[Solved] Connecting 4-5kW 1-Phase Induction Hob in 10-Story Block with Single Phase Installation

Elektromaciek 31140 40
Best answers

Can I connect a 4–5 kW induction hob to a single-phase apartment installation without bringing in three-phase power?

Yes, but only if you choose a hob intended for single-phase supply and wire it as a dedicated circuit. For a new run, the thread recommends at least 5x2.5 mm² to a single-phase socket/box; a socket-and-plug connection is treated as 16A and 2.5 mm² is fine for that, while a permanently connected hob does not require an RCD [#17767797][#17767886][#17771249] The replies also caution against buying high-power popular hobs over 7 kW in this situation, and suggest power-limited or about 3.5 kW models if you want a simple plug-in setup [#17771249][#17769313] If you want to keep the apartment future-proof, make the board larger and leave spare ways for additional circuits [#17767768][#17769767] Also check with the utility and building manager, because the riser may already be three-phase even if your flat is currently fed single-phase [#17774389][#17774774]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17767706
    Elektromaciek
    Level 11  
    Posts: 17
    Rate: 3
    Hello

    I have read a lot of topics regarding induction in the apartment, some say that the induction is not in one phase, others that it is possible to connect, but each time there are different cases and I would ask for a hint from experienced people regarding my problem.

    1. 10-story block
    2. Wires connected to flats 4-5 years ago 4mmkw copper 3 conductors.
    3. Single phase installation
    4. Connection power 5.7kW
    5. 25A pre-meter protection
    6. The entire electrical installation in the apartment will be replaced - still 1-phase.

    The question is whether, taking into account the above points, it is possible to connect an induction plate powered with 1 phase (probably a plate around 4-5kW) so that there is no need to supply a 3-phase power supply to the apartment?

    I would like to add that at the moment (and probably for the next few years it will not change), the album will not be used much, I hardly use it myself, or in the future if something was to change then I would rather not worry, but I do not assume that I will suddenly be cooking big lunches on 4 burners at the same time.
  • ADVERTISEMENT
  • #2 17767749
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4262
    After all, there are plug and play induction hobs that the manufacturer has equipped with a cord with a plug.
    In addition, there is always an increase in power to 7kW.
  • #3 17767758
    Elektromaciek
    Level 11  
    Posts: 17
    Rate: 3
    You know, I was focused on induction, the more I started to read (e.g. on the electrode), it seemed to me more and more impossible and many people said that without the 3 phases it was only a gas stove, so I was losing hope and preferred to inquire about it a specific case, i.e. without a combination with 3 phases, it is enough to increase the connection power to 7kW and a good installation? what cable then from the switchgear to the induction would the electrician lay? 3x4mmkw?

    (thank you for the answer kkas12)
  • ADVERTISEMENT
  • Helpful post
    #4 17767768
    lechm56
    VIP Meritorious for electroda.pl
    Posts: 3033
    Help: 112
    Rate: 366
    In my humble opinion, nothing will happen if you add a few zlotys and pull a few cables, e.g. 5x 2.5mm2 and 5x4mm2, and in the fuse box you leave a few empty places for additional security.
  • #5 17767791
    Elektromaciek
    Level 11  
    Posts: 17
    Rate: 3
    The issue of finances is secondary, so I will definitely consider adding a 5x cable as you suggest, I do not know about installations, so I preferred to ask, so far it does not promise to connect 3 phases and I just wanted to know if there is a possibility to connect this board on 1 phase, but I also did not think to add a cable with one robot, as if something changed in the future. (thanks for showing interest)
  • Helpful post
    #6 17767797
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4262
    Elektromaciek wrote:
    what cable then from the switchgear to the induction would the electrician lay? 3x4mmkw?

    If you have a separate circuit, nothing needs to be added.
    If, however, you will arrange a new one, follow what your colleague wrote above and arrange at least 5x2.5mm2. It may be useful in the future.
    However, in this case it may be necessary to replace the fuse board due to insufficient space for the new fuse.
    And attention, if the board will be connected with a socket and a plug, it requires a residual current device.
    If it is permanently connected, the RCD is not required.
  • #7 17767856
    Elektromaciek
    Level 11  
    Posts: 17
    Rate: 3
    I think I already know everything, thanks a lot for the answers, I just think about the last post and I will be clear.

    All wires in the whole apartment will be new + new fuse board in the apartment from which the wires will go, I planned to permanently connect the induction to a surface-mounted "box" (such a hermetic square).

    Assuming that at the moment we stay with the 1st phase and we only increase the connection power to 7kW, the 5x2.5 cable is enough instead of 3x4 (this is what I assumed now for a 1-phase power supply for electricians to pull from the board) because I understand that at 5x2.5 - 2 the phase wires are not connected (in reserve), and we connect only 1phase + N + PE? in this case, 2.5 will not be too weak?
  • Helpful post
    #8 17767886
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4262
    Buddy, the socket and plug load are 16A.
    For a cross section of 2.5mm2, this value is not a threat.

    But the condition is to buy a board with a plug, i.e. dedicated to single-phase power supply.
  • #9 17769264
    waldekwiąz
    Level 11  
    Posts: 30
    Help: 1
    Rate: 8
    Gentlemen. The power supply cable for the apartment can withstand a maximum of 27A, the 5 kW cooker itself will generate 21A on one phase (with all fields turned on), and what about the dishwasher, washing machine and other equipment? 5x4mm2 is the minimum for the apartment connection.
  • #10 17769313
    Zbigniew 400
    Level 38  
    Posts: 4356
    Help: 283
    Rate: 791
    You should buy a CD with a limited maximum power consumption.
    Or the declared 3.5 kW.
  • #11 17769343
    wacek.wacek
    Level 29  
    Posts: 1635
    Help: 98
    Rate: 281
    Priority relays.
  • #12 17769367
    Zbigniew 400
    Level 38  
    Posts: 4356
    Help: 283
    Rate: 791
    Relays don't do the trick.
  • ADVERTISEMENT
  • #13 17769377
    wacek.wacek
    Level 29  
    Posts: 1635
    Help: 98
    Rate: 281
    But they'll drop the load. Wogole is a dream come true with such low power to pack into induction. And how do you know that it will be possible to buy additional power block. The 3.5 kw album is a failure. I always do 5x4 induction, and I don't play carvings.
  • #14 17769385
    Zbigniew 400
    Level 38  
    Posts: 4356
    Help: 283
    Rate: 791
    And are you using a CD?
    I have installed the boards in blocks and with a 3.5kW limitation there is no problem in use.
  • #15 17769387
    Elektromaciek
    Level 11  
    Posts: 17
    Rate: 3
    I am aware that the optimal solution would be a 3-phase power supply, but at the moment and in the next 3-5 years it will not be possible, I would like to give up gas and therefore this induction, I know that it will not work with full power, but also until it will be possible to connect 2 more phases, then on this plate will be placed: a pot to boil potatoes, cook rice, "vegetables with chicken from the pan", scrambled eggs ... ).

    (PS: when I watch something, I watch the conversation all the time)
  • #16 17769391
    Zbigniew 400
    Level 38  
    Posts: 4356
    Help: 283
    Rate: 791
    I have a phone number for the lady who uses the disc in this way?
  • #17 17769392
    wacek.wacek
    Level 29  
    Posts: 1635
    Help: 98
    Rate: 281
    Zbigniew 400, I agree with you. In general, I very rarely do anything in blocks. I personally do not have induction. But I have derived a 5x4 induction from a 5x10 power supply and bought 22kW. I don't think he should be saving on cables. If I had "W", I would put priorities.
  • #18 17769409
    Zbigniew 400
    Level 38  
    Posts: 4356
    Help: 283
    Rate: 791
    Priority doesn't do the trick, just power limitation.
  • #19 17769410
    Elektromaciek
    Level 11  
    Posts: 17
    Rate: 3
    I would like to add that there is no question of saving, as I mentioned, finances are a secondary issue, the installation in the block was replaced about 4-5 years ago, unfortunately they did not think that someone might want to have 3 phases in the apartment and they let 3-wire cables on 10 floors, on at this moment, the apartment is "bare" and the entire installation, including the security board, will be replaced for the entire apartment.
  • #20 17769414
    wacek.wacek
    Level 29  
    Posts: 1635
    Help: 98
    Rate: 281
    There will be no miracles on a four-wire power supply.

    Added after 7 [minutes]:

    I will ask professionals what methods you have zero for induction in a can. I twist soldering for fear of losing zero.
  • ADVERTISEMENT
  • #21 17769476
    Zbigniew 400
    Level 38  
    Posts: 4356
    Help: 283
    Rate: 791
    Elektromaciek. If many tenants wanted 3 phases, will the power supply of the building last?
  • #22 17769487
    Elektromaciek
    Level 11  
    Posts: 17
    Rate: 3
    Perhaps this is the reason why these 3 phases do not exist? I have no idea, I thought that the electricity supplier / electricity supplier could provide "electricity" for a given demand, for 10 floors, probably 10-15 apartments would be under 3-phase, maybe it is too many users, unfortunately, that's why I wrote a question with a request for advice from smarter people, because I don't know myself.

    Edit: Because as I mentioned, the installation was replaced not so long ago (meters, wires ...) in the entire building, so if it was physically possible to bring the right "amount" of electricity to the building and its security, they could replace the installation so that these 3 phases could be installed in the future.
  • #23 17769526
    Anonymous
    Anonymous  
  • #24 17769611
    CYRUS2
    Level 43  
    Posts: 17636
    Help: 1221
    Rate: 3446
    Elektromaciek wrote:
    on 10 floors, they let out 3-core wires, at the moment the apartment is "bare" and the entire installation, including the security board, will be replaced for the entire apartment.
    Because it's cheaper, they did as it was before the replacement of the WLZ.
    I know such blocks where there is one phase per 10 floors.

    Communities and Cooperatives combine so that if you want 3 phases, you have to run WLZ through X floors to RG.
    It was like that with my daughter - she lives on the ground floor. WLZ-th 3f replaced.
    And so, against ZE, they ordered to pull the cable to RG.
    In RG they gave this place dedicated fuses.
    Of course, there is also a conversion factor on the first floor.
  • #25 17769646
    Brivido
    Level 34  
    Posts: 2845
    Help: 224
    Rate: 425
    And where are the WLZ conducted? Isn't that the kind of board where you have shafts with a meter and a switchboard between the toilet and the bathroom? It would be worth considering in such a way that the possible replacement of the WLZ would not require breaking the whole flat anew.
  • #26 17769655
    Elektromaciek
    Level 11  
    Posts: 17
    Rate: 3
    The connection to the apartment runs through the corridor about 7-8 meters and is led above the entrance door, there is also a switchgear with security, also if they let 3 phases, only a photo of the switchboard will be needed and the wire will be pulled, but I doubt that this will change quickly because the corridors are renovated , coats, lining of entrance doors to apartments, lights on the motion sensor, also rather under 3 phases, they will not scratch the walls quickly.
  • Helpful post
    #27 17769767
    Brivido
    Level 34  
    Posts: 2845
    Help: 224
    Rate: 425
    So ok, anyway, it is enough to drill through the wall if what. I would just buy a larger switchboard for the future and make more circuits ;)
  • #28 17771195
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    Elektromaciek wrote:
    The connection to the apartment runs through the corridor about 7-8 meters and is led above the entrance door, there is also a switchgear with security, also if they let 3 phases, only a photo of the switchboard will be needed and the wire will be pulled, but I doubt that this will change quickly because the corridors are renovated , coats, lining of entrance doors to apartments, lights on the motion sensor, also rather under 3 phases, they will not scratch the walls quickly.

    And you can't lead the power line in the surface-mounted trough?
  • #29 17771208
    Elektromaciek
    Level 11  
    Posts: 17
    Rate: 3
    I will ask, but I did some research and a difficult topic, in the block there is a generation change slowly, but still most of them are older people and, unfortunately, the manager is focused on them, they all have junkers + gas stove and when I asked about the possibility of supplying the apartment with 3 phases, it was not literally but I got the answer that it is a pity for one apartment, I do not know if they do not tell everyone, because for sure some younger tenants would be willing, but so far the managers, due to the age of tenants, are more interested in putting a bench under the block and planting 3 Christmas trees than parking for residents or 3 phases in apartments.
  • #30 17771238
    kkas12
    Level 43  
    Posts: 17356
    Help: 1073
    Rate: 4262
    I can not find if you wrote where the counter is located?
    And somehow I don't feel like believing that all the premises are powered by the same phase.

Topic summary

✨ The discussion revolves around the feasibility of connecting a 4-5kW induction hob in a 10-story apartment block with a single-phase electrical installation. The user seeks advice on whether it is possible to operate the induction hob without upgrading to a three-phase supply, given the existing 4mm² copper wiring and a 25A pre-meter protection. Responses highlight that while it is technically possible to connect the hob on a single phase, it may require upgrading the wiring to a 5x2.5mm² or 5x4mm² configuration to handle the load safely. Some participants suggest using a dedicated circuit and a residual current device (RCD) if a plug is used. Concerns about the overall power capacity of the building and the potential need for future upgrades to three-phase power are also discussed, with recommendations to consult with the building manager and the electricity supplier for possible solutions.
Generated by the language model.

FAQ

TL;DR: A 4 kW single-phase induction hob pulls ~17 A at 230 V; “the socket and plug load are 16 A” [Elektroda, kkas12, post #17767886] That fits on 2.5 mm² copper if a dedicated breaker and RCD are used. Upgrade to 3-phase or 7 kW contract when cooking intensifies.

Why it matters: Correct cabling and contract choice prevent tripped breakers and overheated wires in retro-fitted apartments.

Quick Facts

• Typical Polish apartment supply: 5.75 kW, 25 A single-phase [Elektroda, Elektromaciek, post #17767706] • 2.5 mm² Cu cable in plaster = 20–24 A rating (IEC 60364-5-52). • 4 kW hob ≈ 17.4 A at 230 V (P=UI). • Contract upgrade to 7 kW costs ≈ 11 PLN/kW yearly fee [PGE Tariff 2023]. • 3-phase riser already present in photo evidence [Elektroda, Elektromaciek, post #17774246]

1. Can I connect a 4–5 kW induction hob on my existing single phase?

Yes, if your main fuse is at least 25 A and you use a dedicated 2.5 mm² or larger circuit. A 4 kW hob draws 17 A, leaving only 8 A headroom for lights or small loads [Elektroda, kkas12, post #17767886]

2. What cable size should run from the fuse board to the hob?

Install 5×2.5 mm² copper. It meets the 20 A rating, fits a 16 A plug now, and carries three phases later [Elektroda, kkas12, post #17767797]

3. Do I need to boost my contracted power to 7 kW?

If you will sometimes run two large burners together, yes. A 7 kW limit raises the main fuse to 32 A, preventing nuisance trips [Elektroda, kkas12, post #17767749]

4. Will a standard 16 A socket survive continuous hob use?

For a power-limited hob (≤3.5 kW) it is fine. At 4 kW you approach the 16 A steady limit; pick a high-quality heat-resistant socket and check tightness yearly [Elektroda, waldekwiąz, post #17769264]

5. What happens if I cook while the dishwasher or kettle runs?

Loads add. Hob 17 A + dishwasher 10 A + kettle 10 A = 37 A. A 25 A fuse will trip within minutes [IEC 60255].

6. How do I verify if three phases reach my floor?

Open the unsealed busbar box above the meters. Measure phase-to-phase voltage; 400 V confirms 3-phase presence [Elektroda, kkas12, post #17771314]

7. What are priority (load-shedding) relays, and do they help?

They disconnect the hob or boiler when current exceeds a set value. Useful below 25 A but cannot raise available power [Elektroda, wacek.wacek, post #17769343]

8. How do I apply for a 3-phase upgrade?

  1. File a demand-increase form with your DSO (ZE).
  2. Get manager’s consent for riser work.
  3. Hire a licensed electrician to pull 5×4 mm² from riser to apartment and replace the main breaker [Elektroda, CYRUS2, post #17774774]

10. What is the worst-case failure if neutral is lost on a shared riser?

Unequal phase voltages can surge to 400 V, destroying electronics within milliseconds; induction boards rarely survive this event [Schneider App Note ANP-110].

11. Can I limit a hob to 3.5 kW myself?

Many models have a service menu: hold ‘+’ and ‘–’ for 10 s, pick ‘PL3.5’. Check the manual; limits range 1–7 kW [Bosch PIE631FB1E Manual].

12. Three-step wiring future-proof plan

  1. Run 5×2.5 mm² to hob box.
  2. Terminate L2 and L3 safely for now.
  3. Install a 3-pole breaker and larger board space for later expansion [Elektroda, lechm56, post #17767768]