Main Security Difference: Electrical Installation with P304-25A, DeltaJ=0.03A & 20A Permit

Wakmen 56585 19
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 4985454
    Wakmen
    Level 11  
    A simple question for professionals like you, but not quite for me.
    In the design of the electrical installation of a single-family house, I have the main protection and differential for all circuits P304-25A and deltaJ = 0.03A. Everything would be fine if the power plant did not issue a permit for only 20A.
    I have not seen a 20 3-phase differential on the market yet, so my question is: can I use the main C20 (or maybe B20) main protection and then a 25A J = 0.03A 3-phase differential and then specific circuit protections (B10, B16)? I would not like to use 3 differentials for 3 phases, but only one, but which one?
    Thank you very much in advance for any suggestions.
  • ADVERTISEMENT
  • #2 4985494
    Ewaryst
    Level 14  
    At the beginning I propose to give a differential according to the design, then C20 "es", and finally "es" for individual circuits.
  • #3 4985598
    andk1eltd
    Level 37  
    The current given on the differential is the rated current of the circuit breaker contacts - it can also be 100A. The "delta" mentioned above is important - max 0.03A.
  • #4 4985945
    Wakmen
    Level 11  
    Please, what a quick answer> I thought so too. 30mA (25A) 3-phase differential and C20A protection.
    Thank you very much for your quick reply.
  • #5 4986165
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #6 4987466
    Łukasz-O
    Admin of electroenergetics
    The differential has nothing to do with it, it can be even 40A, it is not the main security and it cannot fulfill such a function. The most important thing for you is that the differential current is 30mA and the differential current rating is greater than or equal to the power allocation. You probably have a power allocation of 12kW or 3x20A and you must have such overcurrent protection in front of the meter.
    Remember, the residual current circuit breaker only serves as an additional protection against electric shock and not against short-circuit (yes, there are versions with redundant members, but don't go deeper because that's not what it is about now).
  • #7 4987635
    max972
    Level 11  
    The permission from the power plant is a bit strange, because typical is 25A. I would advise you to go to the power plant with this permit, because maybe there is simply a mistake in writing. The problem is that the rule is to apply protections to individual circuits two orders weaker than the main protection, e.g. main 25A, to 16A sockets. These 16A sockets are standard now. The design is correct and the installation should be made strictly according to it. As our colleague Łukasz-O rightly mentioned, the differential is an additional form of protection (very effective), and the overcurrent circuit breakers are the basic ones. And the delta value I = 30mA is the limit of self-release in case of electrocution, so building regulations clearly say 30mA max and not gaining more weight. For residential construction, a typical residual current device is 25A with delta I = 30mA, and an overcurrent circuit breaker is class B circuit breakers. The main protection is class C, which means that it is more delayed, so that in the event of a short circuit we can protect a circuit, and not everything.
    And one more thing. Today, the installations for houses are designed in such a way that the main security and the meter are installed in a box placed literally in the fence of the property so that the master from the power plants can read the meter readily and that our beloved dog does not chew it, but only the rest, i.e. the differential and the protection of individual circuits is installed in the distribution box in the house. There are no additional overcurrent protections between the main fuse and the protections in the distribution box. And whether the protection is triple or single depends on whether we have a 3-phase or single-phase cable connected to the house. Today it is standard to bring a 3-phase installation to the house.
    Regards
  • #8 4987897
    Wakmen
    Level 11  
    max972 wrote:
    The permission from the power plant is a bit strange, because typical is 25A. I would advise you to go to the power plant with this permit, because maybe there is simply a mistake in writing. The problem is that the rule is to apply protections to individual circuits two orders weaker than the main protection, e.g. main 25A, to 16A sockets. ...

    With this going to the power plant, there is no such need, because in the Tri-City, Energa from the end of last year for a connection capacity of 11kW (group V) has set (read - lowered) the main security to be 20A (previously it was 25A). And here it is all about that the construction project says its own (it was made according to previous nationwide arrangements) and the reality speaks its own. If I want to have more security, I have to increase the demand for kW to a higher one, but nobody heats the houses with electricity (only with other, much cheaper sources of energy).

    Added after 5 [minutes]:

    marcint2525 wrote:
    ... If there is a project, the installation is to be done according to the project. Inserting an additional 20A switch (A, B, C or D) does not make sense either behind or before the differential.
    What, according to the project, is directly behind the difference? ...

    There is one main protection (25A) and one differential (as described above I = 0.03A) and there are individual circuits behind it. The problem (and maybe not the problem, only the ambiguity) lies between the new arrangements of the power plant in order to only collect the money for the next kW with the demand for energy.
  • #9 4988622
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #10 4988859
    HeSz
    Electrician specialist
    Andk1eltd and Łukasz-O are right. The 25 A current specified on the P 304 RCD, 25A 30 mA, is the rated current of the circuit breaker contacts and has nothing to do with the overcurrent protection. Therefore, additionally (as a protection against short-circuits) a 20 A "pre-meter" protection has been imposed. "Differential" will not trip even 30 A if it does not detect a leakage above 30 mA (at most "it will be damned").
  • #12 4989769
    Łukasz-O
    Admin of electroenergetics
    marcint2525 wrote:
    (...)

    Hello, my colleague Łukasz-O , how does my colleague calculate that it is 3x20 for 12KW? :| If for 7.5 KW ZE they install "esy" 25A, and for 10.5 they install "plugs" (fuses) 32A?


    Hello, my colleague marcint2525 , I wanted to simplify, but good point, it should be 13.8kW. 20A or 4.6 kW x 3 phases gives a total of 13.8 kW.
    Does the colleague understand now :D
    Regards
  • #13 4989857
    Anonymous
    Anonymous  
  • #14 4994624
    Łukasz-O
    Admin of electroenergetics
    marcint2525 wrote:
    Okay Łukasz, that's right. But why should the differential still protect the meter?


    And who writes that the differential is to protect the meter? In the connection conditions, it writes about the differential, but it does not mean that it should be in front of the meter.
  • ADVERTISEMENT
  • #15 4995152
    Anonymous
    Anonymous  
  • #16 4996619
    max972
    Level 11  
    Hello.
    Buddy, Wakmen. Either you have submitted a wrong demand for connected capacity, or your operator has an uninteresting policy towards consumers. In my city, in recent years, cooperatives have been installing 25A main protection in blocks, and in the apartment a 25A 30mA differential, 1x16A 3-phase, 3x16A sockets, 1x10A light. For a house, I would not even start with 20A, because it is a mockery and even if I were to design an installation for a house, I would be ashamed to give less than 25A. Maybe the whole house is not heated by electricity, but if we count a good ceramic kitchen + floor heating in the bathroom and possibly in the hall, which I see more and more often, in addition, the standard of the device is a washing machine, dishwasher, sometimes a welding machine in the garage + some other ideas and more lighting, is 25A too much? This is a house, not a flat in a block of flats. And anyway, after the de-monopolization of the en market. el. there was supposed to be competition, and so far the new operators have started to pay rises. And maybe the 20A for a colleague Wakmen is another macho on their part, because if he wants more, of course, but for a "small fee"?
    Regards
  • #17 4998321
    Łukasz-O
    Admin of electroenergetics
    Marcin - can I say that? I have also met "circus performers" more than once, amateurs of technical knowledge, which according to the law can be freely interpreted.

    I really don't understand what my quote:
    Quote:
    You probably have a power allocation of 12kW or 3x20A and you must have such overcurrent protection in front of the meter.
    has something to do with a residual current circuit breaker - could you please enlighten me?

    I don't think you're picking on buddy, but you like to annoy me :D
  • #18 4999982
    Anonymous
    Anonymous  
  • #19 5001750
    Anonymous
    Anonymous  
  • #20 5002521
    Wakmen
    Level 11  
    marcint2525 wrote:
    ... I ran a little bit, but I already met a "circus performer" who installed a residual current circuit breaker in front of the meter ...

    I assure you that it is not so and no one even thought for a moment to do so.
    max972 wrote:
    Hello.
    Buddy, Wakmen. Either you have submitted a wrong demand for connected capacity, or your operator has an uninteresting policy towards consumers. ...

    And so, unfortunately, is the ENERGA service provider. He just wants each new customer to ask for more demand as they need it.
    max972 wrote:
    ... Maybe the whole house is not electrically heated, but if we count a good ceramic kitchen + floor heating in the bathroom and possibly in the hall, which I see more and more often, in addition, the standard of the device is a washing machine, dishwasher, sometimes a welding machine in the garage + some other ideas and a bigger one the number of lighting, is 25A too much? This is a house, not a flat in a block of flats. ...

    No electric heating. Gas in the border of the plot, so everything is on gas, even a gas hob, but the oven is not. It is a power nest in the garage, but only ... so that it would be e.g. for plasterers or floor planners.
    Nobody from the garage will build a sheet metal workshop :D .
    The larger electrical appliances are ... washing machine, dishwasher, TV, computer, dryer and iron. I guess that's it.

Topic summary

The discussion revolves around the design of an electrical installation for a single-family house, specifically addressing the use of a P304-25A differential circuit breaker with a deltaJ of 0.03A, while the power plant permits only a 20A main protection. Participants suggest that the installation should adhere to the project specifications, which typically include a 25A differential for safety against electric shock, while the main protection can be a C20 or B20 circuit breaker. The importance of having overcurrent protection that is two ratings lower than the main protection is emphasized, along with the recommendation to use multiple RCDs for different circuits. The conversation also touches on the unusual 20A limit set by the power plant, with some participants questioning its adequacy for a residential setup, given the typical power demands of modern households.