Why does my Defro Komfort EKO 15 kW controller report “Mosfet temperature too high”, and what should I replace or check to fix it?

The most common fix is to replace the blue 1 µF / 305–400 V capacitor in the controller, because in several cases it had fallen far below nominal value and the boiler returned to normal after replacement [#21254486] [#21395077] The blue part is the cuboid next to the blower-control MOSFET, not the MOSFET itself [#18965066] [#18947190] If the alarm still appears, replace the MOSFET as well; one suggested type was P10NK60ZFP, and in some cases replacing the transistor finally solved the fault [#19709276] [#20183556] Also check the blower for extra load: clean the airflow duct, make sure the fan spins freely, inspect the bearings, and verify the blower capacitor, because added resistance can overheat the MOSFET [#18947190] [#21110526] [#19630183]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 18946694
    darasmul
    Level 6  
    Posts: 6
    Rate: 25
    Hi


    I have a problem with a 6-year-old heating boiler for eco peas, it's about a pop-up alarm regarding too high mosfet temperature.
    Company: Defra
    Model: Eco Comfort 15KW
    Driver: K1P v.2
    Description of the problem:
    The stove works flawlessly and I would sum up as a sensational device, but ...
    For several weeks I have been getting an alarm "Mosfet temperature too high"
    I took off the housing behind the digital display (photos).
    When I open the windows and there is a breeze, everything works fine.
    So something must be overheating somewhere.
    Do you have any idea what it could be and how to fix the problem
    Attachments:
    • Defro Komfort EKO 15KW failure "Mosfet temperature too high" image_123927839.JPG (1.48 MB) You must be logged in to download this attachment.
    • Defro Komfort EKO 15KW failure "Mosfet temperature too high" image_6487327h.JPG (1.81 MB) You must be logged in to download this attachment.
    • Defro Komfort EKO 15KW failure "Mosfet temperature too high" image_6487327.JPG (1.94 MB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • Helpful post
    #2 18947190
    mipix
    Level 38  
    Posts: 4067
    Help: 495
    Rate: 1475
    The mosfet controls the fan speed. Maybe the bearings just ran out and it's working with resistance. Check what is the actual temperature of the mosfet. It's probably the one with the aluminum (bright) heatsink.
  • #3 18963043
    bron67
    Level 11  
    Posts: 41
    Rate: 50
    To replace the capacitor 1mf 305V.
  • ADVERTISEMENT
  • #4 18963452
    darasmul
    Level 6  
    Posts: 6
    Rate: 25
    Added after 3 [minutes]:

    bron67 wrote:
    To replace the capacitor 1mf 305V.


    Certainly 1mf and not 1uf (I don't know but when I put it in google, I see that "mf" does not exist)

    something like that:

    https://allegro.pl/oferta/kondensator-1uf-305v-ac-x2-impu-b32923-x2-mkp-sh-8007380923

    Added after 37 [seconds]:

    mipix wrote:
    The mosfet controls the fan speed. Maybe the bearings just ran out and it's working with resistance. Check what is the actual temperature of the mosfet. It's probably the one with the aluminum (bright) heatsink.



    Unfortunately, I have no way to check the specific temperature.
    The fact is that only the silver one heats up to such a temperature that if you put your finger on it, it burns after 2 seconds. The rest is warm but only this one burns.

    Can this be repaired/replaced?
  • #5 18965066
    bron67
    Level 11  
    Posts: 41
    Rate: 50
    Sorry. Yes 1uf 305V. The mosfet is the blower fan control transistor without a heat sink and is screwed on the board next to the blue capacitor that needs to be replaced.
  • #6 18965205
    darasmul
    Level 6  
    Posts: 6
    Rate: 25
    Thanks for the answer.

    Is that the capacitor I circled in yellow?
    Attachments:
    • Defro Komfort EKO 15KW failure "Mosfet temperature too high" Bez tytułu.jpg (2.69 MB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • Helpful post
    #7 18965210
    mipix
    Level 38  
    Posts: 4067
    Help: 495
    Rate: 1475
    No, the blue cuboid next to it.
  • #8 18965847
    bron67
    Level 11  
    Posts: 41
    Rate: 50
    The one who wrote mipix. The one marked is a mosfet transistor.
  • #9 18976551
    darasmul
    Level 6  
    Posts: 6
    Rate: 25
    mipix wrote:
    No, the blue cuboid next to it.


    I'm sorry I ask so much. Is it the blue one?
    It doesn't overheat, it's not hot at all.
    Attachments:
    • Defro Komfort EKO 15KW failure "Mosfet temperature too high" WhatsApp Image 2020-10-14 at 08.04.48.jpeg (148.33 KB) You must be logged in to download this attachment.
  • #10 18976598
    andrzej55
    Level 37  
    Posts: 3000
    Help: 306
    Rate: 373
    Yes the blue one. Just replace with a new one with the same parameters.
  • #11 18977352
    Gb601
    Level 8  
    Posts: 4
    Rate: 69
    Hello, I have the same problem, only error 203 pops up or something
  • #12 19180339
    Kameleon007
    Level 1  
    Posts: 1
    Rate: 6
    Hello, I have the same problem. I wanted to ask if replacing this blue capacitor solved the problem ...?
  • #13 19181621
    Gb601
    Level 8  
    Posts: 4
    Rate: 69
    So it helped low cost
  • #14 19630115
    maystero
    Level 24  
    Posts: 1010
    Help: 58
    Rate: 204
    Hello.

    I have an identical case. Tech ST K1PV4 driver.
    I checked the driver and the capacitor (blue 1uF) had a loss of capacitance. I replaced with a new (identical) 1uF 305V capacitor and mosfet transistor. Unfortunately, the problem persisted. On the display I still have the message Mosfet temperature too high (error 200).
    I will add that the blower in manual mode works properly (i.e. it is possible to adjust the speed).
    What did I miss? Please help.
  • ADVERTISEMENT
  • #15 19630183
    Gb601
    Level 8  
    Posts: 4
    Rate: 69
    Please check the blower condenser and the blower duct for obstruction.
  • #16 19630489
    maystero
    Level 24  
    Posts: 1010
    Help: 58
    Rate: 204
    Gb601 wrote:
    Please check the capacitor at the blower and the blower duct for obstruction.


    Turbine, okay. New capacitor installed (2uF/400V)
    Defro Komfort EKO 15KW failure "Mosfet temperature too high"

    The problem has not gone away.
  • #17 19699681
    djluki2013
    Level 14  
    Posts: 257
    Help: 1
    Rate: 114
    Hello . I have the same problem in the Tech ST K1PV4 controller error high temperature mosfet error 203. Replacing these 2 capacitors one in the drivers and the other in the blower, can there be something more? A colleague "foreman" wrote that the replacement did not help. Tomorrow I will buy both capacitors given above by you. Are the Tech ST K1PV4 drivers of the same capacity?
  • #18 19700178
    gersik
    Level 33  
    Posts: 1717
    Help: 164
    Rate: 639
    Also replace the mosfet.
  • #19 19700756
    djluki2013
    Level 14  
    Posts: 257
    Help: 1
    Rate: 114
    Do you have the number of this mosfet? I don't have a controller at home, only at Grandma's on the stove and I want to have all the elements to replace because I have a bit of a road. Thanks
  • #20 19709276
    maystero
    Level 24  
    Posts: 1010
    Help: 58
    Rate: 204
    djluki2013 wrote:
    Do you have the number of this mosfet? I don't have a controller at home, only at Grandma's on the stove and I want to have all the elements to replace because I have a bit of a road. Thanks

    P10NK60ZFP by ST
    just watch out for fakes...
  • #21 19709401
    klaudiakol1989
    Level 5  
    Posts: 18
    Rate: 16
    Defro oven, tech k1pv4 controller and the same problem, high temperature mosfet on the manual blower runs for a few seconds and disconnects. What's the problem?

    Added after 1 [minutes]:

    Clearly something with the blowing, but what can I possibly do at this hour to make it work for me at least until the morning to get someone to check what the problem is
  • #22 19709475
    Gb601
    Level 8  
    Posts: 4
    Rate: 69
    Turn off the pod
  • #23 19709479
    klaudiakol1989
    Level 5  
    Posts: 18
    Rate: 16
    Gb601 wrote:
    Turn off the pod

    I mean drink? I have disabled

    Added after 8 [hours] 40 [minutes]:

    Gb601 wrote:
    Turn off the pod

    I mean drink? I have disabled
  • #24 19721560
    djluki2013
    Level 14  
    Posts: 257
    Help: 1
    Rate: 114
    maystero wrote:
    djluki2013 wrote:
    Do you have the number of this mosfet? I don't have a controller at home, only at Grandma's on the stove and I want to have all the elements to replace because I have a bit of a road. Thanks

    P10NK60ZFP by ST
    just watch out for fakes...

    Already the driver works for a week. Replacing the cube in the controller helped, it clearly had no capacity. I also replaced the cube in the blower but this one was good 2uF. I did not have a mosfet and did not replace it, but I will buy it as a spare. Thank you for your help
  • #25 19731191
    agamajkel
    Level 12  
    Posts: 43
    Help: 1
    Rate: 15
    Hello, I have a slightly different problem with the K1PV2, namely with the feeder, when feeding, the feeder stops while feeding fuel, sometimes for a fraction of a second and sometimes 2s and the end of feeding is set to 5s, the stove is set in two states.
    I replaced the relay because it could be heard that it turns on and off after these 5s, but it looks like it was losing electricity somewhere. Has anyone encountered such a problem and has any advice? .
  • #26 19832007
    kaliszfornijczyk
    Level 10  
    Posts: 16
    Rate: 14
    darasmul wrote:
    Hi



    ...I took off the housing behind the digital display (photos).
    When I open the windows and there is a breeze, everything works fine.
    ...

    I have a similar problem in Defro eco 12kw. Can you tell me how did you remove the red cover?? Gray was two screws later I unscrewed 3 screws from the red one and I can't see it anymore and it still won't open ..
  • #27 19838401
    djluki2013
    Level 14  
    Posts: 257
    Help: 1
    Rate: 114
    As I remember correctly, the entire driver moves forward or backward. Then you lift and from the bottom next to the hinges of the display there are 2 screws. Unscrew and remove the red cover.
  • #28 19838455
    kaliszfornijczyk
    Level 10  
    Posts: 16
    Rate: 14
    Thanks. I took three days to do it because I didn't want to break anything.
    In case anyone else is having problems:
    1. First, on the gray cover, unscrew the 2 screws on the sides.
    2. Unscrew the red cover with 2 screws on the sides and one in the middle.
    3. Remove the 2 sheet metal screws connecting the back of the controller housing with the furnace sheet.
    4. Move the entire housing towards you so that the metal plate catches come out.
    5. Lift the front of the housing, paying attention to the cables at the back, and unscrew the 3 left and 3 right screws from the bottom so that you can remove the red cover behind the display.
  • #29 19838466
    djluki2013
    Level 14  
    Posts: 257
    Help: 1
    Rate: 114
    It is exactly as you write :) I did it a few months ago and I don't remember it exactly, but I knew it had to be moved and lifted.

Topic summary

✨ The Defro Eco Comfort 15KW heating boiler equipped with a Tech ST K1P series controller frequently triggers a "Mosfet temperature too high" alarm, indicating overheating of the MOSFET transistor responsible for fan speed control. The MOSFET is mounted on the controller board near a blue 1µF 305V capacitor, which often loses capacitance over time, contributing to the fault. Replacing the blue capacitor and the MOSFET transistor (commonly the ST P10NK60ZFP model) is a primary recommended repair. Additionally, the blower fan capacitor (typically 2µF 400V) should be checked and replaced if degraded. Overheating can also result from mechanical issues such as fan bearing resistance or airflow obstruction in the blower duct. Some users report persistent errors even after capacitor and MOSFET replacement, suggesting the need to inspect the blower and airflow path thoroughly. The MOSFET temperature sensor may also fail, causing error messages. Accessing the controller housing requires removing multiple screws and carefully detaching covers behind the digital display. Proper identification and sourcing of genuine replacement components are critical, as counterfeit transistors have been reported. Overall, maintenance involves capacitor and MOSFET replacement, cleaning the fan and duct, and verifying fan operation to resolve the overheating alarm and restore normal boiler function.