PX2EN1XX200PSCHX Pressure Transducer Output Reads 36mA After Air Compressor Test
321 6
  • Overpressure likely damaged the 4–20 mA transducer
    #1 21675324
    Simon Iversen
  • #2 21675325
    Dean Franks
  • Capacitor placement corrected in wiring diagram
    #3 21675326
    Simon Iversen
  • #4 21675327
    Simon Iversen
  • Grounding check for Arduino and sensor supply
    #5 21675328
    Dean Franks
  • Sensor likely damaged after compressor test
    #6 21675329
    Simon Iversen
  • Possible liquid-only transducer or input damage
    #7 21675330
    J Boz
A PX2EN1XX200PSCHX pressure transducer with a 4-20mA output range for 0-200 PSI was tested using an air compressor but began outputting an erroneous 36mA current at atmospheric pressure instead of the expected 4mA. Initial setup powered the sensor from a Cotek GE-25 power supply providing 10-11V, with the Arduino powered via USB. Voltage measurements between V+ and V- terminals fluctuated, indicating potential grounding or floating power supply issues. Recommendations included verifying proper grounding between the Arduino and sensor, using a 10k resistor to test if power supplies are floating, and connecting the current sense resistor correctly. Despite adjustments, the sensor output remained constant regardless of pressure changes, suggesting sensor damage. It was proposed that the transducer might not be designed for air pressure testing, as air could breach internal seals, or the sensor's input circuitry could have been electrically damaged during testing with the air compressor. Confirmation from the manufacturer is advised to determine if the sensor was compromised by the test conditions.