[Solved] Cable cross-section for WLZ for 18kW, 32A, heat pump and induction - copper or aluminum?

R1990 12183 10
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 19454582
    R1990
    Level 9  
    Hi.
    Technical parameters of the connection:
    Power 18 kW, protection 32A. The length of the WLZ is approximately 22 m. Power-hungry devices - 1-phase heat pump, thermal power 7 kW (electric power max 3.5 on one phase, plus graduated heaters 3-6 kW on the second phase), 7.5 kW induction divided into 2 phases, probably some car charging in the future electric charger 3f 11 kW from the power connector in the garage. Some say 4x10, others 4x16 (for the future), and some say about aluminum, and this is where I started to consider it, because copper prices are a failure. Aluminum is probably 4x25, so I would be 600 hundred points ahead of Cu.
  • ADVERTISEMENT
  • #2 19454610
    stonefree
    Level 27  
    The calculated voltage drop from the point of connection to the last receiver in the installation cannot exceed 3%. In addition, you should check the conditions for the effectiveness of protection against electric shock if the power supply is in the TN system, and, of course, check the load capacity of this cable.
  • Helpful post
    #3 19454627
    tyqva
    Level 35  
    R1990 wrote:
    ...Aluminum is probably 4x25 so I would be 600 hundred points ahead of Cu.

    YAKY 4x25mm² meets your needs.

    Cable cross-section for WLZ for 18kW, 32A, heat pump and induction - copper or aluminum?
  • ADVERTISEMENT
  • Helpful post
    #4 19454731
    retrofood
    VIP Meritorious for electroda.pl
    R1990 wrote:
    Aluminum is probably 4x25, so I would be 600 hundred points ahead of Cu.


    And don`t even think twice about it. Almost all power industry runs on aluminum cables.
  • #5 19456878
    R1990
    Level 9  
    What is the maximum load capacity of a 4x10 Cu cable? So safe that it won`t flood the insulation. Will it pull with 22 kW?
  • ADVERTISEMENT
  • #6 19456913
    retrofood
    VIP Meritorious for electroda.pl
    R1990 wrote:
    What is the maximum load capacity of a 4x10 Cu cable? So safe that it won`t flood the insulation. Will it pull with 22 kW?


    Tables of long-term, permissible load capacity of wires (cables, too, in terms of cross-section of wires) are published. You just need to find one that will suit the way the cable is laid, i.e. the environmental conditions. At the same time, we must not forget about the principle of chain strength. A chain is only as strong as its weakest link. That is, we select the table for the least favorable conditions on the route, even if they occur only at a length of several dozen centimeters.
  • #7 19458926
    R1990
    Level 9  
    Does the presence of PV and current flow in both directions influence the selection of the diameter of the WLZ cables?
  • #8 19458976
    tyqva
    Level 35  
    R1990 wrote:
    Does the presence of PV and current flow in both directions influence the selection of the diameter of the WLZ cables?

    Of course.
    You select the cross-section for greater flow. If you intend to send more to the grid than you have in your energy supply contract, you select the wlz cross-section for sending to the grid, not for receiving from the grid.
    But I don`t think you should decide on a higher PV power than 18 kW, and that`s how much your wlz is selected.

    Added after 10 [minutes]:

    R1990 wrote:
    What is the maximum load capacity of a 4x10 Cu cable? So safe that it won`t flood the insulation. Will it pull with 22 kW?

    22 kW exceeds the permissible current of Cu 4x10mm². In addition, the current flowing is greater than the protection value (32A), and after some time the protection will turn off the circuit.
  • #9 19459003
    R1990
    Level 9  
    tyqva wrote:
    R1990 wrote:
    Does the presence of PV and current flow in both directions influence the selection of the diameter of the WLZ cables?

    Of course.
    You select the cross-section for greater flow. If you intend to send more to the grid than you have in your energy supply contract, you select the wlz cross-section for sending to the grid, not for receiving from the grid.
    But I don`t think you should decide on a higher PV power than 18 kW, and that`s how much your wlz is selected.

    Added after 10 [minutes]:

    R1990 wrote:
    What is the maximum load capacity of a 4x10 Cu cable? So safe that it won`t flood the insulation. Will it pull with 22 kW?

    22 kW exceeds the permissible current of Cu 4x10mm². In addition, the current flowing is greater than the protection value (32A), and after some time the protection will turn off the circuit.

    Thanks.
    I don`t expect the PV to be higher than the connection power :)
    With these 22 kW, I was thinking more about the future and, if necessary, increasing the protection to 40A.
    At 22 kW of power we have about 7.33 kW per phase, which gives a current of practically 32A per phase. A 10mm2 wire won`t withstand 32A for a long time?
  • ADVERTISEMENT
  • #10 19459154
    tyqva
    Level 35  
    R1990 wrote:
    ...A 10mm2 wire won`t withstand 32A for a long time?

    It won`t last under certain conditions, so I wouldn`t sign it.
    But the proposed AL 25 fulfills your dreams; will withstand and 30 kW.
    Cable cross-section for WLZ for 18kW, 32A, heat pump and induction - copper or aluminum?
  • #11 19757320
    R1990
    Level 9  
    using user advice

Topic summary

The discussion revolves around selecting the appropriate cable cross-section for a WLZ (main power supply line) to support an 18 kW load with a 32A protection, considering future expansions such as a heat pump and induction cooktop. Users suggest that a 4x25 mm² aluminum cable would meet the requirements, as it can handle higher loads and is more cost-effective than copper. Concerns about voltage drop, load capacity, and the impact of photovoltaic (PV) systems on cable selection are also addressed. The consensus is that a 4x10 mm² copper cable would not suffice for the anticipated load, especially if future upgrades to 40A protection are considered.