Continuous Lighting Issue: Stairwell Motion Sensor Fails to Turn Off Lamp
kostom 68149 14
Why does a stairwell motion sensor keep the lamp on continuously, and what component could be damaged?
The most likely fault is in the sensor’s electronics, not the lamp itself; in this thread the damaged part was the capacitor, and a swollen electrolytic capacitor near the relay/diode was already suspected visually [#9946633][#9962310][#9966920] First check whether the relay contacts are actually sticking or shorting; if the contacts are normally open when unpowered, the relay is not the cause [#9949986] Then measure the DC voltage on the relay coil while the lamp is on and the voltage on the electrolytic capacitor by the relay; in this case the coil had about 15.5 V and the capacitor about 17.2 V [#9946633][#9949986] Also inspect/test the potentiometers for cracks or bad contact on the tracks, but the final confirmed fault here was the capacitor [#9946633][#9966920]
  • #1 9914120
    kostom
    Rate: 52
    I have a problem with the motion sensor that controls the lighting in the stairwell, when switched on the lamp lights up all the time. At first when I first noticed that the lamp does not stay off I disconnected the power supply from the sensor and switched it on again the problem disappeared for a while. Now disconnecting and switching on the motion sensor does nothing, the lamp lights up all the time (despite the minimum time set). What could have been damaged?
  • #2 9914828
    T502
    Help: 16
    Rate: 10
    The damage is in the electronic circuit. Measure something, write what happens to the voltages and then you can somehow help. Because after such a formulated question, one can only advise you to take the sensor to a service center.
  • #3 9914841
    wojtepanik
    Rate: 9
    In most lamps with a sensor there is the possibility to set the sensitivity of the sensor, the length of light and the time of switching on ( twilight sensor), such knobs under the bottom of the sensor, if the adjustment with it does not work then I recommend to return to service.
  • #4 9914937
    retrofood
    Help: 1140
    Rate: 4800
    T502 wrote:
    The damage is in the electronic circuitry.
    For 99% this is the correct answer. Topic basically to be closed.
  • #5 9933901
    kostom
    Rate: 52
    T502 wrote:
    The damage is in the electronic circuit. Measure something, write what's going on with the voltages and then you can help somehow. Because after such a phrased question, you can only be advised to take the sensor to a service center.
    Which voltages to measure?
    I took pictures, but I have trouble posting on the forum.
  • Check sensor minimum load and lamp heat placement
    #6 9933966
    marcinolesno
    Help: 23
    Rate: 118
    The original lamp with a sensor or separate sensor separate lamp? There are sensors that have a certain minimum power, if this is not exceeded, it happens that the sensor fixes, and, for example, does not turn off. Or another situation, maybe the lamp and the sensor badly located in relation to each other, ie, the heat emitted by the lamp causes the activation of the sensor (as we know, sensors respond to heat emitted by moving objects).
    Lokalizacja uszkodzeń kabli Marcin Czudaj
    Matejki, Olesno, 46-300 | Tel.: 880XXXXXX (Show) | Company Website: www.zwarciaolesno.pl
  • Motion sensor stuck on after four years
    #7 9936570
    kostom
    Rate: 52
    Sensor separately lamp separately. The sensor is used to turn on an additional light in the stairwell. It is connected to a 15W incandescent bulb and worked without fail for about 4 years, until here suddenly after returning from vacation I observed that the light does not go out. The timer is set to minimum because the upper staircase landing is in the middle of the building and the sensor is only used to turn on the light when the kids move between doors.
  • Relay contact sticking diagnosed by continuity test
    #8 9939163
    relisys-js
    Rate: 11
    Sometimes it is so that the relay contacts can "hang up" . More than once it helped to lightly hit the sensor. As you took it off then with a meter you can "ring it" between the L terminal , and the L' (output) terminal . If it conducts then the relay is to blame. If not then, as my colleagues wrote above, the fault lies in the electronics, then service or simply buy a new one at a cost of about 30 zł.
  • Motion sensor relay tested and repair attempted
    #9 9946102
    kostom
    Rate: 52
    The relay works I checked. However, the cost of a new one is a minimum of 50 - 60 zlotys ("360°" sensor). Therefore, I undertook the repair myself if I knew which voltages to measure maybe it would be possible to locate the damaged component. Maybe I will be able (finally) to paste pictures today
    I think I succeeded?
    https://obrazki.elektroda.pl/1351473100_1316531235.jpg
    https://obrazki.elektroda.pl/1746211500_1316531237.jpg
    https://obrazki.elektroda.pl/2646657900_1316531239.jpg
    https://obrazki.elektroda.pl/6639385600_1316531241.jpg
    Check relay coil, capacitor, and potentiometer faults
    #10 9946633
    darek1.65
    Help: 17
    Rate: 98
    To help you, answer these questions:
    1. What does it mean that the relay works, does the relay short-circuit the working contacts when no voltage is applied.
    2. Measure the voltage (DC) on the relay coil when the light bulb is on.
    3. Measure the voltage on the electrolytic capacitor (black by the relay) may have lost capacity (if you have a capacitance meter measure it) because it looks swollen.
    4. Measure the potentiometers cz do not have cracks on the "horseshoes" (I had such a case) whether the sliders adhere to the horseshoes.
  • Relay coil and capacitor voltages measured, timer suspected
    #11 9949986
    kostom
    Rate: 52
    [quote="darek1.65"]To help you out, answer these questions:
    1. What does it mean that the relay is working, does the relay short the working contacts in the no voltage condition?
    No. Without voltage, the contacts normally open.
    2. Measure the voltage (DC) on the relay coil when the bulb is lit.
    15.5V 3. Measure the voltage on the electrolytic capacitor (black one by the relay) it may have lost capacitance (if you have a capacitance meter measure it) because it looks swollen.
    17.2V. Unfortunately I have no way to measure the capacitance 4. Measure the potentiometers cz do not have cracks on the "horseshoes" (I had such a case) whether the sliders are adjacent to the horseshoes.
    I soldered and measured the "horseshoe" from the timer (it is OK) because I think the problem is in this module. The timer is set to minimum so it is on "short circuit". [/b]
  • #13 9957868
    Krzyś33
    Help: 58
    Rate: 104
    Hi. Disconnect the lighting detector and connect the circuit under voltage. If it turns on for a while and then turns off, then you have a defective detector, if not then the electronic circuit to replace. Greetings.
  • #15 9966920
    kostom
    Rate: 52
    Due to the inability to measure the capacitance of the capacitor that "darek1.65" and "lordpakernik" wrote about, I asked a colleague to check the circuit and indeed it turned out that the damaged component was the capacitor. The detector works, thank you for your help and I consider the topic closed.
The discussion revolves around a malfunctioning motion sensor controlling a stairwell lamp, which remains continuously lit despite attempts to reset the sensor. Initial troubleshooting included disconnecting the power supply, which temporarily resolved the issue. However, the problem recurred, leading to suggestions for further diagnostics. Participants recommended measuring voltages across various components, including the relay and electrolytic capacitor, to identify potential faults. It was noted that the sensor and lamp were separate units, with the sensor previously functioning correctly for four years. Ultimately, the faulty component was identified as a swollen capacitor, which was replaced, restoring the sensor's functionality.