Smart light switch when there is only phase in the old switch
PolGraphic 13260 12
How can I install a smart wall switch for two ceiling lights when only phase is available at the old switch and I want to avoid chasing the wall for a neutral wire?
Use a Sonoff Touch at the old switch and make it switch both bulbs together, instead of trying to keep two separate switched circuits. One of the conductors already running from the switch toward the other lamp can be repurposed as the neutral needed by the Sonoff, so you only need to add one wire in the box above the switch and do not have to modify anything at the light source or make a larger wall chase [#17934188] If the existing wall is plastered, running a short groove for that single wire should not be a problem, and the visible section can be kept very small because the box is already above the switch [#17932461][#17932567] A simpler installation is usually better here because it means fewer extra electronics and fewer possible failures [#17932567]
  • #1 17932146
    PolGraphic
    Rate: 10
    I warmly welcome.
    I would like to replace my light switch with "intelligent", ie one that can be switched both manually and via Wifi.
    More precisely, I chose Sonoff Touch due to the ease of reprogramming it (adapting it to my own home management application).
    I have two light sources on the ceiling, I also mean a switch with 2 buttons:
    The problem, however, is that only the phase is fed to the old switch, which it divides into two circuits to both light sources. Sonoff Touch, on the other hand, still needs a neutral wire, as it also includes a microcontroller and a WiFi module.
    This is the current situation with the old switch:
    From what I assume, the neutral cable goes along with the phase cable over the door frame on the right (on the other side of the wall, on the right, above the door frames I have a box and all fuses), then the phase goes down to the switch alone, hence 2 cables for 2 light sources return . And then, together with the neutral, they go to the ceiling and along it (suspended ceiling). I think it confirms this photo from renovation (after replacing the electrical system by an electrician .
    As you can see, the apartment has already been renovated, the walls are freshly painted, there are also frames made of a material similar to a photo wallpaper, very close to the door. That is why I am looking for a solution that finally will not spoil the appearance of the wall and it does not require complete repainting (very problematic due to, among others, the above-mentioned frames from the photo wallpaper) or dusting (problem with securing all elements and frames).
    For every forging, smoothing, laying cables in the wall I am going to hire a suitable specialist - unfortunately, I do not know a trusted man at the moment for plastering / masking cables.
    The solutions I have considered:
    1. Forge (not me personally, of course) from the switch to the neutral cable, connect the Sonoff Touch with the neutral, hide the furrow.
    Advantages: The installation then works exactly as it was supposed to.
    Disadvantages: problem with masking the resulting furrow - can it be done so that it does not stand out from the wall at all? I know the problem will be with the shade of the paint when it's been old for some time, but now I'm thinking more about the edge than the color.
    2. As above, but lead the neutral from the wardrobe to the right next to it (this is the white surface on the right - there I can forge myself and cover everything with a board), from here to the door frame and from the door frame to the light source:
    Advantages: Smaller wall forging area.
    Cons: Still needs to be masked. Cable in the frame.
    3. As in 1. , but run the cables up the wall through the grilles.
    I do not include: I don't like it aesthetically.
    4. Leaving the old switch, mounting in the light sources (of course I already have a phase and neutral output there) one Sonoff (no longer Touch, but an ordinary Wifi-controlled switch).
    Pros: No hammering, no thought of how to leave a wall nice.
    Cons: Installation doesn't quite work as I want. More precisely, there is 1 case: when I turn off the light manually, I can't turn it on via Wifi (and vice versa). It works, however, when I would like to e.g. turn off the light in the room while watching a movie. Worse with turning on.
    5. Smart switches that do not require a neutral cable.
    Disadvantages: none?
    Honestly speaking, I do not understand how such a switch is able to function without a neutral when it cuts off the electricity to the light.
    However, I found switches that supposedly work, e.g. SESOO SY3-02 to radio waves. Integrating it into my home management system would be to build an appropriate emitter.
    What do you think? Maybe you have better ideas or comments on any of the solutions?
    I really don't want to disfigure the wall. However, the difference in the cost of solutions is not that important anymore.
    Added after 27 [minutes]:
    I also found this version of the solution with the use of Sonoff Touch and Sonoff at each light source, with a change in the wiring at the light source, unfortunately I do not fully understand the mechanism of action by which I would use the phase as neutral in Sonoff Touch and how to convert it into 2 light sources:
  • #2 17932461
    Tumiwisizm
    Help: 125
    Rate: 196
    PolGraphic wrote:
    SESOO SY3-02
    let a colleague not buy it, the Chinese do not even distinguish between power and voltage. Probably crap. As for the drawing at the bottom, its lower part, in front of the bulb, there is a Wi-Fi module paired with the one that acts as a key switch, but it also requires a neutral wire to be connected. If there is plaster on the wall, carving a groove and running the cable in it will not be a problem. The photo from the renovation shows the box under the ceiling above the switch, so adding just over a meter of one wire will not disfigure the walls - it can also be invisible. What's the color of the paint there?
    It's already better Sonoff from the 1st photo, touchscreen with Wi-Fi module.
  • #3 17932481
    PolGraphic
    Rate: 10
    Thanks for the answer. Hmm, since Chinese are not certain, I found other ones, for example: B-LINE on Allegro (also probably does not require neutral). Unfortunately, Sonoff Touch needs it.
    But is it also better not to consider this?
    As for the color you asked for, this is it Swan Beckers , but the painting was good 2 years ago, so re-applying the paint only at the furrow will probably be noticeable? And painting the whole thing would be very problematic, incl. due to the fragments of the photo wallpaper stuck on the wall. Anyway, I have access to that particular paint.
    Overall, I am very pleased with how the previous worker has evened and painted the walls (unfortunately he is not accepting any new orders anymore). It is even, smooth and uniform. That's why I really care not to break it, especially if there was a solution without forging. And if it is, then the place on the wall would not be noticeable - only about 1m, but still with an evenly finished apartment, you can see this 1m.
  • #4 17932497
    Tumiwisizm
    Help: 125
    Rate: 196
    My colleague remembers what plaster was applied (I know, absurd because years have passed), the wall is rough to the touch or smooth, as for the wallpaper it is probably smooth? Another question is what light sources are there or will be, because B-LINE will handle at most 100W, if LEDs or energy-saving bulbs are of less power.
  • #5 17932522
    retrofood
    Help: 1140
    Rate: 4800
    I can only advise you to read a few articles so that you know what to expect from a real electrician before the next renovation. Because if you are right now "after", and you only have the phase under the switch, it was not an electrician who did your installation. It was a pseudo-electrician.
    The canless electrical installation is the basis!
    How should a boxless electrical installation be laid?
    Plug-free socket installation, step-by-step
  • #6 17932542
    PolGraphic
    Rate: 10
    It's not that absurd, because maybe I can still find the packaging in the basement, where I keep the remnants of building materials from the renovation. The wall is quite smooth, only slightly even rough, but it's probably the texture of the paint.
    As for the light sources, there are two Hollywood plafonds from Castorama, each with space for 3x GU10.
  • #7 17932555
    Tumiwisizm
    Help: 125
    Rate: 196
    If the texture of the wall is responsible for the paint, then filling the place on the new cable should not be a problem, and by putting a fleece tape on it, you will be sure that the plaster in the place where the cable is placed will not fall off. More than once I have seen a "specialist" carve a groove for a cable, did not remove the dust and, additionally, with a greasy and dirty paw, he leaned on it, and then a piece of plaster fell out of place.
    Okay, but what wattage are the bulbs there? Because if you want to connect Sonoff, you need to pay attention to the power consumed by the light source.
  • #8 17932557
    PolGraphic
    Rate: 10
    I deleted the redundant text. [retrofood]
    Tumiwisizm - so you say not to be afraid of forging? Or maybe just go to this B-LINE?
    As for the power, unfortunately I do not remember exactly now (maybe after 3W but I still have to check - they are hopelessly wriggling this luminaire from Castorama), but I think that I calmly close below the threshold, and if I can't change the light bulb to a slightly weaker - the room is bright and sunny, I don't need mega-enlightenment in the evening ;)
  • #9 17932567
    Tumiwisizm
    Help: 125
    Rate: 196
    Sure not to be afraid! Let a colleague say, the cable from the socket is run in the wall without any trough / pipe? My guess is that there is no, because then it was enough to drag the wire to the top box. If the control from a smartphone is with the broadlink module. This one costs money, but on the other hand
    Personally, I would be in favor of making a groove for the cable, the more electronics, the more possibilities for a fault, and now they make Chinese with a "warranty" for 2 years, and then it breaks down soon and either repair or buy new ones. And in one cable, not a switch (even this Sonoff), there is nothing to break too much. The simplest solutions are the best.
  • #10 17933451
    PolGraphic
    Rate: 10
    The wire is, as you write, Tumiwisim, released without a tube (three cables - the first incoming phase and then two to each light source separately, all three run in one cover through the wall up from the socket).
    Hmm, I called 8 electricians and everyone said that "we don't do such little things". And yet I would rather not go crazy with forging and running a neutral from the can to the switch.
    And this is perhaps a stupid idea:
    1.Replace the light source on the ceiling with sonoff wifi (switch without touch, wifi control only),
    2. then, parallel to this new sonoff, connect the light source which this ceiling sonoff will control,
    3.Instead of the light switch, then give a sonoff touch, the phase of which should be connected normally, and the neutral should be connected as what came out of the switch once (old phase) and which now would go to the sonoff on the ceiling and then to the neutral one.
    And then set it so that it does not turn on anything anymore, but I can read the signal from it by pressing the switch and with this signal (catching it and adding a scenario in my application which is already running 24/7, controlling other things), control the sonoff on the ceiling.
    Do I understand correctly that then the circuit will look like this (in series): neutral -> sonoff on the ceiling (the light source is parallel to it - so turning it off / on will not cut power from the systems in sonoffs) -> sonoff touch in the wall -> phase. Could it even work that way? There would be no forging, only a small modification to the light source (which I can hide under the lampshade).
    In other words, now I think the installation looks like this (not sure if I drew neutral correctly?):
    I marked in green the places where I have free access / I can make changes without hammering the walls (inside the "box" of the switch and at the light sources, under the luminaires.
    And I would like to rewrite it like this:
    Then I control the other light source normally with the sonoff, and the closer one I read the wifi signal of the keystroke and I control the sonoff on the ceiling. Only such a combination in one series of sonoff touch and sonoff (and he is still in parallel with the light source) will work?
    Tumiwisizm
    Help: 125
    Rate: 196
    The idea from the second drawing is fine, but I have a suggestion, but I don't know what a colleague @PolGraphic to this: Give the sonoff touch with one touch in place of the old light connector, but in such a way that sonoff turns on both bulbs at the same time (you can screw in two weaker ones so that they do not consume the current so much and do not burden the switch). One phase conductor going from the switch to the other bulb should be adapted to neutral for sonoff, which requires such a conductor. then we do not combine anything at the light source and without forging in the wall, and it is enough to insert one wire in the box above the switch - I think so, because I do not know what is in this box. What does a colleague say to this?
  • #12 17934536
    PolGraphic
    Rate: 10
    It's a very cool idea, Tumiwisizm - I think I'll use it in the end :)
    However, a bit of innate "investigation", I would like to find out what prevents me from realizing this second drawing.
    Namely, I started with small steps from simply connecting the wires in the cube in place of this lamp in the middle of the second drawing (so far without sonoff on the ceiling and without the lamp on the ceiling).
    I turned on the fuses, everything flickers - the second light comes on with a sonoff touch.
    I went further, in place of this cube I added a ceiling sonoff (yet without light to it, so that it would just close the circuit but not control anything yet).
    I turned on the fuses and ... sonoff touch flashes, the application shows info that neither one nor the other can find the network, and the manual button also does not work and does not switch the light.
    Back to the previous version of "installation" and everything works again - of course, I ruled out a problem with the network by testing it twice.
    What could be causing this behavior? If I solved it and brought it in order, I could close this chapter with a clear heart and do as you write - one switch for both points of light with weaker bulbs - it will be more even and without recombination.
  • #13 18924679
    fr0st
    Did you manage to implement the plan of "returning" the neutral to the switch box? I have a similar situation with myself and I am curious if everything worked out as expected.
The discussion revolves around the challenge of replacing an old light switch with a smart switch, specifically the Sonoff Touch, in a setup where only a phase wire is available. The user seeks a solution that allows for both manual and WiFi control of two ceiling light sources. The Sonoff Touch requires a neutral wire, which is not present in the current installation. Various suggestions are made, including running a new neutral wire, using alternative smart switches like B-LINE that may not require a neutral, and creative wiring solutions to adapt the existing setup without extensive wall modifications. The conversation highlights the importance of understanding electrical installations and the potential pitfalls of DIY approaches.
TL;DR: If your switch box has only a phase, add a neutral or re‑think control. Many budget smart switches advertise "2‑year" warranties; "The simplest solutions are the best." [Elektroda, Tumiwisizm, post #17932567]
Why it matters: This FAQ helps apartment owners with two‑wire switch loops choose smart‑lighting options without damaging finished walls.
Quick facts:
Can I install a Sonoff Touch if my switch box only has a phase wire?
Not without a neutral. Sonoff Touch needs both live and neutral to power its controller. Old two‑wire loops bring only the phase and switched returns. Options: pull a neutral into the box, combine loads and reuse one return as neutral, or move control to the luminaires. Confirm the ceiling box wiring before you decide. [Elektroda, PolGraphic, post #17932146]
What’s the cleanest way to add a neutral without ruining the wall?
Run a short neutral from the ceiling box above the switch. Cut a narrow vertical chase, clean out dust, lay the conductor, and reinforce the patch with fleece tape. That prevents cracking and plaster shedding. With careful prep and paint matching, the repair can be invisible. [Elektroda, Tumiwisizm, post #17932555]
Are "no‑neutral" smart switches worth considering?
They exist, but quality and labeling vary. Some cheap imports misuse terms and can be unreliable. If you try one, verify the load rating and LED compatibility. Favor reputable devices or add a proper neutral. A touchscreen Sonoff remains a better option when neutral is available. [Elektroda, Tumiwisizm, post #17932461]
What happens if I put smart relays at the lights and keep the old switch?
You lose remote control whenever the wall switch is off. With power cut, ceiling Wi‑Fi modules go offline, so the app cannot turn lights back on. This works only if the wall switch stays on, which is not foolproof for households. [Elektroda, PolGraphic, post #17932146]
Can I wire a Sonoff Touch in series with another Sonoff at the ceiling just to read taps?
Avoid this. Testing showed both devices flashed, lost Wi‑Fi, and the physical button stopped working. Powering one smart module through another in series destabilizes their supplies. Use a decoupled smart button or a battery remote paired to the ceiling relay instead. [Elektroda, PolGraphic, post #17934536]
How do I keep both light groups independently controllable without chasing walls?
Install separate smart relays at each ceiling fixture, where neutral and live exist. Leave the wall switch permanently on, or replace it with a wireless remote that does not cut mains. Otherwise, you cannot turn lights on via the app if the switch is off. [Elektroda, PolGraphic, post #17932146]
Is it safe to repurpose one of the two switched wires as a neutral for a smart touch switch?
One approach joins both lights on one gang and converts the spare switched wire into a neutral for the smart switch. This avoids chasing and keeps the controller powered. Ensure the combined load stays under the device rating, and relabel the conductor at both ends. You lose independent control. [Elektroda, Tumiwisizm, post #17934188]
What load limits should I watch for on touch switches like B‑LINE?
Respect the device’s rating. An example discussed was about 100 W for a B‑LINE touch switch. Add your lamps’ wattage and keep margin for safe operation. If combining two circuits on one gang, use lower‑watt bulbs to stay within limits. Overloading risks overheating. [Elektroda, Tumiwisizm, post #17932497]
Is chasing a groove preferable to stacking more electronics?
Yes, often. A single added neutral and a reliable switch mean fewer failure points. “The simplest solutions are the best.” Extra modules add cost, firmware risks, and more fault modes. A neatly patched short chase is easier to live with long term. [Elektroda, Tumiwisizm, post #17932567]
Any tips to avoid plaster failure when patching a cable chase?
Preparation is key. Remove dust thoroughly before filling. Don’t touch the surface with greasy hands. Apply fleece tape over the chase to bridge and reinforce the repair. These steps help bonding and reduce cracking. Finish by matching the wall’s paint texture. [Elektroda, Tumiwisizm, post #17932555]
How do I add a neutral from the junction box above the door? (3 steps)
  1. Identify the ceiling junction box above the switch and verify neutral is present.
  2. Cut a narrow vertical chase to the switch box; keep it straight and clear dust.
  3. Pull a neutral down, connect in the junction box and at the switch; reinforce and patch. [Elektroda, Tumiwisizm, post #17932461]
Why do some electricians refuse small jobs like adding one neutral?
Minimum job sizes and scheduling make small chases uneconomical. In the thread, eight electricians refused as “too small.” If that happens, bundle tasks or find a specialist who handles minor wall repairs and patching. Clear photos and scope help secure acceptance. [Elektroda, PolGraphic, post #17933451]
What wiring standard should I request in my next renovation?
Ask for boxless installation with neutrals in every switch box. This supports smart switches, reduces hidden junctions, and simplifies future upgrades. Align expectations with a licensed electrician before finishing walls to avoid phase‑only switch loops. [Elektroda, retrofood, post #17932522]