Connecting the protective conductor with the neutral in the TN-C network

wprost123 24222 44
Best answers

Can I bond the neutral/PEN to a lamp’s metal housing in an old TN-C installation, and does that make the circuit TN-C-S?

Yes—if your supply is really TN-C, bonding the lamp housing’s protective conductor to the incoming PEN point is the normal TN-C→TN-C-S split, and the conductor before the split should be called PEN, not N [#18364085] If the phase conductor touches the housing, fault current should flow through the protective path back to the split point and clear the fault by blowing/tripping the overcurrent protection [#18364085] The dangerous case is a PEN break before the split: the housing can become live even without a phase-to-housing fault, because there is no proper return path to clear it [#18364085][#18364115] Because old PEN conductors are often smaller and more failure-prone, the sooner you split it the better, and the installation should be periodically inspected and measured [#18364115][#18364291]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 18397752
    CYRUS2
    Level 43  
    Posts: 17642
    Help: 1221
    Rate: 3453
    adwlodar wrote:
    Devices (then) were grounded locally?
    No shock protection was used.
    adwlodar wrote:
    what about the first electric irons? Someone tell this, please
    The irons had a 2-wire cord and did not have anti-shock protection.
    Cooking machines with an exposed spiral were sold.
    I have repaired these many times.
    The first consumer requiring protection was the Frania washing machine.
    (1959-1960)
    The blocks were grounded to the pipe - it was an effective protection.
    Later.
    The second receiver that required grounding was the refrigerator.

    Radios had transformers, TVs without transformers were made of the 2nd class.
  • ADVERTISEMENT
  • #32 18397845
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Hello.
    I assure you that the mentioned irons had anti-shock protection.
    It was called insulation and proper enclosure.
  • ADVERTISEMENT
  • #33 18397888
    Jamesbond664478
    Level 20  
    Posts: 496
    Help: 36
    Rate: 162
    kkas12 wrote:
    My friend does not know that equalizing connections, and therefore the grounding of the neutral wire, have been in force in this country since 1968.

    Haha, that`s not the only thing that gets grounded. EVERY NETWORK IS GROUNDED - right next to the transformer

    kkas12 wrote:
    My friend also does not know that it is not about the grounding (in new installations) of the PEN division, but about the grounding of the PE conductor. However, this should be done at the beginning of the installation, not at the end.

    In new installations, no, if it is a TN S network. Otherwise - in TN C installations, yes. This is about grounding the PEN division (because if I`m not mistaken, we take the N and PE wires from the PEN division) :-D

    You`re right about the equalizing connections. You should not make local equipotential bonding without having main connections
    Moderated By Krzysztof Reszka:

    We do not write the text in capital letters. To change the italics of the text, use the appropriate buttons above the frame (B iu).

  • #34 18397926
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1545
    CYRUS2 wrote:
    The irons had a 2-wire cord and did not have anti-shock protection.

    And I think they also had this third protective wire connecting the iron through the heating cap with two plates on its side.
    Connecting the protective conductor with the neutral in the TN-C network
    Connecting the protective conductor with the neutral in the TN-C network
    As far back as I can remember, it should have looked like this, because even pre-war irons had photos that prove it. And the fact that home electricians did not provide what they should have done was a different story.
  • ADVERTISEMENT
  • #35 18397957
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Because the author should write clearly:
    - if the receivers (irons in this case) had a 2-wire cable, the protection against electric shock was implemented in the same way as modern receivers. in protection class II
    - if there was a 3-core cable, protection was provided either by protective zeroing in the installation or by grounding the housing terminal to e.g. water pipes.
    As for the machines - there are still heating inserts for tiled stoves with "open spirals".
    Nothing new.
  • #36 18398005
    kkas12
    Level 43  
    Posts: 17357
    Help: 1073
    Rate: 4263
    Jamesbond664478 wrote:
    Haha, that`s not the only thing that gets grounded. EVERY NETWORK IS GROUNDED - right next to the transformer
    Distinguish between a network and an installation. In this thread, we are not interested in networks. Moreover, the PEN may break, so this is not a fairy tale from this thread because it is the responsibility of the energy supplier and not the contractor installing the building.
    So it is advisable that you first read sheet 5-54 and then write posts about electrical installations in the facility.

    Jamesbond664478 wrote:
    In new installations, no, if it is a TN S network. Otherwise - in TN C installations, yes. This is about grounding the PEN division (because if I`m not mistaken, we take the N and PE wires from the PEN division)
    You`re talking nonsense. Because even if the PEN division was made in a cable connector distant from the building, the PE bus in the building should still be earthed. But this rail is at the beginning of the installation.
    Therefore, the common opinion about grounding the PEN division is a myth. Describe how to ground such a place when it is located on the tenth floor and the power supply contains three phases and PEN?
    Jamesbond664478 wrote:
    You should not make local equipotential bonding without having main connections
    You keep repeating and you don`t know why.
  • #37 18398057
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1545
    Jamesbond664478 wrote:
    EVERY NETWORK IS GROUNDED - right next to the transformer

    Not true .
  • #38 18398061
    adwlodar
    Level 28  
    Posts: 1067
    Help: 111
    Rate: 245
    kkas12 wrote:
    Therefore, the common opinion about grounding the PEN division is a myth. Describe how to ground such a place when it is located on the tenth floor and the power supply contains three phases and PEN?


    I don`t want to start a worthless conversation on this topic again, but I recently remembered during a LIVE broadcast of a certain YouTuber-electrician that it was said that you should pull a cooper in the shaft together with WLZ and the problem be solved... and interestingly, this theory has mass of supporters.
  • #39 18398082
    kkas12
    Level 43  
    Posts: 17357
    Help: 1073
    Rate: 4263
    There was once a theory that, together with the five-wire wlz, the cooperage should be run along the floors. It was ordered to connect local equalization connections to it, which was obvious nonsense, because it did not guarantee that external and accessible parts would have the same potential.
    Once, one of the inspectors demanded that I cover metal door frames in apartments with local connections. I told him that I would do it when he made the appropriate entry in the construction log. The entry did not appear, so this man`s request remained in the sphere of his unfulfilled dreams.

    And the supporters of this theory are as stupid as the theory itself, because each era (as you can see) has its "discoverers".
  • ADVERTISEMENT
  • #40 18398136
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    kkas12 wrote:
    There was once a theory that, together with the five-wire wlz, the cooperage should be run along the floors. It was ordered to connect local equalization connections to it, which was obvious nonsense, as it did not guarantee that external and accessible parts would have the same potential.


    How about a lightning wire as PE?
    Connecting the protective conductor with the neutral in the TN-C network
    It`s just a sculpture :D
  • #41 18398148
    kkas12
    Level 43  
    Posts: 17357
    Help: 1073
    Rate: 4263
    But it`s four-wire as I see it :)
  • #42 18398194
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    That`s right.

    Here you have 5x + hoop iron:
    Connecting the protective conductor with the neutral in the TN-C network

    And here is an even stranger creation - PE bis, only for grounding the shaft structure:
    Connecting the protective conductor with the neutral in the TN-C network
  • #43 18398207
    kkas12
    Level 43  
    Posts: 17357
    Help: 1073
    Rate: 4263
    Oh, then joyful creativity was in full bloom.
    It was a golden age for various types of home repairers.
    Thank God it lasted so short.
  • #44 18398257
    Jamesbond664478
    Level 20  
    Posts: 496
    Help: 36
    Rate: 162
    kkas12 wrote:
    Jamesbond664478 wrote:
    In new installations, no, if it is a TN S network. Otherwise, in TN C installations, yes. This is about grounding the PEN division (because if I`m not mistaken, we take the N and PE wires from the PEN division)

    kkas12 wrote:
    You`re talking nonsense. Because even if the PEN division was made in a cable connector distant from the building, the PE bus in the building should still be earthed.

    kkas12 wrote:
    Describe how to ground such a place when it is located on the tenth floor and the power supply contains three phases and PEN?

    The same as grounding the PE bus located on the tenth floor, and the wlz contains three phases and PEN

    Added after 2 [minutes]:

    kkas12 wrote:
    Therefore, the common opinion about grounding the PEN division is a myth.

    Oh, probably not :-\ Although grounding the PEN division is not obligatory, it is still performed

    Moderated By Łukasz-O:

    The post adds nothing to the discussion.

  • #45 18398316
    adwlodar
    Level 28  
    Posts: 1067
    Help: 111
    Rate: 245
    Jamesbond664478 wrote:
    The same as grounding the PE bus located on the tenth floor, and the wlz contains three phases and PEN
    Yes, but according to... You?

Topic summary

✨ The discussion revolves around the connection of the protective conductor with the neutral in a TN-C network, particularly in an old installation lacking a dedicated protective conductor. The user describes a setup where the neutral wire is connected to the protective wire of a lamp, raising concerns about safety and compliance with electrical standards. Responses clarify that this connection is acceptable under TN-C conditions, but emphasize the importance of separating the PEN conductor into N and PE for safety. The risks of a damaged PEN conductor leading to potential electric shock are highlighted, along with recommendations for grounding and periodic inspections. The conversation stresses the necessity of proper installation practices and the dangers of outdated methods like zeroing without adequate grounding.
Generated by the language model.

FAQ

TL;DR: For safe PEN-to-PE/N splits, code requires ≥10 mm² Cu (or 16 mm² Al) conductors [Bezel, 2018]; “The sooner you separate it, the better” [Elektroda, michu-michu, post #18364115] Ground earlier, ground properly, and test every 5 years to avoid lethal voltages on metal housings.

Why it matters: A single PEN break can put full 230 V on every exposed metal part in the circuit.

Quick Facts

• Minimum PEN cross-section: 10 mm² Cu / 16 mm² Al [Bezel, 2018] • Fault-loop max resistance (230 V, 16 A B-curve): ≈0.8 Ω [PN-HD 60364-4-41] • Mandatory residential inspection: every 5 years in PL [Dz.U. 2002-75] • 30 mA RCD trip time: ≤40 ms [IEC 61008] • Typical grounding-rod installation cost: PLN 100–150 each [MarketData, 2023]

Is it acceptable to bond the protective conductor to the neutral in a TN-C circuit?

Yes, if the supply is truly TN-C, you may link the lamp’s protective core to PEN; from that point onward the system operates as TN-CS [Elektroda, michu-michu, post #18364085]

What happens if phase touches the lamp housing while PEN is intact?

The fault current flows through PE to PEN, creating a low-impedance loop that trips the 10 A breaker almost instantly [Elektroda, wprost123, post #18364079]

What is the danger if PEN breaks downstream of the split?

With PEN open, the lamp housing can rise to 230 V; no protective device will trip, posing shock and fire risks—an edge-case many overlook [Elektroda, wprost123, post #18364098]

Will moving the PEN split closer to the service entry improve safety?

Yes. Shortening the single PEN section reduces the chance of its damage; “The sooner you separate it, the better” [Elektroda, michu-michu, post #18364115]

Must I ground the PEN split point?

Standards require the PE bus (not necessarily the split lug) to be earthed at the installation’s origin; additional local earths rarely change touch-voltage parameters [IEC 60364-5-54].

Are spring-clamp connectors rated 24 A reliable for 10 A lighting circuits?

Properly installed branded lever clamps meet IEC 60998 and carry 24 A continuously, thus are suitable for your 10 A breaker [Manufacturer datasheet, 2023].

Does using a smaller 10 A breaker reduce the chance of PEN burnout?

No. PEN failure results from poor joints, corrosion or undersized conductors, not breaker rating [Elektroda, CYRUS2, post #18365887]

How often must an old TN-C installation be inspected?

Polish law mandates electrical testing at least every 5 years for dwellings [Dz.U. 2002-75].

When is "zeroing" (PEN–housing link without PE) forbidden?

If any socket shares the circuit with PE-protected outlets, or the PEN is below 10 mm² Cu / 16 mm² Al, you must not zero; upgrade to TN-CS instead [Bezel, 2018].

How can I split PEN safely?

  1. Terminate the incoming PEN on a metal bar rated ≥10 mm² Cu.
  2. Bond that bar to the main earthing terminal.
  3. Run separate N (blue) and PE (green-yellow) conductors to every circuit. Verify loop impedance < 0.8 Ω before energising.

What extra protection does a 30 mA RCD add after the split?

An RCD trips within 40 ms at 30 mA, limiting shock energy to ~1.2 J—below fibrillation threshold [IEC 61008].