Connection Power & 4x4mm2 Cable Cross Section: Tauron 5KW Contract, 25A Fuse & Responsibility
Hetii 15174 11
Can I reconfigure a 4x4 mm² cable to use two cores as phase and two as neutral for a summer house, who is responsible for the cable to the meter box, and is a 5 kW / 25 A connection enough for the planned loads?
You should not use two cores as phase and the other two as neutral, because if one core fails the remaining one would take the full load and you would also lose proper PE protection [#16641379] The exact network arrangement cannot be determined from the description alone; only the energy supplier can confirm it, and the thread suggests it may be TN-C, in which case the WLZ/PEN conductor cross-section may be too small and the cable may need replacement [#16641844][#16641825] The cable between the object and the ZE box is usually paid for by the property owner, ZE is generally not interested in the chosen cable type, and in Tauron the WLZ is typically connected by an electrician hired by the investor [#16643692] With only 5 kW contracted power and roughly 13–15 kW of planned receivers, you need either to request a higher connection power or use priority relays/load management [#16641255][#16641275]
  • Responsibility for meter-side wiring and cable sizing questions
    #1 16641239
    Hetii
    Rate: 420
    Hello kindly.
    A 4x4mm2 cable (diameter of the vein with the cover) is led to the summer house.
    Three veins are one and the same phase, and the fourth lived as neutral.
    The contract with Tauron says that the contracted / connection capacity is 5KW, and the place of connection "Cable connector". Counter 25A protection.
    And now, who is responsible for this cable from the box at home to the box with the meter? Does the first electrician with rights have access to the box with counter-meter protection and has the right to change the configuration of the connected wires, or do you need to take someone from the ZE?
    Why such wiring connections? The current in the circuit flows the same, regardless of whether it is a phase or zero, and therefore symmetry should be maintained.
    I also found in forums that people sometimes have more than 11KW power allocated on a 25A fuse and I ask how it should work if 25A * 230V = 5750W?
    I am also wondering if the current cable will be sufficient when I use two wires as the phase and the other two as neutral, with the load in the house: fridge, 7.2KW induction hob, 4.5Kw water heater, electric kettle, and a few smaller devices. Generally in 13KW I should shut down wanting all devices to be turned on full.
    And so at the end I wonder the thickness of the neutral wire in installations with strength where we have 3 phases. Shouldn't such a vein be thicker than the others?
    Best regards.
  • #2 16641255
    DiZMar
    Help: 2891
    Rate: 6648
    You have 5Kw allocated and you have gently counting almost 15kW receivers and how will you manage?
  • #3 16641275
    Hetii
    Rate: 420
    As a last resort, it will use priority relays or request an increase in connection power.
    It all depends on the costs and possibilities of the existing installation.
  • #4 16641379
    kortyleski
    Help: 957
    Rate: 3860
    Hetii wrote:
    I will use two veins as a phase and the other two as neutral,
    You can't do that. In case of failure of one vein, the other will take over the entire load. Just a step to the fire. Next, what about electric shock protection? Where do you get the PE that your devices require?
  • #5 16641397
    slawekx
    Help: 53
    Rate: 198
    Hetii wrote:
    Hello kindly.
    You can describe it more accurately. Certainly only 3x one phase and N?
  • #6 16641423
    mawerix123
    Help: 482
    Rate: 951
    First of all, what is the layout of the power supply network :?:
  • #7 16641793
    Hetii
    Rate: 420
    100% is 3xL (even checked with an ohmmeter) and 1xN.
    As for PE, it is connected to receivers (3x1.5mm2 for lights and 3x2.5mm2 for sockets) and in the dashboard connected to the rail and a cable as thick as a finger, which most likely goes to some ground of the house.
    Unfortunately, I do not have any plans to install this facility. As for the network layout, I don't have such information yet.
    Added after 3 [hours] 18 [minutes]:
    This is indeed an important problem that should be considered.
    It came to my mind so quickly that you can leave both circuits with phase separate, i.e. both would work with power not exceeding a given vein.
    In the event of a break, some receivers would simply stop functioning.
    However, the neutral wire is a bit problematic, at present there is one circuit for it, but it could also be split into two.
    Is this arrangement legal and technical correct?
  • #8 16641796
    mawerix123
    Help: 482
    Rate: 951
    What cable N in WLZ are you talking about if you don't know the type of network :?:
  • #9 16641825
    Hetii
    Rate: 420
    I am talking about the N wire which goes as the only neutral from the meter box, which is located outside the object (it is not separated into N and PE).
    And looking at the following diagram:
    It will be a TT system, unless this PE conductor flies separately, hidden somewhere (then TN-S), to the ZE box, but I can't tell.
    In my case anyway, the N and PE circuits are not connected with each other.
  • #10 16641844
    mawerix123
    Help: 482
    Rate: 951
    These are only guesses and the answers that the network system can give only an energy supplier.
    From the author's description, one can only suspect that the network layout is TN-C and thus WLZ is to be replaced because the cross-section of the PEN conductor is not sufficient.
  • #11 16643220
    Hetii
    Rate: 420
    I decided to reassess the connection capacity and the contractual change, and change the connection to the box that is closer to the object.
    Who in this case covers the cost of the cable between the object and the ZE box?
    And if these are the costs that I have to cover myself, do I have to conclude that I want to use a YAKY 25mm2 cable instead of YKY, or does ZE force it to a given type of cable?
    Is the connection to their box made by a human or does a first-class electrician have access there?
    I understand that after such a change you need to make measurements of the installation in the facility?
  • #12 16643692
    mawerix123
    Help: 482
    Rate: 951
    Usually powered object owner.
    Ze is not interested.
    Not everyone and access there, but in Tauron WLZ usually connects an electrician hired by the investor.
The discussion revolves around the installation and responsibility for a 4x4mm² cable connected to a summer house under a 5KW contract with Tauron, protected by a 25A fuse. The user inquires about the responsibility for the cable from the home box to the meter box, questioning whether a licensed electrician can modify the connections or if a representative from the energy supplier (ZE) is required. Concerns are raised about the safety of the wiring configuration, particularly regarding the neutral wire and potential overloads, as well as the legality of splitting circuits. The conversation also touches on the costs associated with changing connection capacity and the type of cable required for the installation, emphasizing that the owner typically bears these costs and that an electrician hired by the investor usually performs the connection work.
TL;DR: With 5 kW allocated on a 25 A fuse, your listed loads (~13–15 kW) exceed the contract; “You have 5kW allocated… and almost 15kW receivers.” [Elektroda, DiZMar, post #16641255]
Why it matters: This FAQ helps homeowners planning upgrades or safe rewiring from a utility meter to a summer house in Tauron’s area.
How much power can I draw on a 25 A single-phase meter fuse?
About 5.75 kW (25 A × 230 V). That aligns with a 5 kW contracted capacity, leaving little headroom for startup surges. Plan loads accordingly to avoid nuisance tripping and consider staged operation or contract changes if sustained demand exceeds this level. [Elektroda, Hetii, post #16641239]
Why cant I use two wires as phase and two as neutral to share current?
Do not do this. If one conductor fails, the remaining one takes the full current and can overheat. It also compromises shock protection because you still lack a proper PE. As an expert warned, “You can’t do that.” Use a correctly designed circuit with a dedicated PE. [Elektroda, kortyleski, post #16641379]
My appliances total about 13–15 kW but my contract is 5 kW. What should I do?
Use priority (load‑shedding) relays to keep demand within 5 kW, or request an increase in contracted power. Your list includes a 7.2 kW hob and 4.5 kW heater, so simultaneous use will exceed 5 kW. Prioritizing loads or upgrading the contract solves that mismatch. [Elektroda, Hetii, post #16641275]
Who pays for the cable to the ZE box, and who is allowed to connect it?
The owner typically pays for the cable. ZE generally doesn’t mandate the cable type. In Tauron, the WLZ is usually connected by an electrician hired by the investor, and access to the box is restricted. Coordinate scope and compliance with that electrician. [Elektroda, mawerix123, post #16643692]
Can my electrician reconfigure conductors inside the meter box?
Access is restricted; not everyone can open or modify the meter box. In Tauron’s area, the WLZ connection is usually done by an electrician engaged by the investor under the appropriate permissions and procedures. Confirm access rules before planning changes. [Elektroda, mawerix123, post #16643692]
Does ZE force me to use YAKY 25 mm² instead of YKY for the new run?
ZE is not interested in mandating a specific cable type in this scenario. Select the cable with your electrician based on installation method, protection, and voltage drop, and ensure documentation matches what’s installed. [Elektroda, mawerix123, post #16643692]
How do I confirm whether my system is TT, TN‑S, or TN‑C?
Only the energy supplier can confirm the network system. From the described conditions, a TN‑C layout is suspected, and an undersized PEN would mean the WLZ should be replaced. Request official confirmation before any redesign. [Elektroda, mawerix123, post #16641844]
Is local grounding in my panel enough to declare the system TT?
No. Local grounding and separate PE/N in your panel do not define the upstream network type. Only the supplier can confirm TT or TN. Treat the layout as unknown until verified to avoid unsafe bonding decisions. [Elektroda, mawerix123, post #16641844]
Where should the PE come from in my setup?
Your devices require a dedicated PE. A feed built as 3×L plus N lacks PE and is unsafe. Do not improvise with paralleled conductors. Provide a proper PE path in line with the confirmed network system. [Elektroda, kortyleski, post #16641379]
Can I split the neutral into two parallel neutrals to carry more current?
No. If one neutral opens, the other takes the full return current and can overheat, creating a fire risk. This hack also leaves protective functions compromised. Use a single correctly sized neutral with proper PE. [Elektroda, kortyleski, post #16641379]
How do I safely increase connection power and move the point closer to the building?
  1. Ask the supplier about increasing contracted power and the new connection point.
  2. Hire an electrician to design/route the WLZ and select compliant cable.
  3. Have the investor’s electrician perform the WLZ connection per Tauron’s practice and provide documentation. [Elektroda, mawerix123, post #16643692]
Will priority relays help me stay within a 5 kW contract?
Yes. Priority relays can temporarily disconnect noncritical loads to keep peak demand within 5 kW. This allows using high‑demand appliances sequentially without tripping the 25 A protection. It does not increase contracted capacity; it just manages it. [Elektroda, Hetii, post #16641275]
With 3a0d7a0L plus N to the house, can I run a 7.2 kW hob and 4.5 kW heater together?
Not under a 5 kW contract. Those two alone total 11.7 kW. Expect tripping or overload if used simultaneously. Either stage loads with relays or request a higher contracted power from the supplier to support simultaneous use. [Elektroda, DiZMar, post #16641255]