Why do my apartment socket fuse and meter fuse trip when I test the RCD or use a 2100 W iron, and what should I check first?

The most likely cause is not the iron itself but a faulty power strip/surge protector or another load on that socket, so test the circuit with all strips unplugged and then reconnect devices one by one [#6585063][#6585125] The thread notes that the strips should not be connected in series, and a bad varistor in one strip can make the protection trip too early or even short the circuit [#6585063][#6585125] After disconnecting the computer from the power strip, the problem disappeared, which strongly points to the strip/PC side of the installation rather than the iron or the breakers themselves [#6590995] If the limiter/arrester actually shorts, the nearest protection will trip first, so the pre-meter fuse can go out together with the apartment fuse [#6599082] The remaining advice was to have an electrician check the installation because the circuit is not selective and there may also be a wiring or device fault [#6580584]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 6580366
    130880
    Level 10  
    Posts: 22
    Rate: 11
    Hello
    This is my first post on this forum, so I`d like to say hello.

    I have a fairly new electrical installation (building from 2000). One differential for the entire circuit (25A 30mA) and 5 circuit breakers. The problem is that if I test the differential with the test button, which disconnects the entire circuit and then turns it on, it blows out the socket fuse (16A), and what`s worse, it often blows out the meter fuse (20A) at the same time. . This also happened when my wife was using the iron, it sometimes blew two fuses at the same time: the one at home and the one at the meter. At first I thought it was the fault of the fuse in the house (there was a 10A fuse installed there, so I replaced it with a 16A one). It seemed a bit strange to me that someone installed 10A sockets on the circuit. I checked in the switchboard that the thickness of the wires is the same everywhere, so there shouldn`t be a problem). All elements in the switchgear are new, I replaced them a month ago (mooeler). The problem also existed before the replacement. Please help me solve the problem

    Regards
  • ADVERTISEMENT
  • #2 6580409
    Anonymous
    Level 1  
  • #3 6580439
    130880
    Level 10  
    Posts: 22
    Rate: 11
    The fuses are type B. I tried using type C sockets, but nothing changed. Electronic equipment (DVD, Home Cinema, plasma, computer) is connected to the sockets, but when the system is turned on, the plasma and the computer are turned off.
  • #4 6580513
    Anonymous
    Level 1  
  • #5 6580573
    130880
    Level 10  
    Posts: 22
    Rate: 11
    This is an apartment. I wrote that I tested with a type C fuse on the circuit with sockets and the problem did not disappear. The refrigerator is a completely different circuit. The largest high-power device that I connect to this circuit is an iron (2100W) on which it also throws. I did a test with an iron, I disconnected everything from the sockets, turned on only the iron and after 20 minutes it quit. It blew at a 10A fuse (which gives 2300W) and at 16A (3680W). I replaced the sockets in the entire apartment with new ones about 1 month ago (Polo Optima and I also checked them recently).

    I don`t understand a few things:
    1. Why does it blow 2 fuses in the house and at the meter, e.g. on a connected iron

    2. Does it make sense to use a type C fuse in the house if the meter has a type B fuse? Will selectivity be maintained?

    I`m starting to suspect the fuse next to the meter, maybe it`s worn out. There is a Legrand 20A TyB Eska, but it is sealed
  • #6 6580584
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    A C fuse for a single-phase socket is a bit of style over substance. How much of this equipment do you have at home? refrigerator, vacuum cleaner, and does it happen that they all start at the same time...., the pre-meter may be C, but for socket circuits it is not standard.

    AD.1 There`s clearly something wrong with the installation, call a tester, it`s not the fuses that are to blame, the iron draws 10A and if it outputs 16 and 20, it`s not magic, it`s something wrong, there is a possibility of a life-threatening situation, so it`s not funny anymore.

    AD.2 It`s the other way around, C for the meter and B for the circuits, so it`s a bad idea.
  • #7 6580611
    130880
    Level 10  
    Posts: 22
    Rate: 11
    When turning off the circuit, e.g. with a differential switch, all fuses are on, so when they are turned on there may be a voltage surge, but as I wrote earlier, the problem also occurs when I only connect the iron. Generally, all my equipment is equipped with UPC surge protectors (higher models). The fuse at the meter you B. Why does it blow out two fuses?
  • ADVERTISEMENT
  • #8 6580620
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    Because Skis are not very selective, when overloaded they all crash one by one.

    edit.
    You disconnected the electronics and power strips, and only the iron remained and the fuse blew?

    If you have not disconnected the strips, it is not strange that the fuse blows, when you turn it on, an overvoltage may occur and then the strip shorts and you have your own flying fuse. There is a saying about excess security.... ;)
  • #9 6580663
    130880
    Level 10  
    Posts: 22
    Rate: 11
    I will check everything carefully again and maybe call an electrician.

    Please answer a few more questions:

    1. If a voltage surge were a problem, is there any way to protect against it?

    2. Could a damaged fuse at the meter cause the fuse in the house to also turn off? Recently I checked the fuse on the cage and it seemed to be buzzing a bit.

    3. I`ll go off topic a bit. As I wrote earlier, I replaced all fuses at home. Before the replacement, there was a buzzing noise in the switchboard (it wasn`t a short circuit - something like that can be heard when you walk past a transformer on a pole, only quieter) if something that consumes a little more power was connected, e.g. an iron. After replacing all the components, the buzzing stopped. what could be the reason for such a situation?

    Added after 1 [minute]:

    lubamet wrote:
    Because Skis are not very selective, when overloaded they all crash one by one.

    edit.
    You disconnected the electronics and power strips, and only the iron remained and the fuse blew?

    If you have not disconnected the strips, it is not strange that the fuse blows, when you turn it on, an overvoltage may occur and then the strip shorts and you have your own flying fuse. There is a saying about excess security.... ;)


    The strips were connected
  • #10 6580692
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    130880 wrote:
    I will check everything carefully again and maybe call an electrician.

    Please answer a few more questions:

    1. If a voltage surge were a problem, is there any way to protect against it?

    2. Could a damaged fuse at the meter cause the fuse in the house to also turn off? Recently I checked the fuse on the cage and it seemed to be buzzing a bit.

    3. I`ll go off topic a bit. As I wrote earlier, I replaced all fuses at home. Before the replacement, there was a buzzing noise in the switchboard (it wasn`t a short circuit - something like that can be heard when you walk past a transformer on a pole, only quieter) if something that consumes a little more power was connected, e.g. an iron. After replacing all the components, the buzzing stopped. what could be the reason for such a situation?


    1. Strip, only it works by blowing a fuse, either in the strip, or in the house, or all of them, I use protectors in front of the meter so that it doesn`t blow fuses in the house....
    2.There is no such possibility.
    3. It can be fidgety sometimes, especially from bush companies, the overcurrent element is an electromagnet and if there is any play somewhere, there will be a zzzzzz. (and this does not mean a fuse failure, only the workmanship of... the company KRZA :P )

    Edit. Disconnect the strip, if it doesn`t work, you already know where the problem is, you have too good strips ;) they may be a little too sensitive.
    You can invest in a B+C surge protector for a rail and leave the strips aside.
  • #11 6580784
    130880
    Level 10  
    Posts: 22
    Rate: 11
    Can you describe to me how to attach such a protector? I think I have a Moeller protector somewhere, only it has three halves.
  • #12 6580875
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    If you took a photo of it, it would be nice, attach it in the same way as the differential, but in front of it.

    Arrester > differential > fuses
  • #13 6580889
    130880
    Level 10  
    Posts: 22
    Rate: 11
    lubamet wrote:
    If you took a photo of it, it would be nice, attach it the same way as the differential, but in front of it.

    Arrester > differential > fuses



    http://www.moeller.pl/DesktopDefault.aspx?PageID=317

    I only have a four-field one, but it seems to me that only one field can be used
  • #14 6580918
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    You connect the phase from the top and PE from the bottom
    One field can be used.
    I was misleading because it is a bit different from the differential, basically in parallel to the network and the differential is in series. But it`s a rush :P
    There is a diagram on the Moeller website.
    You don`t unplug anything from the current installation, you plug it in in parallel, that`s the whole philosophy.
  • #15 6581011
    130880
    Level 10  
    Posts: 22
    Rate: 11
    Frequent Breaker Trips: Testing Differential and Fuse Blowouts with Iron Use

    Check if it will be OK, I take PE (yellow-green) from anywhere in the switchboard
  • ADVERTISEMENT
  • #16 6581027
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    All right. Remember about the cross-sections of the cables, no smaller than in the rest of the installation.
  • #17 6581045
    130880
    Level 10  
    Posts: 22
    Rate: 11
    ok, thanks for your help. Tomorrow I will connect the fuse and see if anything improves.

    I will come back to the previous thread. What is the procedure for replacing the fuse at the meter? I understand that I need to contact ZE to have them unseal the fuse. I have my own fuse, do I incur any additional costs related to it (e.g. do I have to pay for an electrician from ZE and are any measurements required after such a replacement?
  • #18 6581086
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    No measurements, the costs are from 50 and up depending on the region, the sealing itself costs money, and you still have to work hard to replace the fuse. ;)
    Sealing costs PLN 30 on average, and for attaching two screws it ranges from PLN 10 to PLN 1,000, free market ;)
  • #19 6581877
    michcio
    Electrician specialist
    Posts: 2597
    Help: 145
    Rate: 481
    130880 wrote:
    Frequent Breaker Trips: Testing Differential and Fuse Blowouts with Iron Use

    Check if it will be OK, I take PE (yellow-green) from anywhere in the switchboard


    Someone probably forgot about N here.
  • #20 6582077
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    Frequent Breaker Trips: Testing Differential and Fuse Blowouts with Iron Use

    Hurry slowly :|
  • #21 6583432
    golonka
    Level 14  
    Posts: 123
    Help: 3
    Rate: 17
    I am returning to the pre-meter ES, it is currently type B, in my opinion it should be type C, at least I am the only one who installs it in accordance with the conditions it receives from ZE. Check your conditions (contract with ZE) imposed by ZE. Maybe it`s the installer`s fault for putting it like this? Has your friend experienced such a phenomenon at the beginning? Or has it been happening for some time? In my opinion, it is worth analyzing the matter thoroughly before taking any action.

    Added after 13 [minutes]:

    Regarding protectors, here`s a link to my friend, it`s worth reading.
    www.spinpol.com.pl/download/Latwy_dobor_2006.pdf
  • #22 6583880
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    Pre-counter, most likely C, in this case C20. Contracted power 4kW.
  • #23 6584101
    130880
    Level 10  
    Posts: 22
    Rate: 11
    This situation existed from the beginning. Coming back to connecting the surge arrester. Can I connect a neutral wire to the second bay in the same way as the phase wire?
  • #24 6584111
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    I drew it, look 2 posts above.
  • #26 6584145
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    That`s why at the beginning I didn`t think about securing N at all, especially since you have a PEN distribution for PE and N somewhere close to your house, but if you secure it, there is no threat.
    And at ISE they discussed a 3-phase network, you have 1 phase.
    And they wrote something about the fuse on N (since there is a fuse on N, it`s not IT/TT), I think someone confused the fuse with the protector :/
    And to top it off, they called the N phase, at least someone wrote that, what a disaster.
    Secure.
  • #27 6584156
    130880
    Level 10  
    Posts: 22
    Rate: 11
    ok, tomorrow I will connect everything and send a photo,
    when I`m done

    Regards
  • #28 6585050
    130880
    Level 10  
    Posts: 22
    Rate: 11
    I connected the limiter, but it seems that the problem still exists. When I turned on the main fuse, the socket fuse at home blew. I will test it more thoroughly today.

    I am sending photos from the installation:

    Frequent Breaker Trips: Testing Differential and Fuse Blowouts with Iron Use

    Frequent Breaker Trips: Testing Differential and Fuse Blowouts with Iron Use
  • #29 6585063
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 289
    There must be a faulty varistor in one of the strips and it releases too quickly, check without the strips, or check the strips one by one.
    The switchboard is not the height of professionalism ;)

    PS It probably came from the socket, where is that bad strip?
  • ADVERTISEMENT
  • #30 6585081
    130880
    Level 10  
    Posts: 22
    Rate: 11
    I didn`t do it separately and it`s much better now than it was when I first opened it. During the next renovation, I plan to replace it and then I will tidy it up. Either way, I have extra security. I will disconnect the strips and check without them (but only in the evening). In total, I have two strips connected in series on this socket, one of which also has a TV antenna connected.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around a user's electrical installation issues, specifically frequent breaker trips and fuse blowouts when using high-power devices like an iron. The user has a 25A 30mA differential switch and 5 circuit breakers, with a 16A socket fuse and a 20A meter fuse. Problems arise when testing the differential or using the iron, leading to simultaneous fuse blowouts. Various responses suggest checking the type of fuses (B vs. C), potential overload from inductive loads, and the need for proper surge protection. The user is advised to disconnect devices, test circuits individually, and consider the condition of the meter fuse. The conversation also touches on the installation of surge protectors and the importance of proper wiring and fuse selection to prevent electrical hazards.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: Up to 70 % of nuisance trips in small flats are caused by surge-bar or cord faults [Schneider, 2021]. “Selectivity fails when identical B-curve breakers sit in series” [Elektroda, Darrieus, post #6580584] Check strips first, then breaker curve mix.

Why it matters: Quick checks can stop double-fuse blowouts, protect appliances, and avoid paid call-outs.

Quick Facts

• B-curve MCBs trip at 3-5× In; C-curve at 5-10× In [IEC 60898]. • 2100 W iron ≈ 9.1 A at 230 V; within a 10 A fuse’s continuous rating. • Pre-meter reseal fee: PLN 30 ± 10 [Elektroda, Darrieus, post #6581086] • Recommended SPD cable size: ≥ link conductors, typically 4 mm² Cu [Moeller SPD Guide]. • Contracted power in thread: 4 kW, protected by C20 breaker [Elektroda, 6583880]

Why does my apartment blow both the room breaker and the pre-meter fuse when I press the RCD test?

All loads restart simultaneously after the RCD resets, creating an inrush that exceeds the identical B-curve trip levels of both breakers; without curve selectivity they open together [Elektroda, 130880, post #6580611][Elektroda, Darrieus, post #6580620]

Can a single 2100 W iron legitimately trip a 16 A socket breaker?

A hot iron draws about 9 A; that is only 56 % of a 16 A breaker’s rating. If it trips, the cause is usually cumulative inrush from other devices or a weak/faulty breaker [Elektroda, 130880, post #6580573]

Do I need type C breakers on socket circuits?

Use C-curve only when inductive or high-inrush loads (compressors, vacuum cleaners) share the line. For mixed electronics, B-curve remains standard; pre-meter protection should then be C for selectivity [IEC 60898][Elektroda, Darrieus, post #6580584]

What’s the fastest way to locate the real culprit?

  1. Unplug all surge strips and multi-plugs. 2. Re-energise circuit. 3. Add devices one by one until the breaker trips. In the thread, removing one power strip stopped all trips [Elektroda, 130880, post #6590995]

Could a buzzing breaker or fuse be the problem?

A mild ‘zzz’ often stems from the electromagnet vibrating inside low-quality MCBs; it’s annoying but not automatically faulty [Elektroda, Darrieus, post #6580692] Persistent buzz plus heat means replace the unit.

How do I wire a single-phase Moeller surge arrester correctly?

Connect phase to the L terminal (top), neutral to N (top or second slot), and PE to earth bar; keep leads as short as possible (<30 cm). The user’s final photo shows correct layout [Elektroda, 6581011]

What happens if the SPD fails short?

The SPD’s varistor turns into a near short; the closest upstream breaker—often the C-curve pre-meter device—opens within milliseconds, isolating the fault [Elektroda, michcio, post #6599082]

Is it safe to daisy-chain two surge strips?

No. Chain increases contact resistance and cumulative inrush. In the thread, two chained strips tripped breakers even under light load [Elektroda, Darrieus, post #6585125]

How much does it cost to legally replace a sealed pre-meter breaker in Poland?

Energy utility unsealing and resealing averages PLN 30; labour varies widely (PLN 50 – 150 typical) and no extra measurements are required for a straight swap [Elektroda, Darrieus, post #6581086]

Edge case: can a neutral-only fault trip the RCD without blowing fuses?

Yes. An N-PE fault induces 30 mA residual current needed for an RCD trip while line current stays below fuse limits. Always secure the N conductor when adding SPDs [Elektroda, michcio, post #6585859]
AI summary based on the discussion. May contain errors.