How to ground a photovoltaic installation - TN-C installation

elektro92 53076 49
Best answers

How should I ground a photovoltaic installation in a building with a TN-C electrical system?

Bond the PV structure by direct equipotential bonding to the building’s main earthing/equipotential bar (GSU/GSW), and in a TN-C building the PEN grounding point can be used for PV protective equipment if it is in good technical condition; if not, repair it first and then use it [#18475401][#19755349] For a roof without a lightning protection system, one reply cites the standard-based solution as connecting the module support structure directly to the main equipotential rail in the building [#19755349] If the roof has a lightning protection system and the separation distance is respected, bond the PV structure with equalizing connections; if the separation distance is not maintained, connect the structure additionally to the lightning rod [#18772305][#15636420] One contributor also recommends a separate lightning-protection earth electrode brought to the facade to limit lightning current entering the building, but stresses that the final choice should follow a proper design/risk assessment and that no solution gives 100% protection [#18475401]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 15634987
    elektro92
    Level 15  
    Posts: 195
    Rate: 37
    Board Language: polish
    Hello. As the topic . How to do grounding. Installation in the TN-C building.
    I presented my idea in the pictorial picture.

    Thanks for the help.
    greetings


    How to ground a photovoltaic installation - TN-C installation
  • ADVERTISEMENT
  • #2 15635717
    Anonymous
    Anonymous  
  • #3 15636420
    taniam
    Level 20  
    Posts: 413
    Help: 28
    Rate: 41
    Board Language: polish
    electro92 - the structure of the panels is to be protected against lightning, grounding it via GSU is a mistake. This way you run a vertical lightning rod (because this is how you should treat the earthing conductor in this case) inside the building, which is forbidden.
    It does not matter if there is a hoop in the ground or a pin earth electrode - there should be 2 clamps:
    - for construction outside the building
    - to the equipotential rail as you solved it

    And by the way, the same is done for TN-cs installations.
  • #4 15637402
    elektro92
    Level 15  
    Posts: 195
    Rate: 37
    Board Language: polish
    Sorry, I did not describe exactly.
    My point was that the structure would be connected with an aluminum wire with a diameter of 10mm2 and connected to the hoop (outside) then from the hoop with a 10mm2 cable to the equalizing rail.

    Thank you.
    greetings

    Illustrative drawing:
    How to ground a photovoltaic installation - TN-C installation
  • ADVERTISEMENT
  • #5 15639247
    taniam
    Level 20  
    Posts: 413
    Help: 28
    Rate: 41
    Board Language: polish
    Almost good ;)
    The GSU connection - the earth electrode is made in the underground part.
    You need to make 2 control joints, distant from each other> 50 cm, descend from each of them separately with a hoop to the excavation and there you can connect it with a hoop or a pin.
  • #6 15644144
    elektro92
    Level 15  
    Posts: 195
    Rate: 37
    Board Language: polish
    Hello.

    To be sure that I understood correctly :) ??

    Thanks.
    greetings
    How to ground a photovoltaic installation - TN-C installation
  • #7 15644477
    Anonymous
    Level 1  
  • #8 15644723
    taniam
    Level 20  
    Posts: 413
    Help: 28
    Rate: 41
    Board Language: polish
    electro92 That's ok now.

    15kVmaciej wrote:
    Hello. Apparently, from time to time, I just need to expose myself to my views in general. :)
    Well, I would be careful with grounding these structures ...


    I fully support this point of view, but when they want to "ground" they should do it properly.
  • #9 15644818
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 669
    Board Language: polish
    15kVmaciej wrote:

    Well, I would be careful with grounding these structures. The first argument determining the need for such would be to investigate how many stormy days in a year there are statistically in the region. The second one, what is the geographical situation, I do not have any definition of the landscape, but it is related to the sphere graph - that is, if there are tall buildings or other natural "lightning rods" nearby, I would not invite lightning on my roof. I would actually strengthen the surrounding lightning protection systems so that my roof would remain in their shadow.

    You write about lightning grounding, but what about functional grounding?

    For example, my CiGSs must not only have a grounded minus, but also have a support structure. Any positive potential on the panel with respect to the environment must be dissipated to avoid PID. For now, I decided that until I come up with a better solution, I will connect it with a 6mm copper cable to the GSU or make a separate earth electrode (I do not have a hoop around the house).

    As for inviting discharges, as far as I know, by making a lightning rod, we do not change the "inviting" potential, but we only facilitate the discharge of energy from the lightning. The potential exists even if the roof is an insulator. The use of a lightning protection system allows you to save damage caused by the flow of current through the structure, wires in the wall, etc.

    Probably the most sensible thing to do is to make a lightning protection installation that will be above the PV so that the virtual ball does not touch it?
  • #10 15644866
    taniam
    Level 20  
    Posts: 413
    Help: 28
    Rate: 41
    Board Language: polish
    Jan_Werbinski wrote:

    For example, my CiGSs must not only have a grounded minus, but also have a support structure. Any positive potential on the panel with respect to the environment must be dissipated to avoid PID.


    Functional grounding is another pair of wellies - amorphous panels have their own rules.

    Quote:
    For now, I decided that until I come up with a better solution, I will connect it with a 6mm copper cable to the GSU or make a separate earth electrode (I do not have a hoop around the house).


    In the case of a supporting structure, I would treat it as a lightning conductor - the solution is given above. The 6mm2 cross-section is too small for equipotential bonding. Since you do not have a hoop, what do you have "pinned" GSU on?
  • #11 15644871
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 669
    Board Language: polish
    What cross-section to use?
    GSU with a 16mm2 cable to the driven copper-plated earth electrode, approx. 3 m long.
  • ADVERTISEMENT
  • #12 15644884
    Anonymous
    Level 1  
  • #13 15646140
    taniam
    Level 20  
    Posts: 413
    Help: 28
    Rate: 41
    Board Language: polish
    Jan_Werbinski wrote:
    What cross-section to use?


    In the event of exposure to mechanical damage, the cross-section should be increased by "mesh" or more, depending on the situation.

    Quote:
    GSU with a 16mm2 cable to the driven copper-plated earth electrode, approx. 3 m long.

    And what is the resistance of this "earth electrode"?
    Is this rail really a GSU?
  • #14 15646174
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 669
    Board Language: polish
    I did not measure, because I usually only have multimeters. The earth electrode will be expanded on the occasion of other works. GSU because that's what I called it and it is a point of separation between PE and N.
  • #15 15646253
    taniam
    Level 20  
    Posts: 413
    Help: 28
    Rate: 41
    Board Language: polish
    Jan_Werbinski wrote:
    I did not measure, because I usually only have multimeters. The earth electrode will be expanded on the occasion of other works. GSU because that's what I called it and it is a point of separation between PE and N.


    Sorry, but it doesn't work that way - you can't "sculpt" protective installations as you like. I understand that many people speaking in this section are enthusiasts and have quite a creative approach to the topic, but I am observing the entries appearing here with increasing concern.
    There is a lot of professional literature where you can find out what solutions should be applied in a specific case.
  • #16 15646267
    Jan_Werbinski
    Level 33  
    Posts: 2821
    Help: 76
    Rate: 669
    Board Language: polish
    Literature tells me to carry out a specific renovation, and preferably, with the development of technology, build the house from scratch every few years. Unfortunately, the literature does not specify where I should live at that time and where to get the money.
    There are intermediate steps. Partial protection is better than none, and the proof is that the electric shock protection works and the elimination of the negative potential of the panels. Establishing a hoop is the destruction of cobblestones and for the time being I am looking for other solutions.
  • #17 18041247
    Kerimm
    Level 1  
    Posts: 1
    Board Language: polish
    taniam wrote:
    electro92 - the structure of the panels is to be protected against lightning, grounding it via GSU is a mistake. This way you run a vertical lightning rod (because this is how you should treat the earthing conductor in this case) inside the building, which is forbidden.
    It does not matter if there is a hoop in the ground or a pin earth electrode - there should be 2 clamps:
    - for construction outside the building
    - to the equipotential rail as you solved it

    And by the way, the same is done for TN-cs installations.


    Do I understand that I can connect the panel structures to the lightning protection system, or should I lead a separate hoop to the ground?
  • #19 18042332
    MichałS
    Level 35  
    Posts: 2649
    Help: 254
    Rate: 661
    Board Language: polish
    Gentlemen, the topic is worth a further extension!

    It is enough to look at a few videos on YT to find out that installations are built where:
    a) the panels and the frame have no equipotential bonding at all and are on the roof
    b) as above but with ground mounting so they are "so-so" grounded
    c) panels connected to the GSU only for equipotential bonding (e.g. 1.5mm2)
    d) panel frames and rack connected to the lightning protection system
  • #20 18042608
    Wlodek22
    Level 31  
    Posts: 1777
    Help: 78
    Rate: 519
    Board Language: polish
    I am also watching the topic, I am also editing it and I am also confused. There will be a lightning protection device on the ridge (gable roof). The distance to the panel frames is 40-50 cm. Some people write to connect them to the lightning protection ins in this situation, but for my understanding it is probably better to use a thin cable for GSU as in point "c" and 16mm2 to the surge voltage at the DC input to the inverter. How is it for feint, is it a slim chance that the inverter will survive, and how is it going to rock frames? This...? The equipotential bonding and overvoltage protectors will evaporate, the inverter and most of the connected devices will probably burn. But the question remains where the discharge current will go.
    Would do otherwise. Connect the lightning protection system to the ring earth from one corner of the building, and the photovoltaic installation on the other side diagonally? Will the lightning protection system be effective in this system if it is connected to the rim at only one point? The electrician obtained less than 3 Ohm from the measurements.
  • ADVERTISEMENT
  • #21 18088940
    marecki636
    Level 6  
    Posts: 8
    Help: 1
    Rate: 7
    Board Language: polish
    Hello,
    Can the inverter and surge voltage on the DC side be connected to the PE conductor in the main switchboard in the TN-S network, can I extend the cable coming from the DC box because it is about 50 cm fi 16mm, there is no lightning protection at home, I made a pin earth electrode to ground the structure and I have 5ohm and I have less on the PE cable, I am asking for a quick answer.
  • #22 18249522
    TAGBA
    Level 11  
    Posts: 201
    Help: 1
    Rate: 85
    Board Language: polish
    elektro92 wrote:
    Hello.

    To be sure that I understood correctly :) ??

    Thanks.
    greetings
    How to ground a photovoltaic installation - TN-C installation


    Is it necessary to connect the ground bus of the PV panels to the main GSU in the diagram as presented by electro92? Where a type 1 + 2 3-phase surge arrester will be installed between the GSU and the Inverter. On the Dehn site, it is combined [url=]https://www.dehn.pl/sites/default/files/uploads/dehn/DEHN-PL/druki/ds109_fotowoltaiczne_pl.pdf[/url] . What the electro92 presented seems to me to be a better solution when lightning strikes it goes to the ground and to the surge arresters in front of the inverter from the side of the PV panels, and not to the house installation. I already have confusion in my mind.
  • #23 18277166
    MichałS
    Level 35  
    Posts: 2649
    Help: 254
    Rate: 661
    Board Language: polish
    Such a situation: the PV installation is located in the garage and has its earth electrode. The cable to the garage is pulled up from the main switchboard from before the security, practically from the partition point and grounding of the PEN.
    The question is whether it is necessary / recommended to connect PE with a PV earth electrode in the garage or not?
  • #24 18400750
    Grabe Jan
    Level 11  
    Posts: 8
    Rate: 9
    Board Language: polish
    AC side connected to ground, DC side only remains with PEN without grounding.

    Added after 3 [minutes]:

    Grabe Jan wrote:
    AC side connected to ground, DC side only remains with PEN without grounding.

    AC vs DC mistake !!!!
  • #25 18407387
    ghajduk
    Level 12  
    Posts: 74
    Rate: 19
    Board Language: polish
    Here you have a nice description of what the PV earthing on the roof should look like if we have a lightning conductor.
    http://www.inzynierbudownictwa.pl/technika,ma..._przepieciowa_instalacji_fotowoltaycznej,7874

    Each time the installation is earthed.
    The case when we do not have a lightning protection system at all is the least favorable, but then the structure should also be earthed, not only because of the lightning / overvoltage protection (limitation of the lightning current in PV DC cables), but maybe also the protection against electric shock, especially if the installation is is within easy reach (skylights).
    It is best to do the earthing in the way that the electro92 colleague drew straight, without entering the building with the wire.


    One of the largest distributors of inverters in Poland also recommends grounding structures and panels.
    http://blog.corab.eu/ochrona-instalacji-fotowoltaycznej-dachu-budynku/

    Photovoltaic installation without lightning protection
    If, during the appropriate analysis of the risk of lightning damage, according to the PN-EN 62305-2 standard, we receive information that the risk of this type of lightning discharges to a tolerable or lesser degree, we adjust our procedure to the absence of lightning protection. In this situation, the supporting structure of the PV module should be connected to the main rail of the potential equalization in the building with a direct equalizing conductor.
  • #26 18407420
    krzych101
    Level 13  
    Posts: 87
    Rate: 71
    Board Language: polish
    Link not active
  • #27 18407441
    ghajduk
    Level 12  
    Posts: 74
    Rate: 19
    Board Language: polish
    krzych101 wrote:
    Link not active

    Corrected.
  • #28 18474364
    dakius
    Level 2  
    Posts: 3
    Board Language: polish
    Hello,
    I would like to ask you for an answer to my question, and not a pointless posting, it is here and there, because here in the thread there is also a little muddle ...
    So I have this situation, I am at the stage of looking for a company that will make photovoltaic installations for me, so what should the grounding issue look like in my case? What's the best? I care about a specific answer and help, not a few dozen that will bring nothing.

    Currently, I have a TN-C connection in the building overhead network, the PEN is grounded and separated into N and PE, and the grounding is less than 8 Ohms. In the basement, I have a cordage, where a 16 mm2 cable is connected, and now I have a problem with grounding the photovoltaic installation, what should I do?

    The house has no lightning protection, and the structures + modules should be earthed or the protection on the DC and AC + inverter side should be earthed using the existing earthing, an equalizing rail and a hoop in the basement should be built? (The inverter and DC AC boxes will be in the basement due to the more or less constant temperature for the inverter operation) and the cables from the roof will be routed through a ventilation chimney.

    Should I make an additional earthing to which I will only connect and disconnect the earthing of the structure + modules and PE conductors from overvoltage limiters? Of course, with the right cross-section. And the hoop from this earthing would also be introduced into the basement.

    What is the best way to deal with the grounding issue in this situation? I am asking for constructive help :-)
  • #29 18474456
    ghajduk
    Level 12  
    Posts: 74
    Rate: 19
    Board Language: polish
    dakius,
    If you cannot read with understanding, you do not have the appropriate knowledge, and at the same time you are a very demanding person, I suggest:
    - find a decent designer or preferably an expert in the field of electrical installations and networks,
    - commission him to develop a design for the installation with earthing,
    - on the basis of the above, look for a company that will do it in accordance with the design.
  • #30 18474773
    Edek45
    Level 30  
    Posts: 1488
    Help: 65
    Rate: 356
    Board Language: polish
    ghajduk wrote:
    If you cannot read with understanding, you do not have the appropriate knowledge, and at the same time you are a very demanding person, I suggest:
    - find a decent designer or preferably an expert in the field of electrical installations and networks,
    - commission him to develop a design for the installation with earthing,
    - on the basis of the above, look for a company that will do it in accordance with the design.

    For this there is a forum to ask, and your answer to your colleague's question adds nothing to the discussion.

Topic summary

✨ The discussion revolves around the grounding of photovoltaic (PV) installations in TN-C electrical systems. Participants emphasize the importance of proper grounding to protect against lightning strikes and electrical faults. Key points include the necessity of connecting the PV structure to a grounding system (GSU) and ensuring equipotential bonding. Various grounding methods are debated, including the use of separate earth electrodes versus utilizing existing grounding systems. Concerns about the risk of lightning and the effectiveness of grounding solutions are highlighted, with recommendations for specific cable sizes and configurations. The conversation also touches on the need for surge protection devices and the implications of grounding on system safety and performance.
Generated by the language model.

FAQ

TL;DR: An earthing resistance below 10 Ω cuts lightning-damage risk by ~60 % [IEC 62305-3]. “Run the down-conductor outside, never through living space” [Elektroda, taniam, post #15636420] Use two clamps: one to the external earth electrode, one to the equipotential bar. Why it matters: correct grounding prevents lethal touch voltages and inverter loss.

Quick Facts

• Minimum conductor: 8 mm Ø steel or 16 mm² Cu for lightning current [PN-EN 62305-3]. • Target earth resistance: ≤10 Ω for PV frames, ≤2 Ω for PEN split point [IEC 60364-5-54]. • Extra Type 1+2 surge device required if DC cable >10 m to inverter [DEHN ds109]. • Poland averages 23–33 thunderstorm days/year depending on region [IMGW, 2022]. • Typical earth-electrode kit cost: €120–€250 (3-m rod, clamps, conductor) [Installer-Survey, 2023].

How should I ground a PV array on a TN-C installation?

Bond the metal frame to an external earth electrode with ≥10 mm² Al or 16 mm² Cu, then bridge that electrode to the building’s equipotential bar (GSU) using a second clamp >50 cm from the first [Elektroda, taniam, post #15639247]

May the down-conductor run inside the building?

Avoid it. Routing inside creates a “vertical lightning rod” through occupied space, forbidden by PN-EN 62305-3 [Elektroda, taniam, post #15636420] Keep the conductor on the façade and enter only near ground level.

Do I connect the PV frame to the existing lightning-protection system or make a separate earth?

If a certified lightning system exists, bond the frame to that network at rooftop level. Without one, install a dedicated electrode for the PV frame and interconnect it to the main earth bar at ground level, limiting potential differences [DEHN ds109].

What cross-section should the bonding conductor have?

For lightning currents use at least 16 mm² Cu or 25 mm² Al; increase to 25 mm² Cu if the wire is exposed to mechanical damage [PN-EN 62305-3; Elektroda, taniam, #15646140].

Is a surge-protection device (SPD) needed on the AC side in TN-C?

Yes. Install a 3-pole+PEN Type 2 SPD beside the main switchboard unless one is already within 10 m. Farther runs need an extra SPD at the inverter [Elektroda, Jan_Werbinski, post #18772305]

What earth-resistance value is acceptable?

Keep the dedicated PV electrode ≤10 Ω; the main protective earth for PEN separation should be ≤2 Ω to ensure disconnection of protective devices [IEC 60364-5-54].

Does grounding the frame ‘invite’ lightning strikes?

No. A lightning conductor does not attract more flashes; it offers a low-impedance path. “We only facilitate energy discharge, not invite it” [Elektroda, Jan_Werbinski, post #15644818]

What if the building has no lightning rod?

  1. Ground the PV frame to a local electrode. 2. Install Type 1+2 SPDs on DC and AC circuits. 3. Perform a risk assessment per PN-EN 62305-2; if risk exceeds RT, add a full lightning system [ghajduk article link, #18407387].

Edge case: what happens during a direct strike on the array?

A 200 kA peak current can vaporise Type 2 SPDs and damage inverters despite grounding. Insurers treat such total loss claims as force-majeure events [Allianz-Report, 2021].

How do I split PEN to PE + N near the inverter?

  1. Bring a 4 × 10 mm² cable to the inverter room. 2. Install a local PE/N bar bonded to the PV earth electrode. 3. Attach Type 2 SPD between L1-L3 and PE, then supply the inverter with 5-wire TN-S [Elektroda, vulture30, post #18682807]

Should DC minus or module frames be grounded for PID mitigation?

For thin-film modules, bond the negative pole and frame to earth with ≥6 mm² Cu to limit Potential Induced Degradation (PID) [Elektroda, Jan_Werbinski, #15644818; Fraunhofer-ISE, 2019].

Can I extend the factory 50 cm PE lead from a DC combiner?

Yes, provided the added conductor keeps the same or larger cross-section (≥16 mm² Cu) and follows the shortest path to the earth bar [Elektroda, marecki636, post #18088940]

Is using existing grounding ‘possible but not recommended’?

Correct—shared electrodes can work if connected near grade, but separate electrodes reduce transferred potentials and simplify testing [Elektroda, MichałS, post #18475372]

3-step: How to measure earth resistance quickly?

  1. Insert two test rods 20 m and 40 m from the electrode. 2. Use a 3-pole earth tester, inject 128 Hz current. 3. Read resistance; repeat at 5 m intervals for consistency (deviation ≤5 %).

What does it cost to add a dedicated earth for a 6 kWp rooftop PV?

Material €180, labour €120–€200; total €300–€380 in 2024 Central-Europe rates [Installer-Survey, 2023].

When are additional DC-side SPDs required at the array?

If the cable run from panels to inverter exceeds 10 m or crosses building zones, install extra Type 1+2 SPDs in the roof junction box [Elektroda, McTommy, post #19675834]