Ariston Velis 50L Boiler: Leaking Safety Valve During Heating - Causes and Solutions

blachunter 53973 32
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 16321093
    blachunter
    Level 11  
    What diaphragm vessel should I wear? and in what place? At the boiler itself, it falls off because it is a bathroom and there is no space.
  • ADVERTISEMENT
  • Helpful post
    #32 16325555
    triakw
    Level 18  
    No matter where, it can be on the hot water pipe. The dish should be white [food] The safety valve is a non-return valve.
  • #33 16364522
    blachunter
    Level 11  
    Hello, today there was a plumber and he installed a diaphragm vessel and everything is ok. The pressure in the installation has dropped from 8.5 bar to 5, so nothing drips anymore :) . Thank you all for the suggestion. Topic to be closed.

Topic summary

The discussion revolves around a leaking safety valve in the Ariston Velis 50L boiler, which occurs during the heating process. Users suggest that the issue may stem from high water pressure in the system, leading to the valve's activation. Recommendations include measuring the system pressure, installing a pressure reducer, and potentially adding a diaphragm vessel to accommodate thermal expansion. The author reports that after installing a diaphragm vessel, the pressure dropped significantly, resolving the leaking issue. The conversation highlights the importance of maintaining appropriate water temperatures and pressure settings to prevent valve leaks.