Kolego @ kamyk828 You have not written anything about the deployment of the installation. While your distributor system is below the level of the heated kitchen floor, you have 100% aerated kitchen coil and heating will not work. The solution to the problem is to mount additional vents at the kitchen floor level. If you have access to the heating tube at the level of the kitchen floor, the easiest way to cut this pipe is to insert a tee, connecting the cut pipe and to the third stub, install a vent such as a radiator and point it up. It gives the possibility of venting the system and its operation. Air bubbles cause a significant flow resistance, which, combined with the length of the loop, prevents any flow.
While this green hose connected to the bottom beam serves to complete the system, try loosening the loop tube on the top bar and unscrewing the water supply and you will find out that I am right with this aeration while venting partially the loop.
As Kolega @Andrzej_;) lukaszewicz wrote, increase the temperature on the intake to at least 60 degrees, close the other radiators and set the pump to max efficiency. If you manage to vent the loop, after about 30-60 min you should notice an increase in the floor temperature.
Personally, I'm not a fan of mixing valves. According to me, it is more reasonable to use each loop of RTL valves on the outlet or in the case of "unheated" as I used ordinary thermostatic radiator valves mounted on the intake of each loop with a capillary mounted on the return of the appropriate loop which works and is much cheaper allowing to regulate each loop separately - checked.