How to check with a meter which cable is 0 and which is phase

JohhnyCage11 102804 39
Best answers LABEL_AI_GENERATED

How do I identify the phase and neutral wires in an apartment using a UNIT-T UT33C multimeter?

Set the meter to AC voltage and measure each conductor against a known grounded point such as a water or heating pipe; the conductor that gives the highest reading, around 230 V, is the phase [#18845283] Do not rely on a single low or unstable reading, because a high-impedance multimeter can show induced voltages and the smaller value alone does not prove a wire is neutral [#18845497] The safer recommendation from the thread is to use a neon tester or, better, a bipolar voltage tester such as a Duspol/UT18C, which directly indicates the phase wire [#18846630][#18848220] Also make sure the meter is set to voltage measurement, not current, because selecting the wrong mode is dangerous [#18845952][#18846270] If you are not confident, call an electrician [#18846630]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #31 18845702
    takijasiu
    Level 25  
    Posts: 748
    Help: 91
    Rate: 161
    JohhnyCage11 wrote:

    Sure please

    PS If something is wrongly done (done about 5 years ago), do I have the right to call him and tell him? All in all, it was paid to the construction company, and she hired an electrician.

    How to check with a meter which cable is 0 and which is phase


    In this photo you can see various interesting bugs:

    - the switchgear has no main switch - the power supply is supplied to the comb that is connected to the lower connectors of the apparatus

    - the presence of the Żo conductors (protective conductor, this is the yellow-green one) indicates that the installation is three-core - but the question of what is the entire protective rail connected to - it cannot be seen in the photo - correctly, depending on the type of power supply network (TN, TT) this rail should be properly handled

    - eeee - regarding the above point - because I did not get a little sleep today - there are wires in the switchgear, but there are no cables in this example socket - this is a question what the masters have done with them - it is not sometimes that the fuse box was in another place and they moved it by adding pieces of 3-wire cables? if you can see something in the switchgear, it should of course also be in the socket - and it is not there

    - lack of a residual current device required by law (Regulation)

    - too large denominations - B20 - there cannot be a socket on the perimeter behind such a device, because the socket has a strength of 16A, and besides, there cannot be a 2.5mm? cable, and probably it is - also the question is why as many as 3 such devices

    - similarly, if you have any lighting with switches, it is also too large a value, because most household switches have a strength of 10A

    - plus the fact that I counted 8 blue wires on the neutral bus, and there are also 8 overcurrent switches, there is also a separate switch for each circuit

    - the supply of cables in the switchgear is too large left

    - I wonder if the bell is secured
  • ADVERTISEMENT
  • #32 18845703
    Anonymous
    Level 1  
  • ADVERTISEMENT
  • #33 18845789
    kaz69
    Level 37  
    Posts: 3357
    Help: 393
    Rate: 543
    It should not be built and released for use.
  • #34 18845943
    kkkamil
    Level 13  
    Posts: 223
    Rate: 23
    kkkamil wrote:
    Heh, the peasant asked a specific question and, as usual, electricians turned out to be philosophers.

    Answer:

    You set the range to alternating voltage (NOT CURRENT!) And take one wire in the paw (yes, the metal one in your hand) and the other pole to the contact. On phase you will have an indication of around 50V, on zero you should have 0V. Of course, this is not professional and "do not do it at home", but if there is no way out ...

    The method is a bit dangerous because if you connect the wires for measuring the current by mistake, you will find out for yourself that you have found the phase. So if you are not familiar with the meter, maybe it's better to call an electrician or buy a neon lamp (a few zlotys is enough).

    greetings. Kamil

    ["kozi966"] You get warnings for such advice on this forum, and that is how it ends in this case.
    This is a highly DANGEROUS tip.
    3.1.11. Publishing posts that do not contain substantive content, with harmful advice, advice that is not an attempt to fix the problem, and posting identical posts in succession or repeating information from the discussion. [/ Mod]


    I understand, thank you for the shot in the back of the head (I got a warning or something), I will not speak again here. Measurement with the multimeter that I gave is healthier for the meter and safer than with neon - much less current flows through a human. But ok. I understand, I will not tell you how to safely measure in the absence of dedicated tools. I don't consider myself guilty.

    Greetings. Kamil.

    Moderated By Łukasz-O:

    I suggest avoiding the electric cannons with a wide arc.

  • ADVERTISEMENT
  • #35 18845952
    Łukasz.K
    Level 28  
    Posts: 989
    Help: 84
    Rate: 152
    The meter may be damaged at any time, shocking the measuring person. Therefore, this method is dangerous.
  • ADVERTISEMENT
  • #36 18846270
    gkwiatkowski
    CCTV and Stationary Alarms specialist
    Posts: 4685
    Help: 650
    Rate: 1230
    kkkamil wrote:
    Łukasz.K wrote:
    The meter may be damaged at any time, shocking the measuring person. Therefore, this method is dangerous.


    I have been using multimeters for 40 years, I have never met at home or with anyone that my friends say that the multimeter would be damaged in this way. But what do I know ...

    Anyway, I am finishing the discussions in this thread because the moderator will finish me off with penalties, if someone has any more comments for me, I invite you to the priva.

    Greetings. Kamil


    The author of the topic is unfamiliar with electricity and may make a mistake in setting the meter. The layman does not distinguish between what is current, voltage, U, V, I, A. He will set it to measure the intensity of the current and he will hurt himself.
    The method of measuring dangerous voltage with a multimeter and your own body can only be proposed to someone very experienced, but only on the basis of MacGywer's final method in the absence of access to civilization.
    Let the author of the topic go to an electrical store and buy a neon lamp for PLN 5.
  • #37 18846630
    RNIC
    Level 16  
    Posts: 105
    Help: 8
    Rate: 23
    For 5 zlotys, it is already "great". The prices of neon samplers range from ~ 3 to ~ 10 PLN.
    Go to the store, buddy, buy a sampler and then you can safely check which phase it is. Unfortunately, when you see a switchgear with 3-core cables and at the same time in only 2 sockets, the knife in your pocket opens by itself. Well, unless the builders just added new circuits to the old existing installation.
    And this, in the absence of knowledge of the subject, for the person asking the question will probably be the safest solution to the question asked.
    Although a visit by a kumaty electrician is also advisable.
  • #38 18847053
    JohhnyCage11
    Level 5  
    Posts: 19
    Rate: 28
    There was an electrician I asked for, but not the same electrician who had done anything here in the past. He also stated the same:

    What he said:
    -the builders used the existing cables already in the wall and added their own 3-wire cables here and there.
    - despite the fact that they added new 3-wire here and there, and so in not all of these places the protective cable was connected (electrician's surprise and mine too)
    - therefore, the sockets in which there was no protective cable (or it was, but not connected at all) applied a patent (if I understood it correctly) - the ground cable first to the pin and from the pin to the ground input in the socket. He said it was always more than nothing.
    -said that in the box it would be necessary to exchange these devices for other ones, because the ones I have are "exaggerated" with the cables I have.
    - the possibility of installing a RDC, although he emphasized that with these cables it makes sense on average ..

    He had a nice large device (computer) with him, as he claims for several thousand, and there I saw he made various measurements on the display, he had a lot of equipment in general.

    When I asked him how to distinguish between a ground cable and a protective cable (he was looking at this large device after it was connected). He said that "you can use a meter", I connect one probe to the phase and the other to the other cable - if the indication is 0 it is "rather protective", although he ordered to buy a multimeter with RFM and then it shows, for example, ~ 50 ..
  • Helpful post
    #39 18847063
    elpapiotr
    Electrician specialist
    Posts: 12210
    Help: 1015
    Rate: 3530
    JohhnyCage11 wrote:
    What he said:
    -the builders used the existing cables already in the wall and added their own 3-wire cables here and there.
    - despite the fact that they added new 3-wire here and there, and so in not all of these places the protective cable was connected (electrician's surprise and mine too)
    The builders took advantage and took advantage of their and their client's ignorance and dragged him to pointless costs. Normal operation for tricksters, but as the saying goes:
    The old truth says - " a bricklayer and a forester are not a craftsman. And the painter is fern "
    The obvious fault of the client / principal, who should know that the builders do not know each other and will not know about electricity.
    I meet such flowers often, even here:

    How to check with a meter which cable is 0 and which is phase
  • #40 18848220
    xray81
    Level 22  
    Posts: 502
    Help: 37
    Rate: 73
    Such a meter is a multimeter and you need to know how to use it, although the Unit releases meters with help where the display shows where to connect the "probes" at the selected setting, but you still need to know what setting the multimeter to choose. It's best if you use a bipolar meter in German called Duspol, e.g. something like UNI-T UT18C where one of the probes will show you where the phase is.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around using a UNIT-T UT 33C multimeter to identify phase and neutral wires in an apartment's electrical installation. Users suggest measuring voltage between the wires and a grounded point, such as a water pipe, with the expectation that the phase wire will show approximately 230V while the neutral wire will show 0V. Concerns are raised about the safety and accuracy of this method, with recommendations to use a neon indicator for safer measurements. The conversation also highlights issues with the existing electrical installation, including the absence of RCDs and proper grounding, and the need for professional electrical work to ensure safety and compliance with regulations.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: 230 V AC can stop a heart in under 0.2 s [HSE, 2018]; "Use a neon probe, not your body" [kaz69, #18845268]. Set the UT33C to 500 V AC, probe each conductor to a verified earth—≈230 V tags the phase. Why it matters: mis-identifying wires risks lethal shock and appliance damage.

Quick Facts

• Polish mains: 230 V ±10 % at 50 Hz [PSE, 2023] • Recommended meter range: ≥500 V AC, CAT II for socket checks “UT33C Manual” • Neon phase tester price: 3–10 PLN [RNIC, #18846630] • RCD trip current for socket circuits: ≤30 mA [PN-HD 60364-4-41] • Wire colours: brown = L, blue = N, yellow/green = PE [IEC 60446]

How do I find phase and neutral with a multimeter?

  1. Switch UT33C to the 500 V AC range. 2. Touch the black probe to a known earth (pipe or PE bar). 3. Touch the red probe to each conductor. ≈230 V identifies phase; ≤5 V shows neutral [Sniezynka, #18845283].

Which meter jacks should I use on the UT33C?

Insert the black lead into “COM” and the red lead into “VΩ” as pictograms on the meter indicate; never use the “10 A” jack for voltage tests to avoid fuse rupture or arc flash “UT33C Manual”.

Why is testing against earth safer than between two unknown wires?

Measuring to earth limits fault current through the meter and keeps one probe on a stable potential, reducing short-circuit risk [Łukasz.K, #18845497].

What if both wires show 120–180 V to earth?

Digital meters have high input impedance, so induced or phantom voltages can appear on open neutrals. Confirm by using a low-impedance tester or neon probe [Anonymous, #18845301].

How accurate is a neon tester compared with a multimeter?

A neon probe draws 0.5–2 mA; it lights only when true phase is present, filtering phantom voltages. Multimeters resolve ±1 V but show misleading readings on floating conductors [RNIC, #18846630].

What setting mistakes can damage the meter?

Selecting the current (A) range and touching the probes across 230 V creates a dead short that can explode the fuse and shock the user [kkkamil, #18845481].

Why do regulations now demand an RCD?

RCDs trip within 40 ms at 30 mA, reducing fatal shock probability by 97 % [HSE, 2018] and are mandatory for household socket circuits since 2009 [PN-HD 60364-4-41].

What breaker size should protect standard sockets?

Use 16 A type B breakers with 2.5 mm² wiring; oversized 20 A devices overload cables and violate Polish standard [ta­ki­ja­siu, #18845702].

How can I retrofit earthing in a two-wire outlet?

Option 1: Pull new 3-core cable. Option 2: Convert the circuit to TN-C (S) by bonding the PEN conductor to the socket earth pin, then distributing PE separately—allowed only where network PEN continuity is verified by a qualified electrician [H3nry, #18845325].

What colour wires should I expect?

Brown (or black) = phase (L); blue = neutral (N); yellow/green = protective earth (PE). Older Polish flats may have two grey wires without PE [IEC 60446].

Could the meter show 0 V yet the wire be live?

Yes. A broken neutral can sit near 0 V to earth until a load operates, suddenly rising to 230 V—an edge-case that causes surprise shocks [Łukasz.K, #18845490].

3-step quick labelling procedure?

  1. Kill power, separate conductors. 2. Re-energise, test each to earth with neon probe; mark the lit one “L”. 3. De-energise, verify continuity of blue wires back to neutral bar before final connection.
AI summary based on the discussion. May contain errors.
ADVERTISEMENT