Circuit board diagram for Auraton 2025RTH - wanted.
wandrzej19 1782 4
  • #1 16203367
    wandrzej19
    circuit board schematic
    A sentence begins with a capital letter.
    A FULL STOP IS PLACED AT THE END OF A SENTENCE, A SENTENCE EQUIVALENT, OR A STATEMENT THAT CONSTITUTES A SEMANTIC AND SYNTACTIC WHOLE.
    3.1.15. Publish entries presenting a problem without providing sufficient information to enable other forum Users to take a substantive stance. The title of the entry should contain the make, model and a brief description of the fault.
  • #2 16203533
  • #3 16206047
    wandrzej19
    I have an Auraton 2025 Rth wireless regulator .The regulator connects to the receiver correctly. The red LED lights up indicating operation , but the output relay contacts do not switch .The voltage on the relay coil at this time is about 15V. The nominal voltage from the description on the relay is 24V DC. The symptom is that sometimes the relay switches in the horizontal position on the table .When mounted on the wall it does not switch on.
  • #4 16206901
  • #5 16208803
    wandrzej19
    After checking the capacitors ;
    1 microfarad - 250 V had a capacitance of approximately 0, 83 microfarad
    0.68 microfarad - 250 V had a capacitance of 0.32 microfarad .
    After replacing this capacitor 0,68 - everything is working properly. The voltage on the relay coil has increased to 22 volts .
    Thank you for your advice .The topic no longer exists.