How can I stop the floor-heating return water from dropping the boiler return temperature below the 68°C setpoint in a Defro Comfort Eco 15 kW installation with a 4D valve?

Connect the floor circuit behind the 4D valve together with the radiators, not directly to the boiler, because in the current layout the valve cannot properly protect the boiler return from cold water [#16655719] [#16655954] The second scheme is considered correct, and the controller can handle an additional 4D actuator with separate control of each circuit [#16656696] An extra pump near the boiler is not needed in that setup if the DHW pump runs all the time; if you do use a boiler circulation pump, the 4D valve alone is still a compromise between precise circuit temperature control and boiler protection [#16656696] [#16656781]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16655606
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #2 16655719
    mietek654
    Level 29  
    Posts: 959
    Help: 140
    Rate: 292
    Hello, in my opinion, all heat consumers should be connected behind the valve. In this diagram, it does not fulfill its role.
  • ADVERTISEMENT
  • #3 16655954
    kolys
    Level 20  
    Posts: 277
    Help: 38
    Rate: 56
    The floor is not connected properly. It should be connected to the 4d valve just like radiators and not directly to the boiler. I would not put an additional pump on the boiler because in this system the HUW pump already has the function of mixing. In addition, until the floor is properly connected, the additional pump at the boiler will not change much.
  • #4 16655997
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #5 16656263
    Sstalone
    Level 31  
    Posts: 2176
    Help: 72
    Rate: 398
    lechumb1 wrote:
    It should look like the first diagram. In my opinion, the second scheme is also legitimate (and I may be wrong). Then I would not have much change, but I do not know if I can put a pump on the return because I have 1 1/4 "there. Unless it can be without this pump by the stove.


    Do you have thermostatic valves on the radiators? You did this installation yourself or did someone do it to you? How is this four-way valve controlled?

    As for the pump on the return, even if you have a 1 1/4 pipe, so what, you have not seen how the pumps are installed in CO even on 2 inch pipes? Do they have 2 inch connectors?
  • ADVERTISEMENT
  • #6 16656340
    Anonymous
    Anonymous  
  • #7 16656696
    kolys
    Level 20  
    Posts: 277
    Help: 38
    Rate: 56
    Both diagrams are checked and will work properly. The second diagram is also OK because your controller will handle an additional 4d valve actuator and will have control over each circuit separately. An additional pump next to the boiler does not need to be installed if the DHW pump is switched on all the time.
  • #8 16656773
    Anonymous
    Anonymous  
  • #9 16656781
    gersik
    Level 33  
    Posts: 1717
    Help: 164
    Rate: 639
    kolys wrote:
    I would not put an additional pump on the boiler because in this system the HUW pump already has the function of mixing.

    For this to be the pump from the hot utility water would have to work in parallel with the CH pump.
    lechumb1 wrote:
    I would like to know if any of the following schemes will solve my problem with flooding the boiler with cold water from return

    Diagram two with a boiler circulation pump.
    The 4d valve itself has the weakness that you will either precisely control the temperature of the water in the circuit or the protection of the boiler.
  • #10 16660540
    Anonymous
    Anonymous  

Topic summary

LABEL_AI_GENERATED
The discussion revolves around a user experiencing low return temperatures (±37°C) in their Defro Comfort Eco 15kW oven, which is set to 68°C. The system includes a K1PV2 controller with PID functionality, operating with a weather sensor and a 4D motor. Users suggest that the floor heating circuit is improperly connected, recommending that it should be linked to the 4D valve like radiators, rather than directly to the boiler. Concerns are raised about the effectiveness of the gravitational flow in the return pipe (1 1/4") and the potential need for an additional pump. The conversation also touches on the possibility of using hydraulic couplings and the importance of proper control over the heating circuits to maintain stable temperatures and prevent cold water from flooding the boiler.