Regarding to Gas Turbine ESD HH Low Frequency Pulsation of GTG
234 7
  • Ground fault on 35 kV feeder tripped both GTGs
    #1 21683487
    Akhmed Mambetnazarov
  • #2 21683488
    Maurizio Di Paolo Emilio
  • #3 21683489
  • #4 21683490
  • #5 21683491
    Alan Gallagher
  • #6 21683492
    Graham Rounce
  • #7 21683493
  • #8 21683494
    Graham Rounce
On 10.11.2019, emergency shutdowns occurred simultaneously on Gas Turbine Generators GTG-B and GTG-C triggered by the "ESD Low frequency pulsation external fault" signal. Investigation identified a single-phase-to-ground short circuit on phase C of a 35kV, 240 mm² power cable at the connection point of power transformer A30-TMM-201A in the HDPE plant. The question raised was why a fault on one outgoing feeder cable caused emergency shutdowns on both GTG-B and GTG-C units. The issue has recurred four times. Follow-up discussion requested schematic layouts and clearer documentation to analyze the problem. It was clarified that the frequency pulsation measurement device involved is a Bently Nevada system used to monitor flame pulsations in the gas turbines. Further detailed drawings were requested for deeper investigation.