Renovating Kitchen: 3-Phase Cable Distribution, Induction, Dishwasher, Oven and 230V Socket

Karwos00 13437 25
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16209523
    Karwos00
    Level 12  
    Hello

    I am in the process of renovating the kitchen and my distribution of receivers will change a bit. I have a few questions about this:
    1. 3-phase cable - normally the oven 230, induction 230 + dishwasher was connected to it.

    Now it's supposed to be induction + Dishwasher.
    Induction - maybe I would finally connect it to 2 phases. Dishwasher - standard -230

    I've seen mini switching stations in building warehouses - for a 3-phase socket + 1-phase socket. Or maybe there are switchboards for a 2-phase socket (for induction) + 1-phase socket - for a dishwasher. Is such a separation of phases on a common neutral and grounding a correct action?? Are additional protections applied in such switchgears? I mean something like this:

    https://www.obi.pl/plugs-and-gniazda/socket-typu-kombi-tk-cee-5-biegunowe16-a/p/6028393



    The second thing is to connect the oven. In the place where it is supposed to be, there is a socket 230.
    But here the fridge + microwave + this unfortunate oven is to be connected. It is known that the oven will not work together with the microwave - maybe with a few exceptions - but does such a connection make sense.
    Will I have to pull another 230V section unfortunately?

    Or is there any other solution?
  • ADVERTISEMENT
  • #2 16209564
    Wojtek 2007
    Level 12  
    First, what do you mean by "2 phase socket"?
    Secondly, so many devices on one circuit is a bit of an exaggeration, unfortunately you will have to lead a new circuit to the kitchen.
  • #3 16209601
    Karwos00
    Level 12  
    The unprofessional term is my 2-phase socket. Generally, I mean connecting the induction not to the cube, but to some kind of socket - e.g. 4-pin - 2 phases + zero + earth - if they are.

    Added after 13 [minutes]:

    I found one more interesting thing in the kitchen - a can - and a grounding wire in it - a cable comes out of it and comes out of the can and wraps a pipe with hot water - rather not to insulate this cable :)

    Of course, I'm interested in the sense of such an old-fashioned solution - whether it can be improved in a simple and correct way. Or maybe leave such a PRL solution as a history museum.
  • #4 16209666
    kkas12
    Level 43  
    This is not an old-fashioned solution.
    This is an equalizing connection that you should not touch.
  • #5 16209683
    Wojtek 2007
    Level 12  
    The two-phase board should be connected straight to the box or through a 400V "power" socket, where you leave one phase contact unconnected. Out of curiosity, what cross-section has the already routed cable and what protection has been used?
  • #6 16209694
    zbich70
    Level 43  
    kkas12 wrote:
    This is an equalizing connection
    ,
    Or earth through a pipe.
    kkas12 wrote:
    that you shouldn't touch.

    And all the rest too.
  • ADVERTISEMENT
  • #7 16209712
    Karwos00
    Level 12  
    It's like this:
    Connecting to the tube - I should probably improve some clamp - a wire wrapped on an old tarnished tube is not a professional solution.

    3-phase cable - what cross-section - I have no idea - black thick cable (like a finger) 5-wire :)

    And the security - what kind of security are you asking about?
    Earlier games with electricity were made by an unspecified person - and now that I have thrown everything out of the kitchen, I know what is there - but I understand that there should be a fuse when connecting the induction there?

    Added after 2 [minutes]:

    I will ask again - if I use a mini switchgear - for a 3-phase socket - with one free pin. Can this third phase be used for an additional 230V socket on a common neutral and ground?

    Added after 5 [minutes]:

    Back to the type of 3-phase cable. I think it's 5x2.5
  • #8 16209757
    polaklbn
    Level 24  
    Karwos00 wrote:
    common neutral and ground?
    either zero or neutral and protective. Tell us friend what network system you have, how thick the power cord is and what protection is installed on this circuit.
  • #9 16209774
    Karwos00
    Level 12  
    Ok - neutral and protective.
    Circuit breaker S - 193 B16.
  • #10 16209998
    Wojtek 2007
    Level 12  
    What's your network layout? TN/TT?
  • #11 16210006
    Karwos00
    Level 12  
    Unfortunately, I don't even know how to check it and rather I won't check it at home.

    It is a block of flats probably built 20-25 years ago.
  • #12 16210130
    mawerix123
    Level 39  
    Karwos00 wrote:
    Generally, I mean connecting the induction not to the cube, but to some kind of socket


    Since there is a cable terminated with connectors without a plug, this device cannot be connected to the installation using a socket and a plug.

    Karwos00 wrote:
    Connecting to the tube - I should probably improve some clamp - a wire wrapped on an old tarnished tube is not a professional solution.


    Here you go, an example clamp --> https://onninen.pl/pl-PL/obejma-uziemniajaca-...wany-tasma-braz-5057507-obo-bettermann,HDF524
  • #13 16210144
    Karwos00
    Level 12  
    Ok - the induction is done
    Dishwasher - can it be easily connected to one of the phases of the cable.
    I do not hide that earlier each phase was on a different device - on induction (for 1 phase) + oven + dishwasher.
  • ADVERTISEMENT
  • #14 16210157
    CYRUS2
    Level 43  
    Quote:
    it comes out of the can and wraps a pipe with hot water - rather not to insulate this cable
    kkas12 wrote:
    This is an equalizing connection
    zbich70 wrote:
    Or earth through a pipe.
    Neither one nor the other, just some kind of partisanship.
    kkas12 wrote:
    that you shouldn't touch.
    He definitely can't stay like this.
  • #15 16210182
    kkas12
    Level 43  
    Sure not. There are grounding straps for this, which were probably not at hand during assembly.
    But it can also be as Zbich writes. However, it won't work from a distance.
  • #16 16210186
    Karwos00
    Level 12  
    I strongly agree with the above statement. Especially since I saw such solutions probably 25 years ago.
    Just what to do with it.
    You can see that this box with the protective cable has been specially placed there only for this one cable.

    Added after 1 [hours] 6 [minutes]:

    I have another aesthetic question.

    Since I already have this cable from the wall, 5 cores and 2 phases are to go to induction and 1 to, say - a standard socket - can it be somehow aesthetically connected and not with cubes that will be closed in a box. In addition, according to the rules, there should still be a differential - maybe there are some ready-made small boxes / switchboards as in the first post - a combi socket. Something not big that will sit behind the furniture - behind the drawers. Even if the differential broke, you could turn it on.
  • #17 16210432
    Wojtek 2007
    Level 12  
    This differential is to be in the switchgear and cover all circuits in the apartment. When was the circuit to the oven conducted?
  • ADVERTISEMENT
  • #18 16210460
    Karwos00
    Level 12  
    So I have something like that :) Once someone mentioned to me that the differential should be with induction - I did not delve into the topic and induction worked for 8 years.

    And when it comes to the oven - it was always connected to 1 phase from a 3-phase.

    Now the plan is to connect to a normal socket (change of position) - only that there is probably 1.5mm - Will I have to run another circuit under the oven in this case?
  • #19 16210466
    CYRUS2
    Level 43  
    Karwos00 wrote:
    You can see that this box with the protective cable has been specially placed there only for this one cable.
    The wire is yellow-green, it does not mean that it is protective.
  • #20 16210489
    Karwos00
    Level 12  
    In this installation, I happened to have it as a phase in several sockets - it's like connecting sockets in series at random and yellow-green becomes a phase .... And in one of the sockets the phase was on the pin.
    Joyful creativity knows no bounds.
  • #21 16210827
    CYRUS2
    Level 43  
    Karwos00 wrote:
    Joyful creativity knows no bounds.
    Karwos00 wrote:
    that's how it is series connection of sockets happens at random
    The text is just fun.
  • #23 16212938
    Karwos00
    Level 12  
    What's fun about this text?

    As for the N - Well, that's what bothers me too.
  • #24 16214890
    Adam_Bandit
    Level 20  
    The fact that it is a serial connection only in your opinion, these sockets are 100% connected in parallel.
  • #25 16215089
    Karwos00
    Level 12  
    I would not exaggerate with these percentages - but if you are so sure of it, please explain - I take out the socket 1 in the room - and the tick has no electricity in any other. It would be nice if it was a parallel connection and the sockets were connected separately to the main "mainstream", but unfortunately this is not the case - someone was happily running other wires from one socket to the next sockets, then broke through the wall and continued happily in the next room. For the latter to be returned to the counter, it would be a problem - but in Poland this type of connection is not used? (but here I'm not sure - or rather, I don't know).
  • #26 16215163
    Akrzy74
    Rest in Peace
    zbich70 wrote:
    Or earth through a pipe.

    There is no such thing as an earth electrode through a pipe!
    Karwos00 wrote:
    or maybe there are switchboards for a 2-phase socket (for induction) + 1-phase socket - for a dishwasher.

    They never existed! Do you know what a switchboard is?
    Karwos00 wrote:
    I am in the process of renovating the kitchen

    Ad-rem - separate circuits for "induction", oven and microwave (all approx. 2 kW), especially at the renovation stage! The so-called sockets "two-phase" does not exist. No diagram, wire cross-sections, protection characteristics, network layout, SPD protection of equipotential bonding...

    I remind you - Electrics, Installations and Networks section. -> read the description of the section.

Topic summary

The discussion revolves around the renovation of a kitchen's electrical distribution system, specifically focusing on the integration of a 3-phase cable for an induction cooktop, dishwasher, and oven. The user seeks advice on connecting the induction cooktop to two phases and the dishwasher to a standard 230V socket. Concerns are raised about the adequacy of existing wiring, the need for proper circuit protection, and the potential use of mini switchgear for managing the connections. Participants emphasize the importance of adhering to electrical standards, ensuring proper grounding, and the necessity of separate circuits for high-power appliances. The conversation also touches on the historical context of existing wiring solutions and the need for modern upgrades to ensure safety and compliance.