Nie, dziękuję Przekieruj mnie tamQuote:Can anything be done about it,
Gronostaj Wojciech wrote:The inverter turns off the installation, the inverter shows the COD 15 inscription. It happens on Sunday and holidays, apparently there is too high voltage in the network, which is up to 253v, but still acceptable, is it possible to do something about it, is it possible to regulate the inverter. I am not an electrician, so the terms are not professional, can someone help me, thank you in advance.
lichtar wrote:I can see that a lot of users have the same problem and so far not resolved effectively. Are there any voltage limiters that could be connected between the inverter and the connection?
Slawek K. wrote:Report to the distribution operator in your area and the problem will be effectively solved by reducing the voltage in the network,
fazik wrote:I wonder what a "specialist" connected it to 2.5mm2 ...I spoke to Growatt. The dear gentleman instructed me to change the cable from the fuse box to the inverter to 5x6mm (currently 5x2.5mm and 15m long).
Claims it will help.
zbyszekkr wrote:In my opinion, it would be necessary to measure the voltage that is present in the network when the inverter turns off.
fazik wrote:zbyszekkr wrote:In my opinion, it would be necessary to measure the voltage that is present in the network when the inverter turns off.
435.9v
Panels power: 3720 kWh
I have a 5x2.5mm cable in my garage - strength. This is my installation in a 10-year-old building. Now I can see that this force is a bit weak. The electrician at the construction stage asked me about the power, and I said I don't know, I don't know myself. He asked if I would use the spike - I say no, and so the 5x2.5mm cable was given. I do not want to criticize anyone, because 10 years ago neither me nor the electrician thought about photovoltaics.
In turn, the gentlemen from photovoltaics connected to what they had. Damn, I can see that everyone would have to be controlled and labs in every area ...
I ordered a 5x6mm YKY cable and I will stick in the box on the facade, where there is a transition from PEN to PE + N, and I will run the cable under the paving stone by the wall. I plan to connect the earthing to the hoop so as not to cut the earthing wire running to the house. Everything will be in front of the differential, which is in the fuse box at home. May be?
fazik wrote:kosmos99 wrote:The distance to the transformer is of greater importance.
A small ... 200 meters.
AT PRO wrote:You have to try to pick up the production at such moments, because the EC does not want it either if there is no one to use it.
AT PRO wrote:kosmos99 wrote:
It is not exactly like that, the transformer works both ways.
Are you sure? I don't think so. But let someone who knows it from practice speak.
TL;DR: 1-phase PV inverters trip when grid voltage tops 253 V; users logged 248-253 V at the meter (≈6 % above nominal) [Elektroda, zerolinux, post #18625298] “Settings other than 253 V are non-compliant” [Elektroda, sq9fmc, post #18610472]
Why it matters: Every unplanned shutdown stops production, voids revenue, and may shorten inverter life.
• Statutory grid window: 230 V ± 10 % → 207–253 V (EN 50160:2010). • Typical inverter reconnection delay: 60–180 s after voltage returns to range [Fronius Datasheet, 2022]. • Max cable voltage drop recommended: ≤1.5 % for PV AC runs (VDE-AR-N 4105). • 6 mm² copper over 50 m carries 3 kW 1-phase with ~1.6 % drop [Elektroda, theo33, post #18625918] • DSO site visit costs: ~PLN 850 if parameters prove compliant [PGE Tariff, 2023].