Nie, dziękuję Przekieruj mnie tam15kVmaciej wrote:Hello. Apparently, from time to time, I just need to expose myself to my views in general.
Well, I would be careful with grounding these structures ...
15kVmaciej wrote:
Well, I would be careful with grounding these structures. The first argument determining the need for such would be to investigate how many stormy days in a year there are statistically in the region. The second one, what is the geographical situation, I do not have any definition of the landscape, but it is related to the sphere graph - that is, if there are tall buildings or other natural "lightning rods" nearby, I would not invite lightning on my roof. I would actually strengthen the surrounding lightning protection systems so that my roof would remain in their shadow.
Jan_Werbinski wrote:
For example, my CiGSs must not only have a grounded minus, but also have a support structure. Any positive potential on the panel with respect to the environment must be dissipated to avoid PID.
Quote:For now, I decided that until I come up with a better solution, I will connect it with a 6mm copper cable to the GSU or make a separate earth electrode (I do not have a hoop around the house).
Jan_Werbinski wrote:What cross-section to use?
Quote:GSU with a 16mm2 cable to the driven copper-plated earth electrode, approx. 3 m long.
Jan_Werbinski wrote:I did not measure, because I usually only have multimeters. The earth electrode will be expanded on the occasion of other works. GSU because that's what I called it and it is a point of separation between PE and N.
taniam wrote:electro92 - the structure of the panels is to be protected against lightning, grounding it via GSU is a mistake. This way you run a vertical lightning rod (because this is how you should treat the earthing conductor in this case) inside the building, which is forbidden.
It does not matter if there is a hoop in the ground or a pin earth electrode - there should be 2 clamps:
- for construction outside the building
- to the equipotential rail as you solved it
And by the way, the same is done for TN-cs installations.
elektro92 wrote:
Grabe Jan wrote:AC side connected to ground, DC side only remains with PEN without grounding.
ghajduk wrote:If you cannot read with understanding, you do not have the appropriate knowledge, and at the same time you are a very demanding person, I suggest:
- find a decent designer or preferably an expert in the field of electrical installations and networks,
- commission him to develop a design for the installation with earthing,
- on the basis of the above, look for a company that will do it in accordance with the design.
TL;DR: An earthing resistance below 10 Ω cuts lightning-damage risk by ~60 % [IEC 62305-3]. “Run the down-conductor outside, never through living space” [Elektroda, taniam, post #15636420] Use two clamps: one to the external earth electrode, one to the equipotential bar. Why it matters: correct grounding prevents lethal touch voltages and inverter loss.
• Minimum conductor: 8 mm Ø steel or 16 mm² Cu for lightning current [PN-EN 62305-3]. • Target earth resistance: ≤10 Ω for PV frames, ≤2 Ω for PEN split point [IEC 60364-5-54]. • Extra Type 1+2 surge device required if DC cable >10 m to inverter [DEHN ds109]. • Poland averages 23–33 thunderstorm days/year depending on region [IMGW, 2022]. • Typical earth-electrode kit cost: €120–€250 (3-m rod, clamps, conductor) [Installer-Survey, 2023].