Hello,
the safety valve in my installation leaks. A standard problem can be said, but I would like to advise you and resolve this issue. Maybe I'll start with the installation description:
- terraced house, installation made about 9.5 years ago.
- Vitodens 200 with Vitocell 100 (120L).
- safety valve Syr 6 bar 3/4 ", Reflex vessel 8L, all kinds of valves.
Here are the photos:
About two years ago I noticed (it may have been before, but I just didn't pay attention) that the valve is leaking. I removed the insert and cleaned it, but it did not help. It was quite stony, so I thought it needed to be replaced. It was some over 1.5 years ago. I bought a new one, it seemed better for some time. But it is still leaking. I have a pressure gauge, so at the time I mentioned, I noticed that the pressure in the network was higher than at the beginning of residence. I wrote to the waterworks asking how it is and whether it has increased. I got the answer that they were modernizing and hence the pressure is higher, from 4.8 to 5.4, although as the pressure gauge (photo) shows is even higher at night. Thus, according to the valve manufacturer's specifications:
"The permissible tolerance for safety valves is + 10% and -20%. This means that the valve with a setting pressure of 6 bar will open fully at 6.6 bar, but will close at the latest when the system pressure drops to 4.8 bar In order to ensure proper operation of the system, the maximum pressure in the system must be at least 20% lower than the safety valve setting pressure to prevent the open valve from closing completely (continuous leakage of water from the valve which ends in damage to the valve seal). "
As I understand, de facto the valve may leak, because the network pressure is often higher than 4.8 bar, right? And even without heating? Hence the questions:
1. What is the best way to do this? Apply a reducer? Or maybe I could, for example, replace the valve with a higher denomination, e.g. 7 bar? I checked the instructions from the heater, and this says about the permissible operating pressure of 10 bar, does it mean that the valve can have a higher setting?
2. If the regulator, what pressure should be set? And what reducer or are those from Syra good? The problem may be with the place where to insert it, because the entry of water into the house is in the garage and on the pipes there is not much space.
I have to do something because I can't have an ever-wet boiler room. And draining water from the valve, as you can see, I do not have.
And one more thing - a diaphragm vessel. I used to check the pressure in it (I turned off the water supply, turned on the water at the nearest point so that there was no pressure and in such conditions I pumped up and measured) and pumped up to 4 bar, because it was a bit smaller. The dish looks ok, no water flowed from the valve when I pressed it. What worries or wonders me is that if you turn on the water somewhere in the house and "close" the battery, the needle on the pressure gauge jumps. You can hear such a blow on it, and as I understand thanks to the dish, it should not be like this. What is going on?
Thanks in advance for any answers,
greetings,
grzesiek
the safety valve in my installation leaks. A standard problem can be said, but I would like to advise you and resolve this issue. Maybe I'll start with the installation description:
- terraced house, installation made about 9.5 years ago.
- Vitodens 200 with Vitocell 100 (120L).
- safety valve Syr 6 bar 3/4 ", Reflex vessel 8L, all kinds of valves.
Here are the photos:


About two years ago I noticed (it may have been before, but I just didn't pay attention) that the valve is leaking. I removed the insert and cleaned it, but it did not help. It was quite stony, so I thought it needed to be replaced. It was some over 1.5 years ago. I bought a new one, it seemed better for some time. But it is still leaking. I have a pressure gauge, so at the time I mentioned, I noticed that the pressure in the network was higher than at the beginning of residence. I wrote to the waterworks asking how it is and whether it has increased. I got the answer that they were modernizing and hence the pressure is higher, from 4.8 to 5.4, although as the pressure gauge (photo) shows is even higher at night. Thus, according to the valve manufacturer's specifications:
"The permissible tolerance for safety valves is + 10% and -20%. This means that the valve with a setting pressure of 6 bar will open fully at 6.6 bar, but will close at the latest when the system pressure drops to 4.8 bar In order to ensure proper operation of the system, the maximum pressure in the system must be at least 20% lower than the safety valve setting pressure to prevent the open valve from closing completely (continuous leakage of water from the valve which ends in damage to the valve seal). "
As I understand, de facto the valve may leak, because the network pressure is often higher than 4.8 bar, right? And even without heating? Hence the questions:
1. What is the best way to do this? Apply a reducer? Or maybe I could, for example, replace the valve with a higher denomination, e.g. 7 bar? I checked the instructions from the heater, and this says about the permissible operating pressure of 10 bar, does it mean that the valve can have a higher setting?
2. If the regulator, what pressure should be set? And what reducer or are those from Syra good? The problem may be with the place where to insert it, because the entry of water into the house is in the garage and on the pipes there is not much space.
I have to do something because I can't have an ever-wet boiler room. And draining water from the valve, as you can see, I do not have.
And one more thing - a diaphragm vessel. I used to check the pressure in it (I turned off the water supply, turned on the water at the nearest point so that there was no pressure and in such conditions I pumped up and measured) and pumped up to 4 bar, because it was a bit smaller. The dish looks ok, no water flowed from the valve when I pressed it. What worries or wonders me is that if you turn on the water somewhere in the house and "close" the battery, the needle on the pressure gauge jumps. You can hear such a blow on it, and as I understand thanks to the dish, it should not be like this. What is going on?
Thanks in advance for any answers,
greetings,
grzesiek