Home 230V Light Switch Installation: Phase or Neutral Wire? Electrician Opinions Divided
ducker1 112333 16
Should a home 230V light switch interrupt the phase (live) wire or the neutral wire?
A 230V light switch should interrupt the phase (live) conductor, not the neutral [#4810591][#4810619][#4810636] If you break the neutral instead, the lamp and switch can still remain at mains potential, which is unsafe when changing a bulb or touching the fitting [#4810619][#4810636] Several replies also note that interrupting N can cause switching overvoltage, especially with inductive or capacitive loads, and that a neutral fault in the supply can put dangerous voltages onto single-phase circuits [#4812097] This is why switches, and likewise fuses, are placed in the phase conductor [#4810636][#4816119] Older installations that switched neutral were described as mistakes, not the correct practice [#4816119]
  • #1 4810526
    ducker1
    Help: 69
    Rate: 83
    Hello. I have a very banal question, but I could not find a clear answer to it. I asked experienced electricians and their opinions were divided. Namely:
    - In a home 230V installation, the light switch (room lamp) should be mounted on the phase or neutral wire ??
    It is obvious that in both possibilities the system will work, i.e. turn the light on and off, but which solution is correct ?? are there any rules that regulate it ?? Because when I once asked a few electricians, this question only caused me to stab between them because some said so and others and I did not get a clear answer.
    Thanks in advance for your answers and best regards
    Damian
  • #2 4810591
    jacur
    Level 32  
    Help: 166
    Rate: 295
    The phase always disconnects !!!!!!!!!!!!
  • #3 4810619
    robebi78
    Help: 5
    Rate: 20
    As a colleague Jacur wrote. We always release the phase through the switch. Firstly, for safety reasons, if we disconnected N, we have a constant tension in the lamp. Secondly, disconnecting N creates overvoltages.
  • #4 4810636
    godos
    Help: 23
    Rate: 14
    Of course, on the phase for two reasons: firstly, for safety, if you turn off the N, there will always be a phase on the lamp, which can be dangerous, for example when replacing the bulb, secondly, if you want to install an electronic switch, you will have problems with it on N. It is similar with fuses, which are always mounted on phase.
  • #5 4810704
    mrrudzin
    Help: 516
    Rate: 580
    And these experienced electricians, what do they do on a daily basis?
    Disconnecting the neutral wire when there is voltage on the phase wire is - to put it mildly dangerous, as colleagues have noticed.
    See that if, for example, the lamp is in phase and the neutral wire is disconnected, all the working elements of the device are at the network potential. Both those connected "from the phase side" and those "from the neutral wire side" - because in such a situation the bulb is a resistor connecting the connected phase line with the unconnected neutral wire line.
    In such a situation, it is best to "save" a little more and instead of a 3-wire installation (L, N, PE), give a two-wire one, and connect the metal lamp housing directly to the neutral wire in it. Of course, the light connector in the N wire is also recommended.
    So a bit different from the topic:
    Maybe a friend develop this thread?
  • #6 4810811
    ducker1
    Help: 69
    Rate: 83
    Well, so my opinion is confirmed.
    I heard opinions from the zero switch because if someone touches them with wet hands ... :) well, but as you wrote above, the network potential comes to the switch.
    The second opinion is that if we break the phase, it will spark and zero will not, I do not agree with this, but maybe my colleague robebi78 will explain to me what is the matter with overvoltage.
    Yes, as an explanation. I am not a complete layman in these matters, I only asked as a confirmation of my assumptions
    Thanks for the answers
  • #7 4810962
    mrrudzin
    Help: 516
    Rate: 580
    In places where there is a probability that someone will touch it with wet hands, connectors with an appropriate IP protection degree must be used. In addition, it is worth considering installing an RCD. Unfortunately, it costs a little, but it can save your life.
    I recommend showing your friends at least THIS skimpy article
  • #8 4812097
    robebi78
    Help: 5
    Rate: 20
    Interrupt N can be the cause of the so-called. switching overvoltage, especially if the loads are capacitive or inductive, e.g. lighting fittings with chokes. This results in damage to the device - when it does not have overvoltage protection or shorten its service life.
    Secondly, interruption of N in the power supply (loosening or burnout of the cable in the switchgear) results in the appearance of inter-phase voltage in single-phase sockets. In order not to be a loudspeaker, I will quote a real-life example:
    Reverse command - we are to attach an additional circuit to a 3-phase box (for even load distribution) supplying single-phase sockets in several rooms to which computers were connected. Unfortunately, they have not been turned off. The power supplies are damaged.
    Breaking the N wire while the device is running (the phases are still running) is not very wise
  • #9 4812301
    patryk-84a
    Help: 40
    Rate: 212
    Well, yes, between the phases will appear on the computers then, but it will spread over 2 computers, more or less half (depending on the power of the power supply), so theoretically nothing should happen. But only theoretically. But it is true that the N conductor does not disconnect, always in phase. In addition, I know that older electricians often give N to the switches, once I met in one room that in the dark, after turning off the light, you could see that the "energy-saving" bulb was barely glowing, the reason was probably bringing the phase to the bulb and some small current leakage somewhere .
  • #10 4812373
    emka371
    Level 19  
    Help: 28
    Rate: 24
    No electrician will not put the switch in the N conductor, and even more so in the PEN. I emphasize an electrician and not someone who considers himself a professional because "he has already changed the bulbs in the chandelier twice" :D
    The glowing of energy-saving light bulbs occurs very often when using switches with backlight. A neon lamp connected in parallel to the switch contact allows sufficient current to flow.
  • #11 4812402
    patryk-84a
    Help: 40
    Rate: 212
    Well, that may be right, because there were illuminated switches, but I'm not 100% sure. As for the "electricians" you are right.
  • #12 4815940
    Arturo2005
    Help: 149
    Rate: 485
    I would love to meet these "electricians". I am interested in their professional experience.
  • #13 4816027
    artur s
    Help: 61
    Rate: 157
    Quite a common patent of ship electricians - but they have other installations there and they do not know [?] What a neutral ...
  • #14 4816119
    Rysio4001
    Heating systems specialist
    Help: 617
    Rate: 1077
    The switch should be mounted on a phase conductor!
    In the past, fuses were also used on both phase and neutral conductors, which was a "mistake" and resulted in many misfortunes. Until now, it happens that such installations are found in old tenement houses.
    Fluorescent lamps can glow slightly in the dark, also when there are no neon switches, when there are switches on the neutral wire. The capacitive currents flowing into the environment are simply enough for fluorescent lamps, especially when the luminaire (housing, chandelier) of the fluorescent lamp is grounded.
    Greetings.
  • #15 4816468
    mrrudzin
    Help: 516
    Rate: 580
    But if you put a small resistor in the luminaire of such a fluorescent lamp that does not allow the capacitors in the fluorescent lamp to charge sufficiently, the problem would be solved by itself :)
  • #16 4816556
    Aleksander_01
    Help: 1167
    Rate: 3435
    [quote = "mrrudzin"]
    Interesting way of thinking.
    Demonstrate it in a schematic (it can be block-based).
  • #17 4817447
    mrrudzin
    Help: 516
    Rate: 580
    In the diagram?
    Resistor plugged in parallel to the lighting fixture. The entire scheme :)
    Current flows through the resistor and neon lamp in the fitting (as someone mentioned above). This current causes charging the capacitor in the fluorescent lamp to the voltage sufficient to start the converter powering our light source. As the energy is supplied to a limited extent (not sufficient for continuous lighting of the fluorescent lamp) - the lamp flashes for a moment, consuming the energy stored in the capacitor and the process starts all over again.
    In better compact fluorescent lamps, this problem was solved - in parallel with the capacitor by mounting a 180 ~ 220 kOhm resistor. It prevents the capacitor in the fluorescent lamp from charging to such a voltage that the inverter starts. Why is this happening, I don't think I need to write anymore.
    Well, it happens in the better ones. In these worse - ladybug, real and other inventions - not only the quality of the light is tragic, but also the above-mentioned resistors are missing (costs are cut at every step).
    In order not to rummage in the fluorescent lamp itself, it is enough to connect the above-mentioned 2W resistor in parallel to its terminals and the problem should disappear.
In a discussion regarding the installation of light switches in a home 230V system, participants overwhelmingly agree that the switch should be mounted on the phase wire rather than the neutral wire. The primary reasons cited include safety concerns, as disconnecting the neutral can leave the lamp energized, posing a risk during bulb replacement. Additionally, interrupting the neutral can lead to overvoltages, particularly with capacitive or inductive loads, which may damage devices. The conversation also touches on the historical practice of using fuses on both phase and neutral, which is now considered a mistake. Participants emphasize the importance of adhering to current electrical standards and practices to ensure safety and functionality.