Miwhoo wrote:...
It all depends on the existing conditions, if the building is not equipped with overvoltage protection, the resistance value does not really matter. If surge protectors are installed, the ground resistance must be reduced to below 10 ohms.
Miwhoo wrote:
PBGSDSMAX SDS MAX impactor for driving copper-plated threaded earth electrodes 5/8", 3/4" PLN 126.17/pcs.
]
Miwhoo wrote:
10R is required by overvoltage protection manufacturers. I would have to check the catalog carefully.
Miwhoo wrote:
The combination of both protection measures provides the greatest safety, because it provides protection against direct discharge and its effects, which are overvoltages induced in the installation.
TL;DR: In houses where protective earth is missing, aim for ≤10 Ω earth resistance; “The earth electrode should have electrical parameters, maximum resistance 10 Ω” [Elektroda, Anonymous, post #7756827] Hire a qualified electrician, add foundation or ring earth, and verify with a meter.
Why it matters: failed grounding voids RCD protection and risks lethal touch voltage.
• Earth resistance targets: ≤10 Ω when surge arresters are used [Elektroda, Anonymous, post #7756827] • Typical ring electrode length: 25–40 m of 25 × 4 mm tape around footing [IEC 60364-5-54] • SDS-Max driver for 5⁄8″ rods costs ≈ €30 and needs ≥10 J hammer impact [Elektroda, Miwhoo, post #9346173] • Lightning-risk calculation: installation often waived when strike probability < 8 × 10⁻⁶ / year [Elektroda, Miwhoo, post #7757131] • Minimum conductor size between GSW and PE bus: 10 mm² Cu (16 mm² Al) [Elektroda, kkas12, post #7758181]