Why Is 3-Phase Power 380 Volts and How Are the Voltages Distributed?

nygusek 55949 5
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 3004010
    nygusek
    Level 11  
    Hello

    I have a trivial question :)

    how many volts are on 3 phases and why is 380 volts

    the answer does not need to be detailed.
  • ADVERTISEMENT
  • #2 3004041
    Elektrooonik
    Level 29  
    between individual phases and 0 is 220V (now 230V), while between the phases is 380, the phases are shifted by 120 degrees, 220 * square root of 3 = 380 (now 230 * square root of 3)
  • ADVERTISEMENT
  • #3 3005104
    Arnold_S.
    Level 26  
    Currently it is 400V, professionally 0.4kV in the LV network (phase-to-phase voltages are rated voltages).

    The picture explains a bit.
    Why Is 3-Phase Power 380 Volts and How Are the Voltages Distributed?
    RMS values are shown here, the image is just such a "freeze frame" to show the nominal values (obviously the phase-to-phase voltage is also a sine wave).

    Phase voltage is the voltage between one phase and earth.
    Interfacial tension is, as the name suggests, the voltage between two phases.

    In vector form (phasor diagram) it looks like this:
    Why Is 3-Phase Power 380 Volts and How Are the Voltages Distributed?
    Drawing "on the spot", so forgive the inaccuracy. :wink:

    And the phase voltages are shifted because this is the structure of the generators. As the rotor rotates, it generates phase voltages successively over time. It is obvious, is it?
    Why Is 3-Phase Power 380 Volts and How Are the Voltages Distributed?
    It's all about the topic.

    Drawings made "by peasant reason", so they should help completely "green" people. :)
  • ADVERTISEMENT
  • #4 3006202
    nygusek
    Level 11  
    Thank you for your answer
  • ADVERTISEMENT
  • #5 3009712
    Arnold_S.
    Level 26  
    You could ask one more question: why in the network, the frequency is 50Hz?

    The frequency is determined by the rotation speed of the generator.
    Turbogenerators rotate at 3000 revolutions per minute (i.e. 50 times per second = 50Hz).

    PS
    50Hz can be generated at lower rotational speeds (generators in hydropower plants), but this requires a different (more complicated) generator design (specifically its rotor).
  • #6 3012105
    _jta_
    Electronics specialist
    You might still ask why 220V ~, why 3 phases, why the angle between phases 120 degrees ...

    220V ~ was based on the assumption that the voltage should not drop below 200V ~, and 10% of this may be losses on the line
    (now they did 230V ~ - but rather they did not increase the assumed losses to 15%, but rather decreased to 10V).

    3 phases ... as if to make two in out-of-phase, it cannot power an asynchronous motor, because it will not be created
    rotating magnetic field; you could give two offset 90 degrees, but that causes a large flow
    neutral conductor currents; minimum to obtain a rotating field without current in the neutral conductor, is
    3 phases with 120 degree angles - so simply "minimalist" design, why more wires?

    And why 50Hz ... the higher the frequency, the greater the losses on transmission lines, the smaller, the more
    higher costs of transformers and losses on them - some compromise had to be made, the USA chose 60Hz,
    Europe 50Hz - a bit strange, because in the US they probably have longer lines - maybe better materials for transformers?