Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes

artudud 88895 26
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 7871019
    artudud
    Level 13  
    Hello, and I have a question for more experienced professionals. The problem is whether the connections inside the switchgear are made with the DY (wire) or LY (cord) cable, the question is whether there are specific regulations when and what kind of cable we use. It is known that the rope is easier and more aesthetic, but recently I heard the opinion of an experienced fitter that it does not comply with the regulations, but he was not able to specify exactly which ones. I would like to mention that these are typical switchgears in single-family houses, etc. installations.
  • ADVERTISEMENT
  • #2 7871061
    czesiu
    Level 37  
    I think that the wire is more aesthetic and faster. There are no rules that distinguish this. It is known that when the cable is exposed to movement (door), we give a rope.
  • #3 7871348
    ElektoMex
    Level 15  
    I don't know anything about the regulation governing a wire or a string. The cable is easier to install in the switchgear (it does not resist unfolding), it can be bent many times as mentioned by a colleague above. The wire is cheaper :) well conducted it can look nice in a switchboard. Only wire for installation in buildings, as few cords as possible. The line works better at higher frequencies (I've read something somewhere else). In our case (50 Hz) it made no difference. Control cabinets again only in ropes, but there is also no recipe for it (I think) that is easier :) )
  • #4 7872282
    tragi
    Level 22  
    As long as I live, I have not yet seen a switchgear connected by a cord. After all, such a switchgear would be a big chaos. The front of the DY is aesthetically and clearly legible, if the wires are routed evenly, the angles of the wire bends will be preserved.
  • ADVERTISEMENT
  • #5 7872372
    Łukasz-O
    Admin of electroenergetics
    tragi wrote:
    As long as I live, I have not yet seen a switchgear connected by a cord. After all, such a switchgear would be a big chaos. The front of the DY is aesthetically and clearly legible, if the wires are routed evenly, the angles of the wire bends will be preserved.


    You probably live for a very short time, or you are just starting your adventure with "electrics"
    Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes
    Photo from the first page found on Google: Link
  • #6 7872380
    retrofood
    VIP Meritorious for electroda.pl
    tragi wrote:
    As long as I live, I have not yet seen a switchgear connected by a cord. After all, such a switchgear would be a big chaos.


    Buddy, have you seen the control cabinets of industrial devices? These are such switchgears, only sometimes and 500 times larger. And there are links everywhere ... And there is no mess, and it can't even be ...
    I am giving this as a curiosity.

    PS. Oh crap, we wrote together :D
  • #7 7872424
    czesiu
    Level 37  
    The switchgear in the picture is quite nice, but I think it would look even better if made of wire. The wire is used to make elegant bends and there is no need for bushings. It is definitely faster.
    As for the control cabinets, the cables in the comb troughs reign supreme - a convenient way to modify / expand.
  • #8 7872484
    tragi
    Level 22  
    The control cabinets are connected by a rope, but I meant home switchgears that are packed into small boxes and they are usually tight there. And the example from the photo of a colleague Łukasz-O is very transparent and everything is well connected, but has a colleague seen such a super switchgear in practice many times? Maybe my adventure with "electrics" does not last too long, but almost 20 years and I have seen a lot during that time. Anyway, I have never connected any switchgear in a home installation with a cable.
  • #9 7872617
    Miwhoo
    Electric installations specialist
    Only in the automation cabinets there are Smile perforated trays everywhere and cables stick out from them. The version for the brave is as my colleague Łukasz wrote, but it is impossible to do without titles.

    Due to its flexibility, the line is easier to guide, you need to be able to handle the wire, bend it well, etc. It's all a matter of practice.

    I make separate wires in my homes, I put all power on rails so that the garlands do not hang under the fuses.

    It is worth remembering not to cross the phase conductors with N and PE, so that they do not touch each other. In the event of any failure, the cables can get burnt and a mess will be created. One side of L, the other side of N and PE. I am starting another construction project in 2 weeks. After assembling the switchboard, I will allow myself to post Smile's photos


    I merged the posts. [Luke]


    Welcome back.

    I found something like that :) in my X archive
    I was commissioned to expand by 1 circuit :) Due to financial reasons, the client did not agree to the tidying up. His answer was:
    "Dear dear, nobody sees it anyway, because it is under that white cover, and besides it looks what it looks like, the most important thing is that it works ..."

    Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes
  • ADVERTISEMENT
  • #10 7872656
    Krzyś33
    Level 25  
    Hello . If it is done correctly, it does not matter whether we do it with a rope or a wire. The rope is more convenient to attach with large cross-sections, and you can organize it very nicely with the help of fastening bands. And for ElektroMax - do not write about what you have no idea, because the lines are used at high frequencies, but they are not ordinary installation lines, but with INSULATED ones! individual strands in the bundle. Greetings.
  • ADVERTISEMENT
  • #11 7872682
    tragi
    Level 22  
    I saw enough switchgears and connected enough switchboards with my own hands, at a time when the DY cables were so hard and clumsy that when one switchboard was connected, bubbles appeared on my fingers, and buying an insulation stripper in the country was only a dream. And they all work so far, so don't worry, buddy, about my competences.

    And such examples as in the photo above are very common.
  • #12 7872806
    elpapiotr
    Electrician specialist
    Hello.

    Well, show your switchboards, buddy hand barrow
  • #13 7872826
    Łukasz-O
    Admin of electroenergetics
    Gentlemen, this discussion was basically nonsense. It is reminiscent of the superiority of Christmas over Easter. It all depends on the switchgear and application. In addition, if someone is experienced, he will do a masterpiece, and if not - see the photo in a friend's post Miwhoo . Here it does not matter whether he does it with a rope or a wire ;)

    PS I always "make" large switchgears with a rope.
  • #14 7873842
    greg16
    Level 15  
    Hello . In my opinion, it does not matter whether we lay a line or a wire. Everyone arranges them as conveniently as possible, as long as they have the right sections. I use both methods.
  • #15 7874940
    zdzisiek1979
    Level 39  
    1 and 3-phase rails, possibly a cable.
  • #16 7875263
    remik_l
    Level 29  
    For larger cross-sections, I definitely recommend the line - you will sweat less.
    Bending the 120mm? cable in a short distance in several places becomes practically impossible and you can lay the line much easier.
    Another disadvantage of wire connections is connecting several with different cross-sections to the same terminal in the apparatus. The effect is that the one with the smallest cross-section is usually loose and with the lines we pack everything into one sleeve and that's it. Of course, this can be prevented by bending it in half, but sometimes it is not possible because all of them will not fit.
    In addition, attention should be paid to the more frequent fact of tearing devices, and in particular ZUGs from rails by wire, if we bend them incorrectly.
  • #17 7876519
    artudud
    Level 13  
    I did not think that this topic would cause such a stir, but thank you very much for the information. The reason why I mentioned this topic is that currently I got an order for a correction after an "electrician with permissions". I do not like to judge someone's work, but what I saw on the spot called for vengeance to heaven. The job was fucked from A to Z. below I add a photo showing the switchgear made by him I replaced the entire switchgear with a larger one, but unfortunately the wires were cut too short so I would have to cut them off, I came up with the idea to make a kind of crossbar on one rail using ZUGÓW, there I will bring all the receiving circuits made with YDYp cables and from I will make connections to cameras with cables from the cable. (I hope that my reasoning is in line with good electro-fitting practice) I will post a photo when I'm finished. Sorry for the quality of the photo but I took it with a bad phone, if someone has another way to solve this knot, I will be grateful for hints and suggestions. Regards
    Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes
  • #18 7877227
    piotr_krak
    Level 25  
    They do both

    When it comes to housing construction, I mostly see DY and when it comes to control cabinets it is LY (regardless of whether it is DC or AC). Anyway, for LY I would use ferrules crimped with a crimper, then it looks more aesthetic.
  • #19 7877338
    retrofood
    VIP Meritorious for electroda.pl
    piotr_krak wrote:
    Anyway, for LY I would use ferrules crimped with a crimper, then it looks more aesthetic.


    This is perhaps an understatement. I consider simply connecting the bare line to be highly unreliable and unacceptable.
  • #20 7877582
    elpapiotr
    Electrician specialist
    Hello.

    Example - a switchgear in a garage:


    Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes
  • #21 7880106
    artudud
    Level 13  
    el_pp a work worthy of a master but an investor you probably let go with the bags :D But seriously, this is what I'm going to try to put together. Installation is a bit less complicated, but it is also a challenge for a beginner. The topic could be closed, but as we are talking (writing) about aesthetics and performance, I have another question from the pool of good practice, namely the approach to flush-mounted cables and not only to the switchgear, I met with three schools:
    1 light wires come in from above and sockets and other receivers. from down,
    2 all wires on one side
    3 neutral conductor approach.
    I know that the type of selected switchgear may also decide about it, I personally prefer switchgears in which I can adjust the position of the mounting rails (SCHNEIDER, Moeller, etc.) are much more expensive, but if the investor gives me a free hand, I definitely choose them, it is easier to keep them in order.
  • #22 7880192
    elpapiotr
    Electrician specialist
    Hello.

    We have an issue - "connections inside the switchgear", so I am giving examples.

    Different garage, different switchgear / fragment

    Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes

    I have a lot of it - different types of switchboards.
    The layout is so convenient that connections can be configured in various ways, without disturbing the drainage pipes.

    PS. I can also post a buble :D
  • #23 7889566
    artudud
    Level 13  
    Ele-pp, do not think that I am picking on the details, but I am interested in the issue of the numbering of individual wires and circuits, I can not figure out how you do it, it is your invention or it results from the switchgear design, I personally did not meet with the electrical installation project. a single-family house where the switchgear would be so precisely drawn (maybe I haven't seen a good project yet) and in fact, the projects only show the symbol of this installation element schematically. On the one hand, it is good because it gives the installer a free hand, but on the other hand, it requires the implementation of post-execution documentation.
  • Helpful post
    #24 7889691
    remik_l
    Level 29  
    In good switchgear schemes, everything is numbered and marked.

    Strips with ZUGs are marked with consecutive numbers X1, X2, X3 etc. each ZUG in a given strip has its own number. 1, 2, 3 etc. The devices in the switchboard also have their numbering: F1, F2, F3 ... Q1, Q2, Q3 ... etc.

    By placing the cable from F1 to ZUG 3 in the X2 strip at the ends, you describe:
    - at ZUG - F1
    - with the X2.3 camera

    Of course, this is only an example because there are certainly many ways of numbering wires.
  • #25 7889718
    elpapiotr
    Electrician specialist
    Hello.
    artudud wrote:
    On the one hand, it is good because it gives the installer a free hand, but on the other hand, it requires the implementation of post-execution documentation.

    As-built documentation is always done by me.
  • #26 7905333
    przemek8626
    Level 11  
    I will add a photo of an ordinary RB for construction :) As I once heard, an electrician, not a baker ...
    Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes

    Added after 9 [minutes]:

    Still something for the collection :)
    Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes Switchgear Connection Types: DY (Wire) vs LY (Cord) Cables & Compliance for Single-Family Homes
  • #27 8244989
    artudud
    Level 13  
    As I wrote, so I did. The investor is happy, that too, the installation works without reservations, it's a pity that I did not have time to take a photo, and now I somehow feel stupid to load someone onto the property just to take a photo. Anyway, thank you to everyone for contributing to the topic. As it turns out, the electrician is not such a strict science. I close the topic

Topic summary

The discussion revolves around the use of DY (wire) and LY (cord) cables in switchgear connections for single-family homes. Participants debate the aesthetic and practical advantages of each type, with DY cables being noted for their rigidity and ease of installation, while LY cables are appreciated for their flexibility and neatness. There is no consensus on specific regulations governing the use of either cable type, although some participants suggest that proper installation practices are more critical than the type of cable used. The conversation also touches on the importance of maintaining clear and organized wiring within switchgear, with recommendations for using ferrules and ensuring proper conductor separation to prevent electrical failures. Various experiences and preferences are shared, highlighting that both cable types can be effectively used depending on the application and installer expertise.
Summary generated by the language model.