Eaton Moeller Z-SCH230/25-40 Contactor Coil Voltage: Can I Use 24V DC to Test?

69 6
ADVERTISEMENT
  • #1 21675216
    ADENIJI SEGUN
    Anonymous  
  • ADVERTISEMENT
  • #2 21675217
    richard gabric
    Anonymous  
  • ADVERTISEMENT
  • #3 21675218
    ADENIJI SEGUN
    Anonymous  
  • #4 21675219
    richard gabric
    Anonymous  
  • ADVERTISEMENT
  • #5 21675220
    ADENIJI SEGUN
    Anonymous  
  • ADVERTISEMENT
  • #6 21675221
    Zachary Pick
    Anonymous  
  • #7 21675222
    richard gabric
    Anonymous  

Topic summary

A user inquired about testing an Eaton Moeller Z-SCH230/25-40 4-pole contactor by applying 24V DC to its coil terminals (A1 and A2) while connecting a 3-phase AC load to the main terminals. The contactor did not actuate, prompting the question of whether a DC voltage source can drive the coil. Responses clarified that the coil is specified for 230V AC operation, and applying 24V DC directly will not energize it. A recommended solution is to use a low-voltage DC supply to control a separate auxiliary relay, which in turn switches the AC coil voltage of the contactor. Alternatively, replacing the contactor with a model having a 24V DC coil is possible but may be more costly than using an intermediate relay. The wiring approach involves connecting the contactor coil to the AC mains and controlling it via the relay energized by the 24V DC source.
Summary generated by the language model.