logo elektroda
logo elektroda
X
logo elektroda

Facade blinds - what to anticipate at the electrical stage so as not to regret l

Wix 17046 15
Best answers LABEL_AI_GENERATED

What wiring and control points should I prepare during the electrical stage for facade blinds so I can keep future options open?

Prepare a universal installation: run a round cable to each facade blind, preferably OWY 5x1 or at least 4x1.5 mm², to a central box/switchgear so you can later use radio, wired, or combined drives [#18574751][#18561678][#18563456] Radio drives need 3 wires (L, N, PE), wired drives need 4 (neutral, up, down, PE), and combination drives with built-in radio plus local switch control need 5 wires [#18574751] Use round insulation because the Hirschmann connector and cable gland are made for it, and the facade blind holders are adapted to suspending a round cable [#18563456] Add a local control button near each window if you want manual control at the blind [#18567872] If you choose radio control, separate fuses for individual blinds can help because programming may require power-cycling a single drive [#18574751] A central place only really makes sense if you want central or integrated smart control; otherwise one protection for the whole facade perimeter is usually enough [#18567791]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 18561461
    Wix
    Level 9  
    Posts: 124
    Rate: 22
    Hello,
    In a newly built house, I plan facade blinds (protection against the sun + the issue of privacy). The choice of motors / controllers / automation / specific brands is still ahead of me.

    I will probably start finishing the house with the electrical installation. And here's the question... What to anticipate/plan at this stage (maybe even with a reasonable margin) so as not to regret later that I did not spend PLN 200-300 more when I will be so-called. conscious user.

    I'll add in passing:
    - I'm after some preliminary talks, which show that Somfy is a very wonderful thing. And some that additionally only IO radio engines.
    - Here I have doubts about the radio control method - I've always been convinced that a wire is a wire.
    - I think I have a reasonable approach to the idea of a "smart home". No blind control "from anywhere in the world".
    On the other hand, I already have a certain automation scenario that I need from some button (not a remote control, not a smartphone). Maybe the needs will develop… as in life.

    So I repeat ... what to predict at the electrical stage and before plastering?
  • ADVERTISEMENT
  • #2 18561539
    miroslaw wielki
    Conditionally unlocked
    Posts: 3390
    Help: 148
    Rate: 362
    You definitely need to pull the LN PE to the motor if it has a built-in motor with a radio receiver
  • ADVERTISEMENT
  • Helpful post
    #3 18561678
    gaspaccio
    Level 20  
    Posts: 329
    Help: 35
    Rate: 93
    You lead to the blinds, 4x1.5mm^2. All to a central place. There's a little extra switch over there.
    If there is a radio control, it doesn't change anything, but if you dream of a smart home or an alarm, such a solution is very flexible in reconstruction.
  • #4 18561978
    Wix
    Level 9  
    Posts: 124
    Rate: 22
    Thanks for the votes. Just remember that I plan facade blinds , NO blinds.
  • ADVERTISEMENT
  • #5 18562254
    gaspaccio
    Level 20  
    Posts: 329
    Help: 35
    Rate: 93
    Venetian blinds and roller shutters are driven in the same way, only the motors look different.
    4 wires: protective, neutral and two phase (up and down)
  • ADVERTISEMENT
  • #6 18563456
    Marek J.
    VIP Meritorious for electroda.pl
    Posts: 2368
    Help: 526
    Rate: 951
    If you lead to 4x1.5 blinds, it will be enough and will allow you to use both radio and wired motors. However, due to the Hirschmann connectors (and cable gland) used, the cable should be in round insulation and preferably a cord (e.g. 4x1.0)
    Recently, I installed/configured one with Elero control and motor.
    Motor with built-in JA Comfort 868 radio receiver and 6-channel remote controls from the COM series. It is possible to precisely control the tilt of the slats using the touchpad, turn on the solar automation, remember the comfortable position, etc., etc. Of course, two-way communication.
    In this case, a 3-wire installation is sufficient. You only need to make a bridge in the Hirschmann connector (the motor is factory equipped with such).




    https://youtu.be/jxPRs4kOQ8A
  • #7 18567633
    Wix
    Level 9  
    Posts: 124
    Rate: 22
    gaspaccio wrote:
    You lead to the blinds, 4x1.5mm^2. All to a central place. There's a little extra switch over there.


    I understand that the alternative is to pull these wires to the main switchboard?

    What is the advantage of such a "central place - a small additional switchgear"?

    Added after 2 [minutes]:

    Marek J. wrote:
    [...] round insulation and most conveniently [...]


    Is it about the comfort of installation work in cans?
  • Helpful post
    #8 18567791
    Marek J.
    VIP Meritorious for electroda.pl
    Posts: 2368
    Help: 526
    Rate: 951
    Wix wrote:
    I understand that the alternative is to pull these wires to the main switchboard?

    If you want to have each blind on a separate protection, then yes. However, it seems to me that one protection of the perimeter of facade blinds is enough.
    Wix wrote:
    What is the advantage of such a "central place - a small additional switchgear"?

    Only that you can install a central control system for all blinds, which seems logical in the case of roller shutters, but not very practical for façades (unless you plan an "intelligent" system integrated in the switchgear).
    Wix wrote:
    Is it about the comfort of installation work in cans?

    NO. The point is that the Hirschmann connector has chokes to prevent moisture from getting inside, and it's hard to do it on a flat cable. In addition, the facade blinds have specially designed holders for laying/suspending the cable in the housings and these are adapted to the cable in round insulation...
  • #9 18567872
    kood
    CCTV and Stationary Alarms specialist
    Posts: 1896
    Help: 259
    Rate: 443
    Marek J. wrote:
    (e.g. OWY 4x1.0 is enough)


    Here I would not be sure if it is enough, from what I know, the minimum cross-section of the wire in electrical installations is 1.5mm2, but it's better to let someone of my fellow electricians speak.

    Wix wrote:
    What to anticipate/plan at this stage (maybe even with a reasonable margin) so as not to regret later that I didn't spend PLN 200-300 more when I'm already so-called. conscious user.


    Button next to the window to be able to control the blind locally.
  • #10 18567894
    Wix
    Level 9  
    Posts: 124
    Rate: 22
    Marek J. wrote:
    Wix wrote:
    I understand that the alternative is to pull these wires to the main switchboard?

    If you want to have each blind on a separate protection, then yes. However, it seems to me that one protection of the perimeter of facade blinds is enough.


    I do not fully understand ... After all, whether the wires go to the main switchboard or the "small additional switchgear", I can put a separate fuse for each shutter in each of these places.

    I do not insist that I need separate protection for each blind (probably I don't even need it if you write like that) but I am trying to grasp the meaning and understand it.
  • #11 18567991
    Marek J.
    VIP Meritorious for electroda.pl
    Posts: 2368
    Help: 526
    Rate: 951
    There can't be a 100% clear answer since you wrote:
    Wix wrote:
    The choice of motors / controllers / automation / specific brands is still ahead of me.

    There are different motors and different requirements for power supply, control, etc. Therefore, installations will also be different.
    The most universal solution, in my opinion, will be a solution as in the case of roller blinds:
    https://www.elektroda.pl/rtvforum/topic3672233.html#18550566
    except for point 6, where in this case a 4x1.0 round cable is sufficient
  • #12 18568019
    Wix
    Level 9  
    Posts: 124
    Rate: 22
    kood wrote:
    Button next to the window to be able to control the blind locally.


    Well, that's what I was thinking too. Yes, I rather anticipate that I will want to control each blind locally with a button somewhere next to it.

    So, as I understand it, an additional wire from the lintel area to the planned place of the button. Or so? (what wire).

    Added after 47 [minutes]:

    Wix wrote:
    kood wrote:
    Button next to the window to be able to control the blind locally.


    Well, that's what I was thinking too. Yes, I rather anticipate that I will want to control each blind locally with a button somewhere next to it.

    So, as I understand it, an additional wire from the lintel area to the planned place of the button. Or so? (what wire).


    Oh, I read...

    And out of curiosity. Why did you recommend universal 5x for roller blinds and 4x for blinds?
  • #13 18568589
    Marek J.
    VIP Meritorious for electroda.pl
    Posts: 2368
    Help: 526
    Rate: 951
    Wix wrote:
    Why did you recommend universal 5x for roller blinds and 4x for blinds?

    Because in the subject of roller shutters, a universal solution was also asked for, without indicating a specific model.
    And there are motors for roller shutters that are controlled and powered by 5 or even 6 wires (the 6th wire is used rather in awnings for wind and solar automation and in Nice radio motors to control the double-key shutter switch).
    I have not come across more than 4 wires in shutter motors. (3 wires in radio motors and 4 wires in traditional and radio motors).
  • Helpful post
    #14 18574751
    _ZBYCH_
    Level 15  
    Posts: 157
    Help: 10
    Rate: 71
    Want universal cabling?
    Follow the diagram below.

    Facade blinds - what to anticipate at the electrical stage so as not to regret l

    Only radio-controlled drives require three wires (phase, neutral, protective).
    Drives without built-in radio control require four wires (neutral, opening phase, closing phase, protective).
    Combination drives have a built-in radio receiver and additional wired control to the local switch - these require five wires from the blind to the switch box.

    From the switch box to the switchgear, running a five-core power cable (OWY 5x1) and UTP twisted pair + pocket box (with space for a possible control module) makes such an installation very universal.

    As a rule, shutter drives have a piece of cable with a Hirschmann connector. The plug has a gland for a round cable.
    Facade blinds - what to anticipate at the electrical stage so as not to regret l

    Take into account that with radio control, to program the transmitter (remote control or radio wall button), it may be necessary to switch on/off the power supply of a single blind, so separate fuses may make sense in this case.
  • #15 18575046
    Wix
    Level 9  
    Posts: 124
    Rate: 22
    _ZBYCH_ wrote:
    Follow the diagram below.

    Facade blinds - what to anticipate at the electrical stage so as not to regret l


    I was about to ask about the wind sensor, I'm opening a thread and here's the answer :) I will ask ... wind / sun sensor with what cable to connect?

    P.S. Thanks for the detailed answer...
  • #16 18580507
    Wix
    Level 9  
    Posts: 124
    Rate: 22
    gaspaccio wrote:
    You lead to the blinds, 4x1.5mm^2. All to a central place. There's a little extra switch over there.


    How many bays in the switchgear should I reserve for such a set of blinds?

Topic summary

LABEL_AI_GENERATED
In planning the installation of facade blinds in a newly built house, it is crucial to consider the electrical setup early in the process. Users are advised to run a 4x1.5mm² cable to a central location for flexibility in control, whether using wired or radio-controlled motors. The discussion highlights the importance of including protective, neutral, and phase wires for motor operation, with recommendations for using Hirschmann connectors to prevent moisture ingress. Various motor types, including those from brands like Somfy and Elero, are mentioned, emphasizing the need for compatibility with automation systems. Users should also consider local control options and the potential for future integration with smart home systems. The necessity of additional wiring for wind and sun sensors is noted, along with the importance of reserving adequate space in the switchgear for the blinds' control systems.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Most facade blind motors need 3–5 conductors; “Only radio-controlled drives require three wires.” Prewire OWY 5x1 from each switch box to a central switchgear, run round cables to the headbox, and allow space for a control module and per‑blind fuses. [Elektroda, ZBYCH, post #18574751]

Why it matters: For new builds, this tells homeowners and electricians exactly what to wire before plaster so blinds work now and upgrade later.

Quick Facts

What should I prewire for facade blinds before plastering?

Home‑run each blind to a central place. From the wall switch box to the switchgear, pull OWY 5x1 and a UTP twisted pair. Leave a pocket box near the switch for a future control module. Motors typically arrive with a Hirschmann plug that expects round cable at the gland. This layout supports radio, wired, or combination drives without re‑chasing walls. [Elektroda, ZBYCH, post #18574751]

Are facade (venetian) blinds wired differently from roller shutters?

Functionally no. Both use protective, neutral, and two phase conductors for up and down. The motors differ mechanically, but connection logic matches. “Venetian blinds and roller shutters are driven in the same way.” Plan four conductors to the headbox for standard wired drives. [Elektroda, gaspaccio, post #18562254]

Should I route blind cables to a central mini‑switchgear or the main board?

Use a small additional switchgear if you want central control or later “intelligent” integration. One breaker for the facade blind perimeter often suffices. If you want separate protection for each blind, routing to the main board is reasonable. Round cables also suit the manufacturer connectors in blind housings. [Elektroda, Marek J., post #18567791]

Do I need a separate breaker for each blind?

Not typically. One protection for the perimeter of facade blinds is enough. Choose separate protection only if you explicitly want each blind isolated by design. This reduces complexity and saves distribution space. [Elektroda, Marek J., post #18567791]

When should I plan separate fuses per blind?

With radio motors, commissioning can require power‑cycling a single blind. Separate fuses make that easy. If all blinds share one breaker, targeted power‑cycling is awkward. Plan per‑blind fuses when you expect individual radio pairing during setup. [Elektroda, ZBYCH, post #18574751]

Should I place a local wall button next to each window?

Yes. Add a button by each window for convenient local control. It works regardless of remotes or phones and keeps operation simple for guests. [Elektroda, kood, post #18567872]

What wire should I run to support a local wall button?

For combination drives, run five wires from the blind to the nearby switch box. From the switch box to the switchgear, pull OWY 5x1 and a UTP twisted pair. Leave box space for a possible control module. This supports local and central control. [Elektroda, ZBYCH, post #18574751]

Is 4x1.5 mm² to each blind a safe baseline?

Yes. Run 4x1.5 mm² to every blind and home‑run them to a central place. This also keeps you ready for radio control and later smart‑home or alarm integration without rewiring. [Elektroda, gaspaccio, post #18561678]

How do radio and wired drives differ in wiring?

Radio drives use three wires: phase, neutral, protective. Wired drives use four: neutral, two phase (up/down), protective. Combination drives add a local wired control path, so you need five wires to the switch. [Elektroda, ZBYCH, post #18574751]

Why use round cable at the headbox instead of flat cable?

Blind motors often include a Hirschmann plug with a gland designed for round cable. Flat cable is hard to seal and can admit moisture. Housings also have clips sized for round insulation, improving strain relief and reliability. [Elektroda, Marek J., post #18567791]

How do I wire an Elero JA Comfort 868 radio motor?

Use a 3‑wire installation and make the factory bridge in the Hirschmann connector. The system enables precise slat tilt, comfort positions, solar automation, and two‑way communication with 6‑channel COM remotes. “Two‑way communication” aids feedback during setup. [Elektroda, Marek J., post #18563456]

Which cable should I prepare for a wind/sun sensor?

Pull a UTP twisted pair from the switch box to the switchgear along with OWY 5x1. Leave space for a control module that interfaces wind/sun sensors. This universal run preserves options for sensor integration later. [Elektroda, ZBYCH, post #18574751]

How many switchgear bays should I reserve for blinds?

Allow room for one group breaker and optional per‑blind fuses, plus a control module if desired. Extra space simplifies commissioning when radio motors need single‑blind power cycling. Leave headroom rather than sizing too tightly. [Elektroda, ZBYCH, post #18574751]

How do I prewire for universal blind control (3 steps)?

  1. From each blind to the wall switch box, route the conductors required by your drive (3, 4, or 5).
  2. From the switch box to the switchgear, pull OWY 5x1 plus a UTP twisted pair.
  3. Leave a pocket box near the switch for a future control module and ensure round cable suits the Hirschmann gland. [Elektroda, ZBYCH, post #18574751]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT