Nie, dziękuję Przekieruj mnie tamharlejowiec wrote:I would give a conduit, the cost is higher, but if necessary, the cable can be replaced.
gintur wrote:The installation will be replaced in the apartment. The electrician did some research, he drew what where and how. He stated that to put 3x1.5 YDYp into the sockets in the rooms and let it go without forging in the skirting board. However, the situation has changed a bit because it turned out that there is some kind of the insulating board is then roofing felt and screed, i.e. practically only sand (apartment on the ground floor) Unfortunately, the roofing felt sticks out in the middle, the screed is quite cracked and give it all an unpleasant smell in the apartment. all over the apartment. I wonder if I will use these corridors to lay wires. Now I do not know whether to use 3x2.5 YDYp and that is enough or to use 3x2.5 round but in a conduit? What is your advice?
marcint2525 wrote:
3x1.5 mm² YDYp per socket? The socket circuits are made of a 2.5 mm² cable. 1.5 mm² for lighting !!!
Quote:and I will not allow your installation to move."Do as she wants"
Quote:Minimum cross-section of a permanently laid cable, protected against damage
mechanical, is 1.5 mm² Cu. The minimum cross-section of the wires is assumed
in electrical installations arranged inside buildings, for lighting circuits
- 1.5 mm² Cu, for plug sockets - 2.5 mm² Cu.
gintur wrote:I decided to do it in this way, everywhere around the walls, channels will be cut out in the screed. In the trays, a rigid protective pipe (not a conduit) with a diameter of 18mm will be placed. The YDYp 3x2.5mm2 cable will be inserted into the pipes, then the entire corridor will be filled with assembly foam, and at the very end the screed will be placed in the whole apartment. Can the cable in the tube be covered with foam, is it a good way?
jarecki 86 wrote:marcint2525 , a lot of these laws and regulations, but just right absolutely nothing does not follow from them.
This is not literature, my friend.
Besides, in buildings not all socket circuits are of general purpose.
The role of the site inspector is to check that the work has been carried out in accordance with the building design.
So much and so much.
And it's good to know the specific rules.
gintur wrote:The installation will be replaced in the apartment, the electrician did some research, he drew what where and how. He stated that the sockets in the rooms should be equipped with 3x1.5 YDYp and let it go without forging in the skirting board. However, the situation has changed a bit because it turned out that there is some kind of the insulating board is then roofing felt and screed, i.e. practically only sand (apartment on the ground floor) Unfortunately, the roofing felt sticks out in the middle, the screed is quite cracked and give it all an unpleasant smell in the apartment. all over the apartment. I wonder if I will use these corridors to lay wires. Now I do not know whether to use 3x2.5 YDYp and that is enough or to use 3x2.5 round but in a conduit? What is your advice?
Łukasz-O wrote:I also have a question for the "inspector" Is the cause of burning the "zero" sometimes a loose contact or badly tightened?
The same situation would be if you used even 25mm2.
Besides, loose contact is not only the electrician's fault, but above all the lack of maintenance for a number of years.
Buddy, like "there is no electricity" and in this case you only have a phase everywhere in the entire building, you always start work by unscrewing the switchgear. You would find the cause right away and not run around the house looking for phase-to-phase voltage in the socket. These 20 years must have been my colleague sitting behind the desk. Sorry, I wasn't going to write anything on this topic, but I couldn't.
Quote:
Either you will discuss the merits - or yellow cards will fall!
Enough teasing!
gintur wrote:YDY cable with or without conduit?
jozefg wrote:Either you will discuss the merits - or yellow cards will fall!
marcint2525 wrote:"(Question: Which colleague will say what is the Long Term Rating Limit for this cable?)."
"output to the feeder rail, the connection is to be made LG16mm^2 (terminals soldered or a clamped sleeve)."
Added after 6 [minutes]:
HeSz wrote:Mr. Superintendent. You know the rules, but you don't read them!
In the PN-IEC 60364-5-52:2002 standard you quoted "Electrical installations in buildings - Selection and assembly of electrical equipment - Wiring" on page 17 there is "Table 52J - minimum cross-sections of wires", and in it "like a bull" it is written : for fixed installation, cables and insulated wires, in lighting and POWER circuits, the minimum cross-section is: 1.5 mm^2 for copper and 2.5 mm^2 for aluminium.
Regards
dj_stopa wrote:
16mm² is more or less from 50 to 80A, depending on the environment in which it is located, and as for the connections in the switchgear, what standard says that an LGY cable must be used? I have been using DY for many years and somehow no one has had any doubts about the switchgear in my implementation![]()
jarecki 86 wrote:
The thing is that it is impossible to conduct a substantive discussion in a situation where the provoking party avoids any answers to the questions asked.
So if we are left with a choice between accepting absolute reason inspector and silence, I choose the latter.
Quote:In the example given by me, the conditions require that the power wires have a cross-section of 10 mm^2
Quote:That is, from the pole to the YKY 4x35mm^2 connector, from the connector to the YKY 5x35 meter and from the meter to the YKY 5x35mm^2 switchgear.
Quote:There should be a LG 16mm^2 line. (Question: Which colleague will say what is the Long Term Rating Limit for this cable?).
HeSz wrote:My post was about MINIMUM cross-sections. This does not mean that other parameters such as long-term load capacity, short-circuit strength or voltage drop should not be taken into account. The comment concerned only that it was a mistake to order installations with a cross-section below 2.5mm^2 without analyzing the circuit.
marcint2525 wrote:Quote:Minimum cross-section of a permanently laid cable, protected against damage
mechanical, is 1.5 mm² Cu. accepts the minimum cross-section of the wires
in electrical installations arranged inside buildings, for lighting circuits
- 1.5 mm² Cu, for plug sockets - 2.5 mm² Cu.
...a quote from the first Electrician Installer's guide
marcint2525 wrote:and I will not allow your installation to move.
TL;DR: In Polish flats, 2.5 mm² copper can carry ~24 A continuously [PN-IEC 60364] yet “swap-out becomes near impossible after three bends” [harlejowiec, 4999405]. Use rigid 18 mm conduit plus 3×2.5 YDY to future-proof sockets. Why it matters: Repairing a buried run later can cost 3× more than installing conduit now.
• 3×2.5 mm² YDY flat: ≈24 A long-term current capacity in concrete [PN-IEC 60364-5-523]. • 18 mm rigid PVC conduit (RKGL 20 × 14.5): crush strength 320 N; floor-rated [jarecki 86, 5009250]. • Retail price: YDYp 3×2.5 flat ≈2.50 PLN/m; round ≈5 PLN/m [gintur, 5003489][saimon79, 5009887]. • PN-IEC 60364-5-52 minimum socket conductor: 1.5 mm² Cu; many inspectors enforce 2.5 mm² [HeSz, 5006718]. • Practical pull limit in corrugated conduit: <10 m with 3 bends for 3×2.5 mm² [Wakmen, 5002562].