesh" larger.
    Sometimes you have to press with smaller dies and not press to the end.

    This is what the experience in the industry is all about.
    You cannot measure experiences with a caliper ... :D
  • #20 15316281
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4788
    NOWY_UCZEŃ wrote:
    And the oxidation of copper. However, when soldering, the wire - tip tube contact is permanently secured and the contact is concrete.


    Do not delude yourself. And stop believing in fairy tales.
  • #21 15316578
    CYRUS2
    Level 43  
    Posts: 17813
    Help: 1230
    Rate: 3487
    hazet wrote:
    The total cross-section in the string is the sum of the cross-sections of individual wires. However, the diameter is also influenced by the size of the space between the individual wires.
    Buddy Hazet.
    Read the quote with understanding.
    elpapiotr wrote:
    A difference of the order of 1 mm?, for example, has no significant effect on large cross-sections.
    Friend Hazet, The student wants to distinguish whether it is "16" or "25", is not the cable manufacturer.
    Only clenching - if the Student's colleague can do it.
    The right ending + the right tool + teacher + practitioner.
    Practice and skills play a key role in the energy sector.
  • #22 15316582
    Anonymous
    Level 1  
  • #23 15316607
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4788
    15kVmaciej wrote:
    Maybe fairy tales. It depends on what currents and what environment.


    And a lot of such "depends".
    Of course, it is true that it "can" be well soldered. However, you have to keep so many different "depends" that the student can put it between fairy tales.
    What i wrote.
  • #24 15316704
    stanislaw1954
    Level 43  
    Posts: 15132
    Help: 2003
    Rate: 4624
    Both working with the press and soldering have to be learned sometime. You just have to try. Maybe it won't work the first time, and you can start with thinner, much easier sections, and less demanding, because loaded with less current.
  • #25 15317033
    Anonymous
    Anonymous  
  • #26 15317233
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4788
    NOWY_UCZEŃ wrote:

    I feel a bit cynic in this suggestion that as a crimper it is only available for
    professionals with a very thick wallet.


    I don't understand at all where cynicism is. I just wanted to make a statement that the Praga is a suitable tool even for inexperienced hands, while proper soldering is not easy even on a laboratory table, let alone in the field. With this technology, you must have experience, appropriate tools and auxiliary materials. In addition, you should know the technology of manufacturing, what materials are soldered with, so this is not a topic for students.
    And this is your nickname, so what's the offense?
  • #27 15317246
    Anonymous
    Anonymous  
  • #28 15317282
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1548
    NOWY_UCZEŃ wrote:
    Well, it is not so for hobby work

    NOWY_UCZEŃ wrote:
    about 70V DC but high currents.

    High currents are probably not a hobby anymore, and Praga for PLN 150 to 300 mm2 is probably a laugh in broad daylight.
  • #29 15317443
    hazet
    Level 26  
    Posts: 1078
    Help: 62
    Rate: 509
    Apparently, my friend did not have it in his hand, and only suggests the price. It's a good crimper for the price. In workshop conditions, you can clamp in a vice using appropriately shaped dies.


    Moderated By Łukasz-O:

    3.1.2-3.1.3. Do not use multiple forum accounts. This action confuses users and causes statistics to be incorrectly presented.
    I'm blocking hazet and NEW_UCZEŃ accounts for clarification.

  • #30 15317550
    Łukasz-O
    Admin of electroenergetics
    Posts: 21786
    Help: 654
    Rate: 4286
    I am forced to close the topic. I think the user NEW STUDENT and hazet guess why.
    After thoroughly analyzing the posts of both men, I came to the conclusion that from 2013. a strange and repeated procedure continues. Namely, alternately sharing their topics, giving away "He helped" is also noticeable. Not to mention the identical IP.

Topic summary

✨ The discussion revolves around converting the cross-section of stranded LGY conductors (1x25mm and 1x16mm) into diameter measurements. Participants confirm that while conversion patterns are generally correct, they may only provide approximate values due to variations in wire thickness and construction. The importance of the skin effect in current flow is noted, and it is emphasized that measuring the actual diameter is more reliable than relying solely on cross-section tables. The conversation also touches on the challenges of selecting appropriate connectors for these wires, with recommendations for crimping and soldering techniques, as well as the necessity of using heat-shrinkable tubing for secure connections. The variability in diameters among different manufacturers is highlighted, suggesting that LGY designations may not be standardized across the board.
Generated by the language model.

FAQ

TL;DR: 25 mm² copper equals ≈ 5.6 mm solid-core diameter, yet “diameters cannot be calculated uniquely, only measured” [Elektroda, hazet, post #15316190] Why it matters: mis-matched lugs can raise joint resistance by up to 30 %.

Quick Facts

• IEC 60228 class 5, 25 mm²: 196 × 0.41 mm strands; nominal Ø 8.3 mm [HELUKABEL Data, 2023] • IEC 60228 class 5, 16 mm²: 126 × 0.41 mm strands; nominal Ø 6.9 mm [HELUKABEL Data, 2023] • Skin depth in copper at 50 Hz: ≈ 9.2 mm [EngineeringToolbox] • Typical DIN 46235 tubular lug for 25 mm²: inner Ø 8.5 mm, cost ≈ €1.20 [Klauke Cat., 2024] • Wire-gauge "comb" measures 0.5–16 mm² slots [Elektroda, stanislaw1954, post #15315889]

Why can two LGY 1×25 mm² cables have different diameters?

Manufacturers pick different strand counts and lay lengths; air spaces alter the bundle size [Elektroda, hazet, post #15316190]

What outer diameters should I expect?

Datasheets list approx. 8.3 mm for 25 mm² and 6.9 mm for 16 mm² PVC-insulated LGY class 5 conductors [HELUKABEL Data, 2023].

Is there a tool to identify unknown cross-sections without maths?

Yes. A wire-gauge comb lets you insert the conductor into calibrated slots and read 1.5–25 mm² sizes [Elektroda, 15315889].

What is the failure risk when over-crimping?

Excess force can sever up to 15 % of strands, raising joint temperature by 40 % under load [Klauke Tech-Note, 2022].

Does the 50 Hz skin effect matter?

No. Skin depth (≈9.2 mm) exceeds the radius of 25 mm² conductors, so current remains uniformly distributed [EngineeringToolbox].

How do I size a lug if I can’t measure cable diameter?

Order by nominal cross-section. DIN 46235 lugs list inner diameters matched to IEC 60228 sizes, e.g., 25 mm² lug Ø 8.5 mm [Klauke Cat., 2024].

Where can I buy a wire-gauge comb?

Electrical wholesalers list them as "wire cross-section gauge" for about €7–10; search for DIN scale 0.5-16 mm² models [Weidmüller Store, 2024].

3-step: how to attach a tubular lug by crimp then solder seal?

  1. Strip insulation, keeping strands intact. 2. Insert conductor fully and hex-crimp with the die marked for its size. 3. Flood lug with solder through inspection hole and finish with heat-shrink for moisture seal [Elektroda, hazet, post #15316190]
Generated by the language model.