How do you select a differential protection device, and are there any mathematical rules for choosing its rated current and trip current?
There are no universal mathematical formulas for selecting a differential protection device; it is chosen from the installation conditions, the type of network, and what it is meant to protect [#2103653][#2104316] The main selection parameter is the residual current: 30 mA is used for protection against electric shock in residential installations, while higher values such as 100 mA, 200 mA, or 300 mA are used in other cases, for example industrial or fire protection [#2104316][#2104342][#2104679] The current marking on the device, such as 40/0.03, means the contact current capacity is 40 A and the residual trip threshold is 0.03 A; the current rating should be above the expected continuous load current, often about one order higher [#2104316] A differential device is not overload or short-circuit protection, so it must be used together with fuses or an overcurrent breaker; combined devices are marked with both the overcurrent characteristic and the residual trip current, such as C25A 0.03A [#2104679][#2104779][#2104828] Also remember that a 30 mA RCD does not necessarily trip exactly at 30 mA, because its operating current can begin at about 0.5×ΔI, i.e. around 15 mA for a 30 mA device, so leakage currents and selectivity must be considered [#2138187][#2104391]
  • #1 2103608
  • #2 2103653
    CZAPLIK
    Help: 5
    Rate: 18
    There are no mathematical relationships. Security is selected depending on the conditions and what it is supposed to protect. It's best to take a book where the environmental conditions and the amount of protection are given. If I find it, I will provide it, if necessary, i.e. the size of the security and from what book.
  • #3 2104251
    lisos
    Help: 21
    Rate: 98
    is selected depending on the value of the residual current - for protection against electric shock. typically 30 mA
    on the load current, but it is best (to exaggerate) e.g. 63A
    selection depending on the selectivity of protection (RCD-selective)
    selection depending on the nature of the power supply - 3-phase, 1-phase
  • #4 2104316
    KAPAS
    Help: 15
    Rate: 10
    The general rule is that the residual current circuit breaker (commonly known as a differential switch) is selected for the residual current value. If the switch is installed in a residential building (single-family house, apartment, etc.), its value cannot be higher than 0.03A (30mA). For industrial installations it may be higher, e.g. 0.3A (300mA).
    The residual current circuit breaker is not an overcurrent or overload protection, so the current value given in the marking - e.g. 40 /0.03 refers to the current capacity of the main contacts of the circuit breaker. As written earlier, it is safer to assume it is one order higher than the expected continuous current in the installation. All this data can be read from the circuit breaker characteristics, which should be attached to it.
    Moreover, you also need to know what the power supply system is like in the protected installation, because using a "differential" only makes sense in an installation separated by a PE and N cable.
  • #5 2104342
    janusz7273
    There are also 100 and 200 mA residual current protection devices.
  • #6 2104391
    KAPAS
    Help: 15
    Rate: 10
    That's why I wrote: "For industrial installations it may be more, e.g. 0.3A (300mA). "
    For your information, there are also circuit breakers with lower residual current values. Moreover, when selecting a switch, you should take into account the type of current that will flow through the switch - alternating sinusoidal, "half-wave" sinusoidal or rectified. I am leaving aside issues related to the selectivity of switches in series-connected circuits, etc.
  • #7 2104679
    Enpro
    Help: 39
    Rate: 97
    What Kapas writes is all correct, I will only add that all differential switches above 30mA are intended to protect the installation against fire, not to save lives, because a current of 100mA is a lethal current for humans. The differential is only leakage protection and is not protection against short circuits or overloads, then it only acts as an ordinary switch, so it cannot be used without short circuit protection, i.e. fuses must be used at the same time, although in one case it will work if the short circuit is to the PE wire or phase. or zero but still treats it as the smoothness of the installation even though there is a short circuit.
  • #8 2104779
    rambler_
    Help: 5
    There are also differential switches with overcurrent switches. You can recognize them by the fact that they have a characteristic written next to the max current, e.g.: 25A 0.03A - this is a differential with a maximum current of 25A, while: C25A 0.03A - is a differential with a built-in overcurrent switch that will turn it off after exceeding 25A (with characteristic C ).
    Regards, Robs.
  • #9 2104828
    KAPAS
    Help: 15
    Rate: 10
    This is a detail, but just to clarify the terminology, there are no differential switches with an overcurrent switch, only overcurrent switches with a residual current element.
    As for the 30mA current, as I wrote earlier, differential devices with a maximum leakage current of 30mA can be used for protection against electric shock.
    When it comes to higher education, your friend is absolutely right.
    Regards. :D
  • #10 2106115
  • #11 2124665
    gudi
    Rate: 87
    the standard for an apartment is 30mA / 40A. is completely sufficient. 30mA is a safe limit for humans, but on a well-insulated floor.
  • #12 2131898
    leszek N
    The OHMA law applies
    safe voltage 50 V
    resistance of the ground connection Ω
    AT
    I=R
    In general, the maximum leakage voltage must not exceed
  • #13 2132419
    HenryK3
    Help: 95
    Rate: 192
    leszek N wrote:
    Generally, the maximum leakage voltage cannot p sz estep
  • #14 2133319
  • #15 2136372
    leszek N
    I only provided the basis on which the 30 mA was determined
    because the theoretical resistance of a human and a current of 30 mA gives
    safe voltage
  • #16 2138187
    modlinp
    Help: 7
    Rate: 30
    When installing a differential, we must remember that it should start working at a current of 0.5ΔI, i.e. in the case of a 30 mA differential, its operating current starts from 15 mA. Of course, one will work at this value, the other will not, and therefore if we have old receivers at home with a high leakage current or overclocked contacts, which may cause the protection to operate and switch off the circuits.
Differential protection selection is primarily based on the residual current value, which is crucial for ensuring safety against electric shock. For residential applications, a common threshold is 30 mA, while industrial settings may utilize higher values, such as 300 mA. The selection process also considers the nature of the power supply (single-phase or three-phase) and the characteristics of the circuit breaker, which should be rated higher than the expected continuous current. It is important to note that differential switches are not designed for overcurrent or overload protection; they serve primarily as leakage protection. Additionally, the operating current for a 30 mA differential device begins at 15 mA. The discussion highlights the importance of understanding the installation's grounding and insulation to ensure effective protection.