Nie, dziękuję Przekieruj mnie tamtomhorn1 wrote:Why does my colleague need an earth electrode with a value of 59-50 = 9?On the first spike I had a result of 59 ohms, which is 50 too much.
arcyimperator wrote:There was such a topic somewhere, the explanation was that the pin bends to the sides when pushed hard and does not stick to the surrounding ground very well (there is air between the pin and the ground). Apparently, over time, the ground begins to stick and the resistance value decreases.
kozi966 wrote:arcyimperator wrote:There was such a topic somewhere, the explanation was that the pin bends to the sides when pushed hard and does not stick to the surrounding ground very well (there is air between the pin and the ground). Apparently, over time, the ground begins to stick and the resistance value decreases.
This subject:
https://www.elektroda.pl/rtvforum/topic3508820.html#17497437
My colleague Zbich70 explained it.
emigrant wrote:You can reduce the soil resistivity with such a thing - http://www.budniok.pl/oferta-wg-produktow/sys...em-material-poprawiajacy-rezystywnosc-gruntu/ Does it work? I do not know. Read on, maybe you will find some opinions of people who used it. As if you were not able to connect the vertical earth electrode elsewhere.
emigrant wrote:I think so, you need to make such a cylinder around the pin to some depth and pour it. If you decide on this drug, let me know if it did anything.
tomhorn1 wrote:My friend Cyrus2, maybe I didn't really express myself very precisely .. I mean comparing your experiences in the results at heels, and exactly about such a drastic increase in the result when you get lower. It is known that ultimately I will have nothing else to do but drive another one until the result of 1.28?![]()
kozi966 wrote:My colleague Zbich70 explained it.
zbich70 wrote:This is because the dry clay looks more like rubble than earth when the groove is dug. During backfilling, it needs to be compacted well so that the lumps break down and cover the hoop well, preferably thicken with layers, the first layer as much as possible so that air spaces near the hoop will disappear.
The same vertical earth electrode - when driving, the rod breaks to the sides, the clay compacts and, as a result, the rod only has a point contact, because it is in an earthen "pipe". Pouring water into the hole around the rod gives a good effect. Only slowly, it is best to put the hose on the rod and unscrew the tap for minimal seepage, then the water will silt up from the bottom. If it is too fast, it will only become silted from the top and there will be an airbag at the bottom.
In the same way, the layer above the hoop (about 10-15 cm) can be moistened with water and then run over with a "jumper".
zbich70 wrote:For how long will both be enough.Pouring water into the hole around the rod gives a good effect.
I have no opinion about the so-called linked chemical "soil improvers" - because I have never used them.
tomhorn1 wrote:It is the power line that will not suppress the power surges.ZK on the border of the property is supplied from the overhead line. There is a YKY 5x10 cable from ZK to the building (one core is not used).
gilus1 wrote:There is a good chance that the earth resistance will decrease for some time with each passing day.
tomhorn1 wrote:for an hour I poured a solution of water with a large amount of salt into the gap.
tomhorn1 wrote:Yesterday I checked again. It dropped from 257 to around 200 ? for two days. In the evening, for an hour, I poured a solution of water with a large amount of salt into the crack. This morning I measured and ..... it dropped to 33? (!) Far from ideal, but there was hope. On Monday I will measure again. Possibly, he will strike one more pin and repeat the action with 20 liters of salt water .. I will inform you about the effects
![]()
tomhorn1 wrote:Yes, I would like to prophylactically "pour" a special agent slowly. So far, I have knocked out one more pin, and while driving, I tried hard to move the ground around her. Without adding salt water again, I got 11?. It is a success in this whole situation. After the new year, I will approach it with a special liquid and, if necessary, another pin. At the moment, I can only confirm that during driving, the ground ceases to perfectly "wrap" the pin, hence the result increases. At least it was like that in my case. I will not leave any more ground measurements for dessert .. This is where I will always start.
tomhorn1 wrote:I know what an earth electrode is. I mean, as always, a value below 10, usually there is no problem with a value below 5. My question concerns the sense of hammering more, since the value of the second spike jumped so drastically (from 60 to 260). And ultimately, I will emphasize again, I care about the result in the vicinity of 5 ...
TL;DR: Driving a second rod without soil contact raised resistance from 59 Ω to 259 Ω (↑339 %). “The rod only has point contact” [Elektroda, zbich70, post #17625096] Compact soil or add parallel rods before chemicals.
Why it matters: High earth resistance weakens surge protection and can violate IEC 62305 limits.
• Target earth resistance for Type 1 SPD: ≤10 Ω [PN-EN 62305-3]. • Typical 2.4 m copper-bonded rod costs €15–25 [ERICO, 2023]. • GEM backfill lowers resistivity up to 50 % and lasts ≈25 years [nVent, 2022]. • Clay soil resistivity: 30–150 Ω·m when moist; >1000 Ω·m when dry [IEEE Std 80, 2013]. • Saltwater treatment may cut resistance 80 % for days but triples corrosion rate [Elektroda, Darom, post #17630987]