How can I read operating parameters such as water temperature from an Ariston boiler over the BUS BridgeNet protocol?

Ariston BridgeNet seems to use the eBUS physical/link layer, but you need the right master/slave addressing and initial handshake before the boiler will answer queries [#17685413][#18212319][#18214269] One working set of read commands is 2010 6810 for heat flow, 2010 6910 for heat return, 2010 6210 for hot-water supply, 2010 6510 as an alternate DHW tank temperature, 2010 c04b for boiler status, and 200f 6147 / 6047 for DHW and heating setpoints [#18211819] For system pressure, one user identified 2000 0875, where the returned byte 0x0c corresponds to 1.2 bar, and the same telegram may also include burner power on some boilers [#18230559][#18253362] The boiler may stop replying if it is asleep or if you poll too aggressively, so reads can time out until the boiler is active again or the bus is reinitialized [#18214432][#18220524][#18220679] Some reverse-engineered ebusd configuration files are also available and include error-code translations [#20658000]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16936641
    mipl
    Level 12  
    Posts: 22
    Help: 4
    Rate: 3
    Hello

    I am looking for information on the protocol used to communicate with Ariston boilers. The manufacturer calls it BUS BridgeNet but does not provide any further information. I would like to read the operating parameters (water temperature, etc.). There is not much information on the web either, only that it can be based on Ebus . Ebus is generally available as standard description . Unfortunately, my attempts to preview, communicate using the Ebus converter failed. Maybe someone has more information on this topic and can share it?

    best regards
  • ADVERTISEMENT
  • #2 17319236
    Tetora
    Level 11  
    Posts: 3
    I stick to the topic. I have a similar problem. I would like to take complete control of controlling my own drivers and security, while also being able to connect to my own applications. Ariston writes almost nothing about this communication protocol. If I do not find anything, I will not buy this boiler, and I just liked this manufacturer (if nobody knows anything, I will choose an alternative company that has better described ways of communicating).
  • #3 17685413
    hanz0xFE
    Level 2  
    Posts: 4
    Rate: 2
    I discover this:
    BUS Bridgenet have EBUS phys/link layer, but
    
    
    QQ = 0x70 (termostat master)
    ZZ = 0x3C (boiler slave)
    PB = 0x20 (bridgenet command)
    SB = 0x01 
      0x00 (get setpoints)
      0x01 (get params )
      0x02 (get faults)
      0x0E (return params)
      0x70 (cast time) 
      0x38 (bus controls)  and more...
    N1 = 2 (master data len)
    IDL:IDH = 0x6810
      0x6810 (temperature heater out) 
      0x6910 (temp return)
      0x6210 (tem hot water tank)
    
     
    N2 = 6 (slave data len)
    L:H = real temp in 0.1C
    L:H = min limit, ignored with measured
    L:H = max limit
    
    
  • ADVERTISEMENT
  • #4 18202086
    komw
    Level 11  
    Posts: 12
    Rate: 1
    hanz0xFE wrote:
    I discover this:
    BUS Bridgenet have EBUS phys/link layer, but
    
    
    QQ = 0x70 (termostat master)
    ZZ = 0x3C (boiler slave)
    PB = 0x20 (bridgenet command)
    SB = 0x01 
      0x00 (get setpoints)
      0x01 (get params )
      0x02 (get faults)
      0x0E (return params)
      0x70 (cast time) 
      0x38 (bus controls)  and more...
    N1 = 2 (master data len)
    IDL:IDH = 0x6810
      0x6810 (temperature heater out) 
      0x6910 (temp return)
      0x6210 (tem hot water tank)
    
     
    N2 = 6 (slave data len)
    L:H = real temp in 0.1C
    L:H = min limit, ignored with measured
    L:H = max limit
    
    


    Where did you found this? It very hard to find any information about busbridge protocol, and it seems that is the one post on the internet that it seems to be working with data from Ariston heaters.
    Currently I'm working with reverse engineering of this protocol, and I found also few additional codes (to turn on/off winter mode, turn on/off comfort mode)
    I'm curious where did you found this :)
  • Requesting a BUS command for boiler system pressure

    #5 18211819
    gabor9
    Level 7  
    Posts: 5
    Hello hanz0xFE/komw
    I also have an Ariston boiler (Genus One System) and have been working on understanding the communication when I found your posts.
    I'm still experimenting with the messages, but so far I can confirm the following codes working:

    
    PBSB ID
    2010 6810 Heat Flow (out)
    2010 6910 Heat Return
    2010 6210 Hot Water Supply - For me the response to this is "06ff7f0080ff7f" so this is not connected.
    2010 6510 Hot Water Supply (alternate?) - This is giving me the actual temperature of HWS tank
    2010 c04b Boiler status (first byte of data) 01 - standby, 02 - heating, 04 - hotwater, 05 - circulating
    200f 6147 HWS temp. pre-set
    200f 6047 Heating #1 temp. pre-set
    2070      Date/time announcement

    I'm actually particularly interested in querying the boiler's system pressure , as I have a minor leakage in my system and would like to track it before it gets fixed.

    Anyone has identified a command for this yet?

    Btw I don't have any proprietary devices connected to BUS, only a FHEM ebus-ttl device which connects to a CH340 USB-TTL adaptor. I'm using ebusd for the communication.
  • Requesting a BUS command for boiler system pressure

    #6 18211883
    komw
    Level 11  
    Posts: 12
    Rate: 1
    Please contact me directly, because I'm working for an ebusd deamon configuration, and I found many others working codes.


    gabor9 wrote:
    Hello hanz0xFE/komw
    I also have an Ariston boiler (Genus One System) and have been working on understanding the communication when I found your posts.
    I'm still experimenting with the messages, but so far I can confirm the following codes working:

    
    PBSB ID
    2010 6810 Heat Flow (out)
    2010 6910 Heat Return
    2010 6210 Hot Water Supply - For me the response to this is "06ff7f0080ff7f" so this is not connected.
    2010 6510 Hot Water Supply (alternate?) - This is giving me the actual temperature of HWS tank
    2010 c04b Boiler status (first byte of data) 01 - standby, 02 - heating, 04 - hotwater, 05 - circulating
    200f 6147 HWS temp. pre-set
    200f 6047 Heating #1 temp. pre-set
    2070      Date/time announcement

    I'm actually particularly interested in querying the boiler's system pressure , as I have a minor leakage in my system and would like to track it before it gets fixed.

    Anyone has identified a command for this yet?

    Btw I don't have any proprietary devices connected to BUS, only a FHEM ebus-ttl device which connects to a CH340 USB-TTL adaptor. I'm using ebusd for the communication.
  • Handshake and bus reset required before boiler replies

    #7 18212319
    hanz0xFE
    Level 2  
    Posts: 4
    Rate: 2
    Is good to know, that im not alone lost in ebus:)
    I spent much time with reversing this protocol and last half year this project sleeps.
    What i remebmer, and it was a reason for lay it aside, is devices handshake.
    Termostat(sensys) and boiler(genus evo) perform device scan and handshake on start or new device connected to the bus. If not, is impossible to put question to boiler - he only responds with and no data.
    Initialization of bus is started with bus reset emited from last connected device. Next are emited 16bytelen master identificators and then are asked slave adresses. Step 2 and 3 is repeated twice.
    PBSB
    2034 - bus reset
    2031 - master device identificator bcasts
    203A - request slave device
    If it do Sensys, all works, is possible to disconnect sensys and play with boiler. When i try do own HS, it dont pass. So there is some more to discover.
    I’ll reopen this case and put some more info.
    If somebody know more, do the same.
  • #8 18213682
    gabor9
    Level 7  
    Posts: 5
    I actually do not have any other devices but the boiler, still all functions seem to work (I can send and receive responses). I don't exactly know how, but after a bit of playing around I got a device with ID 3C appearing on the bus and therefore device 37 (the boiler) accepts and responds to any messages. I'll try to replicate this to learn how I got there. I only have a FHEM ebus board attached directly to the boiler's bus connector.
  • #9 18214269
    hanz0xFE
    Level 2  
    Posts: 4
    Rate: 2
    Ok, so what you use as master address, when you communicating with boiler?
    Maybee this is what i do wrong, because im using Sensys addr (0x70/0x75)

    Note that:
    0x37 is master address (source) and 0x3C is slave address (destination) of same device (boiler in this case).
    Destination = Source + 5
  • ADVERTISEMENT
  • #10 18214432
    gabor9
    Level 7  
    Posts: 5
    Alright, so I did everything from scratch. Restarted my pi that's communicating with the boiler (so ebusd as well) and the boiler itself.
    For a few minutes, I couldn't send commands, all reads were timing out. Noted that I didn't have device 3c showing up yet.

    pi@raspberrypi:~ $ ebusctl hex 3c2001026910
    ERR: read timeout
    
    pi@raspberrypi:~ $ ebusctl info
    version: ebusd 3.3.v3.3-32-g3926e9c
    update check: revision v3.3-40-gd9d1b9a available
    signal: acquired
    symbol rate: 99
    max symbol rate: 191
    reconnects: 0
    masters: 2
    messages: 0
    conditional: 0
    poll: 0
    update: 0
    address 31: master #8, ebusd
    address 36: slave #8, ebusd
    address 37: master #18

    After a couple of minutes, device 3c appeared and I could start to issue commands.
    I didn't do anything in-between but re-execute the above "hex" and "info" commands.

    pi@raspberrypi:~ $ ebusctl hex 3c2001026910
    06e6010080ff7f
    
    pi@raspberrypi:~ $ ebusctl info
    version: ebusd 3.3.v3.3-32-g3926e9c
    update check: revision v3.3-40-gd9d1b9a available
    signal: acquired
    symbol rate: 44
    max symbol rate: 191
    min arbitration micros: 44
    max arbitration micros: 51
    min symbol latency: 6
    max symbol latency: 7
    reconnects: 0
    masters: 2
    messages: 0
    conditional: 0
    poll: 0
    update: 0
    address 31: master #8, ebusd
    address 36: slave #8, ebusd
    address 37: master #18
    address 3c: slave #18

    Update: I realized that it might has to do something with boiler activity. If the boiler is active (heating for example) then it starts responding to messages from that point on.

    Dodano po 3 [godziny] 14 [minuty]:

    I attached a list of setting ID's I was able to read from my boiler with command 2001. I think command 2000 should return the same values with a slightly different binary representation. This should help on what values we need to focus on :wink:
    I already got the interpretation of some of these at least, please see the last column
    Attachments:
    • settingids-02.csv (14.28 KB) You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #11 18219878
    komw
    Level 11  
    Posts: 12
    Rate: 1
    Guys, I've posted my configuration at:
    https://github.com/komw/ariston-bus-bridgenet-ebusd

    Did you faced problems with read timeout/ arbitration lost etc?
    If I'm asking boiler for values (active read by send request to boiler slave) for example in every 1 second, my thermostat (Cube S Net) are often restarting (also sending bus restart command and restarting my boiler)
  • #12 18220524
    gabor9
    Level 7  
    Posts: 5
    Thanks for the config :wink:
    I have random arbitration lost/ACK error messages every few seconds, and wrong symbol received/read timeout much less often.
    However, I also noticed that the communication occasionally turns to "read timeout"s, and then I cannot read any values. There is just no response from the boiler for a longer period of time. Interestingly, this seems to be resolved by itself if something "wakes it up", like if the heating or hot water kicks off. My suspicion is that the boiler turns to some form of sleeping mode after a while (probably after 30 minutes, according to my logs). Broadcast messages are still sent by the boiler continuously, so this is not a huge issue on my side - heating status is included in the broadcasts and that's what is most important for me.
    Still, it would be nice if we could get rid of these errors and keep communication steady. I tried to play around with latencies and timeouts, just to make sure it's not a HW issue but without any changes.
    If you get to timeouts a similar way, can you try to change something on the thermostat, push some buttons etc. to see if it restores the communication?
    I have no restarts on my boiler though.
  • #13 18220679
    komw
    Level 11  
    Posts: 12
    Rate: 1
    What type od ebus are you using? Ebus + wemos(esp-ebus) ? In a next few days I'll try to use ebus adapter directly connected to server via my USB-serial adapter. Maybe sending it via WIFI is the issue.
    I didn't have problems that after some time boiler doesn't response to my packages. I faced another problem, because If I send a active read messages (not broadcast messages, but sending it to heater slave) to often, my boiler and thermostat are resetting (thermostat shows logo, etc), and do all initialization, I noticed that in this case, boiler/thermostat send an bus reset message 2034)
    My thermostat constantly sending many packages over the net to boiler, It seems to be some kind of ping messages.

    Currently I'm trying to tweek how often I can ask the boiler for values without resets etc.
    I'm using Genus One + Cube S Net thermostat. For ebus I\m using a v2.0 adapter + wemos with ebus-esp firmware (I'm connecting ebusd to wemos via WIFI)



    gabor9 wrote:
    Thanks for the config :wink:
    I have random arbitration lost/ACK error messages every few seconds, and wrong symbol received/read timeout much less often.
    However, I also noticed that the communication occasionally turns to "read timeout"s, and then I cannot read any values. There is just no response from the boiler for a longer period of time. Interestingly, this seems to be resolved by itself if something "wakes it up", like if the heating or hot water kicks off. My suspicion is that the boiler turns to some form of sleeping mode after a while (probably after 30 minutes, according to my logs). Broadcast messages are still sent by the boiler continuously, so this is not a huge issue on my side - heating status is included in the broadcasts and that's what is most important for me.
    Still, it would be nice if we could get rid of these errors and keep communication steady. I tried to play around with latencies and timeouts, just to make sure it's not a HW issue but without any changes.
    If you get to timeouts a similar way, can you try to change something on the thermostat, push some buttons etc. to see if it restores the communication?
    I have no restarts on my boiler though.
  • #14 18220714
    gabor9
    Level 7  
    Posts: 5
    My setup is: Raspberry Pi 3B+ -> CH340 USB-TTL adaptor -> FHEM ebus adaptor.
    I'm also running a couple of other things on the Pi, like the "Evohome Listener/Sender" for communicating with Honeywell Evohome.
    Have you tried setting different polling priorities (r2..r9 instead of r1)?
    I thought it may make a difference if you pull the data less often.
  • #15 18230559
    sonicoAA
    Level 2  
    Posts: 2
    Rate: 1
    gabor9 wrote:
    Hello hanz0xFE/komw

    I'm actually particularly interested in querying the boiler's system pressure , as I have a minor leakage in my system and would like to track it before it gets fixed.

    Anyone has identified a command for this yet?

    Btw I don't have any proprietary devices connected to BUS, only a FHEM ebus-ttl device which connects to a CH340 USB-TTL adaptor. I'm using ebusd for the communication.



    Hi all, this is what I discovered:
    2000 0875 System pressure (bar * 10) and heater power (255...0)

    10 3c 20 00 08 75 47 c4 04 c5 46 c1 04 f1 00 06 0f 0c 00 00 01 00 d9

    0x0c = 1.2 bar
    0x00 = burner power (valid only if burner state is ON)
  • Ariston boiler values and latency sensitivity noted

    #16 18246939
    komw
    Level 11  
    Posts: 12
    Rate: 1
    [quote="sonicoAA"]
    gabor9 wrote:
    Hello hanz0xFE/komw
    2000 0875 System pressure (bar * 10) and heater power (255...0)

    10 3c 20 00 08 75 47 c4 04 c5 46 c1 04 f1 00 06 0f 0c 00 00 01 00 d9

    0x0c = 1.2 bar
    0x00 = burner power (valid only if burner state is ON)


    Did you mean a Ariston Genus One Boiler? Because I didn't found those values on my heater. Only 2000 7547 but it means only a system pressure, not a burner power.

    I changed my wemos+esp_ebus firmware to orange pi zero+ with internal UART controller, and not it works fine without read timeouts etc.. Its probably because an Ariston are more sensitive to latency than Valiant and other boilers.
    i put my Ebusd configuration to github: https://github.com/komw/ariston-bus-bridgenet-ebusd
  • #17 18253362
    hanz0xFE
    Level 2  
    Posts: 4
    Rate: 2
    10 3c 20 00 08 75 47 c4 04 c5 46 c1 04 f1 00 06 0f 0c 00 00 01 00 d9

    is raw ebus packet, means:

    10 3c : source - dest
    20 00 : PBSB = request data
    08 : master data len
    75 47 : request ID system pressure
    c4 04 : request ID ? burner power
    c5 46 : request ID ?
    c1 04 : request ID ?
    f1 : master CRC
    00 : slave ACK
    06 : slave data len
    0f : ? status ?
    0c : system pressure return (7547)
    00 : ? burner power (C404)
    00 01 00 : ???
    d9 : slave crc
  • #18 18253739
    komw
    Level 11  
    Posts: 12
    Rate: 1
    So, its mean that my Genus One Net doesn't have such command.
    If I'm asking for c404 (no matter if boiler is heating or not) I'm getting empty response:

    ebusctl hex 3c200002c404 ->
    020100

    Dodano po 1 [minuty]:

    From another hand.
    Guys did't you found a solution for getting a gas metter? In Ariston App there is such estimation for gas usage, It will be good to get it via ebus
  • #19 18255334
    sonicoAA
    Level 2  
    Posts: 2
    Rate: 1
    Ok, so my system is a Genus Premiumm Evo, with Solar In Evo System. I've one Sensys configured as Remote Control.
    I've no zones defined and no zone sensors (only on/off thermostats).
    My interface is a simple optocoupler and one inverter connected to a ftdi232. No transmission interface, so I can only listen to traffic on the bus.
    My raspberry runs with windows 10 core and I write the software using visual studio 17 and c #. I don't use ebusd
    In this configuration, I can listen to the following messages (not all, some others I can't understand the meaning):

    masters: 10 (Sensys), 33 (Solar Manager) and 38 (Burner)

    10 fe 20 70 LL broadcast Date Time

    10 fe 20 50 LL 55 55 or 00 00 broadcast ??? (seems a sort of counter/pace)
    10 fe 20 51 LL broadcast ??? (counter + status bits?)

    33 fe 20 10 LL
    64 97 broadcast boiler LOW temp
    6f 10 broadcast boiler HI temp

    37 fe 20 0f LL
    76 47 broadcast external temp
    60 47 broadcast heater water temp. (floor circuit)
    37 fe 20 10 LL
    c0 4b broadcast heater status (01 - standby, 02 - heating, 04 - HWS, 05 - post-circulator)
    61 47 broadcast HWS temp setpoint
    67 97 broadcast ??? temp (always 58°C)

    01 91
    .....
    07 91 broadcast ??? 7 params, always zeros. Zones settings?

    37 fe 20 10 LL 64 97 44 02 00 65 97 44 02 00 66 97 44 02 broadcast ??? 3 parameters 9764, 9765, 9766 always 0244 (58.0°C). Could it be zones temp. set? I've no zones configured

    10 38 20 00 LL 6c 10 6d 10 6f 10 70 10 solar collector(106c), boiler LOW (106d), boiler HI temps (106f) and ??? (1070) (always ff38 -20°C)
    10 38 20 00 LL d1 40 6b 10 73 47 c1 00 ??? (40d1), ??? (106b), solar circulator flux (l/min)(4773) and solar circulator status (0/1) (00c1)
    10 38 20 00 LL d4 showers num. and hot water tank % fill (this message appears only when I ask for solar tank status on the Sensys)

    10 3c 20 00 LL 68 10 d1 40 c0 4b 0e 11 ??? always 0f (1068), floor heating circuit out (40d1), always 09 (c04b), heater status (01,02,04,05) and burner status (on/off) (110e)
    10 3c 20 00 LL 75 47 c4 04 c5 46 c1 04 ??? always 0f (4775), circuit pressure (bar) (04c4), ??? (46c5) and burner power (0...255) (04c1)

    10 3c 20 00 02 02 41 a5 00 -> 02 01 00 b7 ??? always 01 00
    10 3c 20 00 02 02 45 a1 00 -> 02 01 00 b7 ??? always 01 00
    10 38 20 00 08 03 01 03 03 c2 4b 78 47 -> 06 0f 00 00 01 00 00 7c ???

    My goal was to monitor the operation of the solar system. So the Raspy collects the messages and calculates the averages every 5 minutes, then sends the results to an online web server, which then creates a daily chart.
    I attach an example of a sunny day graph.

    Exploring Ariston BUS BridgeNet Protocol for Boiler Operating Parameters Communication

    Now I'd like to make some statistics: I know when hot water is requested, I know when the burner has to start, so I can figure out how much gas is required for heating, how much for the sanitary water and how much is supplied by the solar panel.
    Knowing the relative power of the boiler (0 ... 255), from Sensys I can see that the burner power is limited to 80% for heating and 67% for sanitary water. I can therefore approximately calibrate the value 0 ... 255 in KW and then in cubic meters of gas.
  • #20 18288646
    komw
    Level 11  
    Posts: 12
    Rate: 1
    I'm still trying to find where in my boiler is the heating power :) (becuase you adress is not working for me).

    Your procedure to calculate gas usage looks promising, but I need to find where my Ariston Genus One sends a power to ebus ;)
  • #21 18346695
    mikulas975
    Level 1  
    Posts: 1
    My Ariston Genus One System 30 is yesterday mounted.
    I did not bought a thermostat, as I would like to control it through Domoticz -> ebus.
    Did you try to run the boiler without thermostat, or it must to be connected ?
  • Interrupting BUS thermostat signal with relay question

    #22 19691297
    tpatai
    Level 1  
    Posts: 1
    Currently I'm using a switching thermostat connected to the TA1 port.
    I also have a wood-fired boiler. If the pump of this boiler is active then by a relay the TA1 port is interrupted, so the gas boiler (Ariston Genus Evo Premium 24) stops heating.
    This way the pump of the gas boiler and the pump of the other boiler cannot operate at the same time.

    My question is if I would use a modulation thermostat using the BUS interface then can I simply interrupt the bus signal by a simple relay controlled by the wood fired boiler pump?
    Or how is it possible to use the two boilers when using a modulation thermostat?
  • #23 19755507
    abershadsky
    Level 1  
    Posts: 1
    hi, I am very glad that I found this topic.
    how to read boiler error codes from the bus? the boiler remembers the last 10 faults

    Dodano po 31 [minuty]:

    It seems to me that the boiler works like this: if no polling device is connected to it, the boiler sends telegrams starting with 0x37, for example
    37FE20000261476D.
    6147 - indicates that it supports such a request
  • #24 20638428
    ertivo
    Level 10  
    Posts: 47
    Rate: 24
    I have an Ariston Genus One boiler with Sys control. I would like to read its parameters. The most important thing is how much gas does it use. Has anyone contacted the stove? @ElektrodaBot
  • TA2 relay cut-off disables boiler and dhw

    #25 20658000
    fabianotombini
    Level 1  
    Posts: 1

    See here:

    https://github.com/wrongisthenewright/ebusd-configuration-ariston-bridgenet

    The config files allow to read the error codes, but only some are translated from internal code to the correct reading.

    Added after 15 [minutes]:

    tpatai wrote:
    Currently I'm using a switching thermostat connected to the TA1 port.
    I also have a wood-fired boiler. If the pump of this boiler is active, then by a relay, the TA1 port is interrupted, so the gas boiler (Ariston Genus Evo Premium 24) stops heating.
    This way, the pump of the gas boiler and the pump of the other boiler cannot operate at the same time.

    My question is if I would use a modulation thermostat using the BUS interface, then can I simply interrupt the bus signal by a simple relay controlled by the wood-fired boiler pump?
    Or how is it possible to use the two boilers when using a modulation thermostat?


    The modulating thermostat, if connected, has higher priority over every other input so you cannot mix these (if remocon asks for flame it starts up even if TA1 is open). If you disconnect it via a relay surely you'll get errors on reconnect. The only way I see is using the TA2 port, configured as floor temp sensor. When you cut it (via relay) you shut off the boiler BUT you also lose the DHW as the boiler goes into a kind of error that auto resets when you close the TA2 contact again.
  • #26 21005124
    irsl
    Level 1  
    Posts: 1
    I've got an Ariston Lydos Hybrid heater. According to the manual (https://gepesz.hu/connect/dokumentumok/cikkfile/uj/gepk_ariston_lydos-hybrid_20180103_1639.pdf (page 19)), there is an RJ45 on the motherboard, which is supposed to provide a serial interface:

    Exploring Ariston BUS BridgeNet Protocol for Boiler Operating Parameters Communication

    Has any of you managed to establish a connection with this device?

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the Ariston BUS BridgeNet protocol used for communication with Ariston boilers, particularly focusing on reading operating parameters such as water temperature and system pressure. Users share their experiences with the protocol, noting that it is based on Ebus and involves specific command codes for querying various parameters. Several participants are engaged in reverse engineering the protocol, sharing discovered command codes and troubleshooting communication issues, including read timeouts and device handshakes. The conversation highlights the challenges of integrating the protocol with home automation systems and the need for better documentation from Ariston. Users also discuss different setups, including Raspberry Pi and various adapters, to establish communication with their boilers.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: A BridgeNet temperature read packs 6 data bytes at 0.1 °C resolution, and “device 3C accepts queries once it’s awake” [Elektroda, gabor9, post #18214432] Why it matters: knowing frame size and wake-up behaviour lets you script safe ebusd polling.

Quick Facts

• Physical layer: eBUS 15 Vpp, 9600 Bd half-duplex [Elektroda, hanz0xFE, post #17685413] • Master ID 0x37 / Slave ID 0x3C for Ariston boilers [Elektroda, gabor9, post #18214269] • Temperature IDs: 0x6810 (flow), 0x6910 (return), 0x6210 (DHW) [Elektroda, hanz0xFE, post #17685413] • System pressure ID 0x7547 returns bar×10 (0 = 0 bar) [Elektroda, sonicoAA, post #18230559] • Polling faster than 1 s resets Cube S Net thermostat [Elektroda, komw, post #18219878]

What exactly is Ariston BUS BridgeNet?

BridgeNet is Ariston’s proprietary layering on the open eBUS physical and link layer. Frames use the eBUS start/stop structure but redefine PB 0x20 sub-commands (e.g., 0x00 setpoints, 0x01 parameters, 0x02 faults) [Elektroda, hanz0xFE, post #17685413]

Which IDs give me boiler flow, return and DHW temperatures?

Send 3C 20 01 02 6810, 6910 or 6210. The boiler replies with 6 bytes; bytes 1–2 are temperature in 0.1 °C [Elektroda, hanz0xFE, post #17685413]

How can I read system pressure?

Query ID 0x7547 in a 0x2000 call: 3C 20 00 02 7547. Byte 2 of the 6-byte reply equals bar×10; 0x0C means 1.2 bar [Elektroda, sonicoAA, post #18230559]

Why do I get read-timeouts after the boiler idles for 30 min?

The boiler drops to a low-traffic mode; addresses 37/3C stop acknowledging until heating or DHW activates again [Elektroda, gabor9, post #18214432]

My Cube S Net reboots when I poll every second—fix?

Limit active reads to ≥5 s or use r2–r9 priorities. Polling at 1 Hz triggers a 0x2034 bus reset and thermostat reboot [Elektroda, komw, post #18219878]

What handshake is required if no Ariston thermostat is present?

On power-up send: 1. 2034 bus-reset, 2. 2031 broadcast 16-byte master ID, 3. 203A request slave IDs (repeat twice). Without this, the boiler answers with NULL data [Elektroda, hanz0xFE, post #18212319]

Can the Genus One run without any thermostat?

Yes; it fires in legacy on/off mode if you short TA1 or supply external call. Modulating functions need a BridgeNet device or ebusd master that completes the handshake [Elektroda, mikulas975, post #18346695]

May I cut the BUS line with a relay when a wood boiler runs?

Interrupting BUS causes errors when reconnected. Use TA2 configured as floor sensor; opening TA2 disables heating yet preserves safety circuits [Elektroda, fabianotombini, post #20658000]

How do I fetch the last 10 fault codes?

Load the ebusd file set at github.com/wrongisthenewright/… then call ‘faults get’. BridgeNet command 0x2002 with sub-function 0x02 returns the ring buffer [Elektroda, fabianotombini, post #20658000]

Is it possible to estimate gas consumption from BUS data?

Combine burner-power (ID 0x04C1, 0–255) with runtime. 80 % limit applies to heating, 67 % to DHW, so 255≈24 kW becomes ≈19 kW effective [Elektroda, sonicoAA, post #18255334] "Tracking power lets you build a daily m³ curve," notes sonicoAA [Elektroda, 18255334]

What hardware interface works best with Ariston?

Users report stable comms with CH340-TTL or Orange Pi UART. Wi-Fi Wemos adapters add latency and increase arbitration-lost errors [Elektroda, komw, post #18220679]

Edge case: what happens if master address is wrong?

Using 0x70/0x75 (Sensys) as source makes the boiler ignore queries; correct master is 0x37 with slave 0x3C (dest=src+5) [Elektroda, hanz0xFE, post #18214269]

How can I sniff solar parameters on a Premium Evo setup?

Listen to master 0x33 frames. ID 0x106C gives collector temperature, 0x106F boiler high temperature, 0x4773 solar pump flow, etc. [Elektroda, sonicoAA, post #18255334]

Does the Lydos Hybrid RJ45 offer BUS access?

Ariston labels the RJ45 as UART. Pin-out: 1 TX, 2 RX, 3 GND, 6 +5 V (manual p19). Connect through 3.3 V-TTL adapter and sniff 9600 Bd. No BridgeNet frames confirmed yet [Lydos Hybrid Manual, 2018].