How can I improve an old coal-fired central heating boiler so it holds temperature better, stops leaking around 60°C, and needs less constant tending?

Repair the leaks and boiler controls first, then use a properly calibrated draft regulator instead of installing a blower/controller [#16793117][#16794675] A boiler temperature of about 65°C is not dangerous; 50°C is too low and can waste fuel and increase corrosion risk, and many boilers run even around 85°C [#16793117] If the flare nut/cap leaks at around 60°C, drain the water and replace the O-ring or gasket, or the whole valve if the cone or thread is damaged; tow/paste or Teflon tape are only temporary help when the thread itself leaks [#16793711][#16794537] If the differential valve does not open reliably, remove it, clean it, check that the ball moves freely, or replace the valve (about 40 PLN) [#16793117] Calibrate the draft regulator by heating the boiler to 60°C manually, setting the knob about 5°C above the thermometer, adjusting the arm horizontal, and setting the chain so the flap leaves a match-thick gap; do not seal the air supply flap [#16794675] Start by cleaning the filter if circulation is weak [#16793440]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Need advice on stabilizing boiler temperature and leaks

    #1 16789397
    oczko991
    Level 10  
    Posts: 34
    Rate: 2
    Hello, recently I wrote in this topic - https://www.elektroda.pl/rtvforum/topic3018667.html

    Unfortunately, next winter, I have the same problem again, continuous walking to the stove for up to 30 minutes ... I have enough.

    I'll tell my story.

    I am asking for help and advice in burning my CO stove

    Photos of the stove and installation - see the link below.

    I will present what my problem looks like.
    I have no problem with lighting it every day and putting it out in the evening, but the most troublesome for me is to constantly control the temperature and add it to the stove every 30 minutes.

    I smoke on the move. I put in a small amount of coal so as not to boil the stove. I turn on the pump immediately. In the evening I do not add fuel to the stove, and it goes out by itself and I turn off the pump. Unfortunately, at around 60 degrees, water starts to drip / come out from the screw cap. A colleague from work said that it is enough to tighten, but I am not moving because I am afraid it will worsen, because once I tightened the screw above the boiler, it broke completely. It is probably because no one lived in the house for 3 years or smoked in the stove (the water was drained).

    Unfortunately, the measuring device does not work or I do not know how to operate it, it walks hard and does not move at all. If you set the flap to a very small opening, then it burns poorly and does not want to reach a temperature higher than 50 degrees, or it hardly reaches 50 degrees. If, on the other hand, I open the flap more, then the temperature in the furnace quickly rises to 60 or even 65 degrees, and I have to close the flap immediately, and sometimes the damper because I'm afraid that something will boil

    I can't change my stove and I don't want to invest too much because the house has many owners and nobody will pay back the investment.

    What will be the best way to improve my stove? A colleague proposes to install the blower in the damper and the controller.
    On the internet I found https://www.youtube.com/watch?v=15DBdRk5PJQ SUCH a movie, it's probably the same stove.
    But there is another problem, the differential valve above the stove, it does not always open, i.e. when the pump is set to the 3rd level, it moves normally, such a metallic thump as if sucking in is heard, but when it is on the 2nd level it will never surprise and there is no sound.

    Improvement of the old type central heating boiler in Olsztyn
    Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in OlsztynImprovement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn Improvement of the old type central heating boiler in Olsztyn
  • ADVERTISEMENT
  • Differential valve closes when pump speed is low

    #2 16789414
    stanislaw1954
    Level 43  
    Posts: 15248
    Help: 2013
    Rate: 4675
    oczko991 wrote:
    But there is another problem, the differential valve above the stove, it does not always open, i.e. when the pump is set to the 3rd level, it moves normally, such a metallic thump as if sucking in is heard, but when it is on the 2nd level it will never surprise and there is no sound.
    Let me start from the back ---- the valve closes after turning on the pump. How do you explain that it does not work properly in 1st or 2nd gear? Could the pump not pump hot water then?
  • #3 16789635
    oczko991
    Level 10  
    Posts: 34
    Rate: 2
    I do not know if it closes or opens, I do not know what installations
    I think that it does not work in 1st and 2nd gears, because maybe the rubber or plastic ball has got some rust and sticks too much.
    please help me improve the boiler
  • Draft regulator cheaper than fan controller

    #4 16789841
    stanislaw1954
    Level 43  
    Posts: 15248
    Help: 2013
    Rate: 4675
    oczko991 wrote:
    I think it doesn't work in 1st and 2nd gear
    You think, but you are not sure. Just put your ear to the pipes and you can hear whether the pump is working in 1st or 2nd speed. And if it works, it also pumps the water.
    Without a regulator, if it does not work, it is also possible to smoke, only the temperature control on the boiler will not be possible, although by properly setting the ash pan flap, you can also smoke. Reaching the temperature of 60 or 65 degrees is not a reason to fear that you will boil water. If you know how to open the hatch to reach a temperature of 50 degrees, maybe it will be enough "a bit" more, not too much, to be good.
    oczko991 wrote:
    I don't want to invest too much in it
    If so, it is much cheaper to buy a draft regulator than a fan with a controller.
  • ADVERTISEMENT
  • Recommend replacing the differential valve with a ball valve and pump controller

    #5 16789912
    Waldek Osiński
    Level 16  
    Posts: 165
    Help: 11
    Rate: 26
    Hello.
    If you do not hear a click in the first and second gear, and the differential valve does not close, the pump pushes water, but in a short circuit and the ear can be put against the pipe to heat them ... ? As for the regulator, hmmm ... I had one, and in my life I won't. Well, unless the regulator is included in the price of the fan and controller.
    Sorry, I just looked at the topic given in the first post, you can see everything nicely there.
    Remove the differential valve and install a regular ball, plus the simplest pump controller. And please do not write: what will happen when the pump fails? For 20 years no one has let me down ...

    Moderated By ROBSON33:

    3.1.11. Don't post messages that add nothing to the discussion. They are misleading, dangerous or do not solve the user's problem.

  • Helpful post
    #6 16793117
    Xantix
    Level 41  
    Posts: 6483
    Help: 686
    Rate: 1657
    oczko991 wrote:
    I smoke on the move.

    And have you not tried to light from the top?

    oczko991 wrote:
    Unfortunately, at around 60 degrees, water begins to drip / come out of the screw cap on https://photos.app.goo.gl/uC6jaPdYPm32NKPp1 IN THIS photo. A colleague from work said that it is enough to tighten, but I am not moving because I am afraid it will worsen, because once I tightened the screw above the boiler, it broke completely. It is probably because no one lived in the house for 3 years or smoked in the stove (the water was drained).

    When it drips, you can unscrew the flare nut (optionally replace it with a new one if you can see damage to the thread), put new tow on the thread and a decent sealing paste
    threads and dies should not.

    And the door in the boiler is sealed with a glass cord? If not, I would recommend sealing, it is easier to control the operation of the boiler.
    oczko991 wrote:
    Unfortunately, the measuring device does not work or I do not know how to operate it, it walks hard and does not move at all. If you set the flap to a very small opening, then it burns poorly and does not want to reach a temperature higher than 50 degrees, or it hardly reaches 50 degrees. If, on the other hand, I open the flap more, then the temperature in the furnace quickly rises to 60 or even 65 degrees, and I have to close the flap immediately, and sometimes the damper because I'm afraid that something will boil

    First, describe how you calibrate the regulator. Secondly, 65 degrees is the minimum temperature that most boilers should be operating at, not cause for fear. When I smoke, I usually have even 85 degrees sometimes ... Keeping 50 degrees on the stove does not mean burning but burning fuel. In addition, at such a temperature there will be a problem with boiler corrosion.

    oczko991 wrote:
    A colleague proposes to install the blower in the damper and the controller

    It's like treating the flu by putting your leg in a plaster ... :( IMHO won't do much. The blower and the solid fuel boiler do not work very well together. This is mainly a way to waste fuel.
    oczko991 wrote:
    But there is another problem, the differential valve above the stove, it does not always open, i.e. when the pump is set to the 3rd level, it moves normally, such a metallic thump as if sucking in is heard, but when it is on the 2nd level it will never surprise and there is no sound.
    If you suspect that the differential valve is not working, you need to remove it and clean it, checking that this ball moves freely. Alternatively, you can replace the valve with a new one - cost from 40 PLN.

    Waldek Osiński wrote:
    Well, unless the regulator is included in the price of the fan and controller.

    You tell good jokes.

    Waldek Osiński wrote:
    And please do not write: what will happen when the pump fails? For 20 years no one has let me down ...

    May you live a long life and never let any of you fail. Because if it fails ... Seriously - do not offer anyone to install a time bomb in the boiler room.
  • #7 16793373
    oczko991
    Level 10  
    Posts: 34
    Rate: 2
    I want to start burning from the top, I just have to prepare the stove
    at the beginning, I would like to install a new regulator, because after turning it does not respond, I do not know how to operate and calibrate it
    then seal the bottom door that has the largest gap
    replace the filter in front of the pump because the radiators at the top of the house do not heat up fully
    finally, reduce the combustion chamber and cover the vertical grate

    I am asking for instructions which valves to turn on / off to drain the water, and in what order to do it.
    How to install the regulator later and how to vent the entire system?

    Could someone illustrate it by rewriting any of the photos in paint?
    Thank you in advance for your help.

    I will write as if I did it and ask for improvement.
    1. Close all possible valves on the stove.
    2. Attach a garden hose to the outlet of the stove tube on the bottom right and unscrew the valve.
    3. Unscrew the measuring gauge and screw in a new one
    4. Unscrew the filter, clean and fit a new one.
    5. Fill the installations
    6. Bleed the last radiator to the first, then the pump? and is the regulator to be slightly unscrewed? should venting be done on a burning stove or on a cold one? how to know when to stop adding water to the system?
  • #8 16793440
    ROBSON33
    Admin of household appliances group
    Posts: 9730
    Help: 465
    Rate: 1714
    So I would start by cleaning this filter:

    Improvement of the old type central heating boiler in Olsztyn

    Ps. Correct the first post.
  • ADVERTISEMENT
  • #9 16793711
    Zbigniew Rusek
    Level 38  
    Posts: 3613
    Help: 394
    Rate: 1542
    Quote:
    Unfortunately, at around 60 degrees, water begins to drip / come out of the screw cap on https://photos.app.goo.gl/uC6jaPdYPm32NKPp1 IN THIS photo. A colleague from work said that it is enough to tighten, but I am not moving because I am afraid it will worsen, because once I tightened the screw above the boiler, it broke completely. It is probably because no one lived in the house for 3 years or smoked in the stove (the water was drained).

    Xantix wrote:
    When it drips, you can unscrew the flare nut (optionally replace it with a new one if you can see damage to the thread), put new tow on the thread and a decent sealing paste
    threads and dies should not.


    Packs + paste will help if there is a leak in the thread. If it is on the cone (it is leaking from this large nut), it means that either the cone finish (grinding) is damaged - if the flare nut is "ground" conical, without a gasket, or - if the flare nut is flat, the gasket - the gasket is damaged (she grew old). In the latter case, unscrew this large nut (after draining the water), replace the gasket and tighten the nut. If the surface of the cone is damaged or the flare nut is "ground" (without any gasket), it must be replaced. Sometimes it is possible to temporarily seal the damaged flare nut by wrapping it several times with Teflon tape so that when tightened (tightened) the tape forms a seal. It may also be the case that the flare nut is installed misaligned (and therefore leaky).
  • #10 16793887
    stanislaw1954
    Level 43  
    Posts: 15248
    Help: 2013
    Rate: 4675
    Zbigniew Rusek wrote:
    Quotation:
    Unfortunately, at around 60 degrees, water begins to drip / come out of the screw cap on https://photos.app.goo.gl/uC6jaPdYPm32NKPp1 IN THIS photo. A colleague from work said that it is enough to tighten, but I am not moving because I am afraid it will worsen, because once I tightened the screw above the boiler, it broke completely. It is probably because no one lived in the house for 3 years or smoked in the stove (the water was drained).

    Xantix wrote:
    When it drips, you can unscrew the flare nut (optionally replace it with a new one if you can see damage to the thread), put new tow on the thread and a decent sealing paste
    threads and dies should not.


    Packs + paste will help if there is a leak in the thread. If it is on the cone (it is leaking from this large nut), it means that either the cone finish (grinding) is damaged - if the flare nut is "ground" conical, without a gasket, or - if the flare nut is flat, the gasket - the gasket is damaged (she grew old). In the latter case, unscrew this large nut (after draining the water), replace the gasket and tighten the nut. If the surface of the cone is damaged or the flare nut is "ground" (without any gasket), it must be replaced. Sometimes it is possible to temporarily seal the damaged flare nut by wrapping it several times with Teflon tape so that when tightened (tightened) the tape forms a seal. It may also be the case that the flare nut is installed misaligned (and therefore leaky).
    This flare nut has an o-ring.
  • #11 16793944
    ROBSON33
    Admin of household appliances group
    Posts: 9730
    Help: 465
    Rate: 1714
    Zbigniew Rusek wrote:
    Sometimes it is possible to temporarily seal the damaged flare nut by wrapping it several times with Teflon tape so that when tightened (tightened) the tape forms a seal.


    But the photo shows that someone did just that, so it remains to replace the valve with a new one.
  • #12 16793957
    oczko991
    Level 10  
    Posts: 34
    Rate: 2
    it is rather sediment from the water that comes out there.
    it did not leak during the first year of heating, then after the summer period it started to come out each time as the boiler temperature is> 60 degrees
  • ADVERTISEMENT
  • #13 16794537
    stanislaw1954
    Level 43  
    Posts: 15248
    Help: 2013
    Rate: 4675
    If tightening does not help, with a "feeling" not to break, then the replacement of either the o-ring or the entire valve, with a screw connection. It is also possible that it is leaking from the top thread and that water is collecting at the bottom near the nut. To check it, just wrap this part of the screwdriver in the place marked with the arrow in the 1st photo (a little higher, preferably in the middle) with a thin wire. If water runs off the wire, it is flowing from the thread from above.
  • Helpful post
    #14 16794675
    Xantix
    Level 41  
    Posts: 6483
    Help: 686
    Rate: 1657
    oczko991 wrote:
    at the beginning, I would like to install a new regulator, because after turning it does not respond, I do not know how to operate and calibrate it

    Calibration is the basis for the regulator to work well:
    1. Assemble the regulator on the boiler.
    2. You heat the boiler to 60 degrees without the use of a regulator (manually controlling the flap).
    3. You set the regulator knob to a temperature about 5 degrees higher than that on the furnace thermometer.
    4. Use the screw on the regulator to adjust the arm so that it is in the horizontal position.
    5. You attach the chain to the flap by adjusting its length so that the flap has a slot as thick as a match.
    6. Now the regulator should work properly.

    oczko991 wrote:
    then seal the bottom door that has the largest gap

    Just don't seal the air supply flap.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around improving the efficiency of an old central heating boiler in Olsztyn, specifically addressing issues with temperature control and frequent refueling. The user experiences difficulties with the boiler requiring constant monitoring and fuel addition every 30 minutes, leading to water leakage at temperatures above 60 degrees. Participants suggest various solutions, including checking the pump's operation, replacing or sealing valves, and installing a new regulator for better temperature management. Recommendations include cleaning filters, sealing gaps, and ensuring proper calibration of the regulator to enhance boiler performance and reduce fuel waste.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Old coal boilers run best at 65–85°C; “65 degrees is the minimum temperature that most boilers should be operating at.” Fix leaks, clean the filter, calibrate the draft regulator, and service or replace a sticking differential valve. [Elektroda, Xantix, post #16793117] Why it matters: This FAQ helps owners of older solid‑fuel central‑heating boilers reduce babysitting, stop leaks, and heat safely on a budget.

Quick Facts

How do I stabilize an old boiler without adding a fan?

Use the ash‑pan flap and a mechanical draft regulator instead of a blower. Set the flap smaller to hold around 65–70°C. A draft regulator is cheaper than a fan and controller and avoids over‑firing. “Reaching 60 or 65 degrees is not a reason to fear.” [Elektroda, stanislaw1954, post #16789841]

What temperature should I run my boiler at?

Aim for 65–85°C. 65°C is the minimum most boilers should run at; 50°C causes soot and corrosion. The contributor reports operating sometimes at 85°C without issue. This improves combustion and protects the boiler body. “65 degrees is the minimum temperature that most boilers should be operating at.” [Elektroda, Xantix, post #16793117]

How do I calibrate a mechanical draft regulator?

Mount the regulator. Heat the boiler to 60°C manually. Set the knob about +5°C above the boiler thermometer. Level the regulator arm with its screw. Attach the chain so the flap shows a match‑thickness gap. The regulator should now control air reliably. [Elektroda, Xantix, post #16794675]

Should I add a blower and electronic controller to an old solid‑fuel boiler?

Skip the blower. On hand‑fed coal/wood units, blowers often waste fuel and complicate control. Fix air leakage, calibrate the mechanical regulator, and keep a safe operating range instead. Treat root causes first. “The blower and the solid fuel boiler do not work very well together.” [Elektroda, Xantix, post #16793117]

My differential bypass valve sticks or won’t close on pump speed 1–2. What should I do?

Remove and clean the valve. Ensure the internal ball moves freely. If behavior persists, replace the valve; typical new units start from ~40 PLN. A working bypass prevents uncontrolled short‑circuiting when the pump runs. Service it before chasing other faults. [Elektroda, Xantix, post #16793117]

How can I tell if my circulation pump actually runs on low speeds?

Place your ear on the pipes; you should hear the pump and feel flow‑related vibration even on speed 1 or 2. If you hear it, it is pumping water. Then adjust air and fuel rather than blaming the pump immediately. [Elektroda, stanislaw1954, post #16789841]

Water leaks from the screw/flare nut around 60°C—how do I fix it?

If threads leak, reseal with tow and paste after draining. If the cone/gasket leaks, remove the flare nut, replace the gasket, and retighten. Damaged conical faces require part replacement. Temporary Teflon‑tape wraps on a damaged cone are only stopgaps. [Elektroda, Zbigniew Rusek, post #16793711]

Do the boiler doors need sealing?

Yes. Seal the doors with glass cord to stop false air, which destabilizes temperature. Do not seal the air‑supply flap; the regulator must breathe through it. This improves control and reduces fuel waste. [Elektroda, Xantix, post #16793117]

My upstairs radiators are lukewarm—what’s the first fix?

Clean the strainer filter ahead of the pump. A clogged filter starves flow, making upper radiators underheat. This is a low‑cost, high‑impact first step before complex venting or pump replacement. [Elektroda, ROBSON33, post #16793440]

Is running at 50°C harming the boiler?

Yes. 50°C encourages smoldering and condensate, which accelerates boiler corrosion. Increase temperature to at least 65°C for efficient, cleaner burn. Users report reliable operation even at ~85°C when needed. [Elektroda, Xantix, post #16793117]

Quick leak diagnosis: is it the top thread or the flare nut?

How‑To: 1. Gently try tightening with feel; don’t over‑torque. 2. Wrap thin wire at mid‑stem above the nut; watch if water runs off the wire. 3. If it does, reseal the upper thread; if not, service the O‑ring or replace the valve. [Elektroda, stanislaw1954, post #16794537]

Can I light the boiler from the top, and why try it?

Yes. Top‑lighting can give steadier temperature and cleaner startup compared with “on the move” firing. It reduces the need to tend the fire every 30 minutes. Prepare the stove and try top‑lighting during your calibration steps. [Elektroda, Xantix, post #16793117]

Is removing the differential valve safe in case the pump fails?

No. Bypassing safety features risks dangerous overheating if the pump ever stops. The safer path is a functional bypass and calibrated air control. “Do not offer anyone to install a time bomb in the boiler room.” [Elektroda, Xantix, post #16793117]

What’s a simple way to confirm my regulator is actually moving the flap?

After calibration, watch the chain and flap as water heats. The arm should lower and raise, keeping a match‑thickness crack at idle. If it sticks, re‑level the arm and recheck the chain length. [Elektroda, Xantix, post #16794675]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT