tomoman 47420 25
Best answers

Why is there voltage on the grounding pin of my extension cords, and is the fault in the house installation or the extension cords?

It is more likely an installation fault than the extension cords: the thread points to a missing or bad PE/N connection on those sockets, while the 9–10 V seen on a meter or neon screwdriver can be phantom voltage from very small leakage currents [#6661411][#6661532][#6662083][#6661208] Some extension cords can also be the culprit if they are grounded-looking but actually have only two wires inside, so it is worth checking the cord construction too [#6661379] Do not trust the neon tester for this kind of diagnosis; a lamp or other proper load is a better check than a neon screwdriver or simple multimeter reading [#6660880][#6662263] The forums advise checking continuity of the PE conductor and the neutral connections in the board/socket circuit, because a poor neutral or disconnected PE can create exactly these symptoms [#6661411][#6662083] Since you already felt tingling when unplugging, the safest advice was to stop using the affected sockets until an electrician checks the installation [#6661826][#6663198]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 6660787
    tomoman
    Level 10  
    Posts: 6
    Rate: 9
    Hello,

    At the beginning, I apologize for the lack of professional language, but I don't know much about electricity ...

    In short, it looks like that when you connect several electrical devices on the extension cords - voltage appears on the pin on the extension cord - the screwdriver for checking the voltage lights up. It does not matter what specific devices I connect - it does not matter how many extension cords I use - with two - three there is voltage, sometimes when connecting only one extension cord. I thought it was a problem with the installation, so I unscrewed the socket, replaced it with a new one and disconnected the ground wire for testing - still the same.

    Therefore, I have a question - is it the fault of the installation or extension cords in this situation? I prefer to make sure before throwing them all out and buying new ones - extension cords, mostly with filters, from the mid-range price range. Or another question asked - if after disconnecting the grounding socket, there is still this problem on the pin on the extension cord, it means that it has nothing to do with the installation?

    What else I noticed in the installation - it can be useful for problem analysis:

    - the installation is about 6 years old
    - copper wires
    - there is a differential that turns everything off
    - there is also voltage on the ground wire in 3 cans - but they are not related to these electrical sockets (I checked it by turning off the fuse responsible for these boxes - there was still electricity in the sockets)
    - nothing like that happened before, only about a month ago I felt an unpleasant tingling when removing the plug when I touched the pin
  • ADVERTISEMENT
  • #2 6660880
    mr.Sławek
    Level 32  
    Posts: 1290
    Help: 207
    Rate: 206
    These screwdrivers are not generally good for such measurements, so the measurement may be falsified. It would be best to check it with a voltage indicator that forces the flow of more current, which excludes various types of leakage, etc., false measurement.
  • #3 6661000
    Magister_123
    Level 36  
    Posts: 2888
    Help: 378
    Rate: 967
    If you have disconnected the pin from the socket and you have voltage on the `` pin '', it means damage to the extension cord, or an induction may occur.
    What difference? 30mA? The current on the "pin" may be so small that you can feel it, and for the differential it is too small to turn off the circuit.
    I understand that the voltage on the `` pin '' appears without any devices connected ?!
    Coiled or unwound extension cords when checking with neon lights !?
  • #4 6661013
    Pittt
    Level 32  
    Posts: 1550
    Help: 148
    Rate: 213
    Buddy tomoman, problem with the N cable. It's strange only that the differential does not crash you. Installation is control. Such symptoms should not be underestimated
  • #5 6661071
    Anonymous
    Anonymous  
  • #6 6661096
    unemake
    Level 16  
    Posts: 128
    Help: 12
    Rate: 33
    Quote:
    but I don't know much about electricity ...

    And someone advises you to rummage in cans ...
    Call an electrician because your experiments may end badly!
  • #7 6661099
    pawel380V
    Level 19  
    Posts: 303
    Help: 22
    Rate: 71
    Perhaps one of the devices in the installation is causing the problem. Disconnect all devices and check again, it is strange that the differential did not work (probably the operating current is too low), it is best to check the voltage and current with a meter on the pin, then you can look for a further cause.
  • ADVERTISEMENT
  • #8 6661200
    tomoman
    Level 10  
    Posts: 6
    Rate: 9
    Thank you all for the answers - I am completing the data:

    - I measured with a meter - voltage between 9 and 10 V
    - extension cords unfolded - the voltage on the pin appears regardless of whether the devices are connected or not
  • #9 6661208
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 287
    After tightening the wires on the strips in the switchgear.
    Connect a 15W or 40 bulb between the phase and the pin, whatever you have at hand, as the differential will turn it off, ok.

    Quote:
    measured with a meter - voltage between 9 and 10 volts


    These are stray currents with a value of microampere, so the neon lamp is lit, the meter shows 10V and there is really nothing there ;)
  • #10 6661242
    tomoman
    Level 10  
    Posts: 6
    Rate: 9
    As I understand PE - is it a grounding conductor? In one box there are two such wires that are not paired with each other as in other boxes. This could be it?
  • #11 6661277
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 287
    tomoman wrote:
    As I understand PE - is it a grounding conductor? In one box there are two such wires that are not paired with each other as in other boxes. This could be it?


    I do not know what you have in the installation, do this test with the bulb as above. All PE should be connected, maybe this one is not connected anywhere ...

    PE is ground, yellow green ....
  • #12 6661282
    tomoman
    Level 10  
    Posts: 6
    Rate: 9
    lubamet wrote:


    These are stray currents with a value of microampere, so the neon lamp is lit, the meter shows 10V and there is really nothing there ;)


    Do I know - touching the pin is not pleasant, the feeling of tingling in the finger and temporary "sticking" ...
  • ADVERTISEMENT
  • #13 6661309
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 287
    tomoman wrote:
    lubamet wrote:


    These are stray currents with a value of microampere, so the neon lamp is lit, the meter shows 10V and there is really nothing there ;)


    Do I know - touching the pin is not pleasant, the feeling of tingling in the finger and temporary "sticking" ...


    It can't be 10V then
    Something stinks about this installation or your measurements.

    Is it like this in every outlet or does one have such symptoms? Maybe this will clear things up.
  • #14 6661379
    ROBSON33
    Admin of household appliances group
    Posts: 9725
    Help: 465
    Rate: 1712
    tomoman wrote:
    It does not matter what specific devices I connect - it does not matter how many extension cords I use - with two - three there is voltage, sometimes when connecting only one extension cord.

    And here you have the answer.
    In owl practice, I have met an extension cord that had a pin and a suitable plug, and in the cable only 2 wires (extension cord from the supermarket)
    and I suspect that is where the problem is.
  • #15 6661411
    Pittt
    Level 32  
    Posts: 1550
    Help: 148
    Rate: 213
    tomoman: disconnect from the mains all devices with earthed plugs and check what is happening on the PE conductor - just like you did so far. If the symptom has resolved, search by connecting the receivers one after the other - I put on the stove - if the PE pin still has disturbing symptoms, the cause is in the fuse / connection board. Poor connection of N conductors between the apartment installation and the power supply system.
  • #16 6661515
    tomoman
    Level 10  
    Posts: 6
    Rate: 9
    With these devices and extension cords I give up - there is no rule in it - when it seems to me that I found a faulty device / extension cord, it is the same. Oh, the whole thing is only in 3 sockets in the house, but beware - if in the one where I have everything connected, I remove the plug, then the phenomenon does not occur in the other ones and it seems okay.

    I tweaked the cables on the strip, they were not loose anyway.
  • ADVERTISEMENT
  • #17 6661532
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 287
    tomoman wrote:
    With these devices and extension cords I give up - there is no rule in it - when it seems to me that I found a faulty device / extension cord, it is the same. Oh, the whole thing is only in 3 sockets in the house, but beware - if in the one where I have everything connected, I remove the plug, the phenomenon does not occur in the other ones and it seems okay.

    I tweaked the cables on the strip, they were not loose anyway.


    The PE conductor from these 3 sockets is connected together but not connected anywhere - this is indicated by the symptoms.
    Make a test with a light bulb!
  • #18 6661542
    ROBSON33
    Admin of household appliances group
    Posts: 9725
    Help: 465
    Rate: 1712
    tomoman wrote:
    With these devices and extension cords I give up - there is no rule in it - when it seems to me that I found a faulty device / extension cord, it is the same. Oh, the whole thing is only in 3 sockets in the house, but beware - if in the one where I have everything connected, I remove the plug, the phenomenon does not occur in the other ones and it seems okay.

    I tweaked the cables on the strip, they were not loose anyway.


    In my opinion, only a good electrician saves you.
    Regards. :D
  • #19 6661558
    tomoman
    Level 10  
    Posts: 6
    Rate: 9
    lubamet wrote:


    The PE conductor from these 3 sockets is connected together but not connected anywhere - this is indicated by the symptoms.
    Make a test with a light bulb!


    I'll do it tomorrow after work - I have to go for a light bulb and some wires :D

    Exactly, and in cans, all cables should be (of course with colors) fastened together? Because I have in one box, for example, that the PE conductors are fastened together by 2 - 6 wires in total, or 3 pairs - maybe I can fasten them all together?
  • #20 6661578
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 287
    tomoman wrote:
    lubamet wrote:


    The PE conductor from these 3 sockets is connected together but not connected anywhere - this is indicated by the symptoms.
    Make a test with a light bulb!


    I'll do it tomorrow after work - I have to go for a light bulb and some wires :D

    Exactly, and in cans, all cables should be (of course with colors) fastened together? Because I have in one box, for example, that the PE conductors are fastened together by 2 - 6 wires in total, or 3 pairs - maybe I can fasten them all together?


    They should, but you can only wonder what if ...
    Start with the bulb, if the differential doesn't work, connect them together.
    I am also for an electrician because these are not balls.
  • #21 6661745
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    tomoman wrote:


    Exactly, and in cans, all cables should be (of course with colors) fastened together? Because I have in one box, for example, that the PE conductors are fastened together by 2 - 6 wires in total, or 3 pairs - maybe I can fasten them all together?


    At the beginning you wrote that the cans have nothing to do with the sockets / separate circuit /. Leave those cans alone, it's probably the lighting. Unfortunately, in many installations this is the second phase to the chandelier with a switch. This is very confusing so don't interfere.
  • #22 6661826
    przemekjasiu
    Level 14  
    Posts: 112
    Help: 2
    Rate: 44
    My friend, I urge you to invite an electrician to your home, it is about your and your family's safety and there is no joke with electricity
  • #23 6662083
    GBW
    Level 31  
    Posts: 1419
    Help: 123
    Rate: 291
    Call an electrician and let him check the continuity of the PE wire, if it is not connected, he can light the neon lamp and if the insulation between L and the housing is damaged, the differential may not work.
  • #24 6662263
    Darrieus
    Level 38  
    Posts: 3684
    Help: 406
    Rate: 287
    Theoretically, continuity can be checked with a light bulb, it is a not very professional test, but 100 times better than checking with a neon lamp or a multimeter because it misses the point at all - it will almost always show strange things.
  • #25 6662577
    GBW
    Level 31  
    Posts: 1419
    Help: 123
    Rate: 291
    lubamet wrote:
    Theoretically, continuity can be checked with a light bulb, it is a not very professional test, but 100 times better than checking with a neon lamp or a multimeter because it misses the point at all - it will almost always show strange things.

    Of course, you can check with a powerful light bulb, but it requires intervention in the dashboard because the differential will turn off the voltage within hundredths of a second. The author wrote that he knows little about electricity, so it's better to look for a professional.
  • #26 6663198
    serwisant73
    VIP Meritorious for electroda.pl
    Posts: 3158
    Help: 188
    Rate: 1257
    From what you write, it appears that for your own health it would be better if you did not go into the installations yourself. You have received comprehensive answers from your colleagues, leave the rest to the electrician.

Topic summary

✨ The discussion revolves around a user experiencing unexpected voltage readings on the pin of extension cords when connecting various electrical devices. Despite replacing the socket and disconnecting the ground wire, the issue persists, with voltage readings between 9 and 10 volts observed even when no devices are connected. Responses suggest that the problem may stem from faulty extension cords, improper grounding, or issues within the electrical installation itself. Several users recommend using a light bulb to test for stray currents and checking the continuity of the grounding (PE) wire. The consensus emphasizes the importance of consulting a qualified electrician for safety and proper diagnosis.
Generated by the language model.

FAQ

TL;DR: 9–10 V stray voltage was measured on the ground pin [Elektroda, tomoman, post #6661200]; “use a load indicator” advises expert Darrieus [Elektroda, 6661208] The symptom points to a floating PE conductor or a fake-earth extension lead. Why it matters: A broken PE can leave appliance housings at full 230 V and create lethal touch voltage.

Quick Facts

• RCDs in Polish homes trip at 30 mA nominal leakage [Elektroda, Magister_123, post #6661000] • IEC 60364 calls for ≤ 0.5 Ω continuity of protective conductors (typical value, IEC 60364-6). • Electrician call-out in EU cities: approx. €40–€70, test & report included [Checkatrade, 2024]. • Neon screwdrivers draw < 0.5 mA; false indications are common [Fluke, 2022]. • Budget extensions sometimes ship with only 2 cores and a dummy earth pin [Elektroda, ROBSON33, post #6661379]

Why does my extension cord’s earth pin show voltage when nothing is plugged in?

The PE (earth) in the affected sockets is tied together but not bonded to the main earth bar. Capacitive coupling from the live core or a device filter charges the floating conductor, so your neon lights up [Elektroda, Darrieus, post #6661532]

Is 9–10 V on PE dangerous?

Nine volts itself is not hazardous, but the reading signals a broken safety path. Under a fault the same disconnected PE could rise to 230 V and deliver >30 mA, enough to stop the heart [IEC 60364-4-41].

Why do experts say my neon screwdriver is unreliable?

It senses microamp currents; induced or leakage charges light the neon without real fault current. “The meter shows 10 V and there is really nothing there” [Elektroda, Darrieus, post #6661208] Use a tester that draws ≥5 mA, like a two-pole indicator or a 40 W bulb load.

How do I check protective-earth continuity with a light bulb?

  1. Disconnect sensitive loads and RCD.
  2. Wire a 40 W incandescent lamp between phase (L) and PE at the outlet.
  3. Restore power briefly; if the lamp glows full brightness, PE is continuous. If dark, PE is open [Elektroda, Darrieus, post #6661208]

Could a single appliance be back-feeding voltage onto PE?

Yes. Filters inside PCs, TVs or stoves connect L and N to PE through capacitors. A leaking filter can lift PE to ~115 V AC, enough for tingling. Disconnect all earthed devices, then reconnect one at a time to locate the culprit [Elektroda, Pittt, post #6661411]

Why didn’t my 30 mA RCD trip?

Leakage current onto PE is below the 30 mA threshold—often microamps—so the device stays latched [Elektroda, Magister_123, post #6661000] Only a hard fault or your test button injects enough imbalance to open it.

Do coiled or long extension reels worsen the problem?

Long, parallel L and N conductors act as a capacitor to the free-floating PE. The larger the coil, the higher the induced phantom voltage though current stays low [Fluke, 2022].

What’s the worst-case failure if I ignore a floating earth?

A live-to-metal short could energise every exposed chassis at 230 V. Touch current could exceed 100 mA—fatal within seconds—and the RCD may not sense it if PE remains disconnected [Elektroda, GBW, post #6662083]

How much does professional testing cost and what does it include?

A domestic earth-loop and RCD test typically costs €40–€70 and covers continuity, fault-loop impedance and RCD timing using calibrated meters [Checkatrade, 2024].

Are there standards that define acceptable earth resistance?

IEC 60364-6 and Polish PN-HD 60364 require protective-earth continuity ≤0.5 Ω for socket circuits; higher values invalidate safety certificates [IEC 60364-6].

Can using a two-wire “fake-earth” strip be legal?

No. Selling strips with a dummy earth pin violates EU Low Voltage Directive; using them voids appliance warranties and insurance [EU LVD, 2014].

When should I call an electrician?

If PE continuity fails the bulb test, if tingling is felt on plugs, or if more than one socket shows phantom voltage, schedule a qualified electrician immediately for insulation, loop and RCD verification [Elektroda, serwisant73, post #6663198]
Generated by the language model.