On-grid photovoltaics to the socket / microinverter

elvis1987 16323 13
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 19421531
    elvis1987
    Level 13  
    Hello.
    Due to the fact that I do not know the subject of photovoltaics, I wanted to ask about on-grid installations. Recently I heard that installations can be connected directly to the socket. The connection is made by means of a microinverter mounted on the panel.

    I tried to find answers to my questions, but most of the descriptions are related to large installations and separate switchboards with protection.

    I found one representative on the Internet and he replied that you can normally connect it to the socket and everything should work. He also wrote that I do not have to report such a connection to the power industry.

    Has anyone done something like this?
    What if there is a short circuit on the circuit to which the installation is connected and the overcurrent protection in the main switchgear works - the microinverter with the EV panel is still connected and generates energy.

    What about the legalization of such an installation? After all, as it is normally plugged into the socket, you also need all these documents with diagrams and measurements from an electrician?
  • ADVERTISEMENT
  • #2 19421587
    krzywy1
    Level 24  
    Theoretically, if you do not give energy to the grid, but consume everything on an ongoing basis, you do not have to report. But if you have an electronic meter, take into account that any surplus returned to the network will be counted by the meter as your consumption. For peace of mind, it's better to report such an installation.
    elvis1987 wrote:
    What if there is a short circuit on the circuit to which the installation is connected and the overcurrent protection in the main switchgear works - the microinverter with the EV panel is still connected and generates energy.

    In the event of a power failure from the grid, the microinverter will turn off automatically.
  • #3 19422165
    elvis1987
    Level 13  
    Can every on-grid microinverter be plugged into an outlet? I found some microinverters online, but the manual did not mention the possibility of plugging directly into the socket in the apartment.

    Does anyone know of any models that can be connected like this?
  • #4 19422280
    krzywy1
    Level 24  
    Generally, each on-grid inverter plugs into the grid. A part of the network is also an electric socket in the apartment. It's more about power, larger inverters require protection, smaller ones - here you have to read the manual, sometimes they have built-in protection.
    I dug up Commission Regulation (EU) 2016/631 of April 14, 2016 - notification procedure for PV installations, and it turns out that it specifies requirements only for installations with a capacity above 0.8 kW. If the set is smaller, you do not need to submit any documents or report anything, because ZE treat such installations as off-grid.
    There is only a risk, as I wrote in the previous post, that the overproduction will be counted by the electronic counter as consumption. If you have a traditional meter, there is no problem.
    There are whole kits on sale for connecting to the socket in the apartment.
  • ADVERTISEMENT
  • #5 19423394
    MichałS
    Level 35  
    Such a micro installation is a good way to get acquainted with PV. There are also people who install one panel and a microinverter to see if a large installation makes sense in a given location (large trees, blocks of flats, etc.).
  • #6 19424369
    elvis1987
    Level 13  
    That's what I'm trying to do with photovoltaics. I found a few microinverters and on Monday I will call the manufacturers / shops if their devices can be used in such a solution. And whether their microinverters have the appropriate certificates - because I heard that there are problems with some Chinese.
    Do such microinverters also have the ability to control statistics? Do I need to buy an additional module?
  • #7 19424425
    MichałS
    Level 35  
    Check well, even here on the Forum there is a thread about micro inverters, which when they work, there is no question of receiving DVB-T or FM in stereo, and the GSM range is lost in their vicinity.
  • ADVERTISEMENT
  • #8 19426086
    elvis1987
    Level 13  
    That's one more question. The manual says that LL, LV and PE-PE should be connected

    I have a network at home. TN-C system in my switchgear I have a N and PE section. Can such a set of panels and a microinverter also function properly in this case?
  • #9 19426235
    MichałS
    Level 35  
    elvis1987 wrote:

    I have a network at home. TN-C system in my switchgear I have a N and PE section. Can such a set of panels and a microinverter also function properly in this case?
    As for the division into N and PE, the network is TN-S, or TN-CS. I understand that the split point is grounded?

    In the case of a common neutral and protective conductor, there is a risk of voltage appearing on the metal housing of the microinverter.
  • ADVERTISEMENT
  • #10 19426276
    tyqva
    Level 35  
    MichałS wrote:
    ...In the case of a common neutral and protective conductor, there is a risk of voltage appearing on the metal housing of the microinverter.

    You got me interested, please elaborate.
    Give the difference in connecting the inverter to a house installation with undivided PEN into N and PE, and connecting the inverter to a house installation with divided PEN into N and PE.
  • #11 19427920
    elvis1987
    Level 13  
    I live in a block of flats with an exposed south-facing terrace.
    Unfortunately, only two wires come to me. When the electrician was doing a new installation, he made a section (N and PE) in my private switchgear (then L and N for the differential).

    Can I also install these on-grid inverters in such a solution?
  • #12 19427930
    MichałS
    Level 35  
    You can, they will work, but it is necessary to ensure that N and L are not swapped.
  • #13 19857548
    marcin.gawenda
    Level 11  
    krzywy1 wrote:
    I dug up Commission Regulation (EU) 2016/631 of April 14, 2016 - notification procedure for PV installations, and it turns out that it specifies requirements only for installations with a capacity above 0.8 kW. If the set is smaller, you do not need to submit any documents or report anything, because ZE treats such installations as off-grid.


    I see no obstacles to report such an installation below 800W and become a prosumer.
    If the microinverter is on this list http://ptpiree.pl/documents/opracowania/kodek.../2022-02-01-wykaz-certyfikowane--urzadzen.pdf then there should be no problem with receiving such a notification by the DSO.
    The RES Act does not provide for a lower limit of installation capacity :)
  • #14 19857733
    kortyleski
    Level 43  
    Almost everyone has an electronic meter. Therefore, it is worth reporting the installation as a prosumer and obtaining two-way counting. If only so that there is no holiday situation when production will be and consumption will not. And on my return, a wild electricity bill.

Topic summary

The discussion revolves around the feasibility and regulations of connecting on-grid photovoltaic (PV) systems directly to household sockets using microinverters. Users express concerns about the legality of such installations, particularly regarding the need for reporting to power companies and the implications of overproduction being counted as consumption by electronic meters. It is noted that installations below 800W may not require reporting, as they are treated as off-grid by distribution system operators (DSOs). Users seek clarification on specific microinverter models that can be plugged into sockets and the importance of ensuring proper electrical connections (N and PE) to avoid safety risks. The conversation also touches on the potential for interference with radio signals due to microinverter operation and the benefits of monitoring energy production statistics.