theo33 wrote: Only how it is when we have inductive and in production as well as when receiving and the same is with capacitive
Well, simply: the meter sums up the reactive energy, distinguishing whether this energy was taken at P+ or at P-.
5.8.0 - we downloaded X kvarh of reactive (inductive) energy from the network during active power consumption
6.8.0 - we took X kvarh of reactive (inductive) energy from the network during the production of active power
7.8.0 - we delivered X kvarh of reactive (inductive) energy to the grid during the production of active power
8.8.0 - we delivered X kvarh of reactive (inductive) energy to the grid while taking active power from the grid
theo33 wrote: Which, of course, can be eliminated?

In order to lower the voltage, reactive power (inductive by default) should be taken, i.e. work in quadrants I or II. Therefore, the consumption of reactive power (Q+) should be maximized by setting the inverter operating mode with inductive cos phi.
However, it should be noted that if we have a 3-phase system, it may happen that we take reactive power on one phase and give it out on the other. Then Q+ and Q- can light up simultaneously. Even all the arrows can light up at once, which shouldn't surprise anyone. Thus, the values of reactive power supplied and consumed can be simultaneously calculated in different registers of the meter, so this must be taken into account during some analyses.