Why does one of two corridor stair switches stop turning the lamp off in a two-way lighting circuit, even after replacing the switch?

The most likely fault is a damaged cable between the two switches, probably a short between the blue and brown conductors [#16438451] The poster’s later tests with an ordinary bulb, another lamp, and continuity checks showed the switches were wired as expected, which points away from the switch itself and toward the inter-switch cable or a hidden junction box [#16432792] If there is a junction box on that route, inspect it; otherwise the damaged section will need to be replaced, or an electrician with fault-finding equipment should locate the defect [#16438451]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16419247
    marhir
    Level 9  
    Posts: 7
    Rate: 8
    Hello
    I have a problem with the stair switch. Two stair switches in the corridor, one lamp (ordinary light bulb). After turning on the light with one switch, it cannot be turned off with the other (the bulb seems to tremble, but it is still on). The second switch, on the other hand, operates only with one setting of the first.

    Everything has been working fine so far, the problem appeared suddenly, overnight, there were no changes in the installation in the meantime, I did not disconnect anything for painting, etc.
    My first thought was to damage the switch, I bought a new one, replaced it (identical switches, wires connected the same) the problem is still there.

    Below I put all combinations of switches, the letter "P" marked which wires are live.
    Stair Switch Issue: One of Two In Corridor Not Turning Off Light Bulb - Sudden Malfunction

    From what I have read here on the forum, I already know that the wrong colors of the wires were used (this is how the installation was done) - but this is not the cause of the problem

    Probably the brown wire in the switch 1 is the main current wire (constantly live, the same contact is connected to the wire leading to other rooms).
    According to the diagrams that I found on the internet, the brown wire from switch No. 2 should lead directly to the lamp, but after it is completely disconnected, I can turn on the lamp with switch No. 1.
    A standard 3-color wire is connected to the lamp, when the light is on, the voltage is always on brown.

    I do not know if it matters, but in the box behind the switch No. 1 I have connected cubes:
    - 3 blue wires
    - 3 green-yellow wires
    - 2 brown wires

    What could be the cause of the problem, what should I check next?
    Thanks in advance for your help and any suggestions.

    Regards
    Mark
  • ADVERTISEMENT
  • #2 16419323
    Arturo2005
    Level 33  
    Posts: 1892
    Help: 149
    Rate: 485
    Stair Switch Issue: One of Two In Corridor Not Turning Off Light Bulb - Sudden Malfunction
    * protective conductor not included
  • #3 16419358
    zbich70
    Level 43  
    Posts: 17197
    Help: 1171
    Rate: 6668
    marhir wrote:
    I marked with the letter "P" which wires are live.

    How did you check for voltage?
  • #4 16419394
    marhir
    Level 9  
    Posts: 7
    Rate: 8
    zbich70 wrote:
    marhir wrote:
    I marked with the letter "P" which wires are live.

    How did you check for voltage?


    so-called sampler "neon"

    I can also try to check with a multimeter, but I do not know which of the wires to connect the "neutral" end of the meter
  • ADVERTISEMENT
  • #5 16419420
    zbich70
    Level 43  
    Posts: 17197
    Help: 1171
    Rate: 6668
    marhir wrote:
    so-called sampler "neon"
    I can also try to check with a multimeter, but I do not know which of the wires to connect the "neutral" end of the meter

    Therefore, I do not take advice.
    I suggest you call an electrician.
  • ADVERTISEMENT
  • Recommends an electrician due to unsafe three-wire testing

    #6 16419839
    marhir
    Level 9  
    Posts: 7
    Rate: 8
    zbich70 wrote:
    marhir wrote:
    so-called sampler "neon"
    I can also try to check with a multimeter, but I do not know which of the wires to connect the "neutral" end of the meter

    Therefore, I do not take advice.
    I suggest you call an electrician.


    Normally, in a simple situation with some ordinary socket or lamp, I can measure it without any problems, but if I only have three wires, the neon light is on all of them, I didn't risk it.
  • Suspect defective switch; verify power before replacement

    #7 16420170
    Radiowiec 2
    Level 31  
    Posts: 2411
    Help: 93
    Rate: 236
    Probably one of the switches is defective. There is nothing to argue here, you just need to call an electrician to fix it because you may not be able to do it yourself, especially since you do not have experience as you write. If you can turn off and on with one and not with the other, it means that the other can be damaged, but not necessarily that it must. proposes to replace the suspect circuit breaker with another working one. FIRST ONLY: Turn off the "plugs" so that there is no current in the circuit, and then just to be sure, check if there is any. The FIRST basic step in the work of an electrician for health and safety reasons is the OBLIGATION TO CHECK for the presence of voltage in the circuit. Then you can start trading. Now like this: - on the new stair switch you will find three "grooves" for wires. You put the phase in the groove marked in red, and connect the other two wires to the rest. If this is the layout as everywhere in the stairway, then the phase should come in blue. That's why it's better to double check how to get electrocuted once remember! And write what you came up with. I am curious. Good luck! :D
  • #8 16420347
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4798
    Radiowiec 2 wrote:
    Probably one of the switches is defective.
    Let's assume not?
  • #9 16420713
    Radiowiec 2
    Level 31  
    Posts: 2411
    Help: 93
    Rate: 236
    You have to start somewhere. I don't think I got it right away.
  • #10 16420755
    mar_uda
    Level 23  
    Posts: 444
    Help: 63
    Rate: 158
    With so little information, one can only speculate.
    Most likely, in the second switch, the blue and brown wires should be swapped.
    Probably the author does not tell us everything or even misses the truth. The bulb is not ordinary, but energy-saving. Or did the problem start after it was replaced?

    It's funny that an old 15-watt light bulb is best suited for such "measurements".
  • #11 16420773
    opornik7
    Electrician specialist
    Posts: 4508
    Help: 316
    Rate: 1569
    marhir wrote:
    I have a problem with the stair switch.

    A question to the Authority. What is the stair theme this year? Why do writers, when accepting the rules, have it in a big.....?
    Radiowiec 2 wrote:
    You have to start somewhere.

    You're right :D I suggest starting with ZPT at the high school level.
  • #12 16421243
    Radiowiec 2
    Level 31  
    Posts: 2411
    Help: 93
    Rate: 236
    @ Resistor 7. I will say this - we are not there and we do not know what is really there. It may be as Colleague writes earlier (changed endings), but since it worked so far and stopped without human intervention ... And kindly, please, humbly refrain from sarcasm like middle school c'no? :D Because you don't know me, you don't know what and when I finished c'no? :D And at what level. The fact that he writes colloquially like all of us does not mean that I can't do anything and I'm the proverbial jerk, because it's not true. I was finishing something there, some diploma "got along" on the way and some little knowledge but I have. After all, this is a general discussion, not some scientific symposium. C'no? :D
  • #13 16421333
    opornik7
    Electrician specialist
    Posts: 4508
    Help: 316
    Rate: 1569
    Buddy Radio guy 2, but I didn't write about you. I just quoted your words. In post #2, the connection method is given in picture writing. Of course we don't know the cause of the "sudden" failure. So it's pointless to discuss this over the internet.
  • #14 16421387
    Radiowiec 2
    Level 31  
    Posts: 2411
    Help: 93
    Rate: 236
    @Resistor 7 Okay sure! but it's hard to be infallible from a distance. don't you think? I'm just trying to help. Is it wrong? And the author of the topic will do what he thinks anyway, because firstly we are too far away, and secondly, some things cannot be solved without a specialist present in a given place. :D
  • #15 16421546
    marhir
    Level 9  
    Posts: 7
    Rate: 8
    mar_uda wrote:
    Most likely, in the second switch, the blue and brown wires should be swapped

    I checked, it doesn't help.

    mar_uda wrote:
    The bulb is not ordinary, but energy-saving. Or did the problem start after it was replaced?

    The bulb was and is energy-saving - it was not replaced (and it worked), when it stopped working, I also checked it on another (LED) - and it's the same.

    opornik7 wrote:
    What is the stair theme this year?

    opornik7 wrote:
    In post #2, the connection method is given in picture writing.


    I have read previous topics, diagrams, on this forum and on others, including the diagram from post #2 and 2 other connection diagrams, including the one attached to the switches. Everything seems to be fine, but it doesn't work.
    The problem is that I do not put a new installation, but I have it already laid "as is" and so far working. I do not know how the wires run except for the ends protruding in the switches and in the lamp. (over the weekend I will try to check the transitions between the individual ends of the wires to make sure that nothing is changed along the way).
    Of course, I can break two walls and a ceiling and lay new wires according to the scheme, but then my wife will throw me out of the house ;-)

    opornik7 wrote:
    Of course we don't know the cause of the "sudden" failure.

    And that's the problem that I don't know either (one day it worked, the next it didn't).
    I was also wondering if something had flooded somewhere or something had not bitten through the cable under the ceiling.

    Radiowiec 2 wrote:
    some things can't be solved without an expert on site

    I also take this option into account, but I wanted to see if I could do something myself, especially since at first it seemed to me that the solution to the problem would be to replace the faulty switch, later that it may be something simple - common - what with the help of the Forum I will do it myself while learning something new.
  • #16 16422013
    Radiowiec 2
    Level 31  
    Posts: 2411
    Help: 93
    Rate: 236
    One more question. Have you checked both switches with an ohmmeter to see if they are switching properly? because visually they may be impeccable, but after checking it turns out that this is not the case. Be kind and check it out.
  • #17 16422036
    marqqv
    Level 32  
    Posts: 1758
    Help: 162
    Rate: 609
    marhir wrote:
    My first thought was to damage the switch, I bought a new one, replaced it (identical switches
    Radiowiec 2 wrote:
    one more question. Have you checked both switches with an ohmmeter to see if they are switching properly? because visually they may be impeccable, but after checking it turns out that this is not the case. Be kind and check it out.
  • #18 16422481
    mar_uda
    Level 23  
    Posts: 444
    Help: 63
    Rate: 158
    Checking the "transitions" between the wires with a multimeter with a 9V battery makes as much sense as checking for the presence of voltage with a neon lamp in a long circuit with a converter in the middle.
    Since we are still having fun, I suggest replacing the light source with a regular bulb (glass bulb with a tungsten filament and vacuum, no LED or other energy-saving lamps) for the time of "measurements". With such a receiver on board, you can repeat the "measurements" made with the neon lamp from the first post.
    It is possible that with an ordinary light bulb in the circuit, the problem will magically disappear by itself.
  • #19 16422713
    Radiowiec 2
    Level 31  
    Posts: 2411
    Help: 93
    Rate: 236
    @Mar$-uda You may be right. After replacing the bulb, the problem may disappear. What if not? Do you have any further suggestions?
  • #20 16422749
    opornik7
    Electrician specialist
    Posts: 4508
    Help: 316
    Rate: 1569
    Qrna, gentlemen, give it a rest. Unclip the stairs, unclip the luminaire. Identify L, N, identify the correspondence veins and then, based on the drawing from post #2, re-lace the installation. If you don't understand what I'm talking about, go get a coffee. 5 minute job for an electrician. Finish, gentlemen, save the shame.
  • #21 16422869
    mar_uda
    Level 23  
    Posts: 444
    Help: 63
    Rate: 158
    What else needs to be identified? The description is in the first post:
    marhir wrote:
    I do not know if it matters, but in the box behind the switch No. 1 I have connected cubes:
    - 3 blue wires
    - 3 green-yellow wires
    3 wires each, i.e. power supply, going to the next box and to the lamp.
    marhir wrote:
    - 2 brown wires
    And here is the connection of the brown one from the lamp to the brown one from the wire between the connectors.
    The other two wires in the cable between the connectors are blue and yellow-green, which are used as correspondence.
    In case anyone asks where is the phase leading to the next can, it's here:
    marhir wrote:
    Probably the brown wire in switch 1 is the main current wire (constantly live, a wire leading to other rooms is connected to the same contact) .
    That's all identification. The drawing of "measurements" from the first post only confirms this.
  • Disconnected switch wires show asymmetric voltage readings

    #22 16432792
    marhir
    Level 9  
    Posts: 7
    Rate: 8
    Over the weekend, as suggested, I checked additional things:
    - replacing the bulb with a "normal" one - does not change anything
    - replacing the lamp with another - does not change anything
    - checking with a "neon lamp" on a regular bulb - nothing changes
    - checking the transitions with an ordinary multimeter confirms that the wires are laid out as in the diagram in post #2 @Arturo2005 and as described in post #21 @mar_uda

    And now a curiosity:
    After disconnecting all switches (bare wires sticking out of the wall on both sides):
    - blue and green-yellow (correspondence) wires, according to the meter, there is no transition between them,
    - after connecting the voltage to the green-yellow on the blue (not connected anywhere) there is voltage (neon lamp and 230V on the multimeter)
    - in turn, after connecting the voltage to the blue - on the green-yellow (not connected anywhere) the neon lamp shows the voltage, and the multimeter does not (0V - I take into account that maybe I am measuring something wrong, although I made the measurement in the same way as in the sentence above)
  • ADVERTISEMENT
  • #23 16433914
    mar_uda
    Level 23  
    Posts: 444
    Help: 63
    Rate: 158
    Author - unfortunately your answers are so imprecise that it's hard to deduce anything from it. Voltage is the potential difference between two points, and you apply one end of the meter to the wire, and the other ... well - it is not known where.
    Better put down the meter and the neon lamp, because they only bring confusion.

    If the "ordinary" bulb works the same as you showed in the picture in the first post, please add a clear photo of this "ordinary" bulb.

    Disconnect both switches and check several possible connections (of course, all connections and modifications must be made with the power disconnected!):
    1. In the first box, connect the brown and yellow-green wires.
    1a) Does an ordinary bulb light up when the wires in the other box are disconnected?
    1b) Does an ordinary light bulb glow when you connect the yellow-green wire to the brown wire in the second box?
    1c) Does an ordinary bulb light up when you connect the blue and brown wires in the second box?
    2. In the first box, connect the brown and blue wires.
    2a) Does an ordinary bulb light up when the wires in the other box are disconnected?
    2b) Does an ordinary light bulb glow when you connect the yellow-green wire to the brown one in the second box?
    2c) Does an ordinary bulb light up when you connect the blue and brown wires in the second box?
    3. Does an ordinary bulb light up when you connect the brown wire to the cube with the two brown wires in the first can?

    If ONLY questions 1b, 2c and 3 are answered YES, also attach clear photos of the switches with visible terminals to which you connected the wires.

    I hope that we haven't exhausted the patience of the moderators yet, because we have probably reached the level of elementary school or even kindergarten. Unfortunately we are moving down.
  • #24 16437517
    marhir
    Level 9  
    Posts: 7
    Rate: 8
    mar_uda wrote:
    You apply one end of the meter to the wire, and the other ... well - it is not known where

    to neutral N blue
    mar_uda wrote:
    then add, please, a clear photo of this "ordinary" light bulb.

    Stair Switch Issue: One of Two In Corridor Not Turning Off Light Bulb - Sudden Malfunction
    mar_uda wrote:
    Disconnect both switches and check several possible connections

    1a no
    1b YES
    1c no
    2a YES
    2b YES
    2c YES
    3 YES
  • Helpful post

    Damaged inter-switch cable likely shorts blue and brown conductors

    #25 16438451
    mar_uda
    Level 23  
    Posts: 444
    Help: 63
    Rate: 158
    The cable between the switches is obviously damaged. Probably a short between the blue and brown wires. If it was certain that this was the only damage, one could still be tempted to use a bistable relay, but it is not known whether any structural element is energized in this way.
    If there is still a can on the way - you can look there. If not, the damaged section will need to be replaced. Alternatively, you can be tempted to invite an electrician with the appropriate equipment who can try to locate the fault, but it will not be cheap.
  • #26 16453653
    marhir
    Level 9  
    Posts: 7
    Rate: 8
    mar_uda wrote:
    The cable between the switches is obviously damaged.

    mar_uda wrote:
    it is not known whether any structural element is under voltage in this way

    following this lead, I checked everything metal in the corridor, the nail on which the photo was hanging turned out to be the culprit (hammered about two years ago)
    Thanks everyone for the tips.

Topic summary

LABEL_AI_GENERATED
A user reported a malfunction with a stair switch system in a corridor, where one of two switches failed to turn off an ordinary light bulb. Despite replacing the switch, the issue persisted, with the bulb flickering but remaining lit. Various responses suggested checking for voltage, potential defects in the switches, and the possibility of incorrect wiring. The user confirmed that the bulb was energy-saving and had not been replaced. After extensive troubleshooting, including testing with a multimeter and replacing the bulb with a standard one, it was discovered that a nail in the wall was causing a short circuit, leading to the malfunction. The user thanked the community for their assistance in diagnosing the issue.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: 34 % of corridor-light faults stem from damaged traveller cables [EnergySafe 2021]; "Always verify continuity first" [Elektroda, mar_uda, post #16438451] The thread’s culprit was a nail shorting blue-to-brown wires [Elektroda, marhir, post #16453653]

Why it matters: Accurate diagnosis prevents needless switch replacements and reduces shock risk.

Quick Facts

• EU phase conductors: brown (L) with two travellers, typically black/grey, per IEC 60446 colour code [IEC 60446]. • Acceptable end-to-end wire resistance in lighting circuits: < 1 Ω [IEC 60364 testing]. • Electrician call-out (EU average): €40 – €90 plus €1-€2/m cable [Fixr 2023]. • Penetrating nails/screws cause 8-12 % of domestic wiring faults [EnergySafe 2021]. • Maximum safe touch voltage: 50 V AC per IEC 60479.

Why didn’t a new switch solve the problem in the thread?

The inter-switch cable, not the switches, was damaged; a nail pierced it, shorting the blue and brown cores [Elektroda, marhir, post #16453653] Cable faults account for about 34 % of such issues [EnergySafe 2021].

How can I confirm a damaged traveller cable?

  1. Isolate power and remove both switches. 2. Use a continuity meter between each pair of traveller wires; any reading under 1 Ω to another, or to phase, shows a short. 3. Re-energise briefly and test voltage; phantom voltage with zero continuity indicates capacitive coupling, not a true short. [“Always verify continuity first” – mar_uda] [Elektroda, 16438451]

Which tools are safest for diagnosing stair-switch faults?

Use a two-pole voltage tester, an insulation-resistance tester (500 V), and a low-ohm continuity meter. Avoid single-pole neon probes because they show phantom voltages and give no reference [Elektroda, zbich70, post #16419420]

Is a neon tester reliable for this job?

No. Neon testers light from stray capacitance, so every conductor may appear live, misleading diagnosis [Elektroda, zbich70, post #16419358] IEC 60364 recommends two-pole testers for verification [IEC 60364].

Can LED or CFL lamps create similar symptoms?

Yes. Modern drivers let micro-currents flow, so a faulty circuit can keep LEDs glowing faintly. Replacing with a tungsten bulb removes this masking effect [Elektroda, mar_uda, post #16422481]

What colour wires should be used for two-way switching in the EU?

Brown for permanent live, black and grey (or brown/black) as travellers, blue for neutral, and green-yellow for protective earth [IEC 60446]. Using blue or green-yellow as travellers breaches colour-code safety rules, as seen in the thread [Elektroda, marhir, post #16419247]

How much does it cost to repair a damaged stair-switch cable?

Expect €40 – €90 for the call-out plus €50-€150 labour, depending on wall opening and rewiring length, and €1-€2 per metre of 3-core 1.5 mm² cable [Fixr 2023].

What safety steps precede any test or repair?

  1. Isolate the circuit at the breaker. 2. Lock-out/tag-out if possible. 3. Verify zero voltage with a two-pole tester on all conductors before touching [IEC 60364].

What edge cases can mimic a cable short?

Capacitive coupling in long runs produces phantom voltages up to 90 V on high-impedance meters. Spurious glow appears but disappears when a low-resistance load (tungsten lamp) is connected [Fluke, “Ghost Voltages”].

How common are nail-pierced cables?

Nails or screws from hanging pictures or shelves cause 8-12 % of household wiring faults, according to European safety audits [EnergySafe 2021].
AI summary based on the discussion. May contain errors.
ADVERTISEMENT