4.9 kWp Solar Panel Installation: Coping with 253V Voltage Peak on SMA SB 4600 W Inverter

DANIELijuz 43926 19
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16518606
    DANIELijuz
    Level 2  
    Hello.
    I have recently had a photovoltaic installation - 4.9 kWp panels and a single-phase SMA SB 4600 W inverter. After connecting, it turns out that during the peak of energy production, the voltage reaches even 253 V and then the inverter disconnects. I will add that my connection is a 5x16mm? cable (copper) So I do not think that I could improve something more on my part. The voltage in the network is at least 240 V - so normal. During the production it has to be raised, normal, but to do that? on the supplier's side it is an overhead line (I do not know what cross-section, I think it is 32mm? Al) and the distance to the transformer is about 500m. Anyone know what can be improved in such a situation to eliminate this problem?
  • ADVERTISEMENT
  • #2 16518628
    chrobry25
    Level 14  
    I'm surprised you opted for such power in one phase. I have 4.5 kW and similar problems. What is your wire size from the inverter to the meter?
  • ADVERTISEMENT
  • Helpful post
    #3 16518631
    prose
    Level 35  
    1. Change the inverter settings.
    2. Switch to another phase.
    3. Load the phase on which the inverter is located, eg with a heater
    4. As the inverter does not change to another country, the inverter is replaced.
    5. Decompose the installation into 2 phases.
    6 Report overvoltage goes to lower voltage.
    Write what inverter you have.
  • #4 16518704
    DANIELijuz
    Level 2  
    Connection as I wrote - 16mm?, and 10mm? to the inverter

    Added after 6 [minutes]:

    1. Change the inverter settings.
    2. Switch to another phase.
    3. Load the phase on which the inverter is located, eg with a heater
    4. As the inverter does not change to another country, the inverter is replaced.
    5. Decompose the installation into 2 phases.
    6 Report overvoltage goes to lower voltage.
    Write what inverter you have.


    1.Turns off at 253V so according to the standards.
    2. They all have the same tension.
    3.No sense.
    4. See 1.
    5.Single phase inverter.
    6. The most sensible, but will the network operator be interested in such a small fence?
    SMS inverter SB 4600 TL
  • Helpful post
    #5 16518764
    chrobry25
    Level 14  
    As for point 1 you can set to a different standard and it will turn off at higher voltages. For me it is about 260V. The most sensible thing is to get along with the operator about lowering the voltage, but somehow I don't believe it.
  • Helpful post
    #6 16519008
    3301
    Level 34  
    DANIELijuz wrote:
    Connection as I wrote - 16mm2, while to the inverter 10mm2

    Added after 6 [minutes]:



    1. Shuts down at 253v so according to standards.
    2. They all have the same tension.
    3.No sense.
    4. See 1.
    5.Single phase inverter.
    6. The most sensible, but will the network operator be interested in such a small fence?
    SMS inverter sb 4600 TL

    Measure these voltages at the connection, maybe there is a voltage drop at the connections.
    point 2- nevertheless test on the others, the stiffness of the tension is also important, i.e. how much it will rise on each phase.
    Not necessarily the lowest voltage will be the best for the correct operation of the inverter.
  • ADVERTISEMENT
  • #7 16519294
    Anonymous
    Level 1  
  • Helpful post
    #8 16519341
    Jan_Werbinski
    Level 33  
    Connecting heaters or other loads helps. In the long run, change the country and thus the tension through the Guard Code. Then you risk damaging the equipment of other customers on this transformer.
  • #9 16521113
    Frog_Qmak
    Level 25  
    Jan_Werbinski wrote:
    Then you risk damaging the equipment of other customers on this transformer.


    May I have a further explanation of why?
  • #10 16521158
    Jan_Werbinski
    Level 33  
    253V is the maximum voltage that complies with the standard. The neighbor's household appliances that you burn by increasing the voltage on your street to 253V will be faulty and he is to repair it at his own expense. If you burn them at 260V and prove it to you, theoretically you have to cover all the damage.
    I had a similar problem before changing the settings of the inverters. In the afternoon they turned off with the message of too high AC voltage. It was ad hoc to turn on the boiler and washing. Another reason was a drop by a few V due to makeshift and poor contacts - I changed the cable to the PV switchboard to 5x4mm2 and improved the connections, which eliminated the voltage drop. Finally, I changed the standard to EN50438 (no. From memory), the voltage ranges of which were greater than the country where the inverters came from.
    Some people change to Germany and then the upper voltage is probably 260V. Get a Guard Code from SMA and you can change it at your own risk. You have to tell them you're an electrician. ;-)
  • #11 17372598
    wiekam1
    Level 10  
    What is the distance of the inverter from the meter? I had a similar problem, because I installed an inverter next to the panels, several meters from the meter. As a result of the existing resistance and voltage drop on the wires (and possibly poor contacts) there was a voltage difference of a few volts at the meter and the inverter, as a result of which the inverter tried to "catch up" with the voltage, it threw out after exceeding 253V. The problem disappeared after moving the inverter just beyond the meter. There was another one that I also dealt with, but that's a different topic.
  • #12 17373596
    Frog_Qmak
    Level 25  
    wiekam1 wrote:
    There was another one that I also dealt with, but that's a different topic.

    Can a colleague develop a thought? It sounds interesting :)
  • ADVERTISEMENT
  • #13 17374319
    Jan_Werbinski
    Level 33  
    A difference of a few volts over a dozen meters precludes the correctness of the installation.
  • #14 17374506
    wiekam1
    Level 10  
    Frog_Qmak wrote:
    wiekam1 wrote:
    There was another one that I also dealt with, but that's a different topic.

    Can a colleague develop a thought? It sounds interesting :)


    As the inverter was "more rigidly" connected to the network, it began to react to sudden load changes (it is about switching the 2 kW boiler heater on and off) and off. Changing the boiler power phase helped, because earlier the inverter was on the same phase.

    Today I have a bad day, the SOLON model Satis 30/750 inverter has failed after 3 years and only displays the message "STS foul PIC". Probably a small chance, but maybe someone had to deal with this type and accident?

    Added after 6 [minutes]:

    Jan_Werbinski wrote:
    A difference of a few volts over a dozen meters precludes the correctness of the installation.


    Exactly, this was the case I had to deal with. I also noticed that the inverter itself shows a slightly higher voltage (in relation to the meter, assuming, of course, that it measures well) than it does, and I assumed that maybe a standard "overlap" is taken to make it within the accepted standard.
  • #15 18652128
    naitsabes
    Level 11  
    Hello
    I show up here with another problem, my connection is at the very end of the transformer thread and I have very high voltage drops sometimes on one phase, sometimes on the other and for this reason the inverter turns off the photos from the application from the inverter please give a hint for which country what standard switch the inverter so that the inverter shutdown voltage is lower.
    The inverter is SOFAR 6.6KTL-X

    best regards
    Sebastian
  • #16 18652469
    3301
    Level 34  
    You can see a problem mainly with the S phase, the voltage drops below 190V and this is more than the permissible +/- 10% and I think that changing the country will not help here because the other phases are normal, then you would have to report to the operator by presenting photos with voltage indications from their own meter because that might be more convincing
  • #17 18653052
    MichałS
    Level 35  
    Perhaps the problem would be solved by replacing it with an Elnix inverter and setting the lower operating voltage to 180V in the installer menu.
  • #18 18653337
    Leon444
    Level 26  
    MichałS wrote:
    Perhaps the problem would be solved by replacing it with an Elnix inverter and setting the lower operating voltage to 180V in the installer menu.


    If you had too little air in one wheel, you would deflate the other three to improve - a brilliant idea, especially with this Elnix crap.

    You have to report the problem to the operator and they will act correctly, increasing the voltage.
  • #19 18653354
    MichałS
    Level 35  
    But the "blemish" found up to 184V inverter should work normally.
  • #20 18653934
    Leon444
    Level 26  
    You went for advice, if you have a problem with the network, do not report it to the operator, just replace the inverter for a few thousand, brilliant.

Topic summary

The discussion revolves around a 4.9 kWp solar panel installation using a single-phase SMA SB 4600 W inverter, which experiences disconnection due to voltage peaks reaching 253V during energy production. Users suggest various solutions, including changing inverter settings, switching phases, adding loads to balance the phase, and potentially replacing the inverter or splitting the installation across two phases. Concerns about the network operator's willingness to address voltage issues are raised, along with the importance of measuring voltage drops at connections. Some users share experiences with similar problems and recommend adjusting inverter standards to allow for higher voltage tolerances. The conversation highlights the complexities of managing voltage in solar installations, especially with long distances to transformers and varying load conditions.