Immergas Nike Star 24 3 E: Decreased Hot Tap Water Pressure Post-Plumbing Repair

_precious_ 13872 19
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16702608
    _precious_
    Level 9  
    Hello, I would like to ask what could be the reason for the decrease in hot tap water pressure (cold water pressure OK).
    The pressure drop appeared after the plumbing fault was removed in front of my house. There was a freaky water after releasing the water again, I had to clean the strainers in the taps (they were cluttered with dirt).
    Could there be any stuttering on the stove, am I able to remedy it myself or just the service.
    Thank you for your reply and any help.
  • ADVERTISEMENT
  • #2 16702900
    borg77
    Level 31  
    Have you forgotten to check the water filters. Probably in front of the stove. Check the battery. Some types had additional filters, but only available after unscrewing the battery. There is also a filter at the counter from the water. Each clogged filter is a pressure drop.
  • ADVERTISEMENT
  • #3 16703003
    _precious_
    Level 9  
    As I wrote, the cold water pressure is ok
    I checked the taps for approx
    I don't know where the filters are on the stove and if I can choose them somehow.
  • #5 16703359
    _precious_
    Level 9  
    I have nothing in front of the stove, and the instruction does not mention the stove filter.
  • #6 16703387
    borg77
    Level 31  
    Strange that the installer did not put on filters. Now just wait, maybe some spec from your type of boiler will speak, since the external causes have theoretically been eliminated.
  • ADVERTISEMENT
  • #7 16703621
    Magister_123
    Level 36  
    The flow sensor has an orifice (white pellet) and is 100% sand-clogged. In the drawing I have indicated where it is located.
    Immergas Nike Star 24 3 E: Decreased Hot Tap Water Pressure Post-Plumbing Repair
  • #8 16704228
    _precious_
    Level 9  
    Which place is she on the stove?
  • #9 16704341
    Magister_123
    Level 36  
    Four on the diagram.
    Immergas Nike Star 24 3 E: Decreased Hot Tap Water Pressure Post-Plumbing Repair
  • ADVERTISEMENT
  • #10 16704362
    _precious_
    Level 9  
    Is there a problem with removing the purging and reinstalling?
  • Helpful post
    #11 16704478
    Magister_123
    Level 36  
    You need to get new gaskets. It's easy for me and I don't know for you. To unscrew you have two nuts (one from the top, the other smaller at the back). Finally, pull the cotter pin. You lift the whole up so that the brass thread from the photo stays in the cauldron.
  • #12 16704493
    _precious_
    Level 9  
    Are these gaskets special or will I buy them everywhere?
  • #13 16704867
    Magister_123
    Level 36  
    The upper one is plain water but the back is probably rubber (O-ring?). I am not sure because I no longer work in the industry.
  • #14 16704931
    _precious_
    Level 9  
    I do not spin to knock I will not be sure that I will buy the necessary gaskets. I have to undress and fold it and it must work even worse than before trying to repair it.
    If it does not go then the service.
  • #15 16705018
    Magister_123
    Level 36  
    I will not hide that more than once I had situations when I did not have the appropriate seals. At that time I used the old ones lubricating them with silicone grease.
  • #16 16893145
    krzysn33
    Level 10  
    Hello, I have a problem with the immergas furnace, as I unscrew the wide tap, the pressure on the furnace drops as if this water was connected to the circulation. What to do, help. My phone number is 690 955 557.
  • #17 16893247
    Magister_123
    Level 36  
    @ krzysn33 Damaged bithermic exchanger or water admission valve to the system. I do not know how old the boiler is, but in the first case the repair is rather unprofitable.
  • #18 18466769
    kayttt
    Level 9  
    Hello,

    I'm connecting to the topic. I have a furnace immergaz eolo star 24 3e. I am after the exchange of risers, the installer who installed the boiler also did not install the filter at the entrance to the furnace, I am after cleaning the fluxostat and the flow limiter, there was a bit of maras, but I did not notice any improvement.
    I don't know much about immergas boilers, but is there any flow regulation? The problem is that it is impossible to use water in the kitchen and take a shower or use the sink at one time, is this normal with these boilers? with beretts I don't see such a difference.
  • #19 19910403
    karasko
    Level 11  
    _precious_ wrote:
    I do not unscrew it until the knock, I will not be sure that I will buy the necessary gaskets. I have to disassemble and assemble and it has to work no worse than it was before trying to repair it.
    If it fails, the service.


    Good morning,

    has the cause of the fault been found? I have a similar problem :(

    Przemek
  • #20 21518262
    Linux3003
    Level 11  
    And what was the cause of this poor flow?

Topic summary

✨ The discussion addresses a decrease in hot tap water pressure following the resolution of a plumbing fault near the property, while cold water pressure remains normal. Initial troubleshooting involved cleaning tap strainers clogged with dirt. Suggestions included checking for clogged water filters near or inside the Immergas Nike Star 24 3 E boiler, particularly the flow sensor orifice (white pellet), which is prone to sand clogging and can cause pressure drops. The flow sensor is located inside the boiler and requires removal of nuts and a cotter pin for cleaning or replacement, with new gaskets recommended for reassembly. Some users noted the absence of inlet filters installed by the plumber, which could contribute to the issue. Additional comments referenced similar problems with other Immergas models and the possibility of damaged components such as the bithermic exchanger or water admission valve. The discussion also touched on flow regulation limitations in these boilers, affecting simultaneous water usage in multiple outlets. Overall, the problem likely stems from internal boiler components clogged or affected by debris introduced during plumbing repairs, requiring cleaning or professional servicing if self-repair is uncertain.
Generated by the language model.

FAQ

TL;DR: After mains repair, hot-water loss on Immergas Nike/Eolo Star 24 3 E is usually a clogged flow-sensor orifice; disassembly needs 2 nuts and 1 cotter pin. “100% sand-clogged.” [Elektroda, Magister_123, post #16703621]

Why it matters: This FAQ helps owners quickly restore domestic hot-water flow and decide when DIY is safe versus calling service.

Quick Facts

Why did my hot tap water pressure drop right after street plumbing work?

Debris from the network often clogs the domestic hot water flow sensor orifice. This small “white pellet” restriction can choke hot flow while cold remains normal. An expert noted it becomes “100% sand-clogged” after such events. Clean the orifice to restore flow. [Elektroda, Magister_123, post #16703621]

Where exactly is the flow sensor/orifice on Immergas Nike/Eolo Star 24 3 E?

On the manufacturer’s schematic used in the thread, the DHW flow sensor is indicated at position 4. Access it as shown in the shared diagram before attempting cleaning or seal replacement. [Elektroda, Magister_123, post #16704341]

How do I clean the flow sensor orifice on this boiler?

You must access the module and remove it for cleaning.
  1. Undo the upper nut, then the smaller rear nut.
  2. Pull the cotter pin and lift the assembly upward.
  3. Clean the orifice and reassemble with good seals. Use new gaskets where possible. [Elektroda, Magister_123, post #16704478]

Do I need special gaskets when reassembling the flow sensor?

Yes. The upper joint uses a plain water gasket. The rear seal is typically a rubber O‑ring. Replace them if worn. If you cannot source them immediately, plan for service or a temporary workaround. [Elektroda, Magister_123, post #16704867]

What if I don’t have new seals today?

A technician in the thread reused old seals in a pinch, lubricating them with silicone grease to improve sealing. Treat this as temporary until you obtain correct replacements. “It’s easy for me” reflects skilled hands; proceed carefully. [Elektroda, Magister_123, post #16705018]

My installer didn’t fit filters before the boiler. Is that a problem?

Yes. Filters ahead of the boiler protect internal parts from grit. Missing filters increase the risk of clogged orifices and sensors after supply disturbances. The thread flags their absence as unusual practice. Install suitable inlet filtration. [Elektroda, borg77, post #16703387]

Which simple checks should I do before opening the boiler?

Clean faucet strainers at every hot outlet first. After mains work, dirt often collects there and restricts flow. If cold pressure is fine and hot remains weak after cleaning aerators, move on to the boiler’s flow sensor. [Elektroda, precious, post #16702608]

Can clogged faucet filters alone cause my hot-water pressure loss?

Yes. The thread starter found “freaky water” after supply restoration and had to clean multiple tap strainers loaded with debris. Any clogged filter introduces a noticeable pressure drop. Verify all outlet strainers. [Elektroda, borg77, post #16702900]

What tools or actions are involved to access the flow sensor?

Plan for a controlled disassembly: loosen two nuts (upper, smaller rear), pull one cotter pin, and lift the unit. Have replacement gaskets ready. This is a compact job but requires care to avoid leaks on reassembly. [Elektroda, Magister_123, post #16704478]

Is there a user-adjustable flow regulation for DHW on Eolo Star 24 3E?

A participant cleaned the fluxostat and the flow limiter yet still noticed limited simultaneous use. No adjustable DHW flow control was identified in that discussion. Capacity limits remain noticeable with two outlets. [Elektroda, kayttt, post #18466769]

Opening a wide tap drops my boiler pressure—what’s wrong?

This symptom points to an internal fault: a damaged bithermic heat exchanger or a faulty fill valve admitting water to the system. The exchanger repair may be uneconomical depending on age. Seek service assessment. [Elektroda, Magister_123, post #16893247]

When should I stop DIY and call service?

If you lack the correct seals, cannot confirm parts, or reassembly risks worse performance, call service. One user chose service rather than risk a failed reassembly. Prioritize safe, leak-free operation. [Elektroda, precious, post #16704931]

What is the “flow sensor” (fluxostat) and why does it matter?

It detects hot-water demand and meters flow through a single orifice pellet. When grit blocks this one opening, hot flow collapses though cold remains fine. Cleaning restores capacity. “100% sand-clogged” described its failure mode. [Elektroda, Magister_123, post #16703621]

What’s the typical failure edge case after cleaning everything?

If hot flow remains poor or system pressure drops when taps open, suspect a failed bithermic exchanger or a leaky fill valve. The exchanger fix can be cost-ineffective on older units. Schedule diagnostics. [Elektroda, Magister_123, post #16893247]

Do some taps hide extra filters I should check?

Yes. Certain mixer batteries include internal filters only accessible after unscrewing the body. Missing or clogged filters anywhere reduce flow and pressure at the outlet. Inspect and clean these hidden points. [Elektroda, borg77, post #16702900]

What did other users finally report as the root cause?

The thread consensus points to debris blocking the DHW flow sensor orifice after supply work. Cleaning the orifice and renewing seals restores flow in most cases. Position 4 identifies the target component. [Elektroda, Magister_123, post #16704341]