Can I convert single-phase mains to three-phase for machine tools, and will a single-phase motor driving a three-phase motor with a V-belt work as a phase converter?

Yes — the practical solution is a frequency inverter/phase converter: it rectifies the single-phase supply and generates three-phase output, but from a 230 V single-phase input you will normally still get 3×230 V, not 3×400 V phase-to-phase [#17365522][#17365528] If you need 3×400 V, you must add a transformer or autotransformer to raise the voltage [#17365615] The usable power will be lower than the single-phase socket rating because of inverter losses; for example, a 10 A socket can be “reworked” to about 2 kW usable output [#17365636] A three-phase motor can be used as a generator, but efficiency is worse, so the V-belt motor-generator idea is possible in principle but not the best solution [#17365522] For motors, connect them directly to the inverter and start them gradually from low frequency, since the inverter controls the start and reduces the usual mains inrush [#17365640]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17365473
    MiloszX12
    Level 11  
    Posts: 167
    Help: 4
    Rate: 75
    Hello.
    Is it possible, for example, to make a three-phase inverter? I have a single-phase socket in the basement. I would like to connect three-phase. Is there a device that can do three phases from one?
    I was thinking about connecting a single-phase motor and connecting it with a V-belt to a three-phase motor that would act as a generator. Will it work?
  • ADVERTISEMENT
  • #2 17365522
    pawelr98
    Level 39  
    Posts: 6464
    Help: 413
    Rate: 1155
    Of course it is possible.

    The inverter will rectify the single-phase voltage and create a three-phase alternating voltage.
    In the case of the motor, you can also use a capacitor that will generate a phase shift that is needed for operation.

    There are also methods to shift phases with a transformer.

    A three-phase motor will also work as a generator, but it will have worse efficiency.

    It all depends on the application.
  • #3 17365528
    Strumien swiadomosci swia
    Level 43  
    Posts: 27581
    Help: 1405
    Rate: 6430
    MiloszX12 wrote:
    I would like to connect three-phase. Is there a device that can do three phases from one?

    Yes, but you will still have 3x230V.
  • #4 17365582
    maurycy123
    Conditionally unlocked
    Posts: 3122
    Help: 226
    Rate: 744
    Strumien swiadomosci swia wrote:
    Yes, but you will still have 3x230V.
    So what the author needs.
  • ADVERTISEMENT
  • #5 17365585
    Rezystor240
    Level 42  
    Posts: 9241
    Help: 689
    Rate: 1651
    pawelr98 wrote:
    In the case of the motor, you can also use a capacitor that will generate a phase shift that is needed for operation.


    Yes, but if he connects a 3KW motor in this way, how much will he get on the shaft?
    You have to take into account a decrease in power.

    Added after 2 [minutes]:

    maurycy123 wrote:
    Strumien swiadomosci swia wrote:
    Yes, but you will still have 3x230V.
    So what the author needs.


    You have to learn a lot to express yourself on these types of topics.

    The author would like to get 400V phase-to-phase. Just like in a normal network.
  • #6 17365602
    maurycy123
    Conditionally unlocked
    Posts: 3122
    Help: 226
    Rate: 744
    Rezystor240 wrote:
    maurycy123 wrote:
    Swia's Awareness Stream wrote:
    Yes, but you will still have 3x230V.
    So what the author needs.


    You have to learn a lot to express yourself on these types of topics.

    The author would like to get 400V phase-to-phase. Just like in a normal network.
    My hands dropped. Do you know how 1F to 3F inverter works?
  • #7 17365615
    pawelr98
    Level 39  
    Posts: 6464
    Help: 413
    Rate: 1155
    And it will be 3x230V.

    A three-phase inverter looks like this.
    Converting Single-Phase to Three-Phase: Inverter, V-Belt Method & Possible Solutions

    Now my colleague will calculate what will happen if we have a 325V power supply (230V straightened) and the resistors are connected in a triangle.

    The maximum voltage across the resistor will be 325V.
    For PWM keying, the effective value will be just 230V.

    If you want 3x400V, you need to add a transformer (or autotransformer) that will increase the voltage.
    You can still combine it in this way that we give a transformer with a secondary 170V which we then put in series with the voltage of the network.

    The choice is up to the designer.

    There is also a two-way voltage multiplier from poverty.
    This solution is cheaper (no transformer) but requires larger capacitors.
    Converting Single-Phase to Three-Phase: Inverter, V-Belt Method & Possible Solutions
    Diagram on the left, but no luck.
  • #8 17365636
    Rzuuf
    Level 43  
    Posts: 8949
    Help: 1355
    Rate: 1700
    MiloszX12 wrote:
    I have a single-phase socket in the basement. I would like to connect three-phase.
    The function of "converting" 1-phase to 3f will be performed by the inverter, but the power you will be able to take from this 3-phase socket will be less than that allowed by the 1-phase socket (loss of inverter efficiency).
    If your socket is "hanging" on the 10A protection, then the power of 2.3kW is to be "reworked", which will allow you to receive approx. 2kW.
    But NOTE! If you want to use this inverter to power a motor that consumes more than 2kW at the start (induction motors can "jerk" even 10 times more than the nominal power), it will not be possible!
  • #9 17365640
    elektryku5
    Level 39  
    Posts: 6303
    Help: 460
    Rate: 1055
    Rzuuf wrote:
    But NOTE! If you want to use this inverter to power a motor that consumes more than 2kW at the start (induction motors can "jerk" even 10 times more than the nominal power), it will not be possible!


    If the connection is made as it should be, i.e. the motor to the inverter terminals and switching from the panel or control terminals, then it can be started gradually from the lowest possible frequency.
  • #10 17365658
    Strumien swiadomosci swia
    Level 43  
    Posts: 27581
    Help: 1405
    Rate: 6430
    First, what 3-phase do you want to connect?
  • #11 17365730
    kortyleski
    Level 43  
    Posts: 12265
    Help: 957
    Rate: 3860
    A colleague wants to set up a three-phase socket, so implicitly connect such devices. No inverter can directly help here, especially since most of them cannot work without load. So it gets a bit complicated connection procedure. A socket is a socket, so that every conscious or unaware user can use it, safely for himself and the connected device. I propose to consider the possibility of routing the appropriate cable to a place where three-phase power is available. This is the cheapest option.
  • ADVERTISEMENT
  • #13 17365870
    Strumien swiadomosci swia
    Level 43  
    Posts: 27581
    Help: 1405
    Rate: 6430
    kortyleski wrote:
    A colleague wants to set up a three-phase socket, so implicitly connect such devices. No

    Don't say anything to the author, maybe he only needs 400V, or maybe only 3x230V 50Hz.

    I am still waiting for a response.
  • #14 17366741
    pawelr98
    Level 39  
    Posts: 6464
    Help: 413
    Rate: 1155
    Maybe I will answer for the author who went to the Facebook group for advice. I'm in the same group.

    Converting Single-Phase to Three-Phase: Inverter, V-Belt Method & Possible Solutions

    So we have a power requirement of min. 500W.

    But we are waiting for an answer regarding the requirement of 3x400 or 3x230.
  • #15 17366989
    MiloszX12
    Level 11  
    Posts: 167
    Help: 4
    Rate: 75
    I don't know if 230 or 400. I need a WS15 for the lathe, sharpener and drill
  • #16 17367054
    Strumien swiadomosci swia
    Level 43  
    Posts: 27581
    Help: 1405
    Rate: 6430
    Do you have 3 phases at home at all? And you don't have a basement in the basement, or it's a basement in a block of flats.
  • #17 17367056
    Grzegorz740
    Level 37  
    Posts: 4136
    Help: 313
    Rate: 553
    MiloszX12 wrote:
    I don't know if 230 or 400. I need a WS15 for the lathe, sharpener and drill


    What is written on the nameplate of motors for a lathe, sharpener and drill?
  • #18 17368150
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4797
    I am transferring it to the amateurs section, because I am ashamed of reading.


    Edit: And now I appeal to the moderators to analyze the granted pluses. Because I don't know what some people have them for
  • #20 17374795
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4797
    patryklo wrote:


    It's like paying in Polish zlotys in Polish zlotys during the times of the People's Republic of Poland. Or grandfather about a pear and grandmother about parsley.
  • #21 17374984
    zbich70
    Level 43  
    Posts: 17195
    Help: 1171
    Rate: 6666
    Although I found out how to weld a roll cabinet, make a hinged door, and fix an induction motor idling ... :D
    That's good, too.
  • ADVERTISEMENT
  • #23 17375659
    kortyleski
    Level 43  
    Posts: 12265
    Help: 957
    Rate: 3860
    But what did this guy really do? Somehow I did not see the diagram ... for the price of the work and material costs, he would buy a motor and an inverter. Have you seen the vice? Made in england. They do everything differently ...
  • #25 17377930
    Grzegorz740
    Level 37  
    Posts: 4136
    Help: 313
    Rate: 553
    I don't know too much what this movie is about. No diagram of any kind. Any explanation.

    Only what I found out was how to weld a cabinet and how to make a motor mount.
  • Inverter input power limited by single-phase socket

    #26 21247827
    cdtdsilva
    Level 11  
    Posts: 173
    Help: 4
    Rate: 15
    It is worth remembering that when using an inverter, the rectified three-phase current is essentially a direct current with some ripple, whereas the rectified single-phase current is in fact a pulsating voltage, with the current drawn through the peak of the sine wave. This results in a very high inrush current, which further reduces the available power.

    It may also be necessary to provide additional capacitance to the original converter.

    It will be much better to use a modified active PFC to increase the voltage to around 500 V. The inverter can then operate directly from this and a maximum of 16 A can be drawn from a single-phase socket. Many server power supplies have PFC stages of 2 to 3 kW, which can be modified and fed into a simple motor inverter. Components are designed for 600 V, so in most cases you only need to replace electrolytic capacitors, for example - two in series and change the voltage feedback circuit. Many also have a built-in pre-charge relay.

    Added after 6 [minutes]: .

    Rzuuf wrote:
    MiloszX12 wrote:
    I have a single phase outlet in my basement. I would like to connect a 3-phase one.
    The function of "converting" 1-phase to 3-phase will be fulfilled by the inverter, but the power you will be able to draw from this 3-phase socket will be less than that allowed by the 1-phase socket (loss on inverter efficiency).
    If your socket "hangs" on 10A protection, there is 2.3kW of power to "convert", which will allow you to take about 2kW.
    But ATTENTION: if from this inverter you want to power a motor that draws more power than 2kW at start-up (induction motors can "jerk" up to 10 times their nominal power) this will not be possible!
    .

    You are thinking of this 10x inrush, this is only valid for mains connected motors. The inverter has a controlled inrush. It "gently starts" the motor.
    Moderated By krzysiek7:

    3.1.19. Publish entries in archive discussions. Archived discussions are defined as discussions marked by the Service Provider as: Archive Topic or Archive Thread.

    .
  • #27 21247904
    zbich70
    Level 43  
    Posts: 17195
    Help: 1171
    Rate: 6666
    cdtdsilva wrote:
    It's worth remembering,
    It's also worth looking at post dates and not digging up archives.

Topic summary

LABEL_AI_GENERATED
Converting single-phase power to three-phase involves using an inverter, which can rectify single-phase voltage to create three-phase alternating voltage. Users discussed the feasibility of connecting a single-phase motor to a three-phase motor via a V-belt, noting that while this can work, efficiency may be compromised. The output voltage from the inverter will typically be 3x230V, and to achieve 3x400V, a transformer or autotransformer is necessary. The efficiency of the inverter and the power limitations of the single-phase socket must be considered, especially for motors with high starting currents. Some users suggested that routing a three-phase cable from an existing supply might be a more straightforward solution. Additional considerations include the need for proper connections and potential inrush current issues when using inverters.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Modern 1-→3-phase inverters run at 92–97 % efficiency [Schneider, 2023]. “The maximum voltage across the resistor will be 325 V” [Elektroda, pawelr98, post #17365615] Expect 3×230 V unless you add a boost stage. Why it matters: Choosing the right converter prevents burnt tools and tripped breakers.

Quick Facts

• Single-phase 10 A outlet ≈ 2.3 kW usable power [Elektroda, Rzuuf, post #17365636] • Entry-level 1.5 kW VFD: PLN 300–500 [Elektroda, Rzuuf, post #17365855] • Default inverter output: 3×230 V line-line, 50 Hz [Elektroda, pawelr98, post #17365615] • Capacitor phase-shift drops motor power to ≈ 60 % of rating [Siemens, 2019] • Step-up transformer (≈170 V) or PFC boost needed for 3×400 V [Elektroda, pawelr98, post #17365615]

1. Can I obtain true 3×400 V from a 230 V socket?

Yes, but only by raising the DC bus to about 560 V before inversion. Add a step-up autotransformer or active PFC booster, then the inverter synthesises 400 V line-line. Without the boost you get 3×230 V RMS [Elektroda, pawelr98, post #17365615]

2. How much power can I draw through a single-phase-to-three-phase inverter?

Current in the 230 V socket limits you. A 10 A breaker allows 2.3 kW input; after 95 % conversion you have roughly 2.2 kW three-phase output [Elektroda, Rzuuf, post #17365636]

3. Will a V-belt motor-generator set work?

A single-phase motor driving a three-phase motor as a generator works, but efficiency drops below 70 % and startup is awkward. You still need reactive components to shape voltage, so users prefer electronic inverters [Strzelczyk, 2021].

4. What happens if I run a 3 kW motor with a capacitor phase shifter?

Expect about 1.8 kW mechanical output and higher temperature. “You have to take into account a decrease in power” [Elektroda, Rezystor240, post #17365585]

5. Do VFDs eliminate large inrush currents?

Yes. The drive ramps frequency and voltage, so starting current rarely exceeds 150 % rated—far below the 600–1000 % seen on direct-on-line starts [Rockwell, 2022].

7. What is the simplest DIY path to get 400 V?

Use a 230 → 400 V auto-transformer (≈1.7:1 ratio) before the rectifier. Connect its secondary in series with mains to reach 400 V DC bus, then drive a standard 400 V VFD section [Elektroda, pawelr98, post #17365615]

8. How should I size wiring and protection?

Keep socket breakers ≤ 16 A. Use 2.5 mm² copper for runs up to 20 m. The inverter’s three-phase output needs motor-sized cables; follow IEC 60364 ampacity tables [IEC 60364-5-52].

9. Edge case: What fails if I start a 5 kW lathe on a 10 A outlet?

The inverter will current-limit, causing undervoltage trips. If bypassed, the breaker opens, or supply wires overheat within seconds, risking fire [Elektroda, Rzuuf, post #17365636]

10. How-to: Wire a VFD to a workshop machine

  1. Mount VFD near the machine, away from dust.
  2. Run shielded motor cable from VFD output to motor terminals, earth the shield.
  3. Program motor nameplate data and perform an autotune. Start at 5 Hz, then ramp up.

11. Are transformer-capacitor phase converters legal and safe?

They are legal if they meet EN 60204 clearances and have protective earth. Many homemade units lack enclosures and overload protection, so insurers may reject claims after a fault [TÜV, 2020].

12. Can I repurpose a server PSU PFC stage for boosting?

Yes. Many 2 kW PFC modules operate up to 380 V DC and can be tuned to 500 V. Replace bulk capacitors with 450 V parts and adjust feedback resistors [cdtdsilva, 2024, #21247827].
AI summary based on the discussion. May contain errors.