How should I protect three single-phase circuits from a 3-phase distribution board: with one 3-phase RCD or with separate 1-phase RCDs for each circuit?
Use separate 1-phase RCDs or RCBOs for the three single-phase circuits; if you use one 3-phase RCD for all three, a fault on one circuit will trip it and disconnect the healthy circuits too [#6918903] If you have any true 3-phase loads, put those on a 3-phase RCD and keep the 1-phase circuits on their own 1-phase RCDs [#6971104] One reply also notes that the scheme is more redundant this way, because a leakage fault in one phase does not take down the whole house [#6971180] For selectivity, an upstream main RCD around 100 mA can be used before downstream 30 mA devices [#6971861] If there are no 3-phase receivers now or planned, the thread’s advice leans toward ignoring the 3-phase RCD and using 1-phase RCDs on the selected circuits [#6972013]
  • #1 6918769
    shein48
    I am reworking the installation in an old house and I am asking for advice from more experienced people. In the 3-phase distribution box, I pull 3 circuits, the expected load is approximately equal, and therefore the question is whether to use a differential 1 for 3 phases - or for each circuit separately 1 ph.?
  • #2 6918896
    kierbedz4
    Level 36  
    Help: 307
    Rate: 1008
    Install one 3-phase differential on the rail and right next to it, three single-phase differentials. Connect three phases to the three-phase differential and, at the same time, from the same terminals, connect one phase to the other three differentials. Connect all differentials to the bottom with S-type protections. three-phase security, send the cable to the basement and garage where you will power all receivers and even a three-phase water heater. From the other single-phase security devices you can power the receiving sockets from one of the other, lighting, etc.
  • #3 6918903
    warbipower
    Help: 20
    Rate: 58
    I would use three RCDs or RCBOs. If you use a 3f RCD to supply three 1-phase circuits, it will trip an RCD in the event of a fault (leakage current) in one of the circuits, which will also disconnect the non-faulted circuits.
  • #4 6918915
    kierbedz4
    Level 36  
    Help: 307
    Rate: 1008
    If you would install one differential for the whole house, darkness will envelop the whole house during its operation.
  • #5 6918959
    eventus
    >> Kierbedz4
    What is the function of a 3-f before 3 1-f? Unless the "main" device would have a different (larger) trip current, eg ?I = 500mA, as a fire protection. But you didn't explain that in your post. Regards :)
  • #6 6918994
    Akrzy74
    Rest in Peace
    Help: 363
    Rate: 1504
    The author wrote:
    In a 3-phase distribution box, I pull 3 circuits
    And:
    What is the conclusion of this? That colleague Kierbedz4 writes nonsense! He sped up like a locomotive down the hill ...
    Question to the author - what is the nature of the load (lighting, sockets, and maybe something else?)
  • #7 6919348
    kierbedz4
    Level 36  
    Help: 307
    Rate: 1008
    Read on. 3-phase differential + S type protection garage or instantaneous water heater, hydrophore, welding machine and other three-phase circuits in the garage. Other power supply protected by single-phase differentials not connected to the three-phase differential! with installed S-type protections to protect the remaining circuits.
  • #8 6919375
    wd40
    Help: 21
    Rate: 62
    If there are any other 3f devices at home, it is a 3f differential, if not it is cheaper 3f but better 3x1f.
  • #9 6971104
    jacek hola
    if there are receivers 3f, then and these circuits must be differentials3f on receivers 1f differential1f
  • #10 6971180
    ronwald
    Help: 85
    Rate: 68
    Kolego Akrzy74 take it easy, what is this nonsense written by my colleague Kierbedz4? Three-phase pick-ups require a three-phase differential, and the others one-phase. The installation designed in this way is redundant, the leakage in one phase does not completely deprive the house of AC power. The proposal of my colleague Kierbedz-a4 is correct!
  • #11 6971861
    januszbe
    Level 19  
    Help: 28
    Rate: 65
    Yeah, well described, but there is also something like selectivity. Nobody wrote about it. For the main first RCD - 100mA, then 30mA. If not, this 3-phase differential will be banging anyway
    Regards
  • #12 6972013
    Darrieus
    Help: 406
    Rate: 289
    If there are no power sockets in the house or such sockets, it is not expected in the future, you can ignore the 3-phase differential (the selectivity problem will be eliminated) and install 1-phase differentials on selected circuits.
  • #13 6972278
    retrofood
    Help: 1140
    Rate: 4798
    ronwald wrote:
    Kolego Akrzy74 take it easy, what is this nonsense written by my colleague Kierbedz4? Three-phase pick-ups require a three-phase differential and the others one-phase. The installation designed in this way is redundant, the leakage in one phase does not completely deprive the house of AC power. The proposal of my colleague Kierbedz-a4 is correct!
    I agree that it is correct, but forcibly adapted to the idiotic assumption of Kol. Shein48, which provided insufficient information to get a correct answer, but already has fifteen advisers.
    THIS IS NOT DONE COLLABORED !!!
    Do not provide information on general questions. It is as if someone stood at the crossroads of 10 roads and asked which way to go. You can answer freely, any direction will be correct. But is that the point? After all, man certainly does not know any of these answers.
  • #14 6972325
    Akrzy74
    Rest in Peace
    Help: 363
    Rate: 1504
    Col. Ronwald- I am calm :) I understand it like this:
    The author wrote-
    In a 3-phase-pull distribution box, 3 circuits are expected to load approximately equal
    So: 3-phase power supply, 3 single-phase circuits were made. Why 1-phase? Bo wrote that the three new circuits will have approximately the same load.
    Here the author asked a clear question: a 3-phase differential for these 3 new circuits, or maybe 3 independent 1-phase ...
    Kierbedz4 wrote in one of his posts:
    Install one 3-phase differential on the rail and right next to it, three single-phase differentials. Connect three phases to the three-phase differential and, at the same time, from the same terminals, connect one phase to the other three differentials. Connect all differentials to the bottom with S-type protections. of the three-phase protection, send the cable to the basement and garage where you will power all receivers and even a three-phase water heater. From the other single-phase protections, you can power the receiving sockets from one of the other, lighting, etc.
    -It is not known how much space there is in the switchboard
    -It is not known whether there is e.g. FR in the switchgear
    -It is not known whether the author has a basement and garage and whether he intends to modernize something there, and if he has, if he has an installation prepared for rcd ... (in this basement and garage, which the author did not mention)
    -Since there is speech just about three 1-phase circuits, why "czorta" write about additional rcd, other circuits - which may not exist at all
    -If you think this way- (i.e. from momentum), it might have been necessary to recommend grounding, equipotential bonding Main and local, installation of the limiter. overvoltages, LS, etc ...
    Where did the author (in his first post) mention a garage, hydrophore, welding machine, or other circuits?
    Anyway, even here, one should consider the advisability of using one residual current device (not mentioned the rated current - which is important) for a water heater, hydrophore, welding machine, and other circuits (?)
    The answer should be short and rather unambiguous,and a little more, it will be a paper "Which side is the phase in the hole", or another - with a similar degree of difficulty ...
    I am only asking for one thing - do not write down unnecessarily . Kierbedz4 mentioned a 3-phase and 1-phase rcd (connected in parallel), and here it is already about selectivity, about a 100mA rcd and that something will "bang" - I wonder what can be banging in the switchgear? (Maybe Mrs. Shein48 of Mr. Shein48 on the head, as the 3-phase RCD will turn off the 1-phase circuits and the cake will not bake). It is enough for the topic to refresh, and there will always be someone who does not read and write thoroughly. There are really many topics where the answer can be given in several posts, and ends with a several-page paper - because the topic becomes multi-topic.
    Ps. I don't expect an answer.
  • #15 6972351
    retrofood
    Help: 1140
    Rate: 4798
    Col. Akrzy74!
    It was still necessary to summarize: there is no technically good answer to such an undefined question, because there are so many conditions that every hint may be wrong.
  • #16 6972876
    harlejowiec
    Help: 53
    Rate: 105
    As colleagues wrote, the use of three RCDs has the advantage that triggering one will not cut the voltage on the other phases. But on the other hand, it is important to answer the question of how often this circuit breaker may trip. Hence, one 3-ph can be used and in the case of 3-ph loads (motors) there must also be a 3-ph switch. How big is the apartment the author of the subject has, because if small, only 3-f would be enough.
  • #17 6973162
    ronwald
    Help: 85
    Rate: 68
    I agree with the statement that the topic is not properly described by my colleague Shein48, the technical drawing (installation diagram) is missing from the question posed.
  • #18 6973534
    Akrzy74
    Rest in Peace
    Help: 363
    Rate: 1504
    However, no one (almost) "thought" to even ask the "silent author":
    Akrzy74 wrote:
    A question for the author - what is the nature of the recipient (lighting, sockets, and maybe something else?)
    Everyone wrote as if it was a topic: "Help! Which way to screw the light bulb".
  • #19 6974968
    ronwald
    Help: 85
    Rate: 68
    What loads may be in a typical home; single-phase and three-phase :) )! Let's not ask questions like whether the water is wet? In my opinion, the energy balance and the diagram of the installation that the author intends to perform (modernize) are more interesting.
    Due to the lack of interest of the author - I close the topic. If there are new facts, I am waiting for PW from the author.
    [Akrzy]
The discussion revolves around the choice of differential protection for a 3-phase distribution system in a residential installation. Participants debate whether to use a single 3-phase differential circuit breaker (RCD) for three circuits or individual single-phase RCDs for each circuit. Key points include the risk of a single 3-phase RCD tripping and cutting power to all circuits during a fault, while individual RCDs would allow for continued operation of non-faulted circuits. The importance of load characteristics, selectivity, and the potential for future circuit expansions are also highlighted. Recommendations lean towards using three single-phase RCDs or RCBOs for better reliability and safety.