gintur wrote: I decided to do it in this way, everywhere around the walls, channels will be cut out in the screed. In the trays, a rigid protective pipe (not a conduit) with a diameter of 18mm will be placed. The YDYp 3x2.5mm2 cable will be inserted into the pipes, then the entire corridor will be filled with assembly foam, and at the very end the screed will be placed in the whole apartment. Can the cable in the tube be covered with foam, is it a good way?
Fill the tube with cement and it will be.
Yesterday a lady called me asking for help in repairing the installation. As it turned out.
In this lady's apartment, literally all single- and three-phase devices were "burnt". The client called the Energy Emergency Service because she thought it was the plant's fault. The electrician from the emergency service looked at the connection, connector and connections from the pre-meter protections, through the meter to the disconnector just before the differential switch, and measured the voltages. I apologize for the phrase "took d...a trip" and left. He said he wasn't interested in what's behind the meter. From the ZE side everything was OK!
In the installation in the apartment "zero was missing". Where is the damage?
So I put the meter in any socket - no voltage (everything is included in the board). A moment later I noticed that nothing was connected. I turned on the lights. The light bulb is terrifyingly bright! Phase-to-phase voltage showed up in the socket. So to the blackboard. I've taken the first cover off and I'm looking at the connections. It turned out that the neutral cable coming from the differential to the zero bus simply burned (it was not blue and brown, almost black). The installer used a 4mm² cable and it should be 10mm² according to the design.
The differential didn't work.
My question:
Who and what to blame? Is the standard important or common sense, do I see an installer?
The victim estimated the loss at over PLN 30,000!
20 cm single DY 1x10 mm² how much? 20 - 40 groszy :!:
Added after 17 [minutes]: jarecki 86 wrote: marcint2525 , a lot of these laws and regulations, but just right absolutely nothing does not follow from them.
This is not literature, my friend.
Besides, in buildings not all socket circuits are of general purpose.
The role of the site inspector is to check that the work has been carried out in accordance with the building design.
So much and so much.
And it's good to know the specific rules.
If it's not clear, please:
standards
PN-IEC 60364 standard
- PN-IEC 60364-1:2000 Electrical installations in buildings. Scope, subject and basic requirements.
- PN-IEC 60364-3:2000 Electrical installations in buildings. Establishing general characteristics.
- PN-IEC 60364-4-41:2000 Electrical installations in buildings. Protection to keep you safe. Security
anti-shock.
- PN-IEC 60364-4-42:1999 Electrical installations in buildings. Protection to keep you safe. Security
against the effects of thermal exposure.
- PN-IEC 60364-4-43:1999 Electrical installations in buildings. Protection to keep you safe. Security
against overcurrent.
- PN-IEC 60364-4-443:1999 Electrical installations in buildings. Protection to keep you safe. Security
against surges. Protection against atmospheric or switching overvoltages.
- PN-IEC 60364-4-444:2001 Electrical installations in buildings. Protection to keep you safe. Security
against surges. Protection against electromagnetic interference (EMI) in facility installations
construction.
- PN-IEC 60364-4-45:1999 Electrical installations in buildings. Protection to keep you safe. Security
before the voltage drops.
- PN-IEC 60364-4-473:1999 Electrical installations in buildings. Protection to keep you safe.
Applying security measures. Means of protection against electricity
overcurrent.
- PN-IEC 364-4-481:1994 Electrical installations in buildings. Protection to keep you safe. Selection
protection measures depending on external influences. Selection of means of protection against electric shock
depending on external influences.
- PN-IEC 60364-5-52:2002 Electrical installations in buildings. Selection and installation of electrical equipment.
wiring.
- PN-IEC 60364-5-523:2001 Electrical installations in buildings. Selection and installation of electrical equipment.
Long-term current carrying capacity of wires.
- PN-IEC 60364-5-53:2000 Electrical installations in buildings. Selection and installation of electrical equipment.
Switchgear and control apparatus.
- PN-IEC 60364-5-534:2003 Electrical installations in buildings. Selection and installation of electrical equipment.
Surge protection devices.
- PN-IEC 60364-5-54:1999 Electrical installations in buildings. Selection and installation of electrical equipment.
Earthing and protective conductors.
- PN-IEC 60364-6-61:2000 Electrical installations in buildings. Verification. Acceptance check.
- PN-IEC 60364-7-701:1999 Electrical installations in buildings. Special requirements
installation or location. Rooms equipped with a bathtub and/or a shower basin.
139
Other standards
- N SEP-E-004 SEP standard. Power and signal cable lines. Design and construction.
- PN-EN 50146:2002 (U) Equipment for fastening cables in electrical installations.
- PN-EN 50368:2004 (U) Cable supports for electrical installations.
- PN-EN 61537:2003 (U) Systems of cable trays and installation ladders for cable management.
- PN-EN 50086-1:2001 Systems of installation pipes for cable management.
Part 1 General requirements.
- PN-EN 50086-2-1:2001 Systems of installation pipes for cable management.
Part 2-1: Particular requirements for rigid conduit systems.
- PN-EN 50086-2-2:2001 Systems of installation pipes for cable management.
Part 2-2: Particular requirements for flexible conduit systems.
- PN-EN 50086-2-3:2001 Systems of installation pipes for cable management.
Part 2-3: Particular requirements for flexible conduit systems.
- PN-EN 50086-2-4:2001 Systems of installation pipes for cable management.
Part 2-4: Particular requirements for buried conduit systems
- PN-EN 61386-1:2005 Systems of installation pipes for cable management.
Part 1: General requirements.
- PN-EN 61386-21:2005 Systems of installation pipes for cable management.
Part 21: Specific requirements. Rigid pipe systems.
- PN-EN 61386-22:2005 Systems of installation pipes for cable management.
Part 22: Specific requirements. Flexible pipe systems.
- PN-EN 61386-23:2005 Systems of installation pipes for cable management.
Part 23: Specific requirements. Flexible pipe systems.
- PN-EN 50085-1:2005 Systems of open trunking and closed trunking
for electrical installations. Part 1: General requirements.
- N SEP-E-001 SEP standard. Low voltage power grids. Shock protection.
- N SEP-E-002 SEP standard. Electrical installations in buildings. Electrical Installations
in residential buildings. Basics of planning.
and read it carefully.
I know what I do (20 years already), I like it and they pay quite well for it.
Added after 20 [minutes]: If it is difficult for someone to find these standards, I am posting a table taken from one of the sample projects.