I've read a bit and it seems to me that these answers should be refined. The motor power in star/delta connection depends on the available voltages. If we have, for example, a 1.1 kW, 220V/380V motor; triangle/star; 4.9A/2.8A; cosφ; then this engine will achieve its rated power rating in both configurations because:
Py=√3*380*2.8*0.77=1419W
PΔ=√3*220*4.9*0.77=1437W
(Power should be outweighed by efficiency, there will be power on the shaft)
The power will drop significantly when we want to power it not with 3*380V but with 3*220V in the star. Then all the answers that the power will drop 3 times will make sense. The same will happen if we are dealing with a 380V/660V delta/star motor and we want to power it from the home network. We can power it in a delta configuration (we have rated voltages available), but also in a star configuration with a voltage of 3*380V, but then the power will be lower.
To sum up, the engine power will change, but in the case of a star configuration, we will power it with delta voltage. If we supply power with rated parameters, the power in both configurations will be the same.
Ps. I wrote the old markings, i.e. 220/380V, so as not to mix things up too much.