Best Electronic DC Loads for 6.5kW 400V Applications—Recommendations and Experiences
315 12
What load options can handle about 6.5 kW at 400 Vdc for a distorted-voltage test, and what equipment have people had good experiences with?
For a 6.5 kW, 400 Vdc test, the thread recommends using a resistive load bank or heater assembly rather than a purpose-built electronic load: commercial HVAC duct heaters can be rewired for DC use, sized in many ranges, and cooled with standard fans [#21660073] One practical resistor-based approach is Ohmite 225 W resistors with forced air; one reply estimates about 260 cfm of airflow for 30 resistors at 6.5 kW and says they would not derate them for a simple test load [#21660071] Another option is TE Connectivity 2500 W resistors, with three units suggested as an inexpensive load [#21660072] Hotwatt finned strip heaters were also recommended for kilowatt-range loads, again with lots of forced air [#21660080], and Watlow was mentioned as making both air-cooled and water-cooled loads [#21660082] If you do need an active electronic load, Amrel DC loads were mentioned as a good experience, while Chroma and California Instruments were cited for AC loads with adjustable PF and phase angle, but at high cost [#21660079][#21660075]
  • Need 10 kW, 500 V electronic load recommendations
    #1 21660070
    Jim Mikolich
  • #2 21660071
    DAVID CUTHBERT
  • #3 21660072
    DAVID CUTHBERT
  • #4 21660073
    Peter Blackford
  • #5 21660074
    DAVID CUTHBERT
  • Heating elements as resistive load-bank substitute
    #6 21660075
    Kevin Parmenter
  • #7 21660076
    Jim Mikolich
  • #8 21660077
    Jim Mikolich
  • Dual-use load setup for 3-phase qualification testing
    #9 21660078
    Jim Mikolich
  • #10 21660079
    Kevin Parmenter
  • #11 21660080
    David Erickson
  • #12 21660081
    Per Zackrisson
  • #13 21660082
    DAVID CUTHBERT
The discussion addresses the need for a high-power variable resistive load capable of handling approximately 6.5 kW to 10 kW at around 400 V DC for distorted voltage testing and THD adjustment on the rectified side of a bridge. Several solutions are proposed, including using multiple high-wattage resistors such as Ohmite 225 W resistors with forced air cooling, TE Connectivity 2500 W resistors requiring fewer units, and Huntington FSE1000-1.0 1000 W resistors. Commercial HVAC duct heaters and finned strip heaters from Hotwatt are suggested as cost-effective, high-power resistive loads that can be rewired for DC use with adequate forced air cooling. Light bulbs and heating elements in ceramic sockets are also mentioned for low inductance loads, though with caution regarding inrush currents. For more advanced and adjustable electronic loads capable of AC testing with power factor and phase angle control, brands like Chroma and California Instruments are referenced, though these are significantly more expensive. Amrel DC loads are noted for DC applications but may require a bridge for AC testing. WATLOW is mentioned as a manufacturer of air-cooled and water-cooled loads. The discussion highlights considerations such as derating, thermal management, safety features, and cost comparisons between building resistor banks and renting commercial electronic loads.
TL;DR: For ~6.5 kW at ~400 Vdc, 30×225 W resistors need ~260 cfm airflow; they “work well” with forced air. [Elektroda, DAVID CUTHBERT, post #21660071]
Why it matters: This FAQ helps power engineers choose safe, affordable high‑power DC loads for distortion and qualification tests, fast.
What’s the most cost‑effective way to sink ~6.5 kW at ~400 Vdc?
Use a resistor bank with forced air. One proven setup uses 30×225 W Ohmite parts and ~260 cfm total airflow. This achieves the target power with controlled temperature rise. Keep wiring short and use proper guarding and fusing. “The … resistors … work well especially with some forced air.” [Elektroda, DAVID CUTHBERT, post #21660071]
Can I use an HVAC duct heater as a DC load?
Yes. Commercial duct heaters scale well at multi‑kilowatt levels and can be rewired from three‑phase to a DC (single‑phase) configuration. Add standard fans for heat removal and design for electrical and thermal safety clearances. Verify resistance and mounting per your test plan. [Elektroda, Peter Blackford, post #21660073]
Are finned strip heaters a viable option?
Finned strip heaters in the kilowatt range are convenient and reasonably priced. They need strong forced air. They are commonly run from AC; for DC use, check resistance stability and inductance against your measurement needs before committing. [Elektroda, David Erickson, post #21660080]
How many resistors and how much airflow do I need for 6.5 kW?
A practical example from the thread specifies 30 pieces of 225 W resistors with about 260 cfm airflow. That supports a 50 °C air rise at 6.5 kW total. Use baffles to distribute airflow evenly across the bank. [Elektroda, DAVID CUTHBERT, post #21660071]
I need variable R up to ~50 Ω—how do I approach switching?
A 1 Ω/1 kW element array needs roughly 50 pieces to reach 50 Ω steps, plus contactors and cabinet hardware. Switching networks add cost, complexity, and safety requirements, which can rival renting a commercial load for short projects. [Elektroda, Jim Mikolich, post #21660076]
Do light bulbs or screw‑in heating elements work as loads?
They can, but beware of high inrush current on incandescent lamps. Ceramic sockets with screw‑in heating elements are an option for resistive loading. For adjustable AC loads with power‑factor control, commercial gear exists but costs more. [Elektroda, Kevin Parmenter, post #21660075]
When should I rent a programmable electronic load instead of building?
If you need fast setup, programmability, and protection features at high voltage, rental can beat build time and safety engineering. The thread notes that DIY switching and safety hardware can approach commercial load budgets, making rental attractive. [Elektroda, Jim Mikolich, post #21660076]
What safety measures are essential for high‑power resistive loads?
Provide forced cooling, thermal fuses or sensors, guarded terminals, and clearances. Use fans rated for the temperature rise and ensure safe wiring and mounting. As one poster advises, configure for both electrical and thermal safety from the start. [Elektroda, Peter Blackford, post #21660073]
What is an electronic DC load (in this thread’s context)?
It refers to a commercial programmable load that sinks power from a DC source or a rectified AC source. Such loads provide adjustable current, voltage limits, and protections, and can replace ad‑hoc resistor banks when precision is required. [Elektroda, Kevin Parmenter, post #21660079]
How do I handle a three‑phase device when tests target each phase?
Keep a three‑phase‑capable load available if your equipment under test is three‑phase. You can still perform per‑phase distortion tests while benefiting from a 3φ load bank for broader qualification or dual‑use needs. [Elektroda, Jim Mikolich, post #21660077]
3‑step: How do I assemble a forced‑air resistor load bank?
  1. Size power: target ~6.5 kW and a 50 °C air rise.
  2. Install ~30×225 W resistors on heat‑safe mounts in a ducted plenum.
  3. Provide ~260 cfm airflow and add thermal protection and guards. [Elektroda, DAVID CUTHBERT, post #21660071]
Who makes turnkey air‑ or water‑cooled load banks?
Watlow manufactures air‑cooled and water‑cooled resistive loads appropriate for high‑power testing. These products can simplify mechanical and thermal integration compared with scratch‑built banks. Consult datasheets for voltage ratings and mounting. [Elektroda, DAVID CUTHBERT, post #21660082]
Which brands were used or mentioned for sources and loads in the thread?
California Instruments MX series was used as a source. Amrel was mentioned for DC loads. Chroma and California Instruments provide active AC loads with adjustable power factor and phase angle for advanced testing. [Elektroda, Kevin Parmenter, post #21660079]
What DC current am I dealing with at 6.5 kW and ~400 Vdc?
Current is power divided by voltage: 6,500 W ÷ 400 V ≈ 16.25 A. Select conductors, fuses, and shunts with adequate DC ratings and temperature rise margins for this current. Validate against your source and load ratings before energizing. [Elektroda, Jim Mikolich, post #21660070]
Any edge cases or failure modes to watch?
Incandescent lamps show large inrush, which can trip supplies or damage switches. Resistor banks without enough airflow overheat, drifting resistance and risking failure. Use staged startup and interlocks to prevent overstress events. “Watch out for the inrush currents.” [Elektroda, Kevin Parmenter, post #21660075]