Hello.
I have some doubts about the characteristics of the inverter SUN2000-20KTL-M2.
In the user manual, it is written that there is a DC switch, but it is recommended to install a PV circuit breaker with a rated voltage greater than or equal to 1100 V DC and a rated current of 15 A. Why? If there is integrated DC protection into the inverter with the DC switch, why should I install another one?
The second doubt is this: Even if I have to install the PV circuit breaker, why is the recommended rated current 15A? In the datasheet, it is written that MPPT current is 22A, while the short circuit current is 30A. According to this, I can install PV modules with MPPT current higher than 11A (but lower than 22A) and short circuit current higher than 15A (but lower than 30A). With this configuration, I must use one input per MPPT.
I need a clarification for this one. I installed already Risen 545 W modules with Impp= 17.22 A and Isc=18.23 A (under STC conditions). I am using 18 PV modules per string and having 2 different strings that will enter different MPPT. If this is not satisfying the characteristics of the inverter, I should change it immediately. Do you think that I will have a problem with this configuration?
Thank you.
I have some doubts about the characteristics of the inverter SUN2000-20KTL-M2.
In the user manual, it is written that there is a DC switch, but it is recommended to install a PV circuit breaker with a rated voltage greater than or equal to 1100 V DC and a rated current of 15 A. Why? If there is integrated DC protection into the inverter with the DC switch, why should I install another one?
The second doubt is this: Even if I have to install the PV circuit breaker, why is the recommended rated current 15A? In the datasheet, it is written that MPPT current is 22A, while the short circuit current is 30A. According to this, I can install PV modules with MPPT current higher than 11A (but lower than 22A) and short circuit current higher than 15A (but lower than 30A). With this configuration, I must use one input per MPPT.
I need a clarification for this one. I installed already Risen 545 W modules with Impp= 17.22 A and Isc=18.23 A (under STC conditions). I am using 18 PV modules per string and having 2 different strings that will enter different MPPT. If this is not satisfying the characteristics of the inverter, I should change it immediately. Do you think that I will have a problem with this configuration?
Thank you.