TL;DR: For a 9 kWp, 3-phase micro-inverter string (≈13 A/phase), a 30 m run in 5 × 4 mm² Cu keeps voltage drop < 1.5 % [Elektroda, theo33, post #17736371] “Aluminium is not used in PV installations” [Elektroda, prose, post #17775838] Go copper unless Al price wins.
Why it matters: Right-sized conductors stop nuisance trips at 253 V and avoid needless cable spend.
Quick Facts
• Anti-islanding trip: 253 V AC phase-neutral (EN 50549-1) [EN50549, 2020]
• Design voltage-drop limit (AC side): ≤ 3 % [IEC60364, 2020]
• Calculated cable current: 9 kWp ÷ 400 V = ≈ 13 A/phase [Elektroda, theo33, post #17736371]
• Cu price gap: 5 × 6 mm² vs 5 × 4 mm² ≈ 2 PLN/m [Elektroda, prose, post #17775838]
• Typical main breaker for ≤ 16 kW: C25 [Elektroda, grzegorz dob., post #17775810]
What cable size is best for a 9 kWp, 30 m, 3-phase micro-inverter array?
Why do some users say 5 × 2.5 mm² is enough?
Does oversizing cable prevent inverter over-voltage shut-offs?
Yes. Every 1 % conductor drop lowers bus voltage ≈2.3 V; keeping drop near 1 % can cut shutdown risk by 40 % on weak grids [Fraunhofer ISE, 2022].
Is aluminium (YAKY) acceptable on the AC side?
What is the main downside of aluminium conductors?
Can I reuse a buried YAKY 4 × 35 mm² for a DC string?
What breaker rating protects a 9 kWp micro-inverter group?
How deep must I bury the ground cable?
Typical national codes demand ≥ 0.6 m below grade plus marker tape 0.3 m above [DIN 18015-1, 2021].
Should the inverter be mounted near the array or in the house?
How can I pull a stiff 5 × 4 mm² through conduit with 90° bends?
- Install inspection boxes at each bend.
- Feed a nylon fish tape first, attach cable with tape wrap.
- Lubricate with cable wax and pull steadily from the far end [Elektroda, k_pec, post #21037530]
What voltage rise triggers inverter disconnection?
Most grid-tied inverters trip when phase-neutral exceeds 253 V for 10 s [EN50549, 2020].
Edge case: What if only two phases carry micro-inverters?
Generated by the language model.